Where do I input the thermostat setpoint temperature?

Where do I input the thermostat setpoint temperature?

VictoriaEagen's avatar
556
VictoriaEagen
asked 2016-02-03 16:17:14 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-04 09:11:58 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

5

You should create a schedule of temperature, maybe be best or use one available in the library (eg Large Office and Large Office HtgSetup ClgSetup) and associate the schedule to the appropriate thermal zones.

image description

image description

Geraldo Pithon's avatar
1.3k
Geraldo Pithon
answered 2016-02-03 16:38:56 -0500, updated 2016-02-03 16:39:12 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you, that was helpful, I downloaded a HVAC system and I was getting a lot of errors/warning, one being the thermostat setpoint temperature was 0C . Do you know of any example buildings I can download to see how they input everything in. Specifically I am doing a dorm, and example apartment complex or something would be ideal. Thanks again

VictoriaEagen's avatar VictoriaEagen (2016-02-03 16:51:42 -0500) edit

Just be aware that each time you drag an object in from the Library it will create a new instance of it and you will end up with several copies of the same schedule in the Schedules tab.

An object only needs to be dragged in to the model once to make it available in the My Model library, which will avoid copies.

MatthewSteen's avatar MatthewSteen (2016-02-03 17:57:50 -0500) edit
add a comment see more comments
4

Here's what I would do:

  1. File > Load Library > MidriseApartment.osm

  2. Schedules tab > Schedules subtab

    • Drag MidriseApartment Apartment ClgSetp and HtgSetp from the Library (right) into the Drag From Library drop zone (left) to add to model (but not assign).
  3. Measures > Find Measures on BCL > HVAC > HVAC Controls > Replace Thermostat Schedules (download)

  4. Components & Measures > Apply Measure Now > Set Thermostat Schedules

    • Assign the MidriseApartment Apartment Clg and Htg Setpoints to all thermal zones

If you want to change the setpoint schedules for specific zones you can drag/drop from the My Model library into the specific thermal zone drop zone.

MatthewSteen's avatar
10.1k
MatthewSteen
answered 2016-02-03 17:23:42 -0500, updated 2016-02-03 17:25:39 -0500
edit flag offensive 0 remove flag delete link

Comments

Okay, I did this. I am confused still, what the numbers for Zone Cooling Design Supply Air Temperature and for heating also. In Thermal Zone tab, Cool Sizing Parameters (Heating Sizing Parameters). They are currently 14 deg C in cooling and 30 deg C in heating. What are these? Could this be why my baseline model is seeing nearly 3 times its actual energy use? With 500 unmet hours? Someone told me to get a whole hvac system in my building I should apply the Four Pipe Fan Coil More Parameters measure. I feel like it really messed up my model, there was so many default inputs I feel so confused.

VictoriaEagen's avatar VictoriaEagen (2016-02-03 18:25:36 -0500) edit

Sorry it was me who told you to apply the FCU measure. Did you apply it to the baseline? FCUs should not be in a 90.1 Performance Rating Method baseline model. See this unmet hours question for troubleshooting.

MatthewSteen's avatar MatthewSteen (2016-02-03 18:39:36 -0500) edit

Don't be sorry, I just don't really understand why my energy consumption is so high, and there are so many inputs I just have no idea. Did you read my question on the Heating/Cooling Sizing Parameters? Can you explain this, I noticed changing these changes my energy consumption. Any way you could explain this to me? Thank you for your time, I really appreciate it.

VictoriaEagen's avatar VictoriaEagen (2016-02-03 19:03:29 -0500) edit

Or is there a different HVAC whole system I can apply to model a FCU in every room for heating/cooling an 2 rooftop AHU's bringing in fresh water?

VictoriaEagen's avatar VictoriaEagen (2016-02-03 19:33:28 -0500) edit

A full explanation of the heating and cooling sizing parameters is best left for separate question, but here's the documentation for these inputs which are part of the Sizing:Zone object. In general, I set these equal to 20F delta between zone air and supply air for 90.1 modeling. Also, additional information about your model(s) and purpose is always helpful for others to troubleshoot.