Fan Motor Efficiency
I'm trying to make base and change cases for energy efficiency comparisons for HVAC optimization. One measure I plan to implement is premium efficiency motors on HVAC fans. The only thing I see that ties into this would come from the fan efficiency field. Can anyone explain what goes into the fan efficiency, and how I would be able to directly change the motor efficiency of the fan in Open Studio or energy plus?
Comments
Okay, this gives me a few follow up questions. First, I'm assuming changing to a VFD controlled fan would change the fan efficiency component of the total fan efficiency (not the motor efficiency since this is a nameplate value?). Secondly, the pressure rise would also potentially change, in a manner that is not immediately obvious to me. Additionally, the fan power curve coefficients that are in the variable volume fan class that are not in the constant volume fan class could be set at default values, or would they need to be modified? If the coefficients would need to be modified, how and wh
Check out the Fan Part-Flow Power Curve table in the COMNET MGP. It's on page 104 of the PDF I have. This lists typical part-load curves for different types of fans.