Four pipe induction fan coil units issues

Hi all, I am having two problems with four pipe induction FCUs. The first one is with dangling exhaust nodes, it doesn't seem I can get rid of it. I used a script to apply induction FCUs to the select zones with minimal tweaking in the model afterwards. There was a posting on this June with OS version 1.7, but doesn't look like it's solved. I can export the E+ idf file out and fix it in idf, but I won't be able to import this back to openstudio to meet the reporting requirements.

Second, these four pipe FCUs (>40 of them in the model), when one fails to have design capacity meets load, EnergyPlus stops and produces error for this particular FCU. In my case, I have 10 FCUs that were having troubles, I had to run E+ 10 times to go thru all the FCUs. Is there a fast way to fix it?

Thanks!

xfang's avatar
163
xfang
asked 2015-12-07 10:04:40 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-05-19 12:41:30 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Can you share your model? I'll take a look. This seems to be a stubborn problem, but until know I thought we had put it to rest.

Kyle Benne's avatar Kyle Benne (2015-12-07 13:41:59 -0500) edit
add a comment see more comments

1 Answer

2

I fixed a problem in OpenStudio uncovered by @xfang's model.

https://github.com/NREL/OpenStudio/pu...

I expect we will roll this into the 1.10.0 release.