Component Sizing Summary report

Hello, I would like to know which condition of capacity for equipment shown in Component Sizing Summary Report in Energyplus: It's the gross rated capacity at standard condition (26.7 DB, 19.4 WB, 35oC outdoor DB) and specified cooling air temp/humidity ratio in sizing:zone and sizing:sytem ) or at max ambient condition of design period and sizing:system/zone data ? Thanks

ngkhanh's avatar
2.2k
ngkhanh
asked 2015-11-09 03:40:19 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-11-09 07:02:39 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The sizing simulation run the simulation of the design periods and provide the Component Sizing Summary Report based on the calculated maximum capacity of the design periods. The results depend on DB temperature, wind speed, solar condition, and etc. You can't determine the "max ambient condition" before you run the sizing simulation.