Outside Convection coefficient in EnergyPlus

Hi

I defined the outside face convection coefficient as an output. I see in some hours during the simulation, this coefficient is 1000 !!! How is that possible? And also in general , which method is more accurate? Because I changed the SurfaceConvectionAlgorithm:Outside from DOE-2 to AdaptiveConvectionAlgorithm and saw a significant difference in one of my outputs.

s_pourm's avatar
775
s_pourm
asked 2015-11-01 11:41:12 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-11-01 15:10:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

According to Energyplus Engineering Reference (http://bigladdersoftware.com/epx/docs...):

Note that when the outside environment indicates that it is raining, the exterior surfaces (exposed to wind) are assumed to be wet. The convection coefficient is set to a very high number (1000) and the outside temperature used for the surface will be the wet-bulb temperature. (If you choose to report this variable, you will see 1000 as its value.)

It seems that you have rain data included in your weather file.

ecoeficiente's avatar
638
ecoeficiente
answered 2015-11-01 14:14:21 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you. Thats right.