5

Use measured airflow rate in DOAS?

I have the measured airflow rate with 1-minute interval (variable speed fan) for the DOAS system. Can EnergyPlus specify the airflow of the airloop or fan to match the measured airflow rate?

Yixing Chen's avatar
921
Yixing Chen
asked 2015-10-06 09:03:33 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-10-06 09:26:48 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

EnergyPlus will typically operate the fan to meet the load the system sees (either ventilation, heating, or cooling).

Since your DOAS operates only to meet the ventilation requirement, you can set the ventilation requirements using the DesignSpecification:OutdoorAir object's Outdoor Air Flow Rate Fraction Schedule Name field.

You can also set the flow rate of the fan directly using an EMS Actuator on the "Fan Air Mass Flow Rate".

Neal Kruis's avatar
4.7k
Neal Kruis
answered 2015-10-06 10:10:34 -0500, updated 2015-10-06 10:19:40 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks Neal, I was having problems with OA.

IgnacioFurnies's avatar IgnacioFurnies (2015-10-26 10:38:46 -0500) edit