Unbalanced ventilation systems in energy plus (design builder) [closed]

Hi everyone, I am working with an energy model for LEED certification and since I am new to energy plus (I am using Design Builder), I was wondering what the best way to model unbalanced ventilation systems is. I have DOAS, which supplies more air than it exhausts; and exhaust only systems, some of which serve multiple zones. Overall, building's ventilation systems are balanced, so excessive supply air from some zones is to be extracted by exhaust only systems.

I have a doubt whether I should use airflow network model or I can try to indicate, that exhaust air in rooms with negative pressure is compensated with air with thermally neutral temperature. If the later approach is possible, how should I proceed with it?

Thank you, Dmitry

Dmitry's avatar
51
Dmitry
asked 2015-10-03 06:09:20 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-10-04 08:41:44 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by Dmitry 2015-10-11 09:14:53 -0500

Comments

add a comment see more comments

1 Answer

3

Hi Dmitry,

You can use ZoneMixing (one-way flow) or ZoneCrossMixing (two-way flow) to move air between the zones, but you must specify airflow rates and schedules for this flow, and it cannot be automatically linked to HVAC system operation.

EnergyPlus airflow network model can be connected with the HVAC system, but for limited system types only (such as CAV).

Yixing Chen

Yixing Chen's avatar
921
Yixing Chen
answered 2015-10-08 02:06:02 -0500
edit flag offensive 0 remove flag delete link

Comments

Hi Yixing, thank you for an answer and referring to ZoneMixing object.

Dmitry's avatar Dmitry (2015-10-11 09:14:45 -0500) edit