Water-side Economizer - ECWT

I'am using waterside-economizer with a electric chiller (Chiller:Electric:EIR), fluid cooler (FluidCooler:TwoSpeed) and build up the application based on example file "WaterSideEconomizer_Integrated.idf". But water-cooled chillers have a minimum ECWT for operating. How is it possible to take into consideration this fact?

nielex's avatar
139
nielex
asked 2015-09-18 09:53:57 -0500, updated 2015-09-18 09:55:08 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

The economizer loop should shut off at high outdoor temps. the fluid cooler must be sized to be able to deliver the minimum at design conditions.

Jean Marais's avatar
101
Jean Marais
answered 2015-10-02 04:35:01 -0500