Hey,

how is a proper way to model the ground(temperature) in E+(i use Version 8.1)? Is there maybe a easy way (where the ground temperature depends just on the outside temperature)?

Thank you very much!

antifx's avatar
495
antifx
asked 2015-08-14 08:57:12 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-20 13:40:49 -0500
edit flag offensive 0 remove flag close merge delete

Comments

For your bonus question; use OutputControl:Table:Style and select unit conversion JtoKWH

Julien Marrec's avatar Julien Marrec (2015-08-14 11:18:37 -0500) edit

I would encourage you to separate out the question about units to be an entirely different topic.

JasonGlazer's avatar JasonGlazer (2015-08-14 11:39:29 -0500) edit

Or just delete it from the posting

Julien Marrec's avatar Julien Marrec (2015-08-14 12:07:41 -0500) edit
add a comment see more comments

1 Answer

0

Regarding my question i read this: Object: Site:GroundTemperature:BuildingSurface "Otherwise, take the indoor air temperature and subtract 2C as a reasonable starting value to use for most commercial applications in the U.S."

So should I simulate (in my example a 1 zone house) without HVAC (the house is located in europa/germany) - take the averrage monthly room temperature and substract 2C - and this are the values for Site:GroundTemperature:BuildingSurface?

And if there is a HVAC system - same approach (modeling without HVAC, set ground temperature)?

Thank you very much.

antifx's avatar
495
antifx
answered 2015-08-16 10:04:55 -0500
edit flag offensive 0 remove flag delete link

Comments

1

This extra information should be added to your original question, not here as an answer. The short answer though is no, you can't do what you propose for a house. The edge effects are too large so the ground under the building won't be in the kind of equilibrium found under a large commercial building.

Jamie Bull's avatar Jamie Bull (2015-08-16 18:19:22 -0500) edit
add a comment see more comments