Error in UserDefined HVAC Objects assembled
Hi everybody. I try to emulate a complex heating solar system with experimental equipment so I decided to initially use two ZoneHVAC:ForcedAir:UserDefined and use a AirTerminal:SingleDuct:UserDefined (this is because the two systems has after mixing air a gas burner in case is not enough with solar heaters) and this Air Terminal is finally connected to the zone. My code is:
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:AIRDISTRIBUTIONUNIT ===========
ZoneHVAC:AirDistributionUnit,
TunnelTerminal, !- Name
TunnelInlet, !- Air Distribution Unit Outlet Node Name
AirTerminal:SingleDuct:UserDefined, !- Air Terminal Object Type
AirMixer; !- Air Terminal Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========
ZoneHVAC:EquipmentList,
SolarHeatingSystem, !- Name
SequentialLoad, !- Load Distribution Scheme
ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
TunnelTerminal, !- Zone Equipment 1 Name
3, !- Zone Equipment 1 Cooling Sequence
3, !- Zone Equipment 1 Heating or No-Load Sequence
, !- Zone Equipment 1 Sequential Cooling Fraction Schedule Name
, !- Zone Equipment 1 Sequential Heating Fraction Schedule Name
ZoneHVAC:ForcedAir:UserDefined, !- Zone Equipment 2 Object Type
IndirectSolarAirHeater, !- Zone Equipment 2 Name
2, !- Zone Equipment 2 Cooling Sequence
2, !- Zone Equipment 2 Heating or No-Load Sequence
, !- Zone Equipment 2 Sequential Cooling Fraction Schedule Name
, !- Zone Equipment 2 Sequential Heating Fraction Schedule Name
ZoneHVAC:ForcedAir:UserDefined, !- Zone Equipment 3 Object Type
DirectSolarAirHeater, !- Zone Equipment 3 Name
1, !- Zone Equipment 3 Cooling Sequence
1; !- Zone Equipment 3 Heating or No-Load Sequence
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========
ZoneHVAC:EquipmentConnections,
ThermalZone, !- Zone Name
SolarHeatingSystem, !- Zone Conditioning Equipment List Name
TunnelInlet, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
TunnelZoneNode; !- Zone Air Node Name
!- =========== ALL OBJECTS IN CLASS: OUTDOORAIR:NODE ===========
OutdoorAir:Node,
OA_DSAH_Node; !- Name
OutdoorAir:Node,
OA_ISAH_Node; !- Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:FORCEDAIR:USERDEFINED ===========
ZoneHVAC:ForcedAir:UserDefined,
DirectSolarAirHeater, !- Name
DirectSolarHeatingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
OA_DSAH_Node, !- Primary Air Inlet Node Name
DSAHOutletNode, !- Primary Air Outlet Node Name
, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0; !- Number of Plant Loop Connections
ZoneHVAC:ForcedAir:UserDefined,
IndirectSolarAirHeater, !- Name
IndirectSolarHeatingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
OA_ISAH_Node, !- Primary Air Inlet Node Name
ISAHOutletNode, !- Primary Air Outlet Node Name
, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0; !- Number of Plant Loop Connections
!- =========== ALL OBJECTS IN CLASS: AIRTERMINAL:SINGLEDUCT:USERDEFINED ===========
AirTerminal:SingleDuct:UserDefined,
AirMixer, !- Name
AirMixingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
DSAHOutletNode, !- Primary Air Inlet Node Name
TunnelInlet, !- Primary Air Outlet Node Name
ISAHOutletNode, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0, !- Number of Plant Loop Connections
AMXRPlantInletNode, !- Plant Connection 1 Inlet Node Name
AMXRPlantOutletNode; !- Plant Connection 1 Outlet Node Name
But it throws the following error:
** Severe ** GetUserDefinedComponents: No matching Air Distribution Unit for AirTerminal:SingleDuct:UserDefined = AIRMIXER
But as you can see, I'm using "TunnelInlet" in Primayr Air Outlet Node Name. So I don't know the origin of the error. Something I missing?
Error in UserDefined HVAC Objects assembled
Hi everybody. I try to emulate a complex heating solar system with experimental equipment so I decided to initially use two ZoneHVAC:ForcedAir:UserDefined and use a AirTerminal:SingleDuct:UserDefined (this is because the two systems has after mixing air a gas burner in case is not enough with solar heaters) and this Air Terminal is finally connected to the zone. My code is:
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:AIRDISTRIBUTIONUNIT ===========
ZoneHVAC:AirDistributionUnit,
TunnelTerminal, !- Name
TunnelInlet, !- Air Distribution Unit Outlet Node Name
AirTerminal:SingleDuct:UserDefined, !- Air Terminal Object Type
AirMixer; !- Air Terminal Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========
ZoneHVAC:EquipmentList,
SolarHeatingSystem, !- Name
SequentialLoad, !- Load Distribution Scheme
ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
TunnelTerminal, !- Zone Equipment 1 Name
3, !- Zone Equipment 1 Cooling Sequence
3, !- Zone Equipment 1 Heating or No-Load Sequence
, !- Zone Equipment 1 Sequential Cooling Fraction Schedule Name
, !- Zone Equipment 1 Sequential Heating Fraction Schedule Name
ZoneHVAC:ForcedAir:UserDefined, !- Zone Equipment 2 Object Type
IndirectSolarAirHeater, !- Zone Equipment 2 Name
2, !- Zone Equipment 2 Cooling Sequence
2, !- Zone Equipment 2 Heating or No-Load Sequence
, !- Zone Equipment 2 Sequential Cooling Fraction Schedule Name
, !- Zone Equipment 2 Sequential Heating Fraction Schedule Name
ZoneHVAC:ForcedAir:UserDefined, !- Zone Equipment 3 Object Type
DirectSolarAirHeater, !- Zone Equipment 3 Name
1, !- Zone Equipment 3 Cooling Sequence
1; !- Zone Equipment 3 Heating or No-Load Sequence
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========
ZoneHVAC:EquipmentConnections,
ThermalZone, !- Zone Name
SolarHeatingSystem, !- Zone Conditioning Equipment List Name
TunnelInlet, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
TunnelZoneNode; !- Zone Air Node Name
!- =========== ALL OBJECTS IN CLASS: OUTDOORAIR:NODE ===========
OutdoorAir:Node,
OA_DSAH_Node; !- Name
OutdoorAir:Node,
OA_ISAH_Node; !- Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:FORCEDAIR:USERDEFINED ===========
ZoneHVAC:ForcedAir:UserDefined,
DirectSolarAirHeater, !- Name
DirectSolarHeatingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
OA_DSAH_Node, !- Primary Air Inlet Node Name
DSAHOutletNode, !- Primary Air Outlet Node Name
, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0; !- Number of Plant Loop Connections
ZoneHVAC:ForcedAir:UserDefined,
IndirectSolarAirHeater, !- Name
IndirectSolarHeatingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
OA_ISAH_Node, !- Primary Air Inlet Node Name
ISAHOutletNode, !- Primary Air Outlet Node Name
, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0; !- Number of Plant Loop Connections
!- =========== ALL OBJECTS IN CLASS: AIRTERMINAL:SINGLEDUCT:USERDEFINED ===========
AirTerminal:SingleDuct:UserDefined,
AirMixer, !- Name
AirMixingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
DSAHOutletNode, !- Primary Air Inlet Node Name
TunnelInlet, !- Primary Air Outlet Node Name
ISAHOutletNode, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0, !- Number of Plant Loop Connections
AMXRPlantInletNode, !- Plant Connection 1 Inlet Node Name
AMXRPlantOutletNode; !- Plant Connection 1 Outlet Node Name
But it throws the following error:
** Severe ** GetUserDefinedComponents: No matching Air Distribution Unit for AirTerminal:SingleDuct:UserDefined = AIRMIXER
But as you can see, I'm using "TunnelInlet" in Primayr Air Outlet Node Name. So I don't know the origin of the error. Something I missing?
Error in UserDefined HVAC Objects assembled
Hi everybody. I try to emulate a complex heating solar system with experimental equipment so I decided to initially use two ZoneHVAC:ForcedAir:UserDefined and use a AirTerminal:SingleDuct:UserDefined (this is because the two systems has after mixing air a gas burner in case is not enough with solar heaters) and this Air Terminal is finally connected to the zone. My code is:
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:AIRDISTRIBUTIONUNIT ===========
ZoneHVAC:AirDistributionUnit,
TunnelTerminal, !- Name
TunnelInlet, !- Air Distribution Unit Outlet Node Name
AirTerminal:SingleDuct:UserDefined, !- Air Terminal Object Type
AirMixer; !- Air Terminal Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========
ZoneHVAC:EquipmentList,
SolarHeatingSystem, !- Name
SequentialLoad, !- Load Distribution Scheme
ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
TunnelTerminal, !- Zone Equipment 1 Name
3, !- Zone Equipment 1 Cooling Sequence
3, !- Zone Equipment 1 Heating or No-Load Sequence
, !- Zone Equipment 1 Sequential Cooling Fraction Schedule Name
, !- Zone Equipment 1 Sequential Heating Fraction Schedule Name
ZoneHVAC:ForcedAir:UserDefined, !- Zone Equipment 2 Object Type
IndirectSolarAirHeater, !- Zone Equipment 2 Name
2, !- Zone Equipment 2 Cooling Sequence
2, !- Zone Equipment 2 Heating or No-Load Sequence
, !- Zone Equipment 2 Sequential Cooling Fraction Schedule Name
, !- Zone Equipment 2 Sequential Heating Fraction Schedule Name
ZoneHVAC:ForcedAir:UserDefined, !- Zone Equipment 3 Object Type
DirectSolarAirHeater, !- Zone Equipment 3 Name
1, !- Zone Equipment 3 Cooling Sequence
1; !- Zone Equipment 3 Heating or No-Load Sequence
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========
ZoneHVAC:EquipmentConnections,
ThermalZone, !- Zone Name
SolarHeatingSystem, !- Zone Conditioning Equipment List Name
TunnelInlet, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
TunnelZoneNode; !- Zone Air Node Name
!- =========== ALL OBJECTS IN CLASS: OUTDOORAIR:NODE ===========
OutdoorAir:Node,
OA_DSAH_Node; !- Name
OutdoorAir:Node,
OA_ISAH_Node; !- Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:FORCEDAIR:USERDEFINED ===========
ZoneHVAC:ForcedAir:UserDefined,
DirectSolarAirHeater, !- Name
DirectSolarHeatingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
OA_DSAH_Node, !- Primary Air Inlet Node Name
DSAHOutletNode, !- Primary Air Outlet Node Name
, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0; !- Number of Plant Loop Connections
ZoneHVAC:ForcedAir:UserDefined,
IndirectSolarAirHeater, !- Name
IndirectSolarHeatingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
OA_ISAH_Node, !- Primary Air Inlet Node Name
ISAHOutletNode, !- Primary Air Outlet Node Name
, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0; !- Number of Plant Loop Connections
!- =========== ALL OBJECTS IN CLASS: AIRTERMINAL:SINGLEDUCT:USERDEFINED ===========
AirTerminal:SingleDuct:UserDefined,
AirMixer, !- Name
AirMixingEMS, !- Overall Model Simulation Program Calling Manager Name
, !- Model Setup and Sizing Program Calling Manager Name
DSAHOutletNode, !- Primary Air Inlet Node Name
TunnelInlet, !- Primary Air Outlet Node Name
ISAHOutletNode, !- Secondary Air Inlet Node Name
, !- Secondary Air Outlet Node Name
0, !- Number of Plant Loop Connections
AMXRPlantInletNode, !- Plant Connection 1 Inlet Node Name
AMXRPlantOutletNode; !- Plant Connection 1 Outlet Node Name
But it throws the following error:
** error:
* Severe ** * GetUserDefinedComponents: No matching Air Distribution Unit for AirTerminal:SingleDuct:UserDefined = AIRMIXER
AIRMIXER But as you can see, I'm using "TunnelInlet" in Primayr Air Outlet Node Name. So I don't know the origin of the error. Something I missing?
Error in UserDefined HVAC Objects assembled
Hi everybody. I try to emulate a complex heating solar system with experimental equipment so I decided to initially use two ZoneHVAC:ForcedAir:UserDefined and use a AirTerminal:SingleDuct:UserDefined (this is because the two systems has after mixing air a gas burner in case is not enough with solar heaters) and this Air Terminal is finally connected to the zone. My code is:
But it throws the following error: * Severe * GetUserDefinedComponents: No matching Air Distribution Unit for AirTerminal:SingleDuct:UserDefined = AIRMIXER
But as you can see, I'm using "TunnelInlet" in Primayr Air Outlet Node Name. So I don't know the origin of the error. Something I missing?