Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

![Fig.1]!pf(/uiles/1685977906480560.png)](/upfiles/1686658931924453.png)]

image description

Fig.2 image description

Variables list. image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

![Fig.1]!pf(/uiles/1685977906480560.png)](/upfiles/1686658931924453.png)]

image description

Fig.2 image description

Variables list. image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

![Fig.1]!pf(/uiles/1685977906480560.png)](/upfiles/1686658931924453.png)]

image description

Fig.2 image description

Variables list. image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

![Fig.1]!pf(/uiles/1685977906480560.png)](/upfiles/1686658931924453.png)]

image description

Fig.2 image description

Variables list. image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

![Fig.1]!pf(/uiles/1685977906480560.png)](/upfiles/1686658931924453.png)]

image description![Fig.1](/upfiles/1685977906480560.png)](/upfiles/1686659916235665.png)

Fig.2 image description

Variables list. image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

![Fig.1](/upfiles/1685977906480560.png)](/upfiles/1686659916235665.png)Fig.1

Fig.2 image description

Variables list. image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

Fig.1

Fig.2 image description

Variables list. image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal to 0?

Please find the model file in the link below

Google Drive Link : https://drive.google.com/drive/folders/1ok4E6qwdzwRhyVA_ySynDy8oz8gDnTB5

Fig.1

Fig.1

Fig.2 image description

Phase Phase Change Material as cold thermal energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why Zone Phase Change Material Melting/Freezing Enthalpy is equal this might be?

Do I need to 0? define a specific zone for the PCMs?

Fig.1

Fig.1

Fig.2 image description

Phase Phase Change Material as cold energy storage / Zone Phase Change Material Melting Output Variable / Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why this might be?

Do I need to define a specific zone for the PCMs?

Fig.1

Fig.1

Fig.2 image description

Zone Phase Change Material Melting / Freezing Melting/Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why this might be?

Do I need to define a specific zone for the PCMs?

Fig.1

Fig.1

Fig.2 image description

Zone Phase Change Material Melting/Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Enthalpy as outputs. However, the enthalpies were both equal to zero (Fig.2).

Does anyone have any idea why this might be?

Do I need to define a specific zone for the PCMs?

Fig.1

Fig.1

Fig.2 image description

Zone Phase Change Material Melting/Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) as cold thermal energy storage (CTES) with a melting point of -20°C to the inner surface of the walls in a refrigerated warehouse. The PCM has a melting point of -20°C, the Enthalpy-Temperature function is shown in the Fig. 1 below.

I then set the Zone Phase Change Material Melting/Freezing Melting Enthalpy and Zone Phase Change Material Freezing Enthalpy as outputs. output. However, the enthalpies were both equal to zero (Fig.2)..

Does anyone Do you have any idea why this might be?

Do is happening? Also, do I need to define a specific zone for the PCMs?

Fig.1

Fig.1

Fig.2 image description

Zone Phase Change Material Melting/Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) with a melting point of -20°C to the inner surface of the walls in a refrigerated warehouse. I then set the Zone Phase Change Material Melting Enthalpy and Zone Phase Change Material Freezing Enthalpy as output. However, the enthalpies were both equal to zero.

Do you have any idea why this is happening? Also, do I need to define a specific zone for the PCMs?

Zone Phase Change Material Melting/Freezing Enthalpy

Hello everyone!

I have added Phase Change Materials (PCMs) with a melting point of -20°C to the inner surface of the walls in a refrigerated warehouse. I then set the Zone Phase Change Material Melting Enthalpy and Zone Phase Change Material Freezing Enthalpy as output. However, the enthalpies were both equal to zero.

Do you have any idea why this is happening? Also, do I need to define a specific zone for the PCMs?