Revision history [back]
SetpointManager:WarmestTemperatureFlow interferes with proper autosizing in WinterDesignDay
A bug report. I found that zone air temperature does not meet heating temperature setpoint in WinterDesignDay if AirLoop is controlled by SetpointManager:WarmestTemperatureFlow. You may think SetpointManager:WarmestTemperatureFlow is irrelevant to heating, but actually it affects sizing run in WinterDesignDay. You can see the bug by running the EnergyPlusV22-2-0 ExampleFile: 5ZoneCAVtoVAVWarmestTempFlow.idf for sizing periods.

You will see a larger temperature gap if you set higher thermostat heating setpoint.

Only about one-third of the predicted load is actually heated.


Here are my findings from some tests for now:
- The bug occurs in models with
AirTerminal:SingleDuct:ConstantVolume:ReheatorAirTerminal:SingleDuct:VAV:Reheat, but does not occur in models withAirTerminalSingleDuct:SeriesPIU:ReheatorAirTerminalSingleDuct:ParallelPIU:Reheat. I have not tested all the AirTerminals. - It's not that the reheat coil does not work at all. The reheat coil heats the zone to some extent, but it's insufficient.
- The gap between
Zone Thermostat Heating Setpoint Temperatureand actualZone Air Temperatureis noticeable when the reheat coil type isCoil:Heating:Water. The gap is relatively small (0.1 to 0.3ºC) forCoil:Heating:Electric. - The bug occurs regardless of control strategy (
FlowFirstorTemperatureFirst) - The weird thing is that unmet hour (
Zone Heating Setpoint Not Met While Occupied Time) is not detected (i.e. 0) during the sizing run even though the zone heating setpoint is not met. - No warnings/errors are reported in the err file.
Originally, I found the bug in my ASHRAE90.1 Baseline case: System 7(VAV with Reheat). You know, system 5 through 8 need to have Supply Air Temperature Reset Control as per ASHRAE90.1 G3.1.3.12, and SetpointManager:WarmestTemperatureFlow needs to be used for the control (Note that SetpointManager:Warmest is inappropriate because the control strategy should be FlowFirst rather than TemperatureFirst according to ANSI/ASHRAE/IES Standard90.1 Performance Rating Method Reference Manual 3.6.2.2 Cooling Control, Cooling Supply Air Temperature Control). I got so many unmet hours in my annual simulation as the reheat coil was not autosized properly.
I would like to know if there is a way around the bug. If not, the reheat coil capacity has to be hardsized with reference to Zone Predicted Sensible Load to Heating Setpoint Heat Transfer Rate.
SetpointManager:WarmestTemperatureFlow interferes with proper autosizing in WinterDesignDay
A bug report. I found that zone air temperature does not meet heating temperature setpoint in WinterDesignDay if AirLoop is controlled by SetpointManager:WarmestTemperatureFlow. You may think SetpointManager:WarmestTemperatureFlow is irrelevant to heating, but actually it affects sizing run in WinterDesignDay. You can see the bug by running the EnergyPlusV22-2-0 ExampleFile: 5ZoneCAVtoVAVWarmestTempFlow.idf for sizing periods.

You will see a larger temperature gap if you set higher thermostat heating setpoint.

Only about one-third of the predicted load is actually heated.


Here are my findings from some tests for now:
- The bug occurs in models with
AirTerminal:SingleDuct:ConstantVolume:ReheatorAirTerminal:SingleDuct:VAV:Reheat, but does not occur in models withAirTerminalSingleDuct:SeriesPIU:ReheatorAirTerminalSingleDuct:ParallelPIU:Reheat. I have not tested all the AirTerminals. - It's not that the reheat coil does not work at all. The reheat coil heats the zone to some extent, but it's insufficient.
- The gap between
Zone Thermostat Heating Setpoint Temperatureand actualZone Air Temperatureis noticeable when the reheat coil type isCoil:Heating:Water. The gap is relatively small (0.1 to 0.3ºC) forCoil:Heating:Electric. - The bug occurs regardless of control strategy (
FlowFirstorTemperatureFirst) - The weird thing is that unmet hour (
Zone Heating Setpoint Not Met While Occupied Time) is not detected (i.e. 0) during the sizing run even though the zone heating setpoint is not met. - No warnings/errors are reported in the err file.
Originally, I found the bug in my ASHRAE90.1 Baseline case: System 7(VAV with Reheat). You know, system 5 through 8 need to have Supply Air Temperature Reset Control as per ASHRAE90.1 G3.1.3.12, and SetpointManager:WarmestTemperatureFlow needs to be used for the control (Note that SetpointManager:Warmest is inappropriate because the control strategy should be FlowFirst rather than TemperatureFirst according to ANSI/ASHRAE/IES Standard90.1 Performance Rating Method Reference Manual 3.6.2.2 Cooling Control, Cooling Supply Air Temperature Control). I got so many unmet hours in my annual simulation as the reheat coil was not autosized properly.
I would like to know if there is a way around the bug. If not, the reheat coil capacity has to be hardsized with reference to Zone Predicted Sensible Load to Heating Setpoint Heat Transfer Rate.
SetpointManager:WarmestTemperatureFlow interferes with proper autosizing in WinterDesignDay
A bug report. I found that zone air temperature does not meet heating temperature setpoint in WinterDesignDay if AirLoop is controlled by SetpointManager:WarmestTemperatureFlow. You may think SetpointManager:WarmestTemperatureFlow is irrelevant to heating, but actually it affects sizing run in WinterDesignDay. You can see the bug by running the EnergyPlusV22-2-0 ExampleFile: 5ZoneCAVtoVAVWarmestTempFlow.idf for sizing periods.

You will see a larger temperature gap if you set higher thermostat heating setpoint.

Only about one-third of the predicted load is actually heated.


Here are my findings from some tests for now:
- The bug occurs in models with
AirTerminal:SingleDuct:ConstantVolume:ReheatorAirTerminal:SingleDuct:VAV:Reheat, but does not occur in models withAirTerminalSingleDuct:SeriesPIU:ReheatorAirTerminalSingleDuct:ParallelPIU:Reheat. I have not tested all the AirTerminals. - It's not that the reheat coil does not work at all. The reheat coil heats the zone to some extent, but it's insufficient.
- The gap between
Zone Thermostat Heating Setpoint Temperatureand actualZone Air Temperatureis noticeable when the reheat coil type isCoil:Heating:Water. The gap is relatively small (0.1 to 0.3ºC) forCoil:Heating:Electric. - The bug occurs regardless of control strategy (
FlowFirstorTemperatureFirst) - The weird thing is that unmet hour (
Zone Heating Setpoint Not Met While Occupied Time) is not detected (i.e. 0) during the sizing run even though the zone heating setpoint is not met. - No warnings/errors are reported in the err file.
Originally, I found the bug in my ASHRAE90.1 Baseline case: System 7(VAV with Reheat). You know, system 5 through 8 need to have Supply Air Temperature Reset Control as per ASHRAE90.1 G3.1.3.12, and SetpointManager:WarmestTemperatureFlow needs to be used for the control (Note that SetpointManager:Warmest is inappropriate because the control strategy should be FlowFirst rather than TemperatureFirst according to ANSI/ASHRAE/IES Standard90.1 Performance Rating Method Reference Manual 3.6.2.2 Cooling Control, Cooling Supply Air Temperature Control). I got so many unmet hours in my annual simulation as the reheat coil was not autosized properly.
I would like to know if there is a way around the bug. If not, the reheat coil capacity has to be hardsized with reference to Zone Predicted Sensible Load to Heating Setpoint Heat Transfer Rate.
SetpointManager:WarmestTemperatureFlow interferes with proper autosizing in WinterDesignDay
A bug report. I found that zone air temperature does not meet heating temperature setpoint in WinterDesignDay if AirLoop is controlled by SetpointManager:WarmestTemperatureFlow. You may think SetpointManager:WarmestTemperatureFlow is irrelevant to heating, but actually it affects sizing run in WinterDesignDay. You can see the bug by running the ExampleFile: 5ZoneCAVtoVAVWarmestTempFlow.idf for sizing periods.

You will see a larger temperature gap if you set higher thermostat heating setpoint.

Only about one-third of the predicted load is actually heated.


Here are my findings from some tests for now:
- The bug occurs in models with
AirTerminal:SingleDuct:ConstantVolume:ReheatorAirTerminal:SingleDuct:VAV:Reheat, but does not occur in models withAirTerminalSingleDuct:SeriesPIU:ReheatorAirTerminalSingleDuct:ParallelPIU:Reheat. I have not tested all the AirTerminals. - It's not that the reheat coil does not work at all. The reheat coil heats the zone to some extent, but it's insufficient.
- The gap between
Zone Thermostat Heating Setpoint Temperatureand actualZone Air Temperatureis noticeable when the reheat coil type isCoil:Heating:Water. The gap is relatively small (0.1 to 0.3ºC) forCoil:Heating:Electric. - The bug occurs regardless of control strategy (
FlowFirstorTemperatureFirst) - The weird thing is that unmet hour (
Zone Heating Setpoint Not Met While Occupied Time) is not detected (i.e. 0)during the sizing runeven though the zone heating setpoint is not met. - No warnings/errors are reported in the err file.
Originally, I found the bug in my ASHRAE90.1 Baseline case: System 7(VAV with Reheat). You know, system 5 through 8 need to have Supply Air Temperature Reset Control as per ASHRAE90.1 G3.1.3.12, and SetpointManager:WarmestTemperatureFlow needs to be used for the control (Note that SetpointManager:Warmest is inappropriate because the control strategy should be FlowFirst rather than TemperatureFirst according to ANSI/ASHRAE/IES Standard90.1 Performance Rating Method Reference Manual 3.6.2.2 Cooling Control, Cooling Supply Air Temperature Control). I got so many unmet hours in my annual simulation as the reheat coil was not autosized properly.
I would like to know if there is a way around the bug. If not, the reheat coil capacity has to be hardsized with reference to Zone Predicted Sensible Load to Heating Setpoint Heat Transfer Rate.