Revision history [back]
Multiple SwimmingPool:Indoor objects do not work
A bug report. Two or more SwimmingPool:Indoor
objects do not work properly.
Let me explain using ExampleFIle: 5ZoneSwimmingPool.idf. Oroginally, the examle file has one SwimmingPool:Indoor
object, so it works properly. When I added 4 SwimmingPool:Indoor
objects (all 5 zones have SwimmingPool:Indoor
objects), only "Test Pool5" met the pool setpoint temperature of 27ºC.
The order of the objects matter. When I changed the order as shown below, only "Test Pool" met the pool setpoint temperature.
But the problem is more complicated. I explain using the revised example file with 2 SwimmingPool:Indoor
objects just because 5 pools are too much to explain. The hot water plant loop is as shown below. When there are 2 SwimmingPool:Indoor
objects,
HW SUPPLY OUTLET NODE:System Node Temperature
does not meet the Setpoint of 82ºC.HW SUPPLY OUTLET NODE:System Node Temperature
andHW DEMAND INLET NODE:System Node Temperature
are inconsistent.TEST POOL:Indoor Pool Inlet Water Temperature
andPOOL WATER INLET NODE:System Node Temperature
are inconsistent.TEST POOL2:Indoor Pool Water Temperature
meet the Setpoint of 27ºC even ifTEST POOL2:Indoor Pool Inlet Water Temperature
is lower than 27ºC.
It's a mess. The bug extends beyond SwimmingPool:Indoor
objects to the entire hot water loop, so that zones cannot meet the heating temperature setpoint.
The idf files are here (V22-2-0). You can reproduce the bug.
Personally, I have a few projects with multiple swimming pools, and I don't have time to wait for the future EnergyPlus version to fix the bug... Please let me know if anyone has been able to force multiple SwimmingPool:Indoor
objects to work using EMS or other means.
Multiple SwimmingPool:Indoor objects do not work
A bug report. Two or more SwimmingPool:Indoor
objects do not work properly.
Let me explain using ExampleFIle: 5ZoneSwimmingPool.idf. Oroginally, the examle file has one SwimmingPool:Indoor
object, so it works properly. When I added 4 SwimmingPool:Indoor
objects (all 5 zones have SwimmingPool:Indoor
objects), only "Test Pool5" met the pool setpoint temperature of 27ºC.
The order of the objects matter. When I changed the order as shown below, only "Test Pool" met the pool setpoint temperature.
But the problem is more complicated. I explain using the revised example file with 2 SwimmingPool:Indoor
objects just because 5 pools are too much to explain. The hot water plant loop is as shown below. When there are 2 SwimmingPool:Indoor
objects,
HW SUPPLY OUTLET NODE:System Node Temperature
does not meet the Setpoint of 82ºC.HW SUPPLY OUTLET NODE:System Node Temperature
andHW DEMAND INLET NODE:System Node Temperature
are inconsistent.TEST POOL:Indoor Pool Inlet Water Temperature
andPOOL WATER INLET NODE:System Node Temperature
are inconsistent.TEST POOL2:Indoor Pool Water Temperature
meet the Setpoint of 27ºC even ifTEST POOL2:Indoor Pool Inlet Water Temperature
is lower than 27ºC.
It's a mess. The bug extends beyond SwimmingPool:Indoor
objects to the entire hot water loop, so that zones cannot meet the heating temperature setpoint.
The idf files are here (V22-2-0). You can reproduce the bug.
Personally, I have a few projects with multiple swimming pools, and I don't have time to wait for the future EnergyPlus version to fix the bug... Please let me know if anyone has been able to force multiple SwimmingPool:Indoor
objects to work using EMS or other means.
Multiple SwimmingPool:Indoor objects do not work
A bug report. Two or more SwimmingPool:Indoor
objects do not work properly.
Let me explain using ExampleFIle: 5ZoneSwimmingPool.idf. Oroginally, the examle file has one SwimmingPool:Indoor
object, so it works properly. When I added 4 SwimmingPool:Indoor
objects (all 5 zones have SwimmingPool:Indoor
objects), only "Test Pool5" met the pool setpoint temperature of 27ºC.
The order of the objects matter. When I changed the order as shown below, only "Test Pool" met the pool setpoint temperature.
But the problem is more complicated. I explain using the revised example file with 2 SwimmingPool:Indoor
objects just because 5 pools are too much to explain. The hot water plant loop is as shown below. When there are 2 SwimmingPool:Indoor
objects,
HW SUPPLY OUTLET NODE:System Node Temperature
does not meet the Setpoint of 82ºC.HW SUPPLY OUTLET NODE:System Node Temperature
andHW DEMAND INLET NODE:System Node Temperature
are inconsistent.TEST POOL:Indoor Pool Inlet Water Temperature
andPOOL WATER INLET NODE:System Node Temperature
are inconsistent.TEST POOL2:Indoor Pool Water Temperature
meet the Setpoint of 27ºC even ifTEST POOL2:Indoor Pool Inlet Water Temperature
is lower than 27ºC.
It's a mess. The bug extends beyond SwimmingPool:Indoor
objects to the entire hot water loop, so that zones cannot meet the heating temperature setpoint.
The idf files are here (V22-2-0). You can reproduce the bug.
Personally, I have a few projects with multiple swimming pools, and I don't have time to wait for the future EnergyPlus version to fix the bug... Please let me know if anyone has been able to force multiple SwimmingPool:Indoor
objects to work using EMS or other means.
Multiple SwimmingPool:Indoor objects do not work
A bug report. Two or more SwimmingPool:Indoor
objects do not work properly.
Let me explain using ExampleFIle: 5ZoneSwimmingPool.idf. Oroginally, the examle file has one SwimmingPool:Indoor
object, so it works properly. When I added 4 SwimmingPool:Indoor
objects (all 5 zones have SwimmingPool:Indoor
objects), only "Test Pool5" met the pool setpoint temperature of 27ºC.
The order of the objects matter. When I changed the order as shown below, only "Test Pool" met meets the pool setpoint temperature.
But the problem is more complicated. I explain using the revised example file with 2 SwimmingPool:Indoor
objects just because 5 pools are too much to explain. The hot water plant loop is as shown below. When there are 2 SwimmingPool:Indoor
objects,
HW SUPPLY OUTLET NODE:System Node Temperature
does not meet the Setpoint of 82ºC.HW SUPPLY OUTLET NODE:System Node Temperature
andHW DEMAND INLET NODE:System Node Temperature
are inconsistent.TEST POOL:Indoor Pool Inlet Water Temperature
andPOOL WATER INLET NODE:System Node Temperature
are inconsistent.TEST POOL2:Indoor Pool Water Temperature
meet the Setpoint of 27ºC even ifTEST POOL2:Indoor Pool Inlet Water Temperature
is lower than 27ºC.
It's a mess. The bug extends beyond SwimmingPool:Indoor
objects to the entire hot water loop, so that zones cannot meet the heating temperature setpoint.
The idf files are here (V22-2-0). You can reproduce the bug.
Personally, I have a few projects with multiple swimming pools, and I don't have time to wait for the future EnergyPlus version to fix the bug... Please let me know if anyone has been able to force multiple SwimmingPool:Indoor
objects to work using EMS or other means.
Multiple SwimmingPool:Indoor objects do not work
A bug report. Two or more SwimmingPool:Indoor
objects do not work properly.
Let me explain using ExampleFIle: 5ZoneSwimmingPool.idf. Oroginally, the examle file has one SwimmingPool:Indoor
object, so it works properly. When I added 4 SwimmingPool:Indoor
objects (all 5 zones have SwimmingPool:Indoor
objects), only "Test Pool5" met the pool setpoint temperature of 27ºC.
The order of the objects matter. When I changed the order as shown below, only "Test Pool" meets the pool setpoint temperature.
But the problem is more complicated. I explain using the revised example file with 2 SwimmingPool:Indoor
objects just because 5 pools are too much to explain. The hot water plant loop is as shown below. When there are 2 SwimmingPool:Indoor
objects,
HW SUPPLY OUTLET NODE:System Node Temperature
does not meet the Setpoint of 82ºC.HW SUPPLY OUTLET NODE:System Node Temperature
andHW DEMAND INLET NODE:System Node Temperature
are inconsistent.TEST POOL:Indoor Pool Inlet Water Temperature
andPOOL WATER INLET NODE:System Node Temperature
are inconsistent.TEST POOL2:Indoor Pool Water Temperature
meet the Setpoint of 27ºC even ifTEST POOL2:Indoor Pool Inlet Water Temperature
is lowerthanthant 27ºC.
It's a mess. The bug extends beyond SwimmingPool:Indoor
objects to the entire hot water loop, so that zones cannot meet the heating temperature setpoint.
The idf files are here (V22-2-0). You can reproduce the bug.
Personally, I have a few projects with multiple swimming pools, and I don't have time to wait for the future EnergyPlus version to fix the bug... Please let me know if anyone has been able to force multiple SwimmingPool:Indoor
objects to work using EMS or other means.