Revision history [back]
Four pipe induction terminal: blank field in node definition
Dear all,
I am new with Openstudio. I am simulating a building conditioned by four pipe cooled beams. To do this I used HW CHW Four Pipe Induction Terminals. Modeling the system, I see that it works properly if I simulate a single zone with only one HW CHW Four Pipe Induction Terminal. If I do the same with more than one zone, it occours that the "Thermal Zone Exhaust Node List" has 2 nodes instead of one, as in my opinion it should be. Consequently these two fields are blank: " !- Induced Air Inlet Node Name" and " !- Air Inlet Node Name". If I go inside the IDF exported and I choose one of the two nodes and I fill these spaces it works properly.
This is the error I see running Openstudio: * Severe * IP: IDF line~31436 Error detected in Object=AIRTERMINAL:SINGLEDUCT:CONSTANTVOLUME:FOURPIPEINDUCTION, name=HW CHW FOUR PIPE INDUCTION TERMINAL 1 * ~~~ * Field [Induced Air Inlet Node Name] is required but was blank
This is the way that I fix it in EnergyPlus:
NodeList,
Thermal Zone5-9 Exhaust Node List, !- Name
!Node 238, !- Node Name 1
Node 214; !- Node Name 2
ZoneHVAC:AirDistributionUnit, HW CHW Four Pipe Induction Terminal 2 Air Distribution Unit, !- Name Node 210, !- Air Distribution Unit Outlet Node Name AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, !- Air Terminal Object Type HW CHW Four Pipe Induction Terminal 2; !- Air Terminal Name
AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, HW CHW Four Pipe Induction Terminal 2, !- Name , !- Availability Schedule Name Autosize, !- Maximum Total Air Flow Rate {m3/s} 2.5, !- Induction Ratio Node 213, !- Supply Air Inlet Node Name Node 214, !- Induced Air Inlet Node Name Node 210, !- Air Outlet Node Name , !- Hot Water Inlet Node Name , !- Cold Water Inlet Node Name Coil:Heating:Water, !- Heating Coil Object Type HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Heating Coil Name , !- Maximum Hot Water Flow Rate {m3/s} 0, !- Minimum Hot Water Flow Rate {m3/s} 0.001, !- Heating Convergence Tolerance Coil:Cooling:Water, !- Cooling Coil Object Type HW CHW Four Pipe Induction Terminal CHW Clg Coil 2, !- Cooling Coil Name Autosize, !- Maximum Cold Water Flow Rate {m3/s} 0, !- Minimum Cold Water Flow Rate {m3/s} 0.001, !- Cooling Convergence Tolerance HW CHW Four Pipe Induction Terminal 2 Mixer; !- Zone Mixer Name
Coil:Heating:Water, HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Name Always On Discrete 1, !- Availability Schedule Name Autosize, !- U-Factor Times Area Value {W/K} Autosize, !- Maximum Water Flow Rate {m3/s} Node 249, !- Water Inlet Node Name Node 250, !- Water Outlet Node Name Node 214, !- Air Inlet Node Name HW CHW Four Pipe Induction Terminal 2 Heating Coil Outlet, !- Air Outlet Node Name UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method Autosize, !- Rated Capacity {W} 82.2, !- Rated Inlet Water Temperature {C} 16.6, !- Rated Inlet Air Temperature {C} 71.1, !- Rated Outlet Water Temperature {C} 32.2, !- Rated Outlet Air Temperature {C} 0.5; !- Rated Ratio for Air and Water Convection
Anyone of u has an idea to fix this issue directly into Openstudio?
Am I doing something wrong?
Thank you very much Have a nice day Elena
Four pipe induction terminal: blank field in node definition
Dear all,
I am new with Openstudio. I am simulating a building conditioned by four pipe cooled beams. To do this I used HW CHW Four Pipe Induction Terminals. Modeling the system, I see that it works properly if I simulate a single zone with only one HW CHW Four Pipe Induction Terminal. If I do the same with more than one zone, it occours that the "Thermal Zone Exhaust Node List" has 2 nodes instead of one, as in my opinion it should be. Consequently these two fields are blank: " !- Induced Air Inlet Node Name" and " !- Air Inlet Node Name". If I go inside the IDF exported and I choose one of the two nodes and I fill these spaces it works properly.
This is the error I see running Openstudio: * Severe * IP: IDF line~31436 Error detected in Object=AIRTERMINAL:SINGLEDUCT:CONSTANTVOLUME:FOURPIPEINDUCTION, name=HW CHW FOUR PIPE INDUCTION TERMINAL 1 * ~~~ * Field [Induced Air Inlet Node Name] is required but was blank
This is the way that I fix it in EnergyPlus:
NodeList,
Thermal Zone5-9 Exhaust Node List, !- Name
!Node 238, !- Node Name 1
Node 214; !- Node Name 2
ZoneHVAC:AirDistributionUnit, HW CHW Four Pipe Induction Terminal 2 Air Distribution Unit, !- Name Node 210, !- Air Distribution Unit Outlet Node Name AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, !- Air Terminal Object Type HW CHW Four Pipe Induction Terminal 2; !- Air Terminal Name
AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, HW CHW Four Pipe Induction Terminal 2, !- Name , !- Availability Schedule Name Autosize, !- Maximum Total Air Flow Rate {m3/s} 2.5, !- Induction Ratio Node 213, !- Supply Air Inlet Node Name Node 214, !- Induced Air Inlet Node Name Node 210, !- Air Outlet Node Name , !- Hot Water Inlet Node Name , !- Cold Water Inlet Node Name Coil:Heating:Water, !- Heating Coil Object Type HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Heating Coil Name , !- Maximum Hot Water Flow Rate {m3/s} 0, !- Minimum Hot Water Flow Rate {m3/s} 0.001, !- Heating Convergence Tolerance Coil:Cooling:Water, !- Cooling Coil Object Type HW CHW Four Pipe Induction Terminal CHW Clg Coil 2, !- Cooling Coil Name Autosize, !- Maximum Cold Water Flow Rate {m3/s} 0, !- Minimum Cold Water Flow Rate {m3/s} 0.001, !- Cooling Convergence Tolerance HW CHW Four Pipe Induction Terminal 2 Mixer; !- Zone Mixer Name
Coil:Heating:Water, HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Name Always On Discrete 1, !- Availability Schedule Name Autosize, !- U-Factor Times Area Value {W/K} Autosize, !- Maximum Water Flow Rate {m3/s} Node 249, !- Water Inlet Node Name Node 250, !- Water Outlet Node Name Node 214, !- Air Inlet Node Name HW CHW Four Pipe Induction Terminal 2 Heating Coil Outlet, !- Air Outlet Node Name UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method Autosize, !- Rated Capacity {W} 82.2, !- Rated Inlet Water Temperature {C} 16.6, !- Rated Inlet Air Temperature {C} 71.1, !- Rated Outlet Water Temperature {C} 32.2, !- Rated Outlet Air Temperature {C} 0.5; !- Rated Ratio for Air and Water Convection
Anyone of u has an idea to fix this issue directly into Openstudio?
Am I doing something wrong?
Thank you very much Have a nice day Elena
Four pipe induction terminal: blank field in node definition
Dear all,
I am new with Openstudio. I am simulating a building conditioned by four pipe cooled beams. To do this I used HW CHW Four Pipe Induction Terminals. Modeling the system, I see that it works properly if I simulate a single zone with only one HW CHW Four Pipe Induction Terminal. If I do the same with more than one zone, it occours that the "Thermal Zone Exhaust Node List" has 2 nodes instead of one, as in my opinion it should be. Consequently these two fields are blank: " !- Induced Air Inlet Node Name" and " !- Air Inlet Node Name". If I go inside the IDF exported and I choose one of the two nodes and I fill these spaces it works properly.
This is the error I see running Openstudio: * Severe * IP: IDF line~31436 Error detected in Object=AIRTERMINAL:SINGLEDUCT:CONSTANTVOLUME:FOURPIPEINDUCTION, name=HW CHW FOUR PIPE INDUCTION TERMINAL 1 * ~~~ * Field [Induced Air Inlet Node Name] is required but was blank
This is the way that I fix it in EnergyPlus:
NodeList,
Thermal Zone5-9 Exhaust Node List, !- Name
!Node 238, !- Node Name 1
Node 214; !- Node Name 2
ZoneHVAC:AirDistributionUnit, HW CHW Four Pipe Induction Terminal 2 Air Distribution Unit, !- Name Node 210, !- Air Distribution Unit Outlet Node Name AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, !- Air Terminal Object Type HW CHW Four Pipe Induction Terminal 2; !- Air Terminal Name
AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, HW CHW Four Pipe Induction Terminal 2, !- Name , !- Availability Schedule Name Autosize, !- Maximum Total Air Flow Rate {m3/s} 2.5, !- Induction Ratio Node 213, !- Supply Air Inlet Node Name Node 214, !- Induced Air Inlet Node Name Node 210, !- Air Outlet Node Name , !- Hot Water Inlet Node Name , !- Cold Water Inlet Node Name Coil:Heating:Water, !- Heating Coil Object Type HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Heating Coil Name , !- Maximum Hot Water Flow Rate {m3/s} 0, !- Minimum Hot Water Flow Rate {m3/s} 0.001, !- Heating Convergence Tolerance Coil:Cooling:Water, !- Cooling Coil Object Type HW CHW Four Pipe Induction Terminal CHW Clg Coil 2, !- Cooling Coil Name Autosize, !- Maximum Cold Water Flow Rate {m3/s} 0, !- Minimum Cold Water Flow Rate {m3/s} 0.001, !- Cooling Convergence Tolerance HW CHW Four Pipe Induction Terminal 2 Mixer; !- Zone Mixer Name
Coil:Heating:Water, HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Name Always On Discrete 1, !- Availability Schedule Name Autosize, !- U-Factor Times Area Value {W/K} Autosize, !- Maximum Water Flow Rate {m3/s} Node 249, !- Water Inlet Node Name Node 250, !- Water Outlet Node Name Node 214, !- Air Inlet Node Name HW CHW Four Pipe Induction Terminal 2 Heating Coil Outlet, !- Air Outlet Node Name UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method Autosize, !- Rated Capacity {W} 82.2, !- Rated Inlet Water Temperature {C} 16.6, !- Rated Inlet Air Temperature {C} 71.1, !- Rated Outlet Water Temperature {C} 32.2, !- Rated Outlet Air Temperature {C} 0.5; !- Rated Ratio for Air and Water Convection
Anyone of u has an idea to fix this issue directly into Openstudio?
Am I doing something wrong?
Thank you very much Have a nice day Elena
Four pipe induction terminal: blank field in node definition
Dear all,
I am new with Openstudio. I am simulating a building conditioned by four pipe cooled beams. To do this I used HW CHW Four Pipe Induction Terminals. Modeling the system, I see that it works properly if I simulate a single zone with only one HW CHW Four Pipe Induction Terminal. If I do the same with more than one zone, it occours that the "Thermal Zone Exhaust Node List" has 2 nodes instead of one, as in my opinion it should be. Consequently these two fields are blank: " !- Induced Air Inlet Node Name" and " !- Air Inlet Node Name". If I go inside the IDF exported and I choose one of the two nodes and I fill these spaces it works properly.
This is the error I see running Openstudio: * Severe * IP: IDF line~31436 Error detected in Object=AIRTERMINAL:SINGLEDUCT:CONSTANTVOLUME:FOURPIPEINDUCTION, name=HW CHW FOUR PIPE INDUCTION TERMINAL 1 * ~~~ * Field [Induced Air Inlet Node Name] is required but was blank
This is the way that I fix it in EnergyPlus:
NodeList,
Thermal Zone5-9 Exhaust Node List, !- Name
!Node 238, !- Node Name 1
Node 214; !- Node Name 2
ZoneHVAC:AirDistributionUnit, HW CHW Four Pipe Induction Terminal 2 Air Distribution Unit, !- Name Node 210, !- Air Distribution Unit Outlet Node Name AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, !- Air Terminal Object Type HW CHW Four Pipe Induction Terminal 2; !- Air Terminal Name
AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, HW CHW Four Pipe Induction Terminal 2, !- Name , !- Availability Schedule Name Autosize, !- Maximum Total Air Flow Rate {m3/s} 2.5, !- Induction Ratio Node 213, !- Supply Air Inlet Node Name Node 214, !- Induced Air Inlet Node Name Node 210, !- Air Outlet Node Name , !- Hot Water Inlet Node Name , !- Cold Water Inlet Node Name Coil:Heating:Water, !- Heating Coil Object Type HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Heating Coil Name , !- Maximum Hot Water Flow Rate {m3/s} 0, !- Minimum Hot Water Flow Rate {m3/s} 0.001, !- Heating Convergence Tolerance Coil:Cooling:Water, !- Cooling Coil Object Type HW CHW Four Pipe Induction Terminal CHW Clg Coil 2, !- Cooling Coil Name Autosize, !- Maximum Cold Water Flow Rate {m3/s} 0, !- Minimum Cold Water Flow Rate {m3/s} 0.001, !- Cooling Convergence Tolerance HW CHW Four Pipe Induction Terminal 2 Mixer; !- Zone Mixer Name
Coil:Heating:Water, HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Name Always On Discrete 1, !- Availability Schedule Name Autosize, !- U-Factor Times Area Value {W/K} Autosize, !- Maximum Water Flow Rate {m3/s} Node 249, !- Water Inlet Node Name Node 250, !- Water Outlet Node Name Node 214, !- Air Inlet Node Name HW CHW Four Pipe Induction Terminal 2 Heating Coil Outlet, !- Air Outlet Node Name UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method Autosize, !- Rated Capacity {W} 82.2, !- Rated Inlet Water Temperature {C} 16.6, !- Rated Inlet Air Temperature {C} 71.1, !- Rated Outlet Water Temperature {C} 32.2, !- Rated Outlet Air Temperature {C} 0.5; !- Rated Ratio for Air and Water Convection
Anyone of u has an idea to fix this issue directly into Openstudio?
Am I doing something wrong?
Thank you very much Have a nice day Elena
Four pipe induction terminal: blank field in node definition
Dear all,
I am new with Openstudio. I am simulating a building conditioned by four pipe cooled beams. To do this I used HW CHW Four Pipe Induction Terminals. Modeling the system, I see that it works properly if I simulate a single zone with only one HW CHW Four Pipe Induction Terminal. If I do the same with more than one zone, it occours that the "Thermal Zone Exhaust Node List" has 2 nodes instead of one, as in my opinion it should be. Consequently these two fields are blank: " !- Induced Air Inlet Node Name" and " !- Air Inlet Node Name". If I go inside the IDF exported and I choose one of the two nodes and I fill these spaces it works properly.
This is the error I see running Openstudio: * Severe * IP: IDF line~31436 Error detected in Object=AIRTERMINAL:SINGLEDUCT:CONSTANTVOLUME:FOURPIPEINDUCTION, name=HW CHW FOUR PIPE INDUCTION TERMINAL 1 * ~~~ * Field [Induced Air Inlet Node Name] is required but was blank
This is the way that I fix it in EnergyPlus:
NodeList,
Thermal Zone5-9 Exhaust Node List, !- Name
!Node 238, !- Node Name 1
Node 214; !- Node Name 2
ZoneHVAC:AirDistributionUnit, HW CHW Four Pipe Induction Terminal 2 Air Distribution Unit, !- Name Node 210, !- Air Distribution Unit Outlet Node Name AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, !- Air Terminal Object Type HW CHW Four Pipe Induction Terminal 2; !- Air Terminal Name
AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, HW CHW Four Pipe Induction Terminal 2, !- Name , !- Availability Schedule Name Autosize, !- Maximum Total Air Flow Rate {m3/s} 2.5, !- Induction Ratio Node 213, !- Supply Air Inlet Node Name Node 214, !- Induced Air Inlet Node Name Node 210, !- Air Outlet Node Name , !- Hot Water Inlet Node Name , !- Cold Water Inlet Node Name Coil:Heating:Water, !- Heating Coil Object Type HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Heating Coil Name , !- Maximum Hot Water Flow Rate {m3/s} 0, !- Minimum Hot Water Flow Rate {m3/s} 0.001, !- Heating Convergence Tolerance Coil:Cooling:Water, !- Cooling Coil Object Type HW CHW Four Pipe Induction Terminal CHW Clg Coil 2, !- Cooling Coil Name Autosize, !- Maximum Cold Water Flow Rate {m3/s} 0, !- Minimum Cold Water Flow Rate {m3/s} 0.001, !- Cooling Convergence Tolerance HW CHW Four Pipe Induction Terminal 2 Mixer; !- Zone Mixer Name
Coil:Heating:Water, HW CHW Four Pipe Induction Terminal HW Htg Coil 2, !- Name Always On Discrete 1, !- Availability Schedule Name Autosize, !- U-Factor Times Area Value {W/K} Autosize, !- Maximum Water Flow Rate {m3/s} Node 249, !- Water Inlet Node Name Node 250, !- Water Outlet Node Name Node 214, !- Air Inlet Node Name HW CHW Four Pipe Induction Terminal 2 Heating Coil Outlet, !- Air Outlet Node Name UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method Autosize, !- Rated Capacity {W} 82.2, !- Rated Inlet Water Temperature {C} 16.6, !- Rated Inlet Air Temperature {C} 71.1, !- Rated Outlet Water Temperature {C} 32.2, !- Rated Outlet Air Temperature {C} 0.5; !- Rated Ratio for Air and Water Convection
Anyone of u has an idea to fix this issue directly into Openstudio?
Am I doing something wrong?
Thank you very much Have a nice day Elena