Can 1 AHU (cooling coil) set in more than one plant loop
I am setting 3 refrigerant loops for 3 chillers. I need to split the chiller into 3 loops because I cannot find how to schedule the chillers (their on/off schedules are not the same). But every chiller connect with every AHU in the building (the difference is just their on/off schedule) but when I split the loops and drag the AHU to the refrigerant loops, I have found that 1 AHU can only place in only 1 plant loop (when I drag AHU to another loop, the AHU in the first loop has gone). I would like to ask if there is any way to schedule chillers in the same loop or set AHU to many plant loops. Thank you
Can 1 AHU (cooling coil) set in more than one plant loop
I am setting 3 refrigerant loops for 3 chillers. I need to split the chiller into 3 loops because I cannot find how to schedule the chillers (their on/off schedules are not the same). But every chiller connect with every AHU in the building (the difference is just their on/off schedule) but when I split the loops and drag the AHU to the refrigerant loops, I have found that 1 AHU can only place in only 1 plant loop (when I drag AHU to another loop, the AHU in the first loop has gone). I would like to ask if there is any way to schedule chillers in the same loop or set AHU to many plant loops. Thank you