FourPipeFanCoil actuators for external control
Dear All,
I'm trying to control with actuators a ZoneHVAC:FourPipeFanCoil
since now I was able to control the mass flow rate with the following actuator:
EnergyManagementSystem:Actuator,
m_42, !- Name
ZONE1 FAN COIL UNIT SUPPLY FAN, !- Actuated Component Unique Name
Fan, !- Actuated Component Type System Node Setpoint
Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint
I have tried to control the out temperature from the heating coil with the following actuator but I was not able to achieve it:
EnergyManagementSystem:Actuator,
t_42, !- Name
ZONE1 FAN COIL UNIT SUPPLY OUTLET, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Temperature Setpoint; !- Actuated Component Control Type
Any Idea on how I can control the air temperature outlet?
I'm able to do it in an air terminal with AirTerminal:SingleDuct:ConstantVolume:NoReheat
like the following :
AirTerminal:SingleDuct:ConstantVolume:NoReheat, ZONE2 Single Duct CAV No Reheat, !- Name On 24/7, !- Availability Schedule Name Air Loop Zone Splitter Outlet Node 3, !- Air Inlet Node Name ZONE2 Single Duct CAV No Reheat Supply Outlet, !- Air Outlet Node Name 433.830000; !- Maximum Air Flow Rate {m3/s}
By controlling the flowing actuators:
EnergyManagementSystem:Actuator,
t_41, !- Name
AIR LOOP AHU HEATING COIL AIR OUTLET NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Temperature Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
m_41, !- Name
AIR LOOP AHU SUPPLY FAN, !- Actuated Component Unique Name
Fan, !- Actuated Component Type System Node Setpoint
Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint
Here you find the details of the ZoneHVAC:FourPipeFanCoil
ZoneHVAC:FourPipeFanCoil,
ZONE1 Fan Coil Unit, !- Name
FAN COIL_FCA_Heating control schedule, !- Availability Schedule Name
ConstantFanVariableFlow, !- Capacity Control Method
autosize, !- Maximum Supply Air Flow Rate {m3/s}
0.33, !- Low Speed Supply Air Flow Ratio
0.66, !- Medium Speed Supply Air Flow Ratio
0.0, !- Maximum Outdoor Air Flow Rate {m3/s}
, !- Outdoor Air Schedule Name
ZONE1 Fan Coil Unit Return, !- Air Inlet Node Name
ZONE1 Fan Coil Unit Supply Outlet, !- Air Outlet Node Name
OutdoorAir:Mixer, !- Outdoor Air Mixer Object Type
ZONE1 Fan Coil Unit Outdoor Air Mixer, !- Outdoor Air Mixer Name
Fan:ConstantVolume, !- Supply Air Fan Object Type
ZONE1 Fan Coil Unit Supply Fan, !- Supply Air Fan Name
Coil:Cooling:Water, !- Cooling Coil Object Type
ZONE1 Fan Coil Unit Cooling Coil, !- Cooling Coil Name
autosize, !- Maximum Cold Water Flow Rate {m3/s}
0.000000, !- Minimum Cold Water Flow Rate {m3/s}
0.0010, !- Cooling Convergence Tolerance
Coil:Heating:Water, !- Heating Coil Object Type
ZONE1 Coil Unit Heating Coil, !- Heating Coil Name
autosize, !- Maximum Hot Water Flow Rate {m3/s}
0.000000, !- Minimum Hot Water Flow Rate {m3/s}
0.0010; !- Heating Convergence Tolerance
Coil:Heating:Water,
ZONE1 Fan Coil Unit Heating Coil, !- Name
On 24/7, !- Availability Schedule Name
autosize, !- U-Factor Times Area Value {W/K}
autosize, !- Maximum Water Flow Rate {m3/s}
ZONE1 Fan Coil Unit Heating Coil Water Inlet Node, !- Water Inlet Node Name
ZONE1 Fan Coil Unit Heating Coil Water Outlet Node, !- Water Outlet Node Name
ZONE1 Fan Coil Unit Cooling Coil Outlet, !- Air Inlet Node Name
ZONE1 Fan Coil Unit Supply Outlet, !- Air Outlet Node Name
UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
autosize, !- Rated Capacity {W}
80.0, !- Rated Inlet Water Temperature {C}
16.0, !- Rated Inlet Air Temperature {C}
70.0, !- Rated Outlet Water Temperature {C}
35.0, !- Rated Outlet Air Temperature {C}
0.50; !- Rated Ratio for Air and Water Convection
Fan:ConstantVolume,
ZONE1 Fan Coil Unit Supply Fan, !- Name
FAN COIL_Heating control schedule, !- Availability Schedule Name
0.700000, !- Fan Total Efficiency
100.00, !- Pressure Rise {Pa}
autosize, !- Maximum Flow Rate {m3/s}
0.900000, !- Motor Efficiency
1.00, !- Motor In Airstream Fraction
ZONE1 Fan Coil Unit Mixed Air Outlet, !- Air Inlet Node Name
ZONE1 Fan Coil Unit Supply Fan Outlet, !- Air Outlet Node Name
General; !- End-Use Subcategory
FourPipeFanCoil actuators for external control
Dear All,
I'm trying to control with actuators a ZoneHVAC:FourPipeFanCoil
since now I was able to control the mass flow rate with the following actuator:
EnergyManagementSystem:Actuator,
m_42, !- Name
ZONE1 FAN COIL UNIT SUPPLY FAN, !- Actuated Component Unique Name
Fan, !- Actuated Component Type System Node Setpoint
Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint
I have tried to control the out temperature from the heating coil with the following actuator but I was not able to achieve it:
EnergyManagementSystem:Actuator,
t_42, !- Name
ZONE1 FAN COIL UNIT SUPPLY OUTLET, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Temperature Setpoint; !- Actuated Component Control Type
Any Idea on how I can control the air temperature outlet?
I'm able to do it in an air terminal with AirTerminal:SingleDuct:ConstantVolume:NoReheat
like the following :
AirTerminal:SingleDuct:ConstantVolume:NoReheat, ZONE2 Single Duct CAV No Reheat, !- Name On 24/7, !- Availability Schedule Name Air Loop Zone Splitter Outlet Node 3, !- Air Inlet Node Name ZONE2 Single Duct CAV No Reheat Supply Outlet, !- Air Outlet Node Name 433.830000; !- Maximum Air Flow Rate {m3/s}
By controlling the flowing actuators:
EnergyManagementSystem:Actuator,
t_41, !- Name
AIR LOOP AHU HEATING COIL AIR OUTLET NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Temperature Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
m_41, !- Name
AIR LOOP AHU SUPPLY FAN, !- Actuated Component Unique Name
Fan, !- Actuated Component Type System Node Setpoint
Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint
Here you find the details of the ZoneHVAC:FourPipeFanCoil
ZoneHVAC:FourPipeFanCoil,
ZONE1 Fan Coil Unit, !- Name
FAN COIL_FCA_Heating control schedule, !- Availability Schedule Name
ConstantFanVariableFlow, !- Capacity Control Method
autosize, !- Maximum Supply Air Flow Rate {m3/s}
0.33, !- Low Speed Supply Air Flow Ratio
0.66, !- Medium Speed Supply Air Flow Ratio
0.0, !- Maximum Outdoor Air Flow Rate {m3/s}
, !- Outdoor Air Schedule Name
ZONE1 Fan Coil Unit Return, !- Air Inlet Node Name
ZONE1 Fan Coil Unit Supply Outlet, !- Air Outlet Node Name
OutdoorAir:Mixer, !- Outdoor Air Mixer Object Type
ZONE1 Fan Coil Unit Outdoor Air Mixer, !- Outdoor Air Mixer Name
Fan:ConstantVolume, !- Supply Air Fan Object Type
ZONE1 Fan Coil Unit Supply Fan, !- Supply Air Fan Name
Coil:Cooling:Water, !- Cooling Coil Object Type
ZONE1 Fan Coil Unit Cooling Coil, !- Cooling Coil Name
autosize, !- Maximum Cold Water Flow Rate {m3/s}
0.000000, !- Minimum Cold Water Flow Rate {m3/s}
0.0010, !- Cooling Convergence Tolerance
Coil:Heating:Water, !- Heating Coil Object Type
ZONE1 Coil Unit Heating Coil, !- Heating Coil Name
autosize, !- Maximum Hot Water Flow Rate {m3/s}
0.000000, !- Minimum Hot Water Flow Rate {m3/s}
0.0010; !- Heating Convergence Tolerance
Coil:Heating:Water,
ZONE1 Fan Coil Unit Heating Coil, !- Name
On 24/7, !- Availability Schedule Name
autosize, !- U-Factor Times Area Value {W/K}
autosize, !- Maximum Water Flow Rate {m3/s}
ZONE1 Fan Coil Unit Heating Coil Water Inlet Node, !- Water Inlet Node Name
ZONE1 Fan Coil Unit Heating Coil Water Outlet Node, !- Water Outlet Node Name
ZONE1 Fan Coil Unit Cooling Coil Outlet, !- Air Inlet Node Name
ZONE1 Fan Coil Unit Supply Outlet, !- Air Outlet Node Name
UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
autosize, !- Rated Capacity {W}
80.0, !- Rated Inlet Water Temperature {C}
16.0, !- Rated Inlet Air Temperature {C}
70.0, !- Rated Outlet Water Temperature {C}
35.0, !- Rated Outlet Air Temperature {C}
0.50; !- Rated Ratio for Air and Water Convection
Fan:ConstantVolume,
ZONE1 Fan Coil Unit Supply Fan, !- Name
FAN COIL_Heating control schedule, !- Availability Schedule Name
0.700000, !- Fan Total Efficiency
100.00, !- Pressure Rise {Pa}
autosize, !- Maximum Flow Rate {m3/s}
0.900000, !- Motor Efficiency
1.00, !- Motor In Airstream Fraction
ZONE1 Fan Coil Unit Mixed Air Outlet, !- Air Inlet Node Name
ZONE1 Fan Coil Unit Supply Fan Outlet, !- Air Outlet Node Name
General; !- End-Use Subcategory