Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
P.S.
I noticed another problem of AirLoopHVAC:DedicatedOutdoorAirSystem
. Please let me know If I should post as a separate question.
It's not about fan, but about coil of PAU. I updated the idf file from v9-2-0 to v9-6-0, but I got severe error about coil sizing of PAU, and the calculation terminated. All the parameters (flow rate, temperature and humidity ratio) of the coil was autosize, which caused the error. The error disappeared when I hardsized them. When I ran the idf file v9-2-0, I haven't got the error, but I noticed that the coil was not autosized correctly. Inlet Air Temperature was -999°C, and Coil Load was 0W as shown below.
How can the coil for AirLoopHVAC:DedicatedOutdoorAirSystem
be autosized? AirLoopHVAC:DedicatedOutdoorAirSystem
is not listed in Sizing:Zone
, Sizing:System
or Sizing:Plant
, so there is no class that has necessary information to autosize coil.
About fan flow rate, it's ok because it can be autosized by summing each zone outdoor flow rate.
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
P.S.
I noticed another problem of AirLoopHVAC:DedicatedOutdoorAirSystem
. Please let me know If I should post as a separate question.
It's not about fan, but about coil of PAU. I updated the idf file from v9-2-0 to v9-6-0, but I got severe error about coil sizing of PAU, and the calculation terminated. All the parameters (flow rate, temperature and humidity ratio) of the coil was autosize, which caused the error. The error disappeared when I hardsized them. When I ran the idf file v9-2-0, I haven't got the error, but I noticed that the coil was not autosized correctly. Inlet Air Temperature was -999°C, and Coil Load was 0W as shown below.
How can the coil for AirLoopHVAC:DedicatedOutdoorAirSystem
be autosized? AirLoopHVAC:DedicatedOutdoorAirSystem
is not listed in Sizing:Zone
, Sizing:System
or Sizing:Plant
, so there is no class that has necessary information to autosize coil.
About fan flow rate, it's ok because it can be autosized by summing each zone outdoor flow rate.
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
P.S.
I noticed another problem of AirLoopHVAC:DedicatedOutdoorAirSystem
. Please let me know If I should post as a separate question.
It's not about fan, but about coil of PAU. I updated the idf file from v9-2-0 to v9-6-0, but I got severe error about coil sizing of PAU, and the calculation terminated. All the parameters (flow rate, temperature and humidity ratio) of the coil was autosize, which caused the error. The error disappeared when I hardsized them. When I ran the idf file v9-2-0, I haven't got the error, but I noticed that the coil was not autosized correctly. Inlet Air Temperature was -999°C, and Coil Load was 0W as shown below.
How can the coil for AirLoopHVAC:DedicatedOutdoorAirSystem
be autosized? AirLoopHVAC:DedicatedOutdoorAirSystem
is not listed in Sizing:Zone
, Sizing:System
or Sizing:Plant
, so there is no class that has necessary information to autosize coil.
About fan flow rate, it's ok because it can be autosized by summing each zone outdoor flow rate.
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
P.S.
I noticed another problem of AirLoopHVAC:DedicatedOutdoorAirSystem
. Please let me know If I should post as a separate question.
It's not about fan, but about coil of PAU. I updated the idf file from v9-2-0 to v9-6-0, but I got severe error about coil sizing of PAU, and the calculation terminated. All the parameters (flow rate, temperature and humidity ratio) of the coil was autosize, which caused the error. The error disappeared when I hardsized them. When I ran the idf file v9-2-0, I haven't got the error, but I noticed that the coil was not autosized correctly. Inlet Air Temperature was -999°C, and Coil Load was 0W as shown below.
How can the coil for AirLoopHVAC:DedicatedOutdoorAirSystem
be autosized? AirLoopHVAC:DedicatedOutdoorAirSystem
is not listed in Sizing:Zone
, Sizing:System
or Sizing:Plant
, so there is no class that has necessary information to autosize coil.
About fan flow rate, it's ok because it can be autosized by summing each zone outdoor flow rate.
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 during midnight (1am to 6am).
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name
Fan:SystemModel power curve does not work
I have two problems.
Fan Electric Power
ofFan:SystemModel
is constant although the fan airflow is variable.Fan:SystemModel
is ON when Availability Schedule is 0 duringmidnight (1am to 6am).midnight.
This post is related to my previous question. I have modelled PAU+AHU with AirLoopHVAC:DedicatedOutdoorAirSystem
. As you may know, only Fan:SystemModel
is allowed for modelling AirLoopHVAC:DedicatedOutdoorAirSystem
. Fan:VariableVolume
is not allowed. I have modelled PAU with DCV by CO2 concentration, so the outdoor airflow rate is variable, but Fan Electric Power
is constant. I don't know why. Besides, Availability Schedule
makes the outdoor airflow rate 0 during midnight of weekdays, but the fan consumes electric power for 24 hours. Please find the charts below.
My Fan:SystemModel
input is as follows. Is there anything wrong with it?
Fan:SystemModel,
PAU_Tower12_Office_1 Supply Fan, !- Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Cooling Coil Outlet, !- Air Inlet Node Name
PAU_Tower12_Office_1 Supply Fan Outlet, !- Air Outlet Node Name
autosize, !- Design Maximum Air Flow Rate {m3/s}
Continuous, !- Speed Control Method
0.2, !- Electric Power Minimum Flow Rate Fraction
1200, !- Design Pressure Rise {Pa}
0.9, !- Motor Efficiency
1, !- Motor In Air Stream Fraction
autosize, !- Design Electric Power Consumption {W}
TotalEfficiencyAndPressure, !- Design Power Sizing Method
, !- Electric Power Per Unit Flow Rate {W/(m3/s)}
, !- Electric Power Per Unit Flow Rate Per Unit Pressure {W/((m3/s)-Pa)}
0.7, !- Fan Total Efficiency
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Electric Power Function of Flow Fraction Curve Name
, !- Night Ventilation Mode Pressure Rise {Pa}
, !- Night Ventilation Mode Flow Fraction
, !- Motor Loss Zone Name
, !- Motor Loss Radiative Fraction
General; !- End-Use Subcategory
, !- Number of Speeds
, !- Speed 1 Flow Fraction
, !- Speed 1 Electric Power Fraction
Fan curve input is as follows. It is based on ASHRAE90.1 TABLE G3.1.3.15.
I think there should be no problem with it becuase AHUs that have been modelled with Fan:Variable
and with the same coeciffients as this fan power curve have variable Fan Electric Power
.
Curve:Cubic,
ASHRAE90.1 TABLE G3.1.3.15 Fan Power Curve, !- Name
0.0013, !- Coefficient1 Constant
0.147, !- Coefficient2 x
0.9506, !- Coefficient3 x**2
-0.0998, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
AirLoopHVAC:DedicatedOutdoorAirSystem
and Fan:SystemModel
use the same Availability Schedule, so Fan:SystemModel
should be OFF during midnight, but it isn't.
AirLoopHVAC:DedicatedOutdoorAirSystem,
PAU_Tower12_Office_1, !- Name
PAU_Tower12_Office_1 OA System, !- AirLoopHVAC:OutdoorAirSystem Name
LEED_V4_OFFICE_VENTILATION, !- Availability Schedule Name
PAU_Tower12_Office_1 Zone Mixer, !- AirLoopHVAC:Mixer Name
PAU_Tower12_Office_1 Zone Splitter, !- AirLoopHVAC:Splitter Name
4.5, !- Preheat Design Temperature {C}
0.004, !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
17.5, !- Precool Design Temperature {C}
0.012, !- Precool Design Humidity Ratio {kgWater/kgDryAir}
5, !- Number of AirLoopHVAC
VAV_TOWER12_28F, !- AirLoopHVAC 1 Name
VAV_TOWER12_26-27F, !- AirLoopHVAC 2 Name
VAV_TOWER12_25F, !- AirLoopHVAC 3 Name
VAV_TOWER12_23-24F, !- AirLoopHVAC 4 Name
VAV_TOWER12_22F; !- AirLoopHVAC 5 Name