CondenserEnteringReset via PythonPlugin
I would like to reset the condenser water supply temperature via Python Plugin. I have experience with resetting following values: Schedule:Compact > Schedule Value; Pump > Pump Mass Flow Rate ; Fan > Fan Air Mass Flow Rate
What I did: I have found nice examples of condenser water reset in E+ Example folder (files CoolingTower_VariableSpeed_CondEntTempReset.idf CoolingTower_VariableSpeed_CondEntTempReset_MultipleTowers.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint_MultipleTowers.idf
Problem: All these examples use SetpointManager:CondenserEnteringReset or SetpointManager:CondenserEnteringReset:Ideal object to reset the temperature. The issue is I don't know what E+ variable to use to be an actuator handle.
I tried to use OutputVariable as a handle but failed
self.api.exchange.get_actuator_handle(state, "Output:Variable", "System Node Setpoint Temperature", "Condenser Tower", "Outlet Node")
returns -1 (=> it failed)
Could you help me to find right solution for resetting the condenser water temperature?
EDIT: Copying relevant sections from original file CoolingTower_VariableSpeed_IdealCondEntTempSetpoint.idf (see installation/ExampleFiles) where I want to reset the condenser tower outlet temperature.
SetpointManager:CondenserEnteringReset:Ideal,
Condenser Water Loop Setpoint Manager, !- Name
Temperature, !- Control Variable
12, !- Minimum Lift {deltaC}
32, !- Maximum Condenser Entering Water Temperature {C}
Condenser Tower Outlet Node; !- Setpoint Node or NodeList Name
...
CoolingTower:VariableSpeed,
Central Tower, !- Name
Condenser Tower Inlet Node, !- Water Inlet Node Name
Condenser Tower Outlet Node, !- Water Outlet Node Name
YorkCalcUserDefined, !- Model Type
...
Output:Variable,Condenser Tower Outlet Node,System Node Setpoint Temperature,Hourly;
CondenserEnteringReset via PythonPlugin
I would like to reset the condenser water supply temperature via Python Plugin. I have experience with resetting following values: Schedule:Compact > Schedule Value; Pump > Pump Mass Flow Rate ; Fan > Fan Air Mass Flow Rate
What I did: I have found nice examples of condenser water reset in E+ Example folder (files CoolingTower_VariableSpeed_CondEntTempReset.idf CoolingTower_VariableSpeed_CondEntTempReset_MultipleTowers.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint_MultipleTowers.idf
Problem: All these examples use SetpointManager:CondenserEnteringReset or SetpointManager:CondenserEnteringReset:Ideal object to reset the temperature. The issue is I don't know what E+ variable to use to be an actuator handle.
I tried to use OutputVariable as a handle but failed
self.api.exchange.get_actuator_handle(state, "Output:Variable", "System Node Setpoint Temperature", "Condenser Tower", "Outlet Node")
returns -1 (=> it failed)
Could you help me to find right solution for resetting the condenser water temperature?
EDIT: Copying relevant sections from original file CoolingTower_VariableSpeed_IdealCondEntTempSetpoint.idf (see installation/ExampleFiles) where I want to reset the condenser tower outlet temperature.
SetpointManager:CondenserEnteringReset:Ideal,
Condenser Water Loop Setpoint Manager, !- Name
Temperature, !- Control Variable
12, !- Minimum Lift {deltaC}
32, !- Maximum Condenser Entering Water Temperature {C}
Condenser Tower Outlet Node; !- Setpoint Node or NodeList Name
...
CoolingTower:VariableSpeed,
Central Tower, !- Name
Condenser Tower Inlet Node, !- Water Inlet Node Name
Condenser Tower Outlet Node, !- Water Outlet Node Name
YorkCalcUserDefined, !- Model Type
...
Output:Variable,Condenser Tower Outlet Node,System Node Setpoint Temperature,Hourly;
CondenserEnteringReset via PythonPlugin
I would like to reset the condenser water supply temperature via Python Plugin. I have experience with resetting following values: Schedule:Compact > Schedule Value; Pump > Pump Mass Flow Rate ; Fan > Fan Air Mass Flow Rate
What I did: I have found nice examples of condenser water reset in E+ Example folder (files CoolingTower_VariableSpeed_CondEntTempReset.idf CoolingTower_VariableSpeed_CondEntTempReset_MultipleTowers.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint_MultipleTowers.idf
Problem: All these examples use SetpointManager:CondenserEnteringReset or SetpointManager:CondenserEnteringReset:Ideal object to reset the temperature. The issue is I don't know what E+ variable to use to be an actuator handle.
I tried to use OutputVariable as a handle but failed
self.api.exchange.get_actuator_handle(state, "Output:Variable", "System Node Setpoint Temperature", "Condenser Tower", "Outlet Node")
returns -1 (=> it failed)
Could you help me to find right solution for resetting the condenser water temperature?
EDIT: Copying relevant sections from original file CoolingTower_VariableSpeed_IdealCondEntTempSetpoint.idf (see installation/ExampleFiles) where I want to reset the condenser tower outlet temperature.
SetpointManager:CondenserEnteringReset:Ideal,
Condenser Water Loop Setpoint Manager, !- Name
Temperature, !- Control Variable
12, !- Minimum Lift {deltaC}
32, !- Maximum Condenser Entering Water Temperature {C}
Condenser Tower Outlet Node; !- Setpoint Node or NodeList Name
...
CoolingTower:VariableSpeed,
Central Tower, !- Name
Condenser Tower Inlet Node, !- Water Inlet Node Name
Condenser Tower Outlet Node, !- Water Outlet Node Name
YorkCalcUserDefined, !- Model Type
...
Output:Variable,Condenser Tower Outlet Node,System Node Setpoint Temperature,Hourly;
CondenserEnteringReset via PythonPlugin
I would like to reset the condenser water supply temperature via Python Plugin. I have experience with resetting following values: Schedule:Compact > Schedule Value; Pump > Pump Mass Flow Rate ; Fan > Fan Air Mass Flow Rate
What I did: I have found nice examples of condenser water reset in E+ Example folder (files CoolingTower_VariableSpeed_CondEntTempReset.idf CoolingTower_VariableSpeed_CondEntTempReset_MultipleTowers.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint.idf CoolingTower_VariableSpeed_IdealCondEntTempSetpoint_MultipleTowers.idf
Problem: All these examples use SetpointManager:CondenserEnteringReset or SetpointManager:CondenserEnteringReset:Ideal object to reset the temperature. The issue is I don't know what E+ variable to use to be an actuator handle.
I tried to use OutputVariable as a handle but failed
self.api.exchange.get_actuator_handle(state, "Output:Variable", "System Node Setpoint Temperature", "Condenser Tower", "Outlet Node")
returns -1 (=> it failed)
Could you help me to find right solution for resetting the condenser water temperature?