OpenStudio 3.1 erases surfaces when surface matching. Not present in OpenStudio 2.9

See the image below for context. At the top, you'll see the model before surface matching. Below, you'll see the model in OS 2.9 and in 3.1. You'll notice how the boundary condition for the floors changes to Surface for all the surfaces except a sliver that remains adjacent to Ground.

Comparisons

If you look at the roof surfaces, you'll notice this sliver is now missing altogether in OS 3.1.

Missing Sliver

I'm unsure why this is happening. Here is a clue I get when doing the intersect surfaces in OS 3.1

[openstudio.model.Surface] <1> Initial area of surface 'Surface 18' 646.605 does not equal post intersection area 646.605

Link to source in C++ code as far as I can tell. Appears to have something to do with intersection code

Things I have checked:

  • The order in which spaces are matched is identical
  • Both versions of OpenStudio agree upon which spaces intersect.
  • The OpenStudio methods OpenStudio::Model.intersectSurfaces(spaces) and OpenStudio::Model.matchSurfaces(spaces) do not resolve the issue (they made it worse somehow, not sure why).

LINK TO MINIMUM WORKING EXAMPLE:

https://github.com/jugonzal07/stack_overflow_questions/blob/master/unmet_hours/surface_matching_os_2.9_to_3.1/surface_matching_script.rb

Meat of the surface code is under match_spaces on L95

def match_spaces(spaces)

    # Sort spaces for consistency between models
    spaces = sort_spaces(spaces)

    n = spaces.size

    boundingBoxes = []
    (0...n).each do |i|
        boundingBoxes[i] = spaces[i].transformation * spaces[i].boundingBox
    end

    (0...n).each do |i|
        (i+1...n).each do |j|
            next unless boundingBoxes[i].intersects(boundingBoxes[j])
            puts "#{spaces[i].name.to_s} intersects #{spaces[j].name.to_s}"
            spaces[i].intersectSurfaces(spaces[j])
            spaces[i].matchSurfaces(spaces[j])
        end #j
    end #i
end

OpenStudio 3.1 erases surfaces when surface matching. Not present in OpenStudio 2.9

See the image below for context. At the top, you'll see the model before surface matching. Below, you'll see the model in OS 2.9 and in 3.1. You'll notice how the boundary condition for the floors changes to Surface for all the surfaces except a sliver that remains adjacent to Ground.

Comparisons

If you look at the roof surfaces, you'll notice this sliver is now missing altogether in OS 3.1.

Missing Sliver

I'm unsure why this is happening. Here is a clue I get when doing the intersect surfaces surface matching in OS 3.1

[openstudio.model.Surface] <1> Initial area of surface 'Surface 18' 646.605 does not equal post intersection area 646.605

Link to source in C++ code as far as I can tell. Appears to have something to do with intersection codetell

Things I have checked:

  • The order in which spaces are matched is identical
  • Both versions of OpenStudio agree upon which spaces intersect.
  • The OpenStudio methods OpenStudio::Model.intersectSurfaces(spaces) and OpenStudio::Model.matchSurfaces(spaces) do not resolve the issue (they made it worse somehow, not sure why).

LINK TO MINIMUM WORKING EXAMPLE:

https://github.com/jugonzal07/stack_overflow_questions/blob/master/unmet_hours/surface_matching_os_2.9_to_3.1/surface_matching_script.rb

Meat of the surface code is under match_spaces on L95

def match_spaces(spaces)

    # Sort spaces for consistency between models
    spaces = sort_spaces(spaces)

    n = spaces.size

    boundingBoxes = []
    (0...n).each do |i|
        boundingBoxes[i] = spaces[i].transformation * spaces[i].boundingBox
    end

    (0...n).each do |i|
        (i+1...n).each do |j|
            next unless boundingBoxes[i].intersects(boundingBoxes[j])
            puts "#{spaces[i].name.to_s} intersects #{spaces[j].name.to_s}"
            spaces[i].intersectSurfaces(spaces[j])
            spaces[i].matchSurfaces(spaces[j])
        end #j
    end #i
end

OpenStudio 3.1 erases surfaces when surface matching. Not present in OpenStudio 2.9

See the image below for context. At the top, you'll see the model before surface matching. Below, you'll see the model in OS 2.9 and in 3.1. You'll notice how the boundary condition for the floors changes to Surface for all the surfaces except a sliver that remains adjacent to Ground.

Comparisons

If you look at the roof surfaces, you'll notice this sliver is now missing altogether in OS 3.1.

Missing Sliver

I'm unsure why this is happening. Here is a clue I get when doing the surface matching in OS 3.1

[openstudio.model.Surface] <1> Initial area of surface 'Surface 18' 646.605 does not equal post intersection area 646.605

Link to source in C++ code as far as I can tell

Things I have checked:

  • The order in which spaces are matched is identical
  • Both versions of OpenStudio agree upon which spaces intersect.
  • The OpenStudio methods OpenStudio::Model.intersectSurfaces(spaces) and OpenStudio::Model.matchSurfaces(spaces) do not resolve the issue (they made it worse somehow, not sure why).

LINK TO MINIMUM WORKING EXAMPLE:

https://github.com/jugonzal07/stack_overflow_questions/blob/master/unmet_hours/surface_matching_os_2.9_to_3.1/surface_matching_script.rb

Meat of the surface code is under match_spaces on L95

def match_spaces(spaces)

    # Sort spaces for consistency between models
    spaces = sort_spaces(spaces)

    n = spaces.size

    boundingBoxes = []
    (0...n).each do |i|
        boundingBoxes[i] = spaces[i].transformation * spaces[i].boundingBox
    end

    (0...n).each do |i|
        (i+1...n).each do |j|
            next unless boundingBoxes[i].intersects(boundingBoxes[j])
            puts "#{spaces[i].name.to_s} intersects #{spaces[j].name.to_s}"
            spaces[i].intersectSurfaces(spaces[j])
            spaces[i].matchSurfaces(spaces[j])
        end #j
    end #i
end

OpenStudio 3.1 erases surfaces when surface matching. Not present in OpenStudio 2.9

See the image below for context. At the top, you'll see the model before surface matching. Below, you'll see the model in OS 2.9 and in 3.1. You'll notice how the boundary condition for the floors changes to Surface for all the surfaces except a sliver that remains adjacent to Ground.

Comparisons

If you look at the roof surfaces, you'll notice this sliver is now missing altogether in OS 3.1.

Missing Sliver

I'm unsure why this is happening. Here is a clue I get when doing the surface matching in OS 3.1

[openstudio.model.Surface] <1> Initial area of surface 'Surface 18' 646.605 does not equal post intersection area 646.605

Things I have checked:

  • The order in which spaces are matched is identical
  • Both versions of OpenStudio agree upon which spaces intersect.
  • The OpenStudio methods OpenStudio::Model.intersectSurfaces(spaces) and OpenStudio::Model.matchSurfaces(spaces) do not resolve the issue (they made it worse somehow, not sure why).

LINK TO MINIMUM WORKING EXAMPLE:

https://github.com/jugonzal07/stack_overflow_questions/blob/master/unmet_hours/surface_matching_os_2.9_to_3.1/surface_matching_script.rb

Meat of the surface code is under match_spaces on L95L95 https://github.com/jugonzal07/stack_overflow_questions/blob/master/unmet_hours/surface_matching_os_2.9_to_3.1/surface_matching_script.rb

def match_spaces(spaces)

    # Sort spaces for consistency between models
    spaces = sort_spaces(spaces)

    n = spaces.size

    boundingBoxes = []
    (0...n).each do |i|
        boundingBoxes[i] = spaces[i].transformation * spaces[i].boundingBox
    end

    (0...n).each do |i|
        (i+1...n).each do |j|
            next unless boundingBoxes[i].intersects(boundingBoxes[j])
            puts "#{spaces[i].name.to_s} intersects #{spaces[j].name.to_s}"
            spaces[i].intersectSurfaces(spaces[j])
            spaces[i].matchSurfaces(spaces[j])
        end #j
    end #i
end

OpenStudio 3.1 erases surfaces when surface matching. Not present in OpenStudio 2.9

See the image below for context. At the top, you'll see the model before surface matching. Below, you'll see the model in OS 2.9 and in 3.1. You'll notice how the boundary condition for the floors changes to Surface for all the surfaces except a sliver that remains adjacent to Ground.

Comparisons

If you look at the roof surfaces, you'll notice this sliver is now missing altogether in OS 3.1.

Missing Sliver

I'm unsure why this is happening. Here is a clue I get when doing the surface matching in OS 3.1

[openstudio.model.Surface] <1> Initial area of surface 'Surface 18' 646.605 does not equal post intersection area 646.605

Things I have checked:

  • The order in which spaces are matched is identical
  • Both versions of OpenStudio agree upon which spaces intersect.
  • The OpenStudio methods OpenStudio::Model.intersectSurfaces(spaces) and OpenStudio::Model.matchSurfaces(spaces) do not resolve the issue (they made it worse somehow, not sure why).

LINK TO MINIMUM WORKING EXAMPLE:

Meat of the surface code is under match_spaces on L95 https://github.com/jugonzal07/stack_overflow_questions/blob/master/unmet_hours/surface_matching_os_2.9_to_3.1/surface_matching_script.rb

require 'openstudio'

# Helper to load a model in one line
def osload(path)
    translator = OpenStudio::OSVersion::VersionTranslator.new
    ospath = OpenStudio::Path.new(path)
    model = translator.loadModel(ospath)
    if model.empty?
        raise "Path '#{path}' is not a valid path to an OpenStudio Model"
    else
        model = model.get
    end
    return model
end

# Class created for the sole purpose of making spaces comparable.
# Sorting is dependent on space bounding box boundaries
class SpaceSort

    attr_accessor :space, :min_x, :max_x, :min_y, :max_y, :min_z, :max_z

    def initialize(os_space)

        bounding_box = os_space.boundingBox
        @space = os_space
        @min_x = bounding_box.minX.to_f
        @max_x = bounding_box.maxX.to_f
        @min_y = bounding_box.minY.to_f
        @max_y = bounding_box.maxY.to_f
        @min_z = bounding_box.minZ.to_f
        @max_z = bounding_box.maxZ.to_f

    end

    # Sorting for SpaceSort objects follows this hierarchy (from lowest to highest)
    # -min_x, max_x, min_y, max_y, min_z, max_z
    # NOTE: -1 = less than
    #        1 = greater than
    #        0 = equal to
    def <=>(other_space_sort)

        if @min_x < other_space_sort.min_x
            return -1
        elsif @min_x > other_space_sort.min_x
            return 1
        elsif @max_x < other_space_sort.max_x
            return -1
        elsif @max_x > other_space_sort.max_x
            return 1
        elsif @min_y < other_space_sort.min_y
            return -1
        elsif @min_y > other_space_sort.min_y
            return 1
        elsif @max_y < other_space_sort.max_y
            return -1
        elsif @max_y > other_space_sort.max_y
            return 1
        elsif @min_z < other_space_sort.min_z
            return -1
        elsif @min_z > other_space_sort.min_z
            return 1
        elsif @max_z < other_space_sort.max_z
            return -1
        elsif @max_z > other_space_sort.max_z
            return 1
        else
            return 0 #bounding boxes are identical
        end
    end
end

def sort_spaces(spaces)

    # Array of SpaceSort objects, used to sort spaces by their bounding boxes
    space_sort_list = []

    # Construct SurfaceSort objects for sorting surfaces
    spaces.each do |space|
        space_sort_list << SpaceSort.new(space)
    end

    # sort SurfaceSort objects by their bounding box boundaries
    sorted_list = space_sort_list.sort()

    sorted_spaces = []

    # Extract spaces from sorted SurfaceSort objects
    sorted_list.each do |space_sort|
        sorted_spaces << space_sort.space
    end

    return(sorted_spaces)
end

def match_spaces(spaces)

    # Sort spaces for consistency between models
    spaces = sort_spaces(spaces)

    n = spaces.size

    boundingBoxes = []
    (0...n).each do |i|
        boundingBoxes[i] = spaces[i].transformation * spaces[i].boundingBox
    end

    (0...n).each do |i|
        (i+1...n).each do |j|
            next unless boundingBoxes[i].intersects(boundingBoxes[j])
            puts "#{spaces[i].name.to_s} intersects #{spaces[j].name.to_s}"
            spaces[i].intersectSurfaces(spaces[j])
            spaces[i].matchSurfaces(spaces[j])
        end #j
    end #i
end


file_name = 'before_matching_3.1.osm'

model = osload(file_name)

match_spaces(model.getSpaces)

# spaces = OpenStudio::Model::SpaceVector.new
# model.getSpaces.each do |space|
#   spaces << space
# end

#OpenStudio::Model.intersectSurfaces(spaces)
#OpenStudio::Model.matchSurfaces(spaces)

OpenStudio 3.1 erases surfaces when surface matching. Not present in OpenStudio 2.9

When doing regression checks on updating to OpenStudio 3.1 from 2.9 I noticed big shifts in energy. Upon inspection, I found that L shaped buildings had surface matching issues that were not present in our OS 2.9 models. This happens upon the intersection of a plenum space with a perimeter and core section of the building.

See the image below for context. to show what I mean. At the top, you'll see the model before surface matching. Below, you'll see the model in OS 2.9 and in 3.1. You'll notice how the boundary condition for the floors changes to Surface for all the surfaces except a sliver that remains adjacent to Ground.

Comparisons

If you look at the roof surfaces, you'll notice this sliver is now missing altogether in OS 3.1.2.9.

Missing Sliver

I'm unsure why this is happening. Here is a clue I get when doing the surface matching in OS 3.1

[openstudio.model.Surface] <1> Initial area of surface 'Surface 18' 646.605 does not equal post intersection area 646.605

Things I have checked:

  • The order in which spaces are matched is identical
  • Both versions of OpenStudio agree upon which spaces intersect.
  • The OpenStudio methods OpenStudio::Model.intersectSurfaces(spaces) and OpenStudio::Model.matchSurfaces(spaces) do not resolve the issue (they made it worse somehow, not sure why).

LINK TO MINIMUM WORKING EXAMPLE:

Meat of the surface code is under match_spaces on L95 https://github.com/jugonzal07/stack_overflow_questions/blob/master/unmet_hours/surface_matching_os_2.9_to_3.1/surface_matching_script.rb

require 'openstudio'

# Helper to load a model in one line
def osload(path)
    translator = OpenStudio::OSVersion::VersionTranslator.new
    ospath = OpenStudio::Path.new(path)
    model = translator.loadModel(ospath)
    if model.empty?
        raise "Path '#{path}' is not a valid path to an OpenStudio Model"
    else
        model = model.get
    end
    return model
end

# Class created for the sole purpose of making spaces comparable.
# Sorting is dependent on space bounding box boundaries
class SpaceSort

    attr_accessor :space, :min_x, :max_x, :min_y, :max_y, :min_z, :max_z

    def initialize(os_space)

        bounding_box = os_space.boundingBox
        @space = os_space
        @min_x = bounding_box.minX.to_f
        @max_x = bounding_box.maxX.to_f
        @min_y = bounding_box.minY.to_f
        @max_y = bounding_box.maxY.to_f
        @min_z = bounding_box.minZ.to_f
        @max_z = bounding_box.maxZ.to_f

    end

    # Sorting for SpaceSort objects follows this hierarchy (from lowest to highest)
    # -min_x, max_x, min_y, max_y, min_z, max_z
    # NOTE: -1 = less than
    #        1 = greater than
    #        0 = equal to
    def <=>(other_space_sort)

        if @min_x < other_space_sort.min_x
            return -1
        elsif @min_x > other_space_sort.min_x
            return 1
        elsif @max_x < other_space_sort.max_x
            return -1
        elsif @max_x > other_space_sort.max_x
            return 1
        elsif @min_y < other_space_sort.min_y
            return -1
        elsif @min_y > other_space_sort.min_y
            return 1
        elsif @max_y < other_space_sort.max_y
            return -1
        elsif @max_y > other_space_sort.max_y
            return 1
        elsif @min_z < other_space_sort.min_z
            return -1
        elsif @min_z > other_space_sort.min_z
            return 1
        elsif @max_z < other_space_sort.max_z
            return -1
        elsif @max_z > other_space_sort.max_z
            return 1
        else
            return 0 #bounding boxes are identical
        end
    end
end

def sort_spaces(spaces)

    # Array of SpaceSort objects, used to sort spaces by their bounding boxes
    space_sort_list = []

    # Construct SurfaceSort objects for sorting surfaces
    spaces.each do |space|
        space_sort_list << SpaceSort.new(space)
    end

    # sort SurfaceSort objects by their bounding box boundaries
    sorted_list = space_sort_list.sort()

    sorted_spaces = []

    # Extract spaces from sorted SurfaceSort objects
    sorted_list.each do |space_sort|
        sorted_spaces << space_sort.space
    end

    return(sorted_spaces)
end

def match_spaces(spaces)

    # Sort spaces for consistency between models
    spaces = sort_spaces(spaces)

    n = spaces.size

    boundingBoxes = []
    (0...n).each do |i|
        boundingBoxes[i] = spaces[i].transformation * spaces[i].boundingBox
    end

    (0...n).each do |i|
        (i+1...n).each do |j|
            next unless boundingBoxes[i].intersects(boundingBoxes[j])
            puts "#{spaces[i].name.to_s} intersects #{spaces[j].name.to_s}"
            spaces[i].intersectSurfaces(spaces[j])
            spaces[i].matchSurfaces(spaces[j])
        end #j
    end #i
end


file_name = 'before_matching_3.1.osm'

model = osload(file_name)

match_spaces(model.getSpaces)

# spaces = OpenStudio::Model::SpaceVector.new
# model.getSpaces.each do |space|
#   spaces << space
# end

#OpenStudio::Model.intersectSurfaces(spaces)
#OpenStudio::Model.matchSurfaces(spaces)