Revision history [back]
Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load (from the Facility Component Load Summary report) is (significantly) higher than the sum of the non-coincidental zone heating load peaks (pulled from the Zone Component Load Summaries), which should not be the case.
Has anyone had this issue? Any solution?
Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
Context:
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries.
The building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load (from the Facility Component Load Summary report) is (significantly) higher than the sum of the non-coincidental zone heating load peaks (pulled from the Zone Component Load Summaries), which should not be the case.
Has anyone had this issue? Any solution?
Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
Context:
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries.
The building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load (from the Facility Component Load Summary report) is (significantly) higher than the sum of the non-coincidental zone heating load peaks (pulled from the Zone Component Load Summaries), which should not be the case.
Has anyone had this issue? Any solution?
Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
Context:
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries.
The building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load (from the Facility Component Load Summary report) is (significantly) higher than the sum of the non-coincidental zone heating load peaks (pulled from the Zone Component Load Summaries), which should not be the case.
Has anyone had this issue? Any solution?
Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
Context:
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries.
The building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load (from from the Facility Component Load Summary report) report is (significantly) higher than the sum of the non-coincidental zone heating load peaks (pulled pulled from the Zone Component Load Summaries), Summaries, which should not be the case.
Has anyone had this issue? Any solution?
Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
Context:
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries.
The building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries, which should not be the case.
Has anyone had this issue? Any solution?
Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
Context:
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries.
The building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries, which should not be the case. Summaries. Has anyone had this issue, and maybe a resolution?
Has anyone had this issue? Any solution?
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries. Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
Context: For context: the
The attached image shows Facility Summary, with the right-most two columns showing the sum from Zone Summaries.
The building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries. Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
For context: the building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries. Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
For context: the building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries. Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
For context: the building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries. Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
For context: the building is modeled in v8.8 with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries. Another anomaly is that the “Time of Peak Load” is blank in the Facility Summary.
For context: the building is modeled with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution? resolution?
The attached image shows the Facility Summary, with the right-most two columns showing the sum from Zone Summaries. Another anomaly is that in the Facility Component Load Summary report, the “Time of Peak Load” is blank in the Facility Summary.blank...
For context: the building is modeled with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
Another anomaly is that in the Facility Component Load Summary report, the “Time of Peak Load” is blank...
For context: the building is modeled with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
Another anomaly is that in the Facility Component Load Summary report, the “Time of Peak Load” is blank...
For context: the building is modeled with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
Another anomaly is that in the Facility Component Load Summary report, the “Time of Peak Load” is blank...
For context: the building is modeled with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.
E+ 8.8 Block Load: Coincidental Heating Load > Noncoincidental
I'm looking to output (coincidental) building block load envelope components using an E+ model.
The issue is that the coincidental block heating load from the Facility Component Load Summary report is (significantly) higher than the sum of the non-coincidental zone heating load peaks pulled from the Zone Component Load Summaries. Has anyone had this issue, and maybe a resolution?
Another anomaly is that in the Facility Component Load Summary report, the “Time of Peak Load” is blank...
For context: the building is modeled with district heating/cooling, ideal loads air systems, 0 internal loads, annual heating design day object entered for SizingPeriod:DesignDay, and all options in the SimulationControl object set to “yes”.