Who uses ZoneMixing?
I did case studies with a very simple model in order to check the function of ZoneMixing and ZoneCrossMixing.
Two zones (ZoneA and ZoneB) are adjacent to each other through an air wall. They have different cooling setpoint: 30°C for ZoneA and 24°C for ZoneB. Cooling system is HVACTemplate:Zone:IdealLoadAirSystem. I simulated 7 cases with different conditions. The table below summarises each condition and simulation result (annual cooling end use). "AtoB" means that ZoneA is the "source" zone and ZoneB is the "receiving" zone. The same Design Flow Rate was specified inZoneMixing and ZoneCrossMixing, and the schedule was always on.

Case2 and Case4 resulted in lower cooling end use than Case1(No mixing), which means that the cool air in ZoneB was distributed to ZoneA and helped to cool ZoneA, but no additional cooling energy was used in the HVAC system in ZoneB.
On the other hand, Case3 has mush higher cooling end use than Case1(No mixing), which means that the hot air in ZoneA was distributed to ZoneB and the HVAC system in ZoneB required much cooling energy.
These results are consistent with what is described in I/O Reference and EngineeringReference. i.e.,

But then, who would use ZoneMixing? It generates cool/hot air from nothing and completely destroys energy balance and energy simulation.
My case study model has an extreme temperature difference between two zones, but even if the temperature difference is very small, the difference causes inaccuracy of energy simulation.
ZoneCrossMixing makes sense. To me, ZoneMixing looks like a degraded version of ZoneCrossMixing. Is there any case where ZoneMixing would be more useful than ZoneCrossMixing?
P.S.
This post script illustrates my interpretation of @Aaron Boranian 's answer (2 examples of using ZoneMixing). Could you please correct me if I'm wrong?
1. Atrium
What the purpose of this modelling? - I guess it is to estimate how hot the upper part of the atrium will be in summer. However, I think the upper part of the atrium will be Cooled because the air with the same temparature as the lower part of the atrium that is air-conditioned is supplied to the upper part. It is an opposite phenomenon of what happens in actual atriums. How can we solve this problem? I think ZoneMixing is not suitable for modelling the upward airflow due to buoyancy.
Or we may want to know how cold the lower part of the atrium will be in winter, but I think we can't model it because the lower part of the atrium("source" zone) is not affected at all by ZoneMixing. In this case, I think the atrium should not be divided into lower part and upper part, it should be modelled as a single zone.

2. Office and Corridor
Again, what is the purpose of this modelling? If the corridor is not air-conditioned, normally we don't care about the air temperature of the corridor. If the corridor is air-conditioned, the "spilling over" air will help to reduce cooling energy that is consumed in the corridor a bit, but the cooling energy that the spilling over air has comes from nowhere because the office(source zone) is not affected at all by using ZoneMixing. The energy balance is broken. In this case, the total cooling energy consumption will be lower than actual. In order to keep the energy balance, I think we should use ZoneCrossMixing even though the actual flow of the spilling over air is one-way.

Who uses ZoneMixing?
I did case studies with a very simple model in order to check the function of ZoneMixing and ZoneCrossMixing.
Two zones (ZoneA and ZoneB) are adjacent to each other through an air wall. They have different cooling setpoint: 30°C for ZoneA and 24°C for ZoneB. Cooling system is HVACTemplate:Zone:IdealLoadAirSystem. I simulated 7 cases with different conditions. The table below summarises each condition and simulation result (annual cooling end use). "AtoB" means that ZoneA is the "source" zone and ZoneB is the "receiving" zone. The same Design Flow Rate was specified inZoneMixing and ZoneCrossMixing, and the schedule was always on.

Case2 and Case4 resulted in lower cooling end use than Case1(No mixing), which means that the cool air in ZoneB was distributed to ZoneA and helped to cool ZoneA, but no additional cooling energy was used in the HVAC system in ZoneB.
On the other hand, Case3 has mush higher cooling end use than Case1(No mixing), which means that the hot air in ZoneA was distributed to ZoneB and the HVAC system in ZoneB required much cooling energy.
These results are consistent with what is described in I/O Reference and EngineeringReference. i.e.,

But then, who would use ZoneMixing? It generates cool/hot air from nothing and completely destroys energy balance and energy simulation.
My case study model has an extreme temperature difference between two zones, but even if the temperature difference is very small, the difference causes inaccuracy of energy simulation.
ZoneCrossMixing makes sense. To me, ZoneMixing looks like a degraded version of ZoneCrossMixing. Is there any case where ZoneMixing would be more useful than ZoneCrossMixing?
P.S.
This post script illustrates my interpretation of @Aaron Boranian 's answer (2 examples of using ZoneMixing). Could you please correct me if I'm wrong?
1. Atrium
What the purpose of this modelling? - I guess it is to estimate how hot the upper part of the atrium will be in summer. However, I think the upper part of the atrium will be Cooled because the air with the same temparature as the lower part of the atrium that is air-conditioned is supplied to the upper part. It is an opposite phenomenon of what happens in actual atriums. How can we solve this problem? I think ZoneMixing is not suitable for modelling the upward airflow due to buoyancy.
Or we may want to know how cold the lower part of the atrium will be in winter, but I think we can't model it because the lower part of the atrium("source" zone) is not affected at all by ZoneMixing. In this case, I think the atrium should not be divided into lower part and upper part, it should be modelled as a single zone.

2. Office and Corridor
Again, what is the purpose of this modelling? If the corridor is not air-conditioned, normally we don't care about the air temperature of the corridor. If the corridor is air-conditioned, the "spilling over" air will help to reduce cooling energy that is consumed in the corridor a bit, but the cooling energy that the spilling over air has comes from nowhere because the office(source zone) is not affected at all by using ZoneMixing. The energy balance is broken. In this case, the total cooling energy consumption will be lower than actual. In order to keep the energy balance, I think we should use ZoneCrossMixing even though the actual flow of the spilling over air is one-way.

Who uses ZoneMixing?
I did case studies with a very simple model in order to check the function of ZoneMixing and ZoneCrossMixing.
Two zones (ZoneA and ZoneB) are adjacent to each other through an air wall. They have different cooling setpoint: 30°C for ZoneA and 24°C for ZoneB. Cooling system is HVACTemplate:Zone:IdealLoadAirSystem. I simulated 7 cases with different conditions. The table below summarises each condition and simulation result (annual cooling end use). "AtoB" means that ZoneA is the "source" zone and ZoneB is the "receiving" zone. The same Design Flow Rate was specified inZoneMixing and ZoneCrossMixing, and the schedule was always on.

Case2 and Case4 resulted in lower cooling end use than Case1(No mixing), which means that the cool air in ZoneB was distributed to ZoneA and helped to cool ZoneA, but no additional cooling energy was used in the HVAC system in ZoneB.
On the other hand, Case3 has mush higher cooling end use than Case1(No mixing), which means that the hot air in ZoneA was distributed to ZoneB and the HVAC system in ZoneB required much cooling energy.
These results are consistent with what is described in I/O Reference and EngineeringReference. i.e.,

But then, who would use ZoneMixing? It generates cool/hot air from nothing and completely destroys energy balance and energy simulation.
My case study model has an extreme temperature difference between two zones, but even if the temperature difference is very small, the difference causes inaccuracy of energy simulation.
ZoneCrossMixing makes sense. To me, ZoneMixing looks like a degraded version of ZoneCrossMixing. Is there any case where ZoneMixing would be more useful than ZoneCrossMixing?
P.S.
This post script illustrates my interpretation of @Aaron Boranian 's answer (2 examples of using ZoneMixing). Could you please correct me if I'm wrong?
1. Atrium
What the purpose of this modelling? - I guess it is to estimate how hot the upper part of the atrium will be in summer. However, I think the upper part of the atrium will be Cooled because the air with the same temparature as the lower part of the atrium that is air-conditioned is supplied to the upper part. It is an opposite phenomenon of what happens in actual atriums. How can we solve this problem? I think ZoneMixing is not suitable for modelling the upward airflow due to buoyancy.
Or we may want to know how cold the lower part of the atrium will be in winter, but I think we can't model it because the lower part of the atrium("source" zone) is not affected at all by ZoneMixing. In this case, I think the atrium should not be divided into lower part and upper part, it should be modelled as a single zone.

2. Office and Corridor
Again, what is the purpose of this modelling? If the corridor is not air-conditioned, normally we don't care about the air temperature of the corridor. If the corridor is air-conditioned, the "spilling over" air will help to reduce cooling energy that is consumed in the corridor a bit, but the cooling energy that the spilling over air has comes from nowhere because the office(source zone) is not affected at all by using ZoneMixing. The energy balance is broken. In this case, the total cooling energy consumption will be lower than actual. In order to keep the energy balance, I think we should use ZoneCrossMixing even though the actual flow of the spilling over air is one-way.

Who uses ZoneMixing?
I did case studies with a very simple model in order to check the function of ZoneMixing and ZoneCrossMixing.
Two zones (ZoneA and ZoneB) are adjacent to each other through an air wall. They have different cooling setpoint: 30°C for ZoneA and 24°C for ZoneB. Cooling system is HVACTemplate:Zone:IdealLoadAirSystem. I simulated 7 cases with different conditions. The table below summarises each condition and simulation result (annual cooling end use). "AtoB" means that ZoneA is the "source" zone and ZoneB is the "receiving" zone. The same Design Flow Rate was specified inZoneMixing and ZoneCrossMixing, and the schedule was always on.

Case2 and Case4 resulted in lower cooling end use than Case1(No mixing), which means that the cool air in ZoneB was distributed to ZoneA and helped to cool ZoneA, but no additional cooling energy was used in the HVAC system in ZoneB.
On the other hand, Case3 has mush higher cooling end use than Case1(No mixing), which means that the hot air in ZoneA was distributed to ZoneB and the HVAC system in ZoneB required much cooling energy.
These results are consistent with what is described in I/O Reference and EngineeringReference. i.e.,


But then, who would use ZoneMixing? It generates cool/hot air from nothing and completely destroys energy balance and energy simulation.
My case study model has an extreme temperature difference between two zones, but even if the temperature difference is very small, the difference causes inaccuracy of energy simulation.
ZoneCrossMixing makes sense. To me, ZoneMixing looks like a degraded version of ZoneCrossMixing. Is there any a case where ZoneMixing would be more useful than ZoneCrossMixing?