Solving Plant temperatures are getting far too hot
Hello,
Good day to all.
I am modeling an HVAC system for an offices building with 8 floors which has several AHUs and FCUs installed. The simulation stops with the following error (Copied as is):
** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities
** ~~~ ** PlantLoop Name (DemandSide)= HOT WATER LOOP
** ~~~ ** PlantLoop Setpoint Temperature=67.0 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
** ~~~ ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) "NODE 134" has temperature=300.1 {C}
** ~~~ ** PlantLoop Inlet Node (DemandSide) "NODE 133" has temperature=300.2 {C}
** ~~~ ** PlantLoop Minimum Temperature=0.0 {C}
** ~~~ ** PlantLoop Maximum Temperature=100.0 {C}
** ~~~ ** PlantLoop Flow Request (SupplySide)=6.9 {kg/s}
** ~~~ ** PlantLoop Flow Request (DemandSide)=0.6 {kg/s}
** ~~~ ** PlantLoop Node (DemandSide) "NODE 134" has mass flow rate =0.6 {kg/s}
** ~~~ ** PlantLoop PumpHeat (SupplySide)=1982.2 {W}
** ~~~ ** PlantLoop PumpHeat (DemandSide)=185.5 {W}
** ~~~ ** PlantLoop Cooling Demand=6855817.6 {W}
** ~~~ ** PlantLoop Heating Demand=0.0 {W}
** ~~~ ** PlantLoop Demand not Dispatched=0.0 {W}
** ~~~ ** PlantLoop Unmet Demand=-6855817.6 {W}
** ~~~ ** PlantLoop Capacity=411062.5 {W}
** ~~~ ** PlantLoop Capacity (SupplySide)=411062.5 {W}
** ~~~ ** PlantLoop Capacity (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Operation Scheme=HOT WATER LOOP OPERATION SCHEMES
** ~~~ ** PlantLoop Operation Dispatched Load = 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (SupplySide)= 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
I read the other posts asking questions related to what I am asking too but I wasn't able to locate the problem.
The following are photos for the supply/demand of the loop (There are a lot of heating coils so I took two screenshots showing the essentials):

The outlet node supply side set point is set to 80 C. The pumps are intermittent. Both AHUs and FCUs coils inlet water temperatures are set to 80 C and outlet water temperatures to 69 C. The AHUs coils capacities range between 5 kw to 10 kw (I have about 11 coils for the AHUs). The boiler design flow rate is auto-sized. The plant design loop exit temperature is 80 C and loop design temperature difference is 11 C.
I can't seem to solve my problem. Can you assist ?
Many thanks in advance.
Solving Plant temperatures are getting far too hot
Hello,
Good day to all.
I am modeling an HVAC system for an offices building with 8 floors which has several AHUs and FCUs installed. The simulation stops with the following error (Copied as is):
** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities
** ~~~ ** PlantLoop Name (DemandSide)= HOT WATER LOOP
** ~~~ ** PlantLoop Setpoint Temperature=67.0 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
** ~~~ ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) "NODE 134" has temperature=300.1 {C}
** ~~~ ** PlantLoop Inlet Node (DemandSide) "NODE 133" has temperature=300.2 {C}
** ~~~ ** PlantLoop Minimum Temperature=0.0 {C}
** ~~~ ** PlantLoop Maximum Temperature=100.0 {C}
** ~~~ ** PlantLoop Flow Request (SupplySide)=6.9 {kg/s}
** ~~~ ** PlantLoop Flow Request (DemandSide)=0.6 {kg/s}
** ~~~ ** PlantLoop Node (DemandSide) "NODE 134" has mass flow rate =0.6 {kg/s}
** ~~~ ** PlantLoop PumpHeat (SupplySide)=1982.2 {W}
** ~~~ ** PlantLoop PumpHeat (DemandSide)=185.5 {W}
** ~~~ ** PlantLoop Cooling Demand=6855817.6 {W}
** ~~~ ** PlantLoop Heating Demand=0.0 {W}
** ~~~ ** PlantLoop Demand not Dispatched=0.0 {W}
** ~~~ ** PlantLoop Unmet Demand=-6855817.6 {W}
** ~~~ ** PlantLoop Capacity=411062.5 {W}
** ~~~ ** PlantLoop Capacity (SupplySide)=411062.5 {W}
** ~~~ ** PlantLoop Capacity (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Operation Scheme=HOT WATER LOOP OPERATION SCHEMES
** ~~~ ** PlantLoop Operation Dispatched Load = 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (SupplySide)= 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
I read the other posts asking questions related to what I am asking too but I wasn't able to locate the problem.
The following are photos for the supply/demand of the loop (There are a lot of heating coils so I took two screenshots showing the essentials):

The outlet node supply side set point is set to 80 C. The pumps are intermittent. Both AHUs and FCUs coils inlet water temperatures are set to 80 C and outlet water temperatures to 69 C. The AHUs coils capacities range between 5 kw to 10 kw (I have about 11 coils for the AHUs). The boiler design flow rate is auto-sized. The plant design loop exit temperature is 80 C and loop design temperature difference is 11 C.
I can't seem to solve my problem. Can you assist ?
Many thanks in advance.
Solving Plant temperatures are getting far too hot
Hello,
Good day to all.
I am modeling an HVAC system for an offices building with 8 floors which has several AHUs and FCUs installed. The simulation stops with the following error (Copied as is):
** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities
** ~~~ ** PlantLoop Name (DemandSide)= HOT WATER LOOP
** ~~~ ** PlantLoop Setpoint Temperature=67.0 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
** ~~~ ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) "NODE 134" has temperature=300.1 {C}
** ~~~ ** PlantLoop Inlet Node (DemandSide) "NODE 133" has temperature=300.2 {C}
** ~~~ ** PlantLoop Minimum Temperature=0.0 {C}
** ~~~ ** PlantLoop Maximum Temperature=100.0 {C}
** ~~~ ** PlantLoop Flow Request (SupplySide)=6.9 {kg/s}
** ~~~ ** PlantLoop Flow Request (DemandSide)=0.6 {kg/s}
** ~~~ ** PlantLoop Node (DemandSide) "NODE 134" has mass flow rate =0.6 {kg/s}
** ~~~ ** PlantLoop PumpHeat (SupplySide)=1982.2 {W}
** ~~~ ** PlantLoop PumpHeat (DemandSide)=185.5 {W}
** ~~~ ** PlantLoop Cooling Demand=6855817.6 {W}
** ~~~ ** PlantLoop Heating Demand=0.0 {W}
** ~~~ ** PlantLoop Demand not Dispatched=0.0 {W}
** ~~~ ** PlantLoop Unmet Demand=-6855817.6 {W}
** ~~~ ** PlantLoop Capacity=411062.5 {W}
** ~~~ ** PlantLoop Capacity (SupplySide)=411062.5 {W}
** ~~~ ** PlantLoop Capacity (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Operation Scheme=HOT WATER LOOP OPERATION SCHEMES
** ~~~ ** PlantLoop Operation Dispatched Load = 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (SupplySide)= 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
I read the other posts asking questions related to what I am asking too but I wasn't able to locate the problem.
The following are photos for the supply/demand of the loop (There are a lot of heating coils so I took two screenshots showing the essentials):

The outlet node supply side set point is set to 80 C. The pumps are intermittent. Both AHUs and FCUs coils inlet water temperatures are set to 80 C and outlet water temperatures to 69 C. The AHUs coils capacities range between 5 kw to 10 kw (I have about 11 coils for the AHUs). The boiler design flow rate is auto-sized. The plant design loop exit temperature is 80 C and loop design temperature difference is 11 C.
I can't seem to solve my problem. Can you assist ?
Many thanks in advance.
Solving Plant temperatures are getting far too hot
Hello,
Good day to all.
I am modeling an HVAC system for an offices building with 8 floors which has several AHUs and FCUs installed. The simulation stops with the following error (Copied as is):
** QUOTE
*
Severe* ~~~ *
PlantLoop Name (DemandSide)= HOT WATER* ~~~ *
PlantLoop Setpoint Temperature=67.0* ~~~ *
PlantLoop Inlet Node (SupplySide) does not have a* ~~~ *
PlantLoop Inlet Node (DemandSide) does not have a* ~~~ *
PlantLoop Outlet Node (SupplySide) has a* ~~~ *
PlantLoop Outlet Node (DemandSide) does not have a* ~~~ *
PlantLoop Outlet Node (DemandSide) "NODE 134" has temperature=300.1* ~~~ *
PlantLoop Inlet Node (DemandSide) "NODE 133" has temperature=300.2* ~~~ *
PlantLoop Minimum Temperature=0.0* ~~~ *
PlantLoop Maximum Temperature=100.0* ~~~ *
PlantLoop Flow Request (SupplySide)=6.9* ~~~ *
PlantLoop Flow Request (DemandSide)=0.6* ~~~ *
PlantLoop Node (DemandSide) "NODE 134" has mass flow rate =0.6* ~~~ *
PlantLoop PumpHeat (SupplySide)=1982.2* ~~~ *
PlantLoop PumpHeat (DemandSide)=185.5* ~~~ *
PlantLoop Cooling Demand=6855817.6* ~~~ *
PlantLoop Heating Demand=0.0* ~~~ *
PlantLoop Demand not Dispatched=0.0* ~~~ *
PlantLoop Unmet Demand=-6855817.6* ~~~ *
PlantLoop Capacity=411062.5* ~~~ *
PlantLoop Capacity (SupplySide)=411062.5* ~~~ *
PlantLoop Capacity (DemandSide)=0.0* ~~~ *
PlantLoop Operation Scheme=HOT WATER LOOP OPERATION* ~~~ *
PlantLoop Operation Dispatched Load = 0.0* ~~~ *
PlantLoop Operation Dispatched Load (SupplySide)= 0.0* ~~~ *
PlantLoop Operation Dispatched Load (DemandSide)= 0.0UNQUOTE
I read the other posts asking questions related to what I am asking too but I wasn't able to locate the problem.
The following are photos for the supply/demand of the loop (There are a lot of heating coils so I took two screenshots showing the essentials):

The outlet node supply side set point is set to 80 C. The pumps are intermittent. Both AHUs and FCUs coils inlet water temperatures are set to 80 C and outlet water temperatures to 69 C. The AHUs coils capacities range between 5 kw to 10 kw (I have about 11 coils for the AHUs). The boiler design flow rate is auto-sized. The plant design loop exit temperature is 80 C and loop design temperature difference is 11 C.
I can't seem to solve my problem. Can you assist ?
Many thanks in advance.