Revision history [back]
EMS Actuator no change in mass flow rate.
Hi,
I'm trying to control both the setpoint temperature and the mass flow rate of a 5 zone HVAC system. You find the IDF here https://drive.google.com/file/d/1hjnxdoUBych6X7eQp_3Pkk6Z7VWxAoIs/view?usp=sharing.
I can change and the supply setpoint temperature and the overall supply mass flow rate, but I cannot change the individual zone mass flow rate.
EnergyManagementSystem:Actuator,
mdot_fan, !- Name
SUPPLY FAN 1, !- Actuated Component Unique Name
Fan, !- Actuated Component Type
Fan Air mass Flow Rate; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
T_in_air, !- Name
VAV SYS 1 OUTLET NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Temperature Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_air, !- Name
MIXED AIR NODE 1, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_1, !- Name
SPACE1-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_2, !- Name
SPACE2-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_3, !- Name
SPACE3-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_4, !- Name
SPACE4-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_5, !- Name
SPACE5-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Program,
setActions, !- Name
SET T_in_air = 20, !- Program Line 1
SET mdot_fan= mdot_1 + mdot_2 + mdot_3 + mdot_4 + mdot_5; !- Program Line 2
EnergyManagementSystem:Program,
setmdot, !- Name
SET mdot_1 = 0.25, !- Program Line 1
SET mdot_2 = 0.25, !- Program Line 2
SET mdot_3 = 0.25, !- A4
SET mdot_4 = 0.25, !- A5
SET mdot_5 = 0.25; !- A6
EnergyManagementSystem:ProgramCallingManager,
mdot, !- Name
InsideHVACSystemIterationLoop, !- EnergyPlus Model Calling Point
setmdot; !- Program Name 1
EnergyManagementSystem:ProgramCallingManager,
act, !- Name
InsideHVACSystemIterationLoop, !- EnergyPlus Model Calling Point
setActions; !- Program Name 1
Looking at the EDD file I see that for each zone I can use those actuators but none of them makes the change in the zone mass flow rate.
SPACE1-1 IN NODE
SPACE1-1 NODE
SPACE1-1 OUT NODE
SPACE1-1 ZONE COIL AIR IN NODE
SPACE1-1 ATU IN NODE
How can I solve this issue?
EMS Actuator no change in mass flow rate.
Hi,
I'm trying to control both the setpoint temperature and the mass flow rate of a 5 zone HVAC system. You find the IDF here https://drive.google.com/file/d/1hjnxdoUBych6X7eQp_3Pkk6Z7VWxAoIs/view?usp=sharing.
I can change and the supply setpoint temperature and the overall supply mass flow rate, but I cannot change the individual zone mass flow rate.
EnergyManagementSystem:Actuator,
mdot_fan, !- Name
SUPPLY FAN 1, !- Actuated Component Unique Name
Fan, !- Actuated Component Type
Fan Air mass Flow Rate; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
T_in_air, !- Name
VAV SYS 1 OUTLET NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Temperature Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_air, !- Name
MIXED AIR NODE 1, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_1, !- Name
SPACE1-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_2, !- Name
SPACE2-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_3, !- Name
SPACE3-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_4, !- Name
SPACE4-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Actuator,
mdot_5, !- Name
SPACE5-1 ZONE COIL AIR IN NODE, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Setpoint; !- Actuated Component Control Type
EnergyManagementSystem:Program,
setActions, !- Name
SET T_in_air = 20, !- Program Line 1
SET mdot_fan= mdot_1 + mdot_2 + mdot_3 + mdot_4 + mdot_5; !- Program Line 2
EnergyManagementSystem:Program,
setmdot, !- Name
SET mdot_1 = 0.25, !- Program Line 1
SET mdot_2 = 0.25, !- Program Line 2
SET mdot_3 = 0.25, !- A4
SET mdot_4 = 0.25, !- A5
SET mdot_5 = 0.25; !- A6
EnergyManagementSystem:ProgramCallingManager,
mdot, !- Name
InsideHVACSystemIterationLoop, !- EnergyPlus Model Calling Point
setmdot; !- Program Name 1
EnergyManagementSystem:ProgramCallingManager,
act, !- Name
InsideHVACSystemIterationLoop, !- EnergyPlus Model Calling Point
setActions; !- Program Name 1
Looking at the EDD file I see that for each zone I can use those actuators but none of them makes the change in the zone mass flow rate.
SPACE1-1 IN NODE
SPACE1-1 NODE
SPACE1-1 OUT NODE
SPACE1-1 ZONE COIL AIR IN NODE
SPACE1-1 ATU IN NODE
How can I solve this issue?issue?
SPACE1-1 ZONE COIL AIR IN NODE