Revision history  [back]

Shading not working when using simple glazing

I have constructed my exterior window and exterior window with an interior blind. I have defined the blind material. I have defined the shading control. I have the simple glazing system. Finally I have defined the construction as "Exterior Window" in the FenestrationSurface:Detailed for each window. When I run the simulations, I get the same results as an with unshaded windows. What am I missing?

    WindowMaterial:SimpleGlazingSystem,
       Glass,                   !- Name
       0.5678,                !- U-Factor {W/m2-K}
       0.1,                    !- Solar Heat Gain Coefficient
       0.7;                    !- Visible Transmittance

        Construction,
                 Exterior Window,         !- Name
                 Glass;                   !- Outside Layer
         Construction,
                window_w_blinds,         !- Name
                Glass,                   !- Outside Layer
                int_blind;               !- Layer 2

        WindowMaterial:Blind,
            int_blind,               !- Name
            Horizontal,              !- Slat Orientation
            0.025,                   !- Slat Width {m}
            0.01875,                 !- Slat Separation {m}
            0.001,                   !- Slat Thickness {m}
            45,                    !- Slat Angle {deg}
            221,                     !- Slat Conductivity {W/m-K}
            0.0,                     !- Slat Beam Solar Transmittance
            0.5,                     !- Front Side Slat Beam Solar Reflectance
            0.5,                     !- Back Side Slat Beam Solar Reflectance
            0.0,                     !- Slat Diffuse Solar Transmittance
            0.5,                     !- Front Side Slat Diffuse Solar Reflectance
            0.5,                     !- Back Side Slat Diffuse Solar Reflectance
            0.0,                     !- Slat Beam Visible Transmittance
            0.5,                     !- Front Side Slat Beam Visible Reflectance
            0.5,                     !- Back Side Slat Beam Visible Reflectance
            0.0,                     !- Slat Diffuse Visible Transmittance
            0.5,                     !- Front Side Slat Diffuse Visible Reflectance
            0.5,                     !- Back Side Slat Diffuse Visible Reflectance
            0.0,                     !- Slat Infrared Hemispherical Transmittance
            0.9,                     !- Front Side Slat Infrared Hemispherical Emissivity
            0.9,                     !- Back Side Slat Infrared Hemispherical Emissivity
            0.050,                   !- Blind to Glass Distance {m}
            0.5,                     !- Blind Top Opening Multiplier
            0.5,                     !- Blind Bottom Opening Multiplier
            0.5,                     !- Blind Left Side Opening Multiplier
            0.5,                     !- Blind Right Side Opening Multiplier
            ,                        !- Minimum Slat Angle {deg}
            ;                        !- Maximum Slat Angle {deg}

            WindowShadingControl,
                Shades-living_unit1_front,     !- Name
                living_unit1,            !- Zone Name
                1,                       !- Shading Control Sequence Number
                InteriorBlind,           !- Shading Type
                window_w_blinds,         !- Construction with Shading Name
                OnIfScheduleAllows,      !- Shading Control Type
                shading_2012iecc,        !- Schedule Name
                ,                        !- Setpoint {W/m2, W or deg C}
                Yes,                     !- Shading Control Is Scheduled
                No,                      !- Glare Control Is Active
                ,                        !- Shading Device Material Name
                ,                        !- Type of Slat Angle Control for Blinds
                ,                        !- Slat Angle Schedule Name
                ,                        !- Setpoint 2 {W/m2 or deg C}
                ,                        !- Daylighting Control Object Name
                Sequential,              !- Multiple Surface Control Type
                Window_ldf1_1_Bot.unit1,      !- Fenestration Surface 1 Name
                Window_ldf1_1_Top.unit1,      !- Fenestration Surface 2 Name
                Window_ldf1_2_Bot.unit1,      !- Fenestration Surface 3 Name
                Window_ldf1_2_Top.unit1,      !- Fenestration Surface 4 Name
                Window_ldf2_1_Bot.unit1,      !- Fenestration Surface 17 Name
                Window_ldf2_1_Top.unit1,      !- Fenestration Surface 18 Name
                Window_ldf2_2_Bot.unit1,      !- Fenestration Surface 19 Name
                Window_ldf2_2_Top.unit1;     !- Fenestration Surface 20 Name


FenestrationSurface:Detailed,
    Window_ldf1_1_Bot.unit1, !- Name
    Window,                  !- Surface Type
    Exterior Window,  !- Construction Name
    Wall_ldf1_1.unit1,       !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    ,                        !- View Factor to Ground
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    2.500000000000,0.000000000000,0.600000000000,  !- X,Y,Z ==> Vertex 1 {m}
    3.823210000000,0.000000000000,0.600000000000,  !- X,Y,Z ==> Vertex 2 {m}
    3.823210000000,0.000000000000,1.273210000000,  !- X,Y,Z ==> Vertex 3 {m}
2.500000000000,0.000000000000,1.273210000000;  !- X,Y,Z ==> Vertex 4 {m}

There are 32 windows such as this (8 per orientation), all with a different name but using "Exterior Construction" as the construction name.

Shading not working when using simple glazing

I have constructed my exterior window and exterior window with an interior blind. I have defined the blind material. I have defined the shading control. I have the simple glazing system. Finally I have defined the construction as "Exterior Window" in the FenestrationSurface:Detailed for each window. When I run the simulations, I get the same results as an with unshaded windows. What am I missing?

    WindowMaterial:SimpleGlazingSystem,
       Glass,                   !- Name
       0.5678,                !- U-Factor {W/m2-K}
       0.1,                    !- Solar Heat Gain Coefficient
       0.7;                    !- Visible Transmittance

        Construction,
                 Exterior Window,         !- Name
                 Glass;                   !- Outside Layer
         Construction,
                window_w_blinds,         !- Name
                Glass,                   !- Outside Layer
                int_blind;               !- Layer 2

        WindowMaterial:Blind,
            int_blind,               !- Name
            Horizontal,              !- Slat Orientation
            0.025,                   !- Slat Width {m}
            0.01875,                 !- Slat Separation {m}
            0.001,                   !- Slat Thickness {m}
            45,                    !- Slat Angle {deg}
            221,                     !- Slat Conductivity {W/m-K}
            0.0,                     !- Slat Beam Solar Transmittance
            0.5,                     !- Front Side Slat Beam Solar Reflectance
            0.5,                     !- Back Side Slat Beam Solar Reflectance
            0.0,                     !- Slat Diffuse Solar Transmittance
            0.5,                     !- Front Side Slat Diffuse Solar Reflectance
            0.5,                     !- Back Side Slat Diffuse Solar Reflectance
            0.0,                     !- Slat Beam Visible Transmittance
            0.5,                     !- Front Side Slat Beam Visible Reflectance
            0.5,                     !- Back Side Slat Beam Visible Reflectance
            0.0,                     !- Slat Diffuse Visible Transmittance
            0.5,                     !- Front Side Slat Diffuse Visible Reflectance
            0.5,                     !- Back Side Slat Diffuse Visible Reflectance
            0.0,                     !- Slat Infrared Hemispherical Transmittance
            0.9,                     !- Front Side Slat Infrared Hemispherical Emissivity
            0.9,                     !- Back Side Slat Infrared Hemispherical Emissivity
            0.050,                   !- Blind to Glass Distance {m}
            0.5,                     !- Blind Top Opening Multiplier
            0.5,                     !- Blind Bottom Opening Multiplier
            0.5,                     !- Blind Left Side Opening Multiplier
            0.5,                     !- Blind Right Side Opening Multiplier
            ,                        !- Minimum Slat Angle {deg}
            ;                        !- Maximum Slat Angle {deg}

            WindowShadingControl,
                Shades-living_unit1_front,     !- Name
                living_unit1,            !- Zone Name
                1,                       !- Shading Control Sequence Number
                InteriorBlind,           !- Shading Type
                window_w_blinds,         !- Construction with Shading Name
                OnIfScheduleAllows,      !- Shading Control Type
                shading_2012iecc,        !- Schedule Name
                ,                        !- Setpoint {W/m2, W or deg C}
                Yes,                     !- Shading Control Is Scheduled
                No,                      !- Glare Control Is Active
                ,                        !- Shading Device Material Name
                ,                        !- Type of Slat Angle Control for Blinds
                ,                        !- Slat Angle Schedule Name
                ,                        !- Setpoint 2 {W/m2 or deg C}
                ,                        !- Daylighting Control Object Name
                Sequential,              !- Multiple Surface Control Type
                Window_ldf1_1_Bot.unit1,      !- Fenestration Surface 1 Name
                Window_ldf1_1_Top.unit1,      !- Fenestration Surface 2 Name
                Window_ldf1_2_Bot.unit1,      !- Fenestration Surface 3 Name
                Window_ldf1_2_Top.unit1,      !- Fenestration Surface 4 Name
                Window_ldf2_1_Bot.unit1,      !- Fenestration Surface 17 Name
                Window_ldf2_1_Top.unit1,      !- Fenestration Surface 18 Name
                Window_ldf2_2_Bot.unit1,      !- Fenestration Surface 19 Name
                Window_ldf2_2_Top.unit1;     !- Fenestration Surface 20 Name


FenestrationSurface:Detailed,
    Window_ldf1_1_Bot.unit1, !- Name
    Window,                  !- Surface Type
    Exterior Window,  !- Construction Name
    Wall_ldf1_1.unit1,       !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    ,                        !- View Factor to Ground
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    2.500000000000,0.000000000000,0.600000000000,  !- X,Y,Z ==> Vertex 1 {m}
    3.823210000000,0.000000000000,0.600000000000,  !- X,Y,Z ==> Vertex 2 {m}
    3.823210000000,0.000000000000,1.273210000000,  !- X,Y,Z ==> Vertex 3 {m}
2.500000000000,0.000000000000,1.273210000000;  !- X,Y,Z ==> Vertex 4 {m}

There are 32 windows such as this (8 per orientation), all with a different name but using "Exterior Construction" as the construction name.

Shading not working when using simple glazing

I have constructed my exterior window and exterior window with an interior blind. I have defined the blind material. I have defined the shading control. I have the simple glazing system. Finally I have defined the construction as "Exterior Window" in the FenestrationSurface:Detailed for each window. When I run the simulations, I get the same results as an with unshaded windows. What am I missing?

 WindowMaterial:SimpleGlazingSystem,
    Glass,                   !- Name
    0.5678,                !- U-Factor {W/m2-K}
    0.1,                    !- Solar Heat Gain Coefficient
    0.7;                    !- Visible Transmittance

     Construction,
              Exterior Window,         !- Name
              Glass;                   !- Outside Layer
      Construction,
             window_w_blinds,         !- Name
             Glass,                   !- Outside Layer
             int_blind;               !- Layer 2

     WindowMaterial:Blind,
         int_blind,               !- Name
         Horizontal,              !- Slat Orientation
         0.025,                   !- Slat Width {m}
         0.01875,                 !- Slat Separation {m}
         0.001,                   !- Slat Thickness {m}
         45,                    !- Slat Angle {deg}
         221,                     !- Slat Conductivity {W/m-K}
         0.0,                     !- Slat Beam Solar Transmittance
         0.5,                     !- Front Side Slat Beam Solar Reflectance
         0.5,                     !- Back Side Slat Beam Solar Reflectance
         0.0,                     !- Slat Diffuse Solar Transmittance
         0.5,                     !- Front Side Slat Diffuse Solar Reflectance
         0.5,                     !- Back Side Slat Diffuse Solar Reflectance
         0.0,                     !- Slat Beam Visible Transmittance
         0.5,                     !- Front Side Slat Beam Visible Reflectance
         0.5,                     !- Back Side Slat Beam Visible Reflectance
         0.0,                     !- Slat Diffuse Visible Transmittance
         0.5,                     !- Front Side Slat Diffuse Visible Reflectance
         0.5,                     !- Back Side Slat Diffuse Visible Reflectance
         0.0,                     !- Slat Infrared Hemispherical Transmittance
         0.9,                     !- Front Side Slat Infrared Hemispherical Emissivity
         0.9,                     !- Back Side Slat Infrared Hemispherical Emissivity
         0.050,                   !- Blind to Glass Distance {m}
         0.5,                     !- Blind Top Opening Multiplier
         0.5,                     !- Blind Bottom Opening Multiplier
         0.5,                     !- Blind Left Side Opening Multiplier
         0.5,                     !- Blind Right Side Opening Multiplier
         ,                        !- Minimum Slat Angle {deg}
         ;                        !- Maximum Slat Angle {deg}

         WindowShadingControl,
             Shades-living_unit1_front,     !- Name
             living_unit1,            !- Zone Name
             1,                       !- Shading Control Sequence Number
             InteriorBlind,           !- Shading Type
             window_w_blinds,         !- Construction with Shading Name
             OnIfScheduleAllows,      !- Shading Control Type
             shading_2012iecc,        !- Schedule Name
             ,                        !- Setpoint {W/m2, W or deg C}
             Yes,                     !- Shading Control Is Scheduled
             No,                      !- Glare Control Is Active
             ,                        !- Shading Device Material Name
             ,                        !- Type of Slat Angle Control for Blinds
             ,                        !- Slat Angle Schedule Name
             ,                        !- Setpoint 2 {W/m2 or deg C}
             ,                        !- Daylighting Control Object Name
             Sequential,              !- Multiple Surface Control Type
             Window_ldf1_1_Bot.unit1,      !- Fenestration Surface 1 Name
             Window_ldf1_1_Top.unit1,      !- Fenestration Surface 2 Name
             Window_ldf1_2_Bot.unit1,      !- Fenestration Surface 3 Name
             Window_ldf1_2_Top.unit1,      !- Fenestration Surface 4 Name
             Window_ldf2_1_Bot.unit1,      !- Fenestration Surface 17 Name
             Window_ldf2_1_Top.unit1,      !- Fenestration Surface 18 Name
             Window_ldf2_2_Bot.unit1,      !- Fenestration Surface 19 Name
             Window_ldf2_2_Top.unit1;     !- Fenestration Surface 20 Name


FenestrationSurface:Detailed,
    Window_ldf1_1_Bot.unit1, !- Name
    Window,                  !- Surface Type
    Exterior Window,  !- Construction Name
    Wall_ldf1_1.unit1,       !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    ,                        !- View Factor to Ground
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    2.500000000000,0.000000000000,0.600000000000,  !- X,Y,Z ==> Vertex 1 {m}
    3.823210000000,0.000000000000,0.600000000000,  !- X,Y,Z ==> Vertex 2 {m}
    3.823210000000,0.000000000000,1.273210000000,  !- X,Y,Z ==> Vertex 3 {m}
2.500000000000,0.000000000000,1.273210000000;  !- X,Y,Z ==> Vertex 4 {m}

There are 32 windows such as this (8 per orientation), all with a different name but using "Exterior Construction" as the construction name.