how can I fix this error in design builder file?

I am PhD student, I use design builder program to study indoor thermal comfort, the case study file which I modeled wasn't simulate completely, and there were error message, I need to know what are the right steps to can fix this file. the error massage :

Program Version,EnergyPlus, Version 8.9.0-40101eaafd, YMD=2020.12.27 16:55,
** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
**   ~~~   ** These values may be inappropriate.  Please consult the Input Output Reference for more details.
** Warning ** CalcSurfaceCentroid: 8 Surfaces have the Z coordinate < 0.
**   ~~~   ** ...in any calculations, Wind Speed will be 0.0 for these surfaces.
**   ~~~   ** ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
**   ~~~   ** ...that is, these surfaces will have conditions as though at ground level.
** Warning ** GetSurfaceData: There are 9 window/glass door(s) that may cause inaccurate shadowing due to Solar Distribution.
**   ~~~   ** For explicit details on each window, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** CalculateZoneVolume: 5 zones are not fully enclosed. For more details use:  Output:Diagnostics,DisplayExtrawarnings; 
** Warning ** CheckUsedConstructions: There are 5 nominally unused constructions in input.
**   ~~~   ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** DeterminePolygonOverlap: Too many figures [>15000]  detected in an overlap calculation. Use Output:Diagnostics,DisplayExtraWarnings; for more details.
** Warning ** Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
** Warning ** Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* Beginning Simulation
** Severe  ** PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
**   ~~~   ** pb =[100920.00], tdb=[-379.81], w=[5.9506811E-003].
**   ~~~   **  Routine=CorrectZoneHumRat, During Warmup, Environment=UNTITLED (28-O5:28-O5), at Simulation time=05/28 08:15 - 08:30
**  Fatal  ** Program terminates due to preceding condition.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
*************
************* ===== Final Error Summary =====
************* The following error categories occurred.  Consider correcting or noting.
************* Nominally Unused Constructions
************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause
************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm
************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 1 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 17 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 10.51sec

Thanks.

how can I fix this error in design builder file?

I am PhD student, I use design builder program to study indoor thermal comfort, the case study file which I modeled wasn't simulate completely, and there were error message, I need to know what are the right steps to can fix this file. the error massage :

Program Version,EnergyPlus, Version 8.9.0-40101eaafd, YMD=2020.12.27 16:55,
** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
**   ~~~   ** These values may be inappropriate.  Please consult the Input Output Reference for more details.
** Warning ** CalcSurfaceCentroid: 8 Surfaces have the Z coordinate < 0.
**   ~~~   ** ...in any calculations, Wind Speed will be 0.0 for these surfaces.
**   ~~~   ** ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
**   ~~~   ** ...that is, these surfaces will have conditions as though at ground level.
** Warning ** GetSurfaceData: There are 9 window/glass door(s) that may cause inaccurate shadowing due to Solar Distribution.
**   ~~~   ** For explicit details on each window, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** CalculateZoneVolume: 5 zones are not fully enclosed. For more details use:  Output:Diagnostics,DisplayExtrawarnings; 
** Warning ** CheckUsedConstructions: There are 5 nominally unused constructions in input.
**   ~~~   ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** DeterminePolygonOverlap: Too many figures [>15000]  detected in an overlap calculation. Use Output:Diagnostics,DisplayExtraWarnings; for more details.
** Warning ** Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
** Warning ** Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* Beginning Simulation
** Severe  ** PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
**   ~~~   ** pb =[100920.00], tdb=[-379.81], w=[5.9506811E-003].
**   ~~~   **  Routine=CorrectZoneHumRat, During Warmup, Environment=UNTITLED (28-O5:28-O5), at Simulation time=05/28 08:15 - 08:30
**  Fatal  ** Program terminates due to preceding condition.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
*************
************* ===== Final Error Summary =====
************* The following error categories occurred.  Consider correcting or noting.
************* Nominally Unused Constructions
************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause
************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm
************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 1 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 17 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 10.51sec

Thanks.

how can I fix this error in design builder file?

I am PhD student, I use design builder program to study indoor thermal comfort, the case study file which I modeled wasn't simulate completely, and there were error message, I need to know what are the right steps to can fix this file. the error massage :

Program Version,EnergyPlus, Version 8.9.0-40101eaafd, YMD=2020.12.27 16:55,
** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
**   ~~~   ** These values may be inappropriate.  Please consult the Input Output Reference for more details.
** Warning ** CalcSurfaceCentroid: 8 Surfaces have the Z coordinate < 0.
**   ~~~   ** ...in any calculations, Wind Speed will be 0.0 for these surfaces.
**   ~~~   ** ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
**   ~~~   ** ...that is, these surfaces will have conditions as though at ground level.
** Warning ** GetSurfaceData: There are 9 window/glass door(s) that may cause inaccurate shadowing due to Solar Distribution.
**   ~~~   ** For explicit details on each window, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** CalculateZoneVolume: 5 zones are not fully enclosed. For more details use:  Output:Diagnostics,DisplayExtrawarnings; 
** Warning ** CheckUsedConstructions: There are 5 nominally unused constructions in input.
**   ~~~   ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** DeterminePolygonOverlap: Too many figures [>15000]  detected in an overlap calculation. Use Output:Diagnostics,DisplayExtraWarnings; for more details.
** Warning ** Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
** Warning ** Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* Beginning Simulation
** Severe  ** PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
**   ~~~   ** pb =[100920.00], tdb=[-379.81], w=[5.9506811E-003].
**   ~~~   **  Routine=CorrectZoneHumRat, During Warmup, Environment=UNTITLED (28-O5:28-O5), at Simulation time=05/28 08:15 - 08:30
**  Fatal  ** Program terminates due to preceding condition.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
*************
************* ===== Final Error Summary =====
************* The following error categories occurred.  Consider correcting or noting.
************* Nominally Unused Constructions
************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause
************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm
************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 1 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 17 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 10.51sec

Thanks.

how can I fix this error in design builder file?

I am PhD student, I use design builder program to study indoor thermal comfort, the case study file which I modeled wasn't simulate completely, and there were error message, I need to know what are the right steps to can fix this file. the error massage :

Program :
rogram Version,EnergyPlus, Version 8.9.0-40101eaafd, YMD=2020.12.27 16:55,
**  * Warning ** * ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
**  * Warning ** * Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
**  *   ~~~   ** * These values may be inappropriate.  Please consult the Input Output Reference for more details.
**  * Warning ** * CalcSurfaceCentroid: 8 Surfaces have the Z coordinate < 0.
**  *   ~~~   ** * ...in any calculations, Wind Speed will be 0.0 for these surfaces.
**  *   ~~~   ** * ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
**  *   ~~~   ** * ...that is, these surfaces will have conditions as though at ground level.
**  * Warning ** * GetSurfaceData: There are 9 window/glass door(s) that may cause inaccurate shadowing due to Solar Distribution.
**  *   ~~~   ** * For explicit details on each window, use Output:Diagnostics,DisplayExtraWarnings;
**  * Warning ** * CalculateZoneVolume: 5 zones are not fully enclosed. For more details use:  Output:Diagnostics,DisplayExtrawarnings; 
**  * Warning ** * CheckUsedConstructions: There are 5 nominally unused constructions in input.
**  *   ~~~   ** * For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
**  * Warning ** * DeterminePolygonOverlap: Too many figures [>15000]  detected in an overlap calculation. Use Output:Diagnostics,DisplayExtraWarnings; for more details.
**  * Warning ** * Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
**  * Warning ** * Output:Meter: invalid Key Name="GAS:FACILITY" - not found.
*************  *** Testing Individual Branch Integrity
*************  *** All Branches passed integrity testing
*************  *** Testing Individual Supply Air Path Integrity
*************  *** All Supply Air Paths passed integrity testing
*************  *** Testing Individual Return Air Path Integrity
*************  *** All Return Air Paths passed integrity testing
*************  *** No node connection errors were found.
*************  *** Beginning Simulation
**  * Severe  ** * PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
**  *   ~~~   ** * pb =[100920.00], tdb=[-379.81], w=[5.9506811E-003].
**  *   ~~~   ** *  Routine=CorrectZoneHumRat, During Warmup, Environment=UNTITLED (28-O5:28-O5), at Simulation time=05/28 08:15 - 08:30
**  *  Fatal  ** * Program terminates due to preceding condition.
 ...Summary of Errors that led to program termination:
 ..... Reference severe error count=1
 ..... Last severe error=PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-3.26553].
*************
************* [-3.26553].


*** ===== Final Error Summary ===== ************* *** The following error categories occurred. Consider correcting or noting. ************* *** Nominally Unused Constructions ************* *** ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause ************* *** ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm ************* *** ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option). ************* ************* option).


*** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 1 Severe Errors. ************* *** EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors. ************* *** EnergyPlus Terminated--Fatal Error Detected. 17 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 10.51sec

Thanks.10.51sec