Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works with just a few of warnings which I will mention (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
Now I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got plenty of these warnings, in one-day simulation, at the time that setpoint rises from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Update: I'm trying an EMS (python) solution like below but it doesn't work:
If demand>0 & PLR1==0 & PLR2==0:
pump1 (actuator) = ON
pump2 (actuator)= ON
pump1 flow (actuator)= max (internal variable)
pump2 flow (actuator)= max (internal variable)
The conditions are right but pumps flow does not change. I don't no why!
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works with just a few of warnings which I will mention seems ok (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
Now I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got plenty several of these warnings, warningss in one-day simulation, at the time that setpoint rises goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Update: I'm trying an EMS (python) solution like below but it doesn't work:
If demand>0 & PLR1==0 & PLR2==0:
pump1 (actuator) = ON
pump2 (actuator)= ON
pump1 flow (actuator)= max (internal variable)
pump2 flow (actuator)= max (internal variable)
The conditions are right but pumps flow does not change. I don't no why!
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works with just a few warnings which seems ok without any warning (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
Now I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got several of these warningss in the time that setpoint goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Update: I'm trying an EMS (python) solution like below but it doesn't work:
If demand>0 & PLR1==0 & PLR2==0:
pump1 (actuator) = ON
pump2 (actuator)= ON
pump1 pump 1 flow (actuator)= max (internal variable)
pump2 pump 2 flow (actuator)= max (internal variable)
The conditions are right but pumps flow does not change. I don't no why!
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works without any warning (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got several of these warningss in the time that setpoint goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Update: I'm trying an EMS (python) solution like below but it doesn't work:
If demand>0 & PLR1==0 & PLR2==0:
pump1 (actuator) = ON
pump2 (actuator)= = ON
pump 1 flow (actuator)= max (internal variable)
= max
pump 2 flow (actuator)= max (internal variable)
= max
The conditions are right but pumps flow does not change. I don't no why!
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works without any warning (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got several of these warningss in the time that setpoint goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Update: I'm trying an EMS (python) solution like below but it doesn't work:
If demand>0 & PLR1==0 & PLR2==0:
pump1 = ON
pump2 = ON
pump 1 flow = max
pump 2 flow = max
The conditions are right but pumps flow does not change. I don't no why!
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works without any warning (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got several of these warningss in the time that setpoint goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Update: I'm trying an EMS solution like below but it doesn't work:
If demand>0 & PLR1==0 & PLR2==0:
pump1 = ON
pump2 = ON
pump 1 flow = max
pump 2 flow = max
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works without any warning (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got several of these warningss in the time that setpoint goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works without any warning (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
control):
I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got several of these warningss in the time that setpoint goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.
Pumping system / Plant Convergence issue
The following configuration of cooling loops in energyplus works worrks without any warning (coolingload
operation control and two setpoints and HX hasoperationschememodulated
control):
I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed
gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed
(only change):
I got several of these warningss warning in the time that setpoint goes from 3 to 6.7:
************* ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=74.812813 Min=0.616959
It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger
is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.