Why does my simulation terminates in the middle of simulation (7h month))

Hi everyone,

I am having the following error. What should I do to solve it? I am a newbie so I would really really appreciate solutions based on components in E+.

  ** Severe  ** Plant temperatures are getting far too hot, check controls and relative loads and capacities
   **   ~~~   **  Environment=RUN PERIOD 1, at Simulation time=09/15 16:50 - 17:00
   **   ~~~   ** PlantLoop Name (DemandSide)= HOT WATER LOOP
   **   ~~~   ** PlantLoop Setpoint Temperature=60.0 {C}
   **   ~~~   ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
   **   ~~~   ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
   **   ~~~   ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
   **   ~~~   ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
   **   ~~~   ** PlantLoop Outlet Node (DemandSide) "NODE 20" has temperature=300.0 {C}
   **   ~~~   ** PlantLoop Inlet Node (DemandSide) "NODE 19" has temperature=300.0 {C}
   **   ~~~   ** PlantLoop Minimum Temperature=0.0 {C}
   **   ~~~   ** PlantLoop Maximum Temperature=100.0 {C}
   **   ~~~   ** PlantLoop Flow Request (SupplySide)=2.3 {kg/s}
   **   ~~~   ** PlantLoop Flow Request (DemandSide)=1.1E-006 {kg/s}
   **   ~~~   ** PlantLoop Node (DemandSide) "NODE 20" has mass flow rate =2.3 {kg/s}
   **   ~~~   ** PlantLoop PumpHeat (SupplySide)=537.4 {W}
   **   ~~~   ** PlantLoop PumpHeat (DemandSide)=0.0 {W}
   **   ~~~   ** PlantLoop Cooling Demand=2380093.2 {W}
   **   ~~~   ** PlantLoop Heating Demand=0.0 {W}
   **   ~~~   ** PlantLoop Demand not Dispatched=0.0 {W}
   **   ~~~   ** PlantLoop Unmet Demand=-2380093.2 {W}
   **   ~~~   ** PlantLoop Capacity=151647.2 {W}
   **   ~~~   ** PlantLoop Capacity (SupplySide)=151647.2 {W}
   **   ~~~   ** PlantLoop Capacity (DemandSide)=0.0 {W}
   **   ~~~   ** PlantLoop Operation Scheme=HOT WATER LOOP OPERATION SCHEMES
   **   ~~~   ** PlantLoop Operation Dispatched Load = 0.0 {W}
   **   ~~~   ** PlantLoop Operation Dispatched Load (SupplySide)= 0.0 {W}
   **   ~~~   ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
   **   ~~~   ** Branches on the Loop.
   **   ~~~   ** Demand Branches:
   **   ~~~   **   HOT WATER LOOP DEMAND INLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:HOT WATER LOOP DEMAND INLET PIPE
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 1
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 1
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 2
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 2
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 3
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 3
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 4
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 4
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 5
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 5
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 6
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 6
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 7
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 7
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 8
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 8
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 9
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 9
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 10
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 10
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 11
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 11
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 12
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 12
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 13
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 13
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 14
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 14
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 15
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 15
   **   ~~~   **   HOT WATER LOOP DEMAND BYPASS BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:HOT WATER LOOP DEMAND BYPASS PIPE
   **   ~~~   **   HOT WATER LOOP DEMAND OUTLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:HOT WATER LOOP DEMAND OUTLET PIPE
   **   ~~~   ** Supply Branches:
   **   ~~~   **   HOT WATER LOOP SUPPLY INLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PUMP:CONSTANTSPEED:PUMP CONSTANT SPEED 1
   **   ~~~   **   HOT WATER LOOP SUPPLY BRANCH 1
   **   ~~~   **     Components on Branch:
   **   ~~~   **       BOILER:HOTWATER:PRIMARY BOILER 517KBTU/HR 0.834 THERMAL EFF
   **   ~~~   **   HOT WATER LOOP SUPPLY BRANCH 2
   **   ~~~   **     Components on Branch:
   **   ~~~   **       BOILER:HOTWATER:SECONDARY BOILER 0KBTU/HR 0.8 AFUE
   **   ~~~   **   HOT WATER LOOP SUPPLY BRANCH 3
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:PIPE ADIABATIC 1
   **   ~~~   **   HOT WATER LOOP SUPPLY OUTLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:PIPE ADIABATIC 2
   **   ~~~   ** *************************
   **   ~~~   ** Possible things to look for to correct this problem are:
   **   ~~~   **   Capacity, Operation Scheme, Mass flow problems, Pump Heat building up over time.
   **   ~~~   **   Try a shorter runperiod to stop before it fatals and look at
   **   ~~~   **     lots of node time series data to see what is going wrong.
   **   ~~~   **   If this is happening during Warmup, you can use Output:Diagnostics,ReportDuringWarmup;
   **   ~~~   **   This is detected at the loop level, but the typical problems are in the components.
   **  Fatal  ** CheckForRunawayPlantTemps: Simulation terminated because of run away plant temperatures, too hot
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=1

Why does my simulation terminates in the middle of simulation (7h month))

Hi everyone,

I am having the following error. What should I do to solve it? I am a newbie so I would really really appreciate solutions based on components in E+.

  ** Severe  ** Plant temperatures are getting far too hot, check controls and relative loads and capacities
   **   ~~~   **  Environment=RUN PERIOD 1, at Simulation time=09/15 16:50 - 17:00
   **   ~~~   ** PlantLoop Name (DemandSide)= HOT WATER LOOP
   **   ~~~   ** PlantLoop Setpoint Temperature=60.0 {C}
   **   ~~~   ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
   **   ~~~   ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
   **   ~~~   ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
   **   ~~~   ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
   **   ~~~   ** PlantLoop Outlet Node (DemandSide) "NODE 20" has temperature=300.0 {C}
   **   ~~~   ** PlantLoop Inlet Node (DemandSide) "NODE 19" has temperature=300.0 {C}
   **   ~~~   ** PlantLoop Minimum Temperature=0.0 {C}
   **   ~~~   ** PlantLoop Maximum Temperature=100.0 {C}
   **   ~~~   ** PlantLoop Flow Request (SupplySide)=2.3 {kg/s}
   **   ~~~   ** PlantLoop Flow Request (DemandSide)=1.1E-006 {kg/s}
   **   ~~~   ** PlantLoop Node (DemandSide) "NODE 20" has mass flow rate =2.3 {kg/s}
   **   ~~~   ** PlantLoop PumpHeat (SupplySide)=537.4 {W}
   **   ~~~   ** PlantLoop PumpHeat (DemandSide)=0.0 {W}
   **   ~~~   ** PlantLoop Cooling Demand=2380093.2 {W}
   **   ~~~   ** PlantLoop Heating Demand=0.0 {W}
   **   ~~~   ** PlantLoop Demand not Dispatched=0.0 {W}
   **   ~~~   ** PlantLoop Unmet Demand=-2380093.2 {W}
   **   ~~~   ** PlantLoop Capacity=151647.2 {W}
   **   ~~~   ** PlantLoop Capacity (SupplySide)=151647.2 {W}
   **   ~~~   ** PlantLoop Capacity (DemandSide)=0.0 {W}
   **   ~~~   ** PlantLoop Operation Scheme=HOT WATER LOOP OPERATION SCHEMES
   **   ~~~   ** PlantLoop Operation Dispatched Load = 0.0 {W}
   **   ~~~   ** PlantLoop Operation Dispatched Load (SupplySide)= 0.0 {W}
   **   ~~~   ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
   **   ~~~   ** Branches on the Loop.
   **   ~~~   ** Demand Branches:
   **   ~~~   **   HOT WATER LOOP DEMAND INLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:HOT WATER LOOP DEMAND INLET PIPE
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 1
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 1
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 2
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 2
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 3
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 3
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 4
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 4
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 5
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 5
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 6
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 6
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 7
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 7
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 8
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 8
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 9
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 9
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 10
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 10
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 11
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 11
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 12
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 12
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 13
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 13
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 14
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 14
   **   ~~~   **   HOT WATER LOOP DEMAND BRANCH 15
   **   ~~~   **     Components on Branch:
   **   ~~~   **       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 15
   **   ~~~   **   HOT WATER LOOP DEMAND BYPASS BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:HOT WATER LOOP DEMAND BYPASS PIPE
   **   ~~~   **   HOT WATER LOOP DEMAND OUTLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:HOT WATER LOOP DEMAND OUTLET PIPE
   **   ~~~   ** Supply Branches:
   **   ~~~   **   HOT WATER LOOP SUPPLY INLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PUMP:CONSTANTSPEED:PUMP CONSTANT SPEED 1
   **   ~~~   **   HOT WATER LOOP SUPPLY BRANCH 1
   **   ~~~   **     Components on Branch:
   **   ~~~   **       BOILER:HOTWATER:PRIMARY BOILER 517KBTU/HR 0.834 THERMAL EFF
   **   ~~~   **   HOT WATER LOOP SUPPLY BRANCH 2
   **   ~~~   **     Components on Branch:
   **   ~~~   **       BOILER:HOTWATER:SECONDARY BOILER 0KBTU/HR 0.8 AFUE
   **   ~~~   **   HOT WATER LOOP SUPPLY BRANCH 3
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:PIPE ADIABATIC 1
   **   ~~~   **   HOT WATER LOOP SUPPLY OUTLET BRANCH
   **   ~~~   **     Components on Branch:
   **   ~~~   **       PIPE:ADIABATIC:PIPE ADIABATIC 2
   **   ~~~   ** *************************
   **   ~~~   ** Possible things to look for to correct this problem are:
   **   ~~~   **   Capacity, Operation Scheme, Mass flow problems, Pump Heat building up over time.
   **   ~~~   **   Try a shorter runperiod to stop before it fatals and look at
   **   ~~~   **     lots of node time series data to see what is going wrong.
   **   ~~~   **   If this is happening during Warmup, you can use Output:Diagnostics,ReportDuringWarmup;
   **   ~~~   **   This is detected at the loop level, but the typical problems are in the components.
   **  Fatal  ** CheckForRunawayPlantTemps: Simulation terminated because of run away plant temperatures, too hot
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=1

Why does my simulation terminates in the middle of simulation (7h month))

Hi everyone,

I am having the following error. What should I do to solve it? I am a newbie so I would really really appreciate solutions based on components in E+.

  **  * Severe  ** * Plant temperatures are getting far too hot, check controls and relative loads and capacities
   **   ~~~   ** *   ~~~   *  Environment=RUN PERIOD 1, at Simulation time=09/15 16:50 - 17:00
   **   ~~~   ** *   ~~~   * PlantLoop Name (DemandSide)= HOT WATER LOOP
   **   ~~~   ** *   ~~~   * PlantLoop Setpoint Temperature=60.0 {C}
   **   ~~~   ** *   ~~~   * PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
   **   ~~~   ** *   ~~~   * PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
   **   ~~~   ** *   ~~~   * PlantLoop Outlet Node (SupplySide) has a Setpoint.
   **   ~~~   ** *   ~~~   * PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
   **   ~~~   ** *   ~~~   * PlantLoop Outlet Node (DemandSide) "NODE 20" has temperature=300.0 {C}
   **   ~~~   ** *   ~~~   * PlantLoop Inlet Node (DemandSide) "NODE 19" has temperature=300.0 {C}
   **   ~~~   ** *   ~~~   * PlantLoop Minimum Temperature=0.0 {C}
   **   ~~~   ** *   ~~~   * PlantLoop Maximum Temperature=100.0 {C}
   **   ~~~   ** *   ~~~   * PlantLoop Flow Request (SupplySide)=2.3 {kg/s}
   **   ~~~   ** *   ~~~   * PlantLoop Flow Request (DemandSide)=1.1E-006 {kg/s}
   **   ~~~   ** *   ~~~   * PlantLoop Node (DemandSide) "NODE 20" has mass flow rate =2.3 {kg/s}
   **   ~~~   ** *   ~~~   * PlantLoop PumpHeat (SupplySide)=537.4 {W}
   **   ~~~   ** *   ~~~   * PlantLoop PumpHeat (DemandSide)=0.0 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Cooling Demand=2380093.2 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Heating Demand=0.0 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Demand not Dispatched=0.0 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Unmet Demand=-2380093.2 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Capacity=151647.2 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Capacity (SupplySide)=151647.2 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Capacity (DemandSide)=0.0 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Operation Scheme=HOT WATER LOOP OPERATION SCHEMES
   **   ~~~   ** *   ~~~   * PlantLoop Operation Dispatched Load = 0.0 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Operation Dispatched Load (SupplySide)= 0.0 {W}
   **   ~~~   ** *   ~~~   * PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
   **   ~~~   ** *   ~~~   * Branches on the Loop.
   **   ~~~   ** *   ~~~   * Demand Branches:
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND INLET BRANCH
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       PIPE:ADIABATIC:HOT WATER LOOP DEMAND INLET PIPE
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 1
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 1
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 2
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 2
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 3
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 3
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 4
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 4
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 5
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 5
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 6
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 6
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 7
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 7
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 8
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 8
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 9
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 9
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 10
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 10
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 11
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 11
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 12
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 12
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 13
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 13
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 14
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 14
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BRANCH 15
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       ZONEHVAC:BASEBOARD:CONVECTIVE:WATER:ZONE HVAC BASEBOARD CONVECTIVE WATER 15
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND BYPASS BRANCH
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       PIPE:ADIABATIC:HOT WATER LOOP DEMAND BYPASS PIPE
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP DEMAND OUTLET BRANCH
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       PIPE:ADIABATIC:HOT WATER LOOP DEMAND OUTLET PIPE
   **   ~~~   ** *   ~~~   * Supply Branches:
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP SUPPLY INLET BRANCH
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       PUMP:CONSTANTSPEED:PUMP CONSTANT SPEED 1
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP SUPPLY BRANCH 1
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       BOILER:HOTWATER:PRIMARY BOILER 517KBTU/HR 0.834 THERMAL EFF
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP SUPPLY BRANCH 2
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       BOILER:HOTWATER:SECONDARY BOILER 0KBTU/HR 0.8 AFUE
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP SUPPLY BRANCH 3
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       PIPE:ADIABATIC:PIPE ADIABATIC 1
   **   ~~~   ** *   ~~~   *   HOT WATER LOOP SUPPLY OUTLET BRANCH
   **   ~~~   ** *   ~~~   *     Components on Branch:
   **   ~~~   ** *   ~~~   *       PIPE:ADIABATIC:PIPE ADIABATIC 2
   **   ~~~   ** *************************
   **   ~~~   ** *   ~~~   * ******* *   ~~~   * Possible things to look for to correct this problem are:
   **   ~~~   ** *   ~~~   *   Capacity, Operation Scheme, Mass flow problems, Pump Heat building up over time.
   **   ~~~   ** *   ~~~   *   Try a shorter runperiod to stop before it fatals and look at
   **   ~~~   ** *   ~~~   *     lots of node time series data to see what is going wrong.
   **   ~~~   ** *   ~~~   *   If this is happening during Warmup, you can use Output:Diagnostics,ReportDuringWarmup;
   **   ~~~   ** *   ~~~   *   This is detected at the loop level, but the typical problems are in the components.
   ** *  Fatal  ** * CheckForRunawayPlantTemps: Simulation terminated because of run away plant temperatures, too hot
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=1
count=1