Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.
UPDATE December 8
Here is what I did. The windows have 3 materials/construction but they are all the same. I created "Windows 1" and when I used the Construction Set to apply to diferent windows the software created "Windows 2" and "Windows 3". I'm not sure why or how this happens but I checked and when I tried to apply more Contructives Set it creates "Windows 4" and so on. My colleage were using the material/construction "Windows 2" to run the simulation cause the material "Windows 1" were apply to very few windows (I was learning to use the tools so I probably get confused) and it didnt work. I used the measure "Wind and Stack" with the material "Windows 1" and the simulation worked.
My questions now are:
Are "Windows 1" the same material/construction as "Windows 2 and 3" (like a shortcut)? When I apply the measure to "Windows 1" it apply to the rest "Windows 2 and 3"?
Its kinda hard to explain but I got try
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.
UPDATE December 8
Here is what I did. The windows have 3 materials/construction but they are all the same. I created "Windows 1" and when I used the Construction Set to apply to diferent windows the software created "Windows 2" and "Windows 3". I'm not sure why or how this happens but I checked and when I tried to apply more Contructives Set it creates "Windows 4" and so on. My colleage were using the material/construction "Windows 2" to run the simulation cause the material "Windows 1" were apply to very few windows (I was learning to use the tools so I probably get confused) and it didnt work. I used the measure "Wind and Stack" with the material "Windows 1" and the simulation worked.
My questions now are:
Are "Windows 1" the same material/construction as "Windows 2 and 3" (like a shortcut)? When I apply the measure to "Windows 1" it apply to the rest "Windows 2 and 3"?
Its kinda hard to explain but I got try
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.
UPDATE December 8
Here is what I did. The windows have 3 materials/construction but they are all the same. I created "Windows 1" and when I used the Construction Set to apply to diferent windows the software created "Windows 2" and "Windows 3". I'm not sure why or how this happens but I checked and when I tried to apply more Contructives Set it creates "Windows 4" and so on. My colleage were using the material/construction "Windows 2" to run the simulation cause the material "Windows 1" were apply to very few windows (I was learning to use the tools so I probably get confused) and it didnt work. I used the measure "Wind and Stack" with the material "Windows 1" and the simulation worked.
My questions now are:
Are "Windows 1" the same material/construction materials as "Windows 2 and 3" (like a shortcut)?
When I apply the measure to "Windows 1" it apply to the rest "Windows 2 and 3"?
Its kinda hard to explain but I got try
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.
UPDATE December 8
Here is what I did. The windows have 3 materials/construction materials but they are all the same. I created "Windows 1" and when I used the Construction Set to apply to diferent windows the software created "Windows 2" and "Windows 3". I'm not sure why or how this happens but I checked and when I tried to apply more Contructives Set it creates "Windows 4" and so on. My colleage were using the material/construction material "Windows 2" to run the simulation cause the material "Windows 1" were apply to very few windows (I was learning to use the tools so I probably get confused) and it didnt work. I used the measure "Wind and Stack" with the material "Windows 1" and the simulation worked.
My questions now are:
Are "Windows 1" the same materials as "Windows 2 and 3" (like a shortcut)? When I apply the measure to "Windows 1" it apply to the rest "Windows 2 and 3"?
Its kinda hard to explain but I got try
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.
UPDATE December 8
Here is what I did. The windows have 3 materials but they are all the same. I created "Windows 1" and when I used the Construction Set to apply to diferent windows the software created "Windows 2" and "Windows 3". I'm not sure why or how this happens but I checked and when I tried to apply more Contructives Set it creates "Windows 4" and so on. My colleage were using the material "Windows 2" to run the simulation cause the material "Windows 1" were apply to very few windows (I was learning to use the tools so I probably get confused) and it didnt work. I used the measure "Wind and Stack" with the material "Windows 1" and the simulation worked.
My questions now are:
Are "Windows 1" the same materials as "Windows 2 and 3" (like a shortcut)?
shortcut)?
When I apply the measure to "Windows 1" it apply to the rest "Windows 2 and 3"?
Its kinda hard to explain but I got try
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.
UPDATE
**UPDATE
December 8Here is what I did. The windows have 3 materials but they are all the same. I created "Windows 1" and when I used the Construction Set to apply to diferent windows the software created "Windows 2" and "Windows 3". I'm not sure why or how this happens but I checked and when I tried to apply more Contructives Set it creates "Windows 4" and so on. My colleage were using the material "Windows 2" to run the simulation cause the material "Windows 1" were apply to very few windows (I was learning to use the tools so I probably get confused) and it didnt work. I used the measure "Wind and Stack" with the material "Windows 1" and the simulation worked.
My questions now are:
Are "Windows 1" the same materials as "Windows 2 and 3" (like a shortcut)?
When I apply the measure to "Windows 1" it apply to the rest "Windows 2 and 3"?
3"?
Its kinda hard to explain but I got try
try**
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.
**UPDATE December 8
Here is what I did. The windows have 3 materials but they are all the same. I created "Windows 1" and when I used the Construction Set to apply to diferent windows the software created "Windows 2" and "Windows 3". I'm not sure why or how this happens but I checked and when I tried to apply more Contructives Set it creates "Windows 4" and so on. My colleage were using the material "Windows 2" to run the simulation cause the material "Windows 1" were apply to very few windows (I was learning to use the tools so I probably get confused) and it didnt work. I used the measure "Wind and Stack" with the material "Windows 1" and the simulation worked.
My questions now are:
Are "Windows 1" the same materials as "Windows 2 and 3" (like a shortcut)? When I apply the measure to "Windows 1" it apply to the rest "Windows 2 and 3"? Its kinda hard to explain but I got try**
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs). In the face with 4 lines of windows only the 2 lines in the middle are operable. In the face with only 1 line they all are operable.(upstairs)
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
This is one of the rooms of the builiding that the measure fail (upstairs)
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Update: We try to use the Airflow Network but it didn't work and showed the same errors. We're trying to simulate the windows to open and close during the day to analyse the natural airflow
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec
Problem with Wind and Stack measure in OS
Hi! Me and my team are running some tests with a model and the measure Wind and Stack are failing. With the simulation alone it works fine but give me a lot of warnings. This is with the measure:
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.11.23 15:24,
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][height_difference] - Value type "string" for input "Default 0.5 Open Fractional Schedule" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][maximum_indoor_temperature] - Value type "string" for input "Autocalculate" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][minimum_indoor_temperature] - "180.000000" - Expected number less than or equal to 100.000000
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Value type "string" for input "18 e 19 - Bloco Menor - Esquerda - Pav Superior" not permitted by 'type' constraint.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #0.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - "18 e 19 - Bloco Menor - Esquerda - Pav Superior" - Failed to match against any enum values.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against child schema #1.
** Severe ** <root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
** Fatal ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=<root>[ZoneVentilation:WindandStackOpenArea][Sub Surface 52_WindandStackOpenArea][opening_effectiveness] - Failed to validate against any child schemas allowed by anyOf constraint.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 8 Severe Errors; Elapsed Time=00hr 00min 0.90sec