Revision history [back]
How to fix fatal error relating to degenerate surfaces?
Hello, I am new to this program. I am looking for some help solving a degenerate surface fatal error. I attached a link to the idf files and copied the error file below. Any help or guidance in the right direction would be greatly apprecaited.
Thank you
https://drive.google.com/drive/folders/1mZLCrXTYYjhVDDJFwdSRW-XYGlUhQEdg?usp=sharing
How to fix fatal error relating to degenerate surfaces?
Hello, I am new to this program. I am looking for some help solving a degenerate surface fatal error. I attached a link to the idf files and copied the error file below. Any help or guidance in the right direction would be greatly apprecaited.
Thank you
https://drive.google.com/drive/folders/1mZLCrXTYYjhVDDJFwdSRW-XYGlUhQEdg?usp=sharing
How to fix fatal error relating to degenerate surfaces?
Hello, I am new to this program. I am looking for some help solving a degenerate surface fatal error. I attached a link to the idf files and copied the error file below. Any help or guidance in the right direction would be greatly apprecaited.
Thank you
https://drive.google.com/drive/folders/1mZLCrXTYYjhVDDJFwdSRW-XYGlUhQEdg?usp=sharing
C:\fakepath\Screen Shot 2020-05-29 Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.05.28 11:55,
* Warning * ManageSizing: For a zone sizing run, there must be at 10.51.34 AM.pngcleast 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
* ~~~ * Found first in surface=SURFACE 21
* ~~~ * Defaults, constant throughout the year of (18.0) will be used.
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 11
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 16
* Warning * GetSurfaceData: There are 11 coincident/collinear vertices; These have been deleted unless the deletion would bring the number of surface sides < 3.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Severe * GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
* ~~~ * These surfaces should be deleted.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Fatal * GetSurfaceData: Errors discovered, program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=5
..... Last severe error=GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
*** Warning: Node connection errors not checked - most system input has not been read (see previous warning).
*** Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
*** EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
*** EnergyPlus Terminated--Fatal Error Detected. 15 Warning; 5 Severe Errors; Elapsed Time=00hr 00min 0.78sec
How to fix fatal error relating to degenerate surfaces?
Hello, I am new to this program. I am looking for some help solving a degenerate surface fatal error. I attached a link to the idf files and copied the error file below. Any help or guidance in the right direction would be greatly apprecaited.
Thank you
https://drive.google.com/drive/folders/1mZLCrXTYYjhVDDJFwdSRW-XYGlUhQEdg?usp=sharing
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.05.28 11:55,
* Warning * ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
* ~~~ * Found first in surface=SURFACE 21
* ~~~ * Defaults, constant throughout the year of (18.0) will be used.
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 11
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 16
* Warning * GetSurfaceData: There are 11 coincident/collinear vertices; These have been deleted unless the deletion would bring the number of surface sides < 3.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Severe * GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
* ~~~ * These surfaces should be deleted.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Fatal * GetSurfaceData: Errors discovered, program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=5
..... Last severe error=GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
*** Warning: Node connection errors not checked - most system input has not been read (see previous warning).
*** Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
*** EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
*** EnergyPlus Terminated--Fatal Error Detected. 15 Warning; 5 Severe Errors; Elapsed Time=00hr 00min 0.78sec
How to fix fatal error relating to degenerate surfaces?
Hello, I am new to this program. I am looking for some help solving a degenerate surface fatal error. I attached a link to the idf files and copied the error file below. Any help or guidance in the right direction would be greatly apprecaited.
Thank you
https://drive.google.com/drive/folders/1mZLCrXTYYjhVDDJFwdSRW-XYGlUhQEdg?usp=sharing
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.05.28 11:55,
* Warning * ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
* ~~~ * Found first in surface=SURFACE 21
* ~~~ * Defaults, constant throughout the year of (18.0) will be used.
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 11
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 16
* Warning * GetSurfaceData: There are 11 coincident/collinear vertices; These have been deleted unless the deletion would bring the number of surface sides < 3.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Severe * GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
* ~~~ * These surfaces should be deleted.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Fatal * GetSurfaceData: Errors discovered, program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=5
..... Last severe error=GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
*** Warning: Node connection errors not checked - most system input has not been read (see previous warning).
*** Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
*** EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
*** EnergyPlus Terminated--Fatal Error Detected. 15 Warning; 5 Severe Errors; Elapsed Time=00hr 00min 0.78sec
How to fix fatal error relating to degenerate surfaces?
Hello, I am new to this program. I am looking for some help solving a degenerate surface fatal error. I attached the idf files and copied the error file below. Any help or guidance in the right direction would be greatly apprecaited.
Thank you
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.05.28 11:55,
* Warning * ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
* ~~~ * Found first in surface=SURFACE 21
* ~~~ * Defaults, constant throughout the year of (18.0) will be used.
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 11
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 16
* Warning * GetSurfaceData: There are 11 coincident/collinear vertices; These have been deleted unless the deletion would bring the number of surface sides < 3.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Severe * GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
* ~~~ * These surfaces should be deleted.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Fatal * GetSurfaceData: Errors discovered, program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=5
..... Last severe error=GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
*** Warning: Node connection errors not checked - most system input has not been read (see previous warning).
*** Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
*** EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
*** EnergyPlus Terminated--Fatal Error Detected. 15 Warning; 5 Severe Errors; Elapsed Time=00hr 00min 0.78sec
How to fix fatal error relating to degenerate surfaces?
Hello, I am new to this program. I am looking for some help solving a degenerate surface fatal error. I attached the idf files and copied the error file below. Any help or guidance in the right direction would be greatly apprecaited.
Thank you
Program Version,EnergyPlus, Version 9.2.0-921312fa1d, YMD=2020.05.28 11:55,
* Warning * ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated.
* Warning * GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
* ~~~ * Found first in surface=SURFACE 21
* ~~~ * Defaults, constant throughout the year of (18.0) will be used.
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 11
* Severe * GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 16
* Warning * GetSurfaceData: There are 11 coincident/collinear vertices; These have been deleted unless the deletion would bring the number of surface sides < 3.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Severe * GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
* ~~~ * These surfaces should be deleted.
* ~~~ * For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
* Fatal * GetSurfaceData: Errors discovered, program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=5
..... Last severe error=GetSurfaceData: There are 3 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
*** Warning: Node connection errors not checked - most system input has not been read (see previous warning).
*** Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
*** EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
*** EnergyPlus Terminated--Fatal Error Detected. 15 Warning; 5 Severe Errors; Elapsed Time=00hr 00min 0.78sec