Revision history [back]
I am getting these errors, I have a four floor building and when I tried to raise the temperature for floor 4, It still gave me same error.
Any help would be great.
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/15 19:08 - 19:15
** ~~~ ** The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface mass flow rate check value iteration history trace: 5.745895,5.836518,3.701269,3.610646,5.745895,5.836518,3.701269,3.610646,5.745895,5.836518,
** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014,
** ~~~ ** Supply-to-demand interface deck 1 temperature check value iteration history trace: 1.232919,1.388355,1.248185,1.092749,1.232919,1.388355,1.248185,1.092749,1.232919,1.388355,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface energy check value iteration history trace: 155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781,
** ~~~ ** Supply-to-demand interface deck 1 energy check value iteration history trace: -9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.549752
** ~~~ ** Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 25.479399
** ~~~ ** Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/17 01:30 - 01:45
** ~~~ ** The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface mass flow rate check value iteration history trace: 2.771039,2.364487,4.904607,5.311160,2.771039,2.364487,4.904607,5.311160,2.771039,2.364487,
** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014,
** ~~~ ** Supply-to-demand interface deck 1 temperature check value iteration history trace: 0.501775,0.355357,0.611962,0.758380,0.501775,0.355357,0.611962,0.758380,0.501775,0.355357,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface energy check value iteration history trace: 75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613,
** ~~~ ** Supply-to-demand interface deck 1 energy check value iteration history trace: -2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.984488
** ~~~ ** Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 26.212952
** ~~~ ** Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:15
** ~~~ ** The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface mass flow rate check value iteration history trace: 0.107130,0.108959,0.111011,0.112904,0.115035,0.116994,0.119207,0.121235,0.123533,0.125631,
** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface temperature check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,7.105427E-015,1.421085E-014,7.105427E-015,0.000000,0.000000,0.000000,
** ~~~ ** Supply-to-demand interface deck 1 temperature check value iteration history trace: 5.784196E-002,5.887640E-002,5.993414E-002,6.100636E-002,6.210293E-002,6.321434E-002,6.435122E-002,6.550332E-002,6.668205E-002,6.787639E-002,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface energy check value iteration history trace: 2906.617738,2956.258632,3011.920632,3063.291526,3121.096331,3174.256724,3234.293739,3289.305213,3351.668207,3408.594517,
** ~~~ ** Supply-to-demand interface deck 1 energy check value iteration history trace: -140.645238,136.714302,-145.856018,141.544113,-151.266927,146.542517,-156.886278,151.715342,-162.722788,157.068619,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 8.788940E-003 [kg/s/iteration]
** ~~~ ** Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.312692,2.307009,2.300713,2.293735,2.286005,2.277439,2.267946,2.257424,2.245754,2.232802,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 5.1311E-003 [C/iteration]
** ~~~ ** Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.713367,25.710149,25.706564,25.702569,25.698114,25.693143,25.687590,25.681379,25.674424,25.666619,
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:08
** ~~~ ** The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface mass flow rate check value iteration history trace: 4.656411E-002,4.771150E-002,4.893847E-002,5.014317E-002,5.143421E-002,5.269904E-002,5.405758E-002,5.538547E-002,5.681516E-002,5.820920E-002,
** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.515627E-002,2.578874E-002,2.643840E-002,2.710313E-002,2.778599E-002,2.848463E-002,2.920240E-002,2.993669E-002,3.069117E-002,3.146293E-002,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface energy check value iteration history trace: 1263.365723,1294.496428,1327.786321,1360.471964,1395.500077,1429.816938,1466.676616,1502.704600,1541.494501,1579.317300,
** ~~~ ** Supply-to-demand interface deck 1 energy check value iteration history trace: -60.568667,60.855088,-63.688241,63.923905,-66.970537,67.146027,-70.424273,70.528978,-74.058666,74.080640,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 6.790174E-003 [kg/s/iteration]
** ~~~ ** Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.349526,2.345909,2.341723,2.336882,2.331285,2.324816,2.317344,2.308717,2.298762,2.287277,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 3.8339E-003 [C/iteration]
** ~~~ ** Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.725495,25.723499,25.721182,25.718491,25.715366,25.711736,25.707518,25.702614,25.696908,25.690265,
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:08 - 23:15
** ~~~ ** The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface mass flow rate check value iteration history trace: 5.458274E-002,5.584920E-002,5.721147E-002,5.853748E-002,5.996723E-002,6.135555E-002,6.285624E-002,6.430974E-002,6.588501E-002,6.740670E-002,
** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,1.421085E-014,7.105427E-015,
** ~~~ ** Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.948172E-002,3.018207E-002,3.090072E-002,3.163482E-002,3.238819E-002,3.315769E-002,3.394747E-002,3.475407E-002,3.558204E-002,3.642755E-002,
** ~~~ ** Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** Check values should be zero. Most Recent values listed first.
** ~~~ ** Demand-to-Supply interface energy check value iteration history trace: 1480.921246,1515.282188,1552.242843,1588.219864,1627.011292,1664.678933,1705.394938,1744.831063,1787.570604,1828.856553,
** ~~~ ** Supply-to-demand interface deck 1 energy check value iteration history trace: -71.067718,71.062155,-74.530622,74.440439,-78.164849,77.977656,-81.979157,81.681142,-85.982781,85.558563,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 7.191971E-003 [kg/s/iteration]
** ~~~ ** Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.344366,2.340385,2.335817,2.330577,2.324568,2.317680,2.309789,2.300752,2.290405,2.278562,
** ~~~ ** Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 4.0801E-003 [C/iteration]
** ~~~ ** Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.723934,25.721730,25.719191,25.716267,25.712898,25.709015,25.704537,25.699371,25.693407,25.686513,
Any help would be great.
I am getting these errors, I have a four floor building and when I tried to raise the temperature for floor 4, It still gave me same error.
Any help would be great.
** * Warning ** * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/15 19:08 - 19:15
** ~~~ ** * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 5.745895,5.836518,3.701269,3.610646,5.745895,5.836518,3.701269,3.610646,5.745895,5.836518,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 1.232919,1.388355,1.248185,1.092749,1.232919,1.388355,1.248185,1.092749,1.232919,1.388355,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.549752
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 25.479399
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,
** * Warning ** * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/17 01:30 - 01:45
** ~~~ ** * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 2.771039,2.364487,4.904607,5.311160,2.771039,2.364487,4.904607,5.311160,2.771039,2.364487,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 0.501775,0.355357,0.611962,0.758380,0.501775,0.355357,0.611962,0.758380,0.501775,0.355357,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.984488
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 26.212952
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,
** * Warning ** * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:15
** ~~~ ** * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 0.107130,0.108959,0.111011,0.112904,0.115035,0.116994,0.119207,0.121235,0.123533,0.125631,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,7.105427E-015,1.421085E-014,7.105427E-015,0.000000,0.000000,0.000000,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 5.784196E-002,5.887640E-002,5.993414E-002,6.100636E-002,6.210293E-002,6.321434E-002,6.435122E-002,6.550332E-002,6.668205E-002,6.787639E-002,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 2906.617738,2956.258632,3011.920632,3063.291526,3121.096331,3174.256724,3234.293739,3289.305213,3351.668207,3408.594517,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -140.645238,136.714302,-145.856018,141.544113,-151.266927,146.542517,-156.886278,151.715342,-162.722788,157.068619,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 8.788940E-003 [kg/s/iteration]
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.312692,2.307009,2.300713,2.293735,2.286005,2.277439,2.267946,2.257424,2.245754,2.232802,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 5.1311E-003 [C/iteration]
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.713367,25.710149,25.706564,25.702569,25.698114,25.693143,25.687590,25.681379,25.674424,25.666619,
** * Warning ** * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:08
** ~~~ ** * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 4.656411E-002,4.771150E-002,4.893847E-002,5.014317E-002,5.143421E-002,5.269904E-002,5.405758E-002,5.538547E-002,5.681516E-002,5.820920E-002,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.515627E-002,2.578874E-002,2.643840E-002,2.710313E-002,2.778599E-002,2.848463E-002,2.920240E-002,2.993669E-002,3.069117E-002,3.146293E-002,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 1263.365723,1294.496428,1327.786321,1360.471964,1395.500077,1429.816938,1466.676616,1502.704600,1541.494501,1579.317300,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -60.568667,60.855088,-63.688241,63.923905,-66.970537,67.146027,-70.424273,70.528978,-74.058666,74.080640,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 6.790174E-003 [kg/s/iteration]
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.349526,2.345909,2.341723,2.336882,2.331285,2.324816,2.317344,2.308717,2.298762,2.287277,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 3.8339E-003 [C/iteration]
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.725495,25.723499,25.721182,25.718491,25.715366,25.711736,25.707518,25.702614,25.696908,25.690265,
** * Warning ** * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:08 - 23:15
** ~~~ ** * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 5.458274E-002,5.584920E-002,5.721147E-002,5.853748E-002,5.996723E-002,6.135555E-002,6.285624E-002,6.430974E-002,6.588501E-002,6.740670E-002,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,1.421085E-014,7.105427E-015,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.948172E-002,3.018207E-002,3.090072E-002,3.163482E-002,3.238819E-002,3.315769E-002,3.394747E-002,3.475407E-002,3.558204E-002,3.642755E-002,
** ~~~ ** * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
** ~~~ ** * ~~~ * Check values should be zero. Most Recent values listed first.
** ~~~ ** * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 1480.921246,1515.282188,1552.242843,1588.219864,1627.011292,1664.678933,1705.394938,1744.831063,1787.570604,1828.856553,
** ~~~ ** * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -71.067718,71.062155,-74.530622,74.440439,-78.164849,77.977656,-81.979157,81.681142,-85.982781,85.558563,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 7.191971E-003 [kg/s/iteration]
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.344366,2.340385,2.335817,2.330577,2.324568,2.317680,2.309789,2.300752,2.290405,2.278562,
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 4.0801E-003 [C/iteration]
** ~~~ ** * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.723934,25.721730,25.719191,25.716267,25.712898,25.709015,25.704537,25.699371,25.693407,25.686513,
Any help would be great.25.723934,25.721730,25.719191,25.716267,25.712898,25.709015,25.704537,25.699371,25.693407,25.686513,
I am getting these errors, I have a four floor building and when I tried to raise the temperature for floor 4, It still gave me same error.
* Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/15 19:08 - 19:15
* ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 5.745895,5.836518,3.701269,3.610646,5.745895,5.836518,3.701269,3.610646,5.745895,5.836518,
* ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014,
* ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 1.232919,1.388355,1.248185,1.092749,1.232919,1.388355,1.248185,1.092749,1.232919,1.388355,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface energy check value iteration history trace: 155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781,
* ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.549752
* ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 25.479399
* ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,
* Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/17 01:30 - 01:45
* ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 2.771039,2.364487,4.904607,5.311160,2.771039,2.364487,4.904607,5.311160,2.771039,2.364487,
* ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014,
* ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 0.501775,0.355357,0.611962,0.758380,0.501775,0.355357,0.611962,0.758380,0.501775,0.355357,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface energy check value iteration history trace: 75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613,
* ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.984488
* ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 26.212952
* ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,
* Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:15
* ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 0.107130,0.108959,0.111011,0.112904,0.115035,0.116994,0.119207,0.121235,0.123533,0.125631,
* ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,7.105427E-015,1.421085E-014,7.105427E-015,0.000000,0.000000,0.000000,
* ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 5.784196E-002,5.887640E-002,5.993414E-002,6.100636E-002,6.210293E-002,6.321434E-002,6.435122E-002,6.550332E-002,6.668205E-002,6.787639E-002,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface energy check value iteration history trace: 2906.617738,2956.258632,3011.920632,3063.291526,3121.096331,3174.256724,3234.293739,3289.305213,3351.668207,3408.594517,
* ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -140.645238,136.714302,-145.856018,141.544113,-151.266927,146.542517,-156.886278,151.715342,-162.722788,157.068619,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 8.788940E-003 [kg/s/iteration]
* ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.312692,2.307009,2.300713,2.293735,2.286005,2.277439,2.267946,2.257424,2.245754,2.232802,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 5.1311E-003 [C/iteration]
* ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.713367,25.710149,25.706564,25.702569,25.698114,25.693143,25.687590,25.681379,25.674424,25.666619,
* Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:08
* ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 4.656411E-002,4.771150E-002,4.893847E-002,5.014317E-002,5.143421E-002,5.269904E-002,5.405758E-002,5.538547E-002,5.681516E-002,5.820920E-002,
* ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
* ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.515627E-002,2.578874E-002,2.643840E-002,2.710313E-002,2.778599E-002,2.848463E-002,2.920240E-002,2.993669E-002,3.069117E-002,3.146293E-002,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface energy check value iteration history trace: 1263.365723,1294.496428,1327.786321,1360.471964,1395.500077,1429.816938,1466.676616,1502.704600,1541.494501,1579.317300,
* ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -60.568667,60.855088,-63.688241,63.923905,-66.970537,67.146027,-70.424273,70.528978,-74.058666,74.080640,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 6.790174E-003 [kg/s/iteration]
* ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.349526,2.345909,2.341723,2.336882,2.331285,2.324816,2.317344,2.308717,2.298762,2.287277,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 3.8339E-003 [C/iteration]
* ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.725495,25.723499,25.721182,25.718491,25.715366,25.711736,25.707518,25.702614,25.696908,25.690265,
* Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:08 - 23:15
* ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 5.458274E-002,5.584920E-002,5.721147E-002,5.853748E-002,5.996723E-002,6.135555E-002,6.285624E-002,6.430974E-002,6.588501E-002,6.740670E-002,
* ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,1.421085E-014,7.105427E-015,
* ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.948172E-002,3.018207E-002,3.090072E-002,3.163482E-002,3.238819E-002,3.315769E-002,3.394747E-002,3.475407E-002,3.558204E-002,3.642755E-002,
* ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy
* ~~~ * Check values should be zero. Most Recent values listed first.
* ~~~ * Demand-to-Supply interface energy check value iteration history trace: 1480.921246,1515.282188,1552.242843,1588.219864,1627.011292,1664.678933,1705.394938,1744.831063,1787.570604,1828.856553,
* ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -71.067718,71.062155,-74.530622,74.440439,-78.164849,77.977656,-81.979157,81.681142,-85.982781,85.558563,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 7.191971E-003 [kg/s/iteration]
* ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.344366,2.340385,2.335817,2.330577,2.324568,2.317680,2.309789,2.300752,2.290405,2.278562,
* ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 4.0801E-003 [C/iteration]
* ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.723934,25.721730,25.719191,25.716267,25.712898,25.709015,25.704537,25.699371,25.693407,25.686513,
I am getting these errors, I have a four floor building and when I tried to raise the temperature for floor 4, It still gave me same error.
* Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/15 19:08 - 19:15 * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 5.745895,5.836518,3.701269,3.610646,5.745895,5.836518,3.701269,3.610646,5.745895,5.836518, * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014,7.105427E-015,7.105427E-015,0.000000,1.421085E-014, * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 1.232919,1.388355,1.248185,1.092749,1.232919,1.388355,1.248185,1.092749,1.232919,1.388355, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781,100481.324411,98021.109977,155988.445348,158448.659781, * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785,-6472.331239,1701.693002,-9038.512848,2035.602785, * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.549752 * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129,1.549752,1.459129, * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 25.479399 * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963,25.479399,25.323963, * Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 01/17 01:30 - 01:45 * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 2.771039,2.364487,4.904607,5.311160,2.771039,2.364487,4.904607,5.311160,2.771039,2.364487, * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014,1.421085E-014,0.000000,0.000000,1.421085E-014, * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 0.501775,0.355357,0.611962,0.758380,0.501775,0.355357,0.611962,0.758380,0.501775,0.355357, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613,133423.691510,144483.431216,75382.631319,64322.891613, * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401,-4486.287611,1512.286446,-2397.762481,853.788401, * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating mass flow rate across iterations with a repeated value of 1.984488 * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040,1.984488,2.391040, * ~~~ * Node named F4-Z1 SUPPLY INLET shows oscillating temperatures across iterations with a repeated value of 26.212952 * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370,26.212952,26.359370, * Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:15 * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 0.107130,0.108959,0.111011,0.112904,0.115035,0.116994,0.119207,0.121235,0.123533,0.125631, * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,7.105427E-015,1.421085E-014,7.105427E-015,0.000000,0.000000,0.000000, * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 5.784196E-002,5.887640E-002,5.993414E-002,6.100636E-002,6.210293E-002,6.321434E-002,6.435122E-002,6.550332E-002,6.668205E-002,6.787639E-002, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 2906.617738,2956.258632,3011.920632,3063.291526,3121.096331,3174.256724,3234.293739,3289.305213,3351.668207,3408.594517, * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -140.645238,136.714302,-145.856018,141.544113,-151.266927,146.542517,-156.886278,151.715342,-162.722788,157.068619, * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 8.788940E-003 [kg/s/iteration] * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.312692,2.307009,2.300713,2.293735,2.286005,2.277439,2.267946,2.257424,2.245754,2.232802, * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 5.1311E-003 [C/iteration] * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.713367,25.710149,25.706564,25.702569,25.698114,25.693143,25.687590,25.681379,25.674424,25.666619, * Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:00 - 23:08 * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 4.656411E-002,4.771150E-002,4.893847E-002,5.014317E-002,5.143421E-002,5.269904E-002,5.405758E-002,5.538547E-002,5.681516E-002,5.820920E-002, * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000, * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.515627E-002,2.578874E-002,2.643840E-002,2.710313E-002,2.778599E-002,2.848463E-002,2.920240E-002,2.993669E-002,3.069117E-002,3.146293E-002, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 1263.365723,1294.496428,1327.786321,1360.471964,1395.500077,1429.816938,1466.676616,1502.704600,1541.494501,1579.317300, * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -60.568667,60.855088,-63.688241,63.923905,-66.970537,67.146027,-70.424273,70.528978,-74.058666,74.080640, * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 6.790174E-003 [kg/s/iteration] * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.349526,2.345909,2.341723,2.336882,2.331285,2.324816,2.317344,2.308717,2.298762,2.287277, * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 3.8339E-003 [C/iteration] * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.725495,25.723499,25.721182,25.718491,25.715366,25.711736,25.707518,25.702614,25.696908,25.690265, * Warning * SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at College Station Easterwood Fl TX USA TMY3 WMO#=722445, 02/03 23:08 - 23:15 * ~~~ * The solution for one or more of the Air Loop HVAC systems did not appear to converge * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for mass flow rate * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface mass flow rate check value iteration history trace: 5.458274E-002,5.584920E-002,5.721147E-002,5.853748E-002,5.996723E-002,6.135555E-002,6.285624E-002,6.430974E-002,6.588501E-002,6.740670E-002, * ~~~ * Supply-to-demand interface deck 1 mass flow rate check value iteration history trace: 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for temperature * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface temperature check value iteration history trace: 7.105427E-015,7.105427E-015,0.000000,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,7.105427E-015,1.421085E-014,7.105427E-015, * ~~~ * Supply-to-demand interface deck 1 temperature check value iteration history trace: 2.948172E-002,3.018207E-002,3.090072E-002,3.163482E-002,3.238819E-002,3.315769E-002,3.394747E-002,3.475407E-002,3.558204E-002,3.642755E-002, * ~~~ * Air System Named = LANGFORD F4_Z1_VAV1 did not converge for energy * ~~~ * Check values should be zero. Most Recent values listed first. * ~~~ * Demand-to-Supply interface energy check value iteration history trace: 1480.921246,1515.282188,1552.242843,1588.219864,1627.011292,1664.678933,1705.394938,1744.831063,1787.570604,1828.856553, * ~~~ * Supply-to-demand interface deck 1 energy check value iteration history trace: -71.067718,71.062155,-74.530622,74.440439,-78.164849,77.977656,-81.979157,81.681142,-85.982781,85.558563, * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing mass flow rate with a trend rate across iterations of 7.191971E-003 [kg/s/iteration] * ~~~ * Node named F4-Z1 SUPPLY INLET mass flow rate [kg/s] iteration history trace (most recent first): 2.344366,2.340385,2.335817,2.330577,2.324568,2.317680,2.309789,2.300752,2.290405,2.278562, * ~~~ * Node named F4-Z1 SUPPLY INLET shows monotonically increasing temperatures with a trend rate across iterations of 4.0801E-003 [C/iteration] * ~~~ * Node named F4-Z1 SUPPLY INLET temperature [C] iteration history trace (most recent first): 25.723934,25.721730,25.719191,25.716267,25.712898,25.709015,25.704537,25.699371,25.693407,25.686513,