Revision history  [back]

Inconsistent Chilled Water Node Temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

Alessandro

Here another graph: node temps at supply side outlet node = node temp at demand side inlet node (light blue over blu line), and about mass flow rates (yellow line over magenta line)

image description


Update:

So, do I have to think it is a sort of "bug" of the plant solver (taht is: the software does not work properly itself)?

Ag


2nd Update:

I've used only adiabatic pipes, so there are no thermal losses along pipes.

Now I've atteched three images about the three nodes to focus on (according to the order with which they appear in the circuit):

  • 2ND HPFC-B SUPPLY SIDE OUTLET

  • 2ND HPFC-B DEMAND SIDE INLET

  • VRXHPCFXDHX:VrtlRmXBXHPCFXDHX Fan Coil Unit Cooling Coil Water Inlet Node

image 1: plant branches scheme

image 2: node water mass flow rates

image 3: node chilled water temperatures

then a link to the IDF file

Inconsistent Chilled Water Node Temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

Alessandro

Here another graph: node temps at supply side outlet node = node temp at demand side inlet node (light blue over blu line), and about mass flow rates (yellow line over magenta line)

image description


Update:

So, do I have to think it is a sort of "bug" of the plant solver (taht is: the software does not work properly itself)?

Ag


2nd Update:

I've used only adiabatic pipes, so there are no thermal losses along pipes.

Now I've atteched three images about the three nodes to focus on (according to the order with which they appear in the circuit):

  • 2ND HPFC-B SUPPLY SIDE OUTLET

  • 2ND HPFC-B DEMAND SIDE INLET

  • VRXHPCFXDHX:VrtlRmXBXHPCFXDHX Fan Coil Unit Cooling Coil Water Inlet Node

image 1: plant branches brnaches scheme

image 2: node water mass flow rates

image 3: node chilled water temperatures

then a link to the IDF file

Inconsistent Chilled Water Node Temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

Alessandro

Here another graph: node temps at supply side outlet node = node temp at demand side inlet node (light blue over blu line), and about mass flow rates (yellow line over magenta line)

image description


Update: Update:

So, do I have to think it is a sort of "bug" of the plant solver (taht is: the software does not work properly itself)?

Ag


2nd Update:

Update I've used only adiabatic pipes, so there are no thermal losses along pipes.

Now I've atteched three images about the three nodes to focus on (according to the order with which they appear in the circuit):

  • 2ND HPFC-B SUPPLY SIDE OUTLET

  • 2ND HPFC-B DEMAND SIDE INLET

  • VRXHPCFXDHX:VrtlRmXBXHPCFXDHX Fan Coil Unit Cooling Coil Water Inlet Node

image 1: plant brnaches scheme

image 2: node water mass flow rates

image 3: node chilled water temperatures

then a link to the IDF file

Inconsistent Chilled Water Node Temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

Alessandro

Here another graph: node temps at supply side outlet node = node temp at demand side inlet node (light blue over blu line), and about mass flow rates (yellow line over magenta line)

image description


Update:

So, do I have to think it is a sort of "bug" of the plant solver (taht is: the software does not work properly itself)?

Ag


2nd Update I've used only adiabatic pipes, so there are no thermal losses along pipes.

Now I've atteched three images about the three nodes to focus on (according to the order with which they appear in the circuit):

  • 2ND HPFC-B SUPPLY SIDE OUTLET

  • 2ND HPFC-B DEMAND SIDE INLET

  • VRXHPCFXDHX:VrtlRmXBXHPCFXDHX Fan Coil Unit Cooling Coil Water Inlet Node

image 1: plant brnaches scheme

image 2: node water mass flow rates

image 3: node chilled water temperatures

then a link to the IDF file

Inconsistent Chilled Water Node Temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

Alessandro

Here another graph: node temps at supply side outlet node = node temp at demand side inlet node (light blue over blu line), and about mass flow rates (yellow line over magenta line)

image description


Update:

So, do I have to think it is a sort of "bug" of the plant solver (taht is: the software does not work properly itself)?

Ag

Inconsistent Chilled Water Node Temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

Alessandro

Here another graph: node temps at supply side outlet node = node temp at demand side inlet node (light blue over blu line), node, and about mass flow rates (yellow line over magenta line)rates

image description

Inconsistent Chilled Water Node Temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

Alessandro

Here another graph: node temps at supply side outlet node = node temp at demand side inlet node, and about mass flow rates

image description

Inconsistent Chilled Water Node Temperatureschilled water node temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop:

15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop)

15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards

regards Alessandro

Inconsistent chilled water node temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro

Inconsistent chilled water node temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the cooling chilling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one cooling chilling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro

Inconsistent chilled water node temperatures

Hi All,

I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main goal is to properly activate the chilling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one chilling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro

Inconsistent chilled water node temperatures

Hi All,

All, I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose main mai goal is to properly activate the chilling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one chilling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro

Inconsistent chilled water node temperatures

Hi All, I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose mai goal is to properly activate the chilling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one chilling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.png

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro

Inconsistent inconsistent chilled water node temperaturestemperature

Hi All, I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose mai goal is to properly activate the chilling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one chilling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

C:\fakepath\node temp.png

C:\fakepath\scheme svg.pngnode temperatures

plant scheme

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro

inconsistent chilled water node temperature

Hi All, I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose mai goal is to properly activate the chilling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one chilling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

node temperatures

plant scheme

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro

inconsistent chilled water node temperature

Hi All, I'm working on a complex chilled water plant on EnergyPlus via DesigBuilder, whose mai goal is to properly activate the chilling resources based on their capacity and COP that vary with external conditions (dry-cooler, open loop ground water source wells, air cooled water chiller ,...).

I spent many efforts without achieving a satisfactory solution (maybe the only effective solution is through the EMS... sorry for sharing the frustration), but what i found really disappointing are intermediate results that are impossible: in more than one chilling resources configuration I found that the inlet temperature to the water terminals ARE DIFFERENT than the outlet supply-side temperature of the same loop: 15,7 °C at the supply side outlet node vs. 22,7 °C at the inlet of the FCU cooling coil (2nd HPFC-B loop) 15,9 °C vs 22,3 °C (2nd CRAC-B)

Here two link to the graph and the scheme for a better understanding and for illustrating that the differencies are on THE SAME LOOP (scheme is a screnshot from the .svg file generated by EnergyPlus).

node temperatures

plant schemenode temperatures

plant scheme

I cannot guess how this is possible.

Any contribution is welcome

Best regards Alessandro