SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Output in version 8.3: Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C C:\fakepath\Modelo8.3.PNG
Output in version 9.1 C:\fakepath\Modelo9.1.PNG
SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Output in version 8.3:
8.3:
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C C:\fakepath\Modelo8.3.PNG02/21 12:00:00 26.021 7.036441441
02/21 12:15:00 26.187 6.954189189
02/21 12:30:00 26.353 6.871936937
02/21 12:45:00 26.519 6.789684685
02/21 13:00:00 26.685 6.707432432
02/21 13:15:00 26.78875 6.7
02/21 13:30:00 26.8925 6.7
02/21 13:45:00 26.99625 6.7
02/21 14:00:00 27.1 6.7
Output in version 9.1
C:\fakepath\Modelo9.1.PNG9.1
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511
SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Output in version 8.3:
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7
Output in version 9.1
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511
SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Output in version 8.3:
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7
Output in version 9.1
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511
SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Output in version 8.3:
Date/Time | Environment:Site Outdoor Air Drybulb Temperature C | CAG CHW SUPPLY OUTLET:System Node Temperature C
02/21 12:00:00 | 26.021 7.036441441
| 7.036441441
02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7
Output in version 9.1
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511
SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Output in version 8.3:
| Date/Time | Environment:Site Outdoor Air Drybulb Temperature C | CAG CHW SUPPLY OUTLET:System Node Temperature C |
| 02/21 12:00:00 | 26.021 | 7.0364414417.036441441 |
02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7
Output in version 9.1
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511
SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Output in version 8.3:
| Date/Time | Environment:Site Outdoor Air Drybulb Temperature C | CAG CHW SUPPLY OUTLET:System Node Temperature C |
| 02/21 12:00:00 | 26.021 | 7.036441441 |
7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7
Output in version 9.1
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511
SetpointManager:OutdoorAirReset
I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.
This is the control I am using:
SetpointManager:OutdoorAirReset,
CAG using:
IDF,SetpointManager:OutdoorAirReset,CAG ChW Temp Manager,
Temperature,
7.2,
15.6,
6.7,
26.7,
CAG Manager,Temperature, 7.2,15.6,6.7,26.7,CAG ChW Supply Setpoint Nodes,
,
,
,
,
;
Nodes,,,,,; Thank
Output in version 8.3:
8.3: Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7
Output in version 9.1
9.1
Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 8.48779409
02/21 12:15:00 26.187 9.433117172 9.433117172
02/21 12:30:00 26.353 8.665709466 8.665709466
02/21 12:45:00 26.519 9.14925803 9.14925803
02/21 13:00:00 26.685 8.77316689 8.77316689
02/21 13:15:00 26.78875 8.651484388 8.651484388
02/21 13:30:00 26.8925 8.694165106 8.694165106
02/21 13:45:00 26.99625 8.541134899 8.541134899
02/21 14:00:00 27.1 8.532365511