Revision history [back]
Meeting Humidity Setpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the first day of January and the first day of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
POST POST SCRIPT
I tried using the 5ZoneWaterCooled_MultizoneMinMaxRHControl.idf example file recommended by @luisclv. I replaced the Humidifier:Steam:Electric with an autosized EvaporativeCooler:Direct:CelDekPad object. Unfortunately it didn't work so well since the humidity is supposed to stay between 40% and 50%. I don't know if that's because the humidity controlling objects don't have the ability to control the evaporative cooler or if it just didn't work that well.
Date/Time SPACE2-1:Zone Air Relative Humidity [%](Hourly)
01/01 01:00:00 50.31020329
01/01 02:00:00 49.92701608
01/01 03:00:00 49.97986723
01/01 04:00:00 49.99523801
01/01 05:00:00 49.99736479
01/01 06:00:00 51.56680174
01/01 07:00:00 50.96907893
01/01 08:00:00 35.96658755
01/01 09:00:00 24.0836249
01/01 10:00:00 23.85472994
01/01 11:00:00 26.63164767
01/01 12:00:00 28.20424186
01/01 13:00:00 30.04195625
01/01 14:00:00 30.61109958
01/01 15:00:00 32.00336106
01/01 16:00:00 33.84653395
01/01 17:00:00 35.05209601
01/01 18:00:00 32.76993293
01/01 19:00:00 32.0742514
01/01 20:00:00 45.01971647
01/01 21:00:00 50.67298555
01/01 22:00:00 50.47234605
01/01 23:00:00 50.30046068
01/01 24:00:00 50.29144461
07/01 01:00:00 46.33591652
07/01 02:00:00 45.85390796
07/01 03:00:00 45.83639027
07/01 04:00:00 46.01406725
07/01 05:00:00 45.84379207
07/01 06:00:00 42.85281703
07/01 07:00:00 37.90633251
07/01 08:00:00 43.31965934
07/01 09:00:00 45.80833789
07/01 10:00:00 41.12565077
07/01 11:00:00 42.58446378
07/01 12:00:00 43.57519621
07/01 13:00:00 45.26842474
07/01 14:00:00 47.4660684
07/01 15:00:00 47.09151596
07/01 16:00:00 46.58557632
07/01 17:00:00 46.81683033
07/01 18:00:00 43.62628617
07/01 19:00:00 41.82965053
07/01 20:00:00 42.81176878
07/01 21:00:00 44.01306324
07/01 22:00:00 44.9922713
07/01 23:00:00 45.76207315
07/01 24:00:00 46.39585662
Meeting Humidity Setpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the first day of January and the first day of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
POST POST SCRIPT
I tried using the 5ZoneWaterCooled_MultizoneMinMaxRHControl.idf example file recommended by @luisclv. I replaced the Humidifier:Steam:Electric with an autosized EvaporativeCooler:Direct:CelDekPad object. Unfortunately it didn't work so well since the humidity is supposed to stay between 40% and 50%. well. I don't know if that's because the humidity controlling objects don't have the ability to control the evaporative cooler or if it just didn't work that well.
Date/Time SPACE2-1:Zone Air Relative Humidity [%](Hourly)
01/01 01:00:00 50.31020329
01/01 02:00:00 49.92701608
01/01 03:00:00 49.97986723
01/01 04:00:00 49.99523801
01/01 05:00:00 49.99736479
01/01 06:00:00 51.56680174
01/01 07:00:00 50.96907893
01/01 08:00:00 35.96658755
01/01 09:00:00 24.0836249
01/01 10:00:00 23.85472994
01/01 11:00:00 26.63164767
01/01 12:00:00 28.20424186
01/01 13:00:00 30.04195625
01/01 14:00:00 30.61109958
01/01 15:00:00 32.00336106
01/01 16:00:00 33.84653395
01/01 17:00:00 35.05209601
01/01 18:00:00 32.76993293
01/01 19:00:00 32.0742514
01/01 20:00:00 45.01971647
01/01 21:00:00 50.67298555
01/01 22:00:00 50.47234605
01/01 23:00:00 50.30046068
01/01 24:00:00 50.29144461
07/01 01:00:00 46.33591652
07/01 02:00:00 45.85390796
07/01 03:00:00 45.83639027
07/01 04:00:00 46.01406725
07/01 05:00:00 45.84379207
07/01 06:00:00 42.85281703
07/01 07:00:00 37.90633251
07/01 08:00:00 43.31965934
07/01 09:00:00 45.80833789
07/01 10:00:00 41.12565077
07/01 11:00:00 42.58446378
07/01 12:00:00 43.57519621
07/01 13:00:00 45.26842474
07/01 14:00:00 47.4660684
07/01 15:00:00 47.09151596
07/01 16:00:00 46.58557632
07/01 17:00:00 46.81683033
07/01 18:00:00 43.62628617
07/01 19:00:00 41.82965053
07/01 20:00:00 42.81176878
07/01 21:00:00 44.01306324
07/01 22:00:00 44.9922713
07/01 23:00:00 45.76207315
07/01 24:00:00 46.39585662
Meeting Humidity Setpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the two design days, the first day week of January January, and the first day week of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
12/21 01:00:00 22.48504471
12/21 02:00:00 22.48504471
12/21 03:00:00 22.48504482
12/21 04:00:00 22.4850445
12/21 05:00:00 22.48504492
12/21 06:00:00 22.48504441
12/21 07:00:00 22.4850446
12/21 08:00:00 22.48504482
12/21 09:00:00 22.48504492
12/21 10:00:00 22.48504482
12/21 11:00:00 22.48504482
12/21 12:00:00 22.48504461
12/21 13:00:00 22.4850445
12/21 14:00:00 22.48504503
12/21 15:00:00 22.48504482
12/21 16:00:00 22.48504482
12/21 17:00:00 22.48504461
12/21 18:00:00 22.48504471
12/21 19:00:00 22.48504466
12/21 20:00:00 22.48504469
12/21 21:00:00 22.48504481
12/21 22:00:00 22.48504482
12/21 23:00:00 22.48504455
12/21 24:00:00 22.48504461
08/21 01:00:00 35.83543615
08/21 02:00:00 35.835436
08/21 03:00:00 35.8354359
08/21 04:00:00 35.83543573
08/21 05:00:00 35.83543556
08/21 06:00:00 35.83543589
08/21 07:00:00 35.83543569
08/21 08:00:00 35.83543565
08/21 09:00:00 35.83543556
08/21 10:00:00 35.83543556
08/21 11:00:00 35.83543506
08/21 12:00:00 35.83543556
08/21 13:00:00 35.83543556
08/21 14:00:00 35.83543606
08/21 15:00:00 35.83543456
08/21 16:00:00 35.83543556
08/21 17:00:00 35.83543606
08/21 18:00:00 35.83543506
08/21 19:00:00 35.83543456
08/21 20:00:00 35.83543506
08/21 21:00:00 35.83543506
08/21 22:00:00 35.83543556
08/21 23:00:00 35.83543572
08/21 24:00:00 35.83543569
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
01/02 01:00:00 29.99843125
01/02 02:00:00 29.99843139
01/02 03:00:00 29.99843139
01/02 04:00:00 29.99843111
01/02 05:00:00 29.99843111
01/02 06:00:00 29.99843152
01/02 07:00:00 30.01718048
01/02 08:00:00 30.0471794
01/02 09:00:00 30.07717699
01/02 10:00:00 30.10717556
01/02 11:00:00 30.11842511
01/02 12:00:00 30.09967666
01/02 13:00:00 30.08842654
01/02 14:00:00 30.0696778
01/02 15:00:00 30.07717741
01/02 16:00:00 30.0884264
01/02 17:00:00 30.08842696
01/02 18:00:00 30.08842724
01/02 19:00:00 30.1071757
01/02 20:00:00 30.11842511
01/02 21:00:00 30.11842511
01/02 22:00:00 30.13717442
01/02 23:00:00 30.12967488
01/02 24:00:00 30.13717371
01/03 01:00:00 30.12967467
01/03 02:00:00 30.11842525
01/03 03:00:00 30.11842554
01/03 04:00:00 30.11842525
01/03 05:00:00 30.13717413
01/03 06:00:00 30.16717209
01/03 07:00:00 30.17842206
01/03 08:00:00 30.19717142
01/03 09:00:00 30.20842041
01/03 10:00:00 30.22716915
01/03 11:00:00 30.23841898
01/03 12:00:00 30.21967038
01/03 13:00:00 30.20842069
01/03 14:00:00 30.18967181
01/03 15:00:00 30.17842254
01/03 16:00:00 30.1784217
01/03 17:00:00 30.17842113
01/03 18:00:00 30.19717156
01/03 19:00:00 30.20842027
01/03 20:00:00 30.22716943
01/03 21:00:00 30.23841828
01/03 22:00:00 30.23841828
01/03 23:00:00 30.25716811
01/03 24:00:00 30.24966797
01/04 01:00:00 30.21966982
01/04 02:00:00 30.20842041
01/04 03:00:00 30.22716985
01/04 04:00:00 30.21966954
01/04 05:00:00 30.20842041
01/04 06:00:00 30.20842015
01/04 07:00:00 30.20842097
01/04 08:00:00 30.22716957
01/04 09:00:00 30.23841916
01/04 10:00:00 30.23841969
01/04 11:00:00 30.21967067
01/04 12:00:00 30.17092321
01/04 13:00:00 30.12967537
01/04 14:00:00 30.09967694
01/04 15:00:00 30.06967851
01/04 16:00:00 30.05842909
01/04 17:00:00 30.05842853
01/04 18:00:00 30.05842909
01/04 19:00:00 30.05842909
01/04 20:00:00 30.03968007
01/04 21:00:00 30.02843066
01/04 22:00:00 30.02843052
01/04 23:00:00 30.02843066
01/04 24:00:00 30.00968136
01/05 01:00:00 29.97968279
01/05 02:00:00 29.9684338
01/05 03:00:00 29.96843324
01/05 04:00:00 29.94968478
01/05 05:00:00 29.93843508
01/05 06:00:00 29.93843508
01/05 07:00:00 29.93843515
01/05 08:00:00 29.9571841
01/05 09:00:00 29.98718282
01/05 10:00:00 29.99843139
01/05 11:00:00 29.97968293
01/05 12:00:00 29.94968436
01/05 13:00:00 29.9196862
01/05 14:00:00 29.90843651
01/05 15:00:00 29.90843665
01/05 16:00:00 29.92718539
01/05 17:00:00 29.93843467
01/05 18:00:00 29.93843439
01/05 19:00:00 29.95718397
01/05 20:00:00 29.9684331
01/05 21:00:00 29.98718268
01/05 22:00:00 29.99843181
01/05 23:00:00 30.01718083
01/05 24:00:00 30.02842996
01/06 01:00:00 30.02843024
01/06 02:00:00 30.04717926
01/06 03:00:00 30.05842867
01/06 04:00:00 30.05842881
01/06 05:00:00 30.07717797
01/06 06:00:00 30.10717598
01/06 07:00:00 30.11842544
01/06 08:00:00 30.13717427
01/06 09:00:00 30.16717285
01/06 10:00:00 30.19717184
01/06 11:00:00 30.18967153
01/06 12:00:00 30.1784224
01/06 13:00:00 30.15967338
01/06 14:00:00 30.14842383
01/06 15:00:00 30.1484234
01/06 16:00:00 30.14842355
01/06 17:00:00 30.14842298
01/06 18:00:00 30.16717285
01/06 19:00:00 30.1784217
01/06 20:00:00 30.17842184
01/06 21:00:00 30.1784224
01/06 22:00:00 30.17842212
01/06 23:00:00 30.17842215
01/06 24:00:00 30.15967338
01/07 01:00:00 30.14842411
01/07 02:00:00 30.12967424
01/07 03:00:00 30.11842582
01/07 04:00:00 30.13717456
01/07 05:00:00 30.12967481
01/07 06:00:00 30.13717385
01/07 07:00:00 30.14842386
01/07 08:00:00 30.14842425
01/07 09:00:00 30.16717228
01/07 10:00:00 30.17842254
01/07 11:00:00 30.17842226
01/07 12:00:00 30.15967296
01/07 13:00:00 30.12967509
01/07 14:00:00 30.0996768
01/07 15:00:00 30.08842668
01/07 16:00:00 30.0884271
01/07 17:00:00 30.08842668
01/07 18:00:00 30.08842668
01/07 19:00:00 30.08842696
01/07 20:00:00 30.08842626
01/07 21:00:00 30.08842696
01/07 22:00:00 30.0884271
01/07 23:00:00 30.08842724
01/07 24:00:00 30.06967808
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
07/02 01:00:00 36.12686096
07/02 02:00:00 36.12686096
07/02 03:00:00 36.12686096
07/02 04:00:00 36.12685995
07/02 05:00:00 36.12685978
07/02 06:00:00 36.1268608
07/02 07:00:00 36.14955326
07/02 08:00:00 36.16316861
07/02 09:00:00 36.16316949
07/02 10:00:00 36.16316884
07/02 11:00:00 36.16316894
07/02 12:00:00 36.16316904
07/02 13:00:00 36.16316886
07/02 14:00:00 36.14047618
07/02 15:00:00 36.12686033
07/02 16:00:00 36.12686028
07/02 17:00:00 36.12686031
07/02 18:00:00 36.12686061
07/02 19:00:00 36.12686033
07/02 20:00:00 36.1268608
07/02 21:00:00 36.13981066
07/02 22:00:00 36.12534957
07/02 23:00:00 36.11940171
07/02 24:00:00 36.1194112
07/03 01:00:00 36.11941053
07/03 02:00:00 36.09674591
07/03 03:00:00 36.08314589
07/03 04:00:00 36.08314577
07/03 05:00:00 36.10581127
07/03 06:00:00 36.11941074
07/03 07:00:00 36.14207582
07/03 08:00:00 36.15567466
07/03 09:00:00 36.15567516
07/03 10:00:00 36.15567533
07/03 11:00:00 36.15567525
07/03 12:00:00 36.15567491
07/03 13:00:00 36.13300987
07/03 14:00:00 36.11941095
07/03 15:00:00 36.1194112
07/03 16:00:00 36.11941069
07/03 17:00:00 36.0967449
07/03 18:00:00 36.08314572
07/03 19:00:00 36.08314648
07/03 20:00:00 36.10581101
07/03 21:00:00 36.11941069
07/03 22:00:00 36.11940994
07/03 23:00:00 36.11941019
07/03 24:00:00 36.11941036
07/04 01:00:00 36.11941086
07/04 02:00:00 36.11941086
07/04 03:00:00 36.11941002
07/04 04:00:00 36.11940985
07/04 05:00:00 36.11933984
07/04 06:00:00 36.12153371
07/04 07:00:00 36.11364399
07/04 08:00:00 36.11369359
07/04 09:00:00 36.1136946
07/04 10:00:00 36.11369446
07/04 11:00:00 36.11369484
07/04 12:00:00 36.11369441
07/04 13:00:00 36.09105561
07/04 14:00:00 36.07747228
07/04 15:00:00 36.07747258
07/04 16:00:00 36.05483345
07/04 17:00:00 36.04125009
07/04 18:00:00 36.0412497
07/04 19:00:00 36.04124935
07/04 20:00:00 36.04124957
07/04 21:00:00 36.0412502
07/04 22:00:00 36.04125004
07/04 23:00:00 36.04124987
07/04 24:00:00 36.04125004
07/05 01:00:00 36.04124987
07/05 02:00:00 36.04125037
07/05 03:00:00 36.0412497
07/05 04:00:00 36.04124936
07/05 05:00:00 36.0412497
07/05 06:00:00 36.04124991
07/05 07:00:00 36.04125004
07/05 08:00:00 36.0412502
07/05 09:00:00 36.04124953
07/05 10:00:00 36.06388884
07/05 11:00:00 36.05483292
07/05 12:00:00 36.04124945
07/05 13:00:00 36.04125004
07/05 14:00:00 36.04125054
07/05 15:00:00 36.01861106
07/05 16:00:00 36.00502667
07/05 17:00:00 35.9823887
07/05 18:00:00 35.96880431
07/05 19:00:00 35.96880506
07/05 20:00:00 35.96880481
07/05 21:00:00 35.99144379
07/05 22:00:00 35.99912995
07/05 23:00:00 35.95881037
07/05 24:00:00 35.94770478
07/06 01:00:00 35.81016103
07/06 02:00:00 35.57496488
07/06 03:00:00 35.55758753
07/06 04:00:00 35.55241445
07/06 05:00:00 35.55244833
07/06 06:00:00 35.57480237
07/06 07:00:00 35.58821505
07/06 08:00:00 35.61056912
07/06 09:00:00 35.60162753
07/06 10:00:00 35.58821455
07/06 11:00:00 35.58821439
07/06 12:00:00 35.58821513
07/06 13:00:00 35.58821488
07/06 14:00:00 35.58821538
07/06 15:00:00 35.58821513
07/06 16:00:00 35.58821463
07/06 17:00:00 35.56585973
07/06 18:00:00 35.55244734
07/06 19:00:00 35.55244758
07/06 20:00:00 35.57480174
07/06 21:00:00 35.58821513
07/06 22:00:00 35.5882148
07/06 23:00:00 35.58821472
07/06 24:00:00 35.58821488
07/07 01:00:00 35.58821522
07/07 02:00:00 35.58821522
07/07 03:00:00 35.58821505
07/07 04:00:00 35.58821434
07/07 05:00:00 35.58821452
07/07 06:00:00 35.58821443
07/07 07:00:00 35.61056929
07/07 08:00:00 35.62398143
07/07 09:00:00 35.62398177
07/07 10:00:00 35.6239821
07/07 11:00:00 35.6239816
07/07 12:00:00 35.62398177
07/07 13:00:00 35.62398193
07/07 14:00:00 35.62398094
07/07 15:00:00 35.62398218
07/07 16:00:00 35.62398168
07/07 17:00:00 35.60162753
07/07 18:00:00 35.58821463
07/07 19:00:00 35.58821463
07/07 20:00:00 35.61056929
07/07 21:00:00 35.62398193
07/07 22:00:00 35.64633584
07/07 23:00:00 35.63739458
07/07 24:00:00 35.62398127
POST POST SCRIPT
I tried using the 5ZoneWaterCooled_MultizoneMinMaxRHControl.idf example file recommended by @luisclv. I replaced the Humidifier:Steam:Electric with an autosized EvaporativeCooler:Direct:CelDekPad object. Unfortunately it didn't work so well. I don't know if that's because the humidity controlling objects don't have the ability to control the evaporative cooler or if it just didn't work that well.using
Meeting Humidity Setpoint with Evaporative Mediain a Computer Room
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the two design days, the first week of January, and the first week of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
12/21 01:00:00 22.48504471
12/21 02:00:00 22.48504471
12/21 03:00:00 22.48504482
12/21 04:00:00 22.4850445
12/21 05:00:00 22.48504492
12/21 06:00:00 22.48504441
12/21 07:00:00 22.4850446
12/21 08:00:00 22.48504482
12/21 09:00:00 22.48504492
12/21 10:00:00 22.48504482
12/21 11:00:00 22.48504482
12/21 12:00:00 22.48504461
12/21 13:00:00 22.4850445
12/21 14:00:00 22.48504503
12/21 15:00:00 22.48504482
12/21 16:00:00 22.48504482
12/21 17:00:00 22.48504461
12/21 18:00:00 22.48504471
12/21 19:00:00 22.48504466
12/21 20:00:00 22.48504469
12/21 21:00:00 22.48504481
12/21 22:00:00 22.48504482
12/21 23:00:00 22.48504455
12/21 24:00:00 22.48504461
08/21 01:00:00 35.83543615
08/21 02:00:00 35.835436
08/21 03:00:00 35.8354359
08/21 04:00:00 35.83543573
08/21 05:00:00 35.83543556
08/21 06:00:00 35.83543589
08/21 07:00:00 35.83543569
08/21 08:00:00 35.83543565
08/21 09:00:00 35.83543556
08/21 10:00:00 35.83543556
08/21 11:00:00 35.83543506
08/21 12:00:00 35.83543556
08/21 13:00:00 35.83543556
08/21 14:00:00 35.83543606
08/21 15:00:00 35.83543456
08/21 16:00:00 35.83543556
08/21 17:00:00 35.83543606
08/21 18:00:00 35.83543506
08/21 19:00:00 35.83543456
08/21 20:00:00 35.83543506
08/21 21:00:00 35.83543506
08/21 22:00:00 35.83543556
08/21 23:00:00 35.83543572
08/21 24:00:00 35.83543569
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
01/02 01:00:00 29.99843125
01/02 02:00:00 29.99843139
01/02 03:00:00 29.99843139
01/02 04:00:00 29.99843111
01/02 05:00:00 29.99843111
01/02 06:00:00 29.99843152
01/02 07:00:00 30.01718048
01/02 08:00:00 30.0471794
01/02 09:00:00 30.07717699
01/02 10:00:00 30.10717556
01/02 11:00:00 30.11842511
01/02 12:00:00 30.09967666
01/02 13:00:00 30.08842654
01/02 14:00:00 30.0696778
01/02 15:00:00 30.07717741
01/02 16:00:00 30.0884264
01/02 17:00:00 30.08842696
01/02 18:00:00 30.08842724
01/02 19:00:00 30.1071757
01/02 20:00:00 30.11842511
01/02 21:00:00 30.11842511
01/02 22:00:00 30.13717442
01/02 23:00:00 30.12967488
01/02 24:00:00 30.13717371
01/03 01:00:00 30.12967467
01/03 02:00:00 30.11842525
01/03 03:00:00 30.11842554
01/03 04:00:00 30.11842525
01/03 05:00:00 30.13717413
01/03 06:00:00 30.16717209
01/03 07:00:00 30.17842206
01/03 08:00:00 30.19717142
01/03 09:00:00 30.20842041
01/03 10:00:00 30.22716915
01/03 11:00:00 30.23841898
01/03 12:00:00 30.21967038
01/03 13:00:00 30.20842069
01/03 14:00:00 30.18967181
01/03 15:00:00 30.17842254
01/03 16:00:00 30.1784217
01/03 17:00:00 30.17842113
01/03 18:00:00 30.19717156
01/03 19:00:00 30.20842027
01/03 20:00:00 30.22716943
01/03 21:00:00 30.23841828
01/03 22:00:00 30.23841828
01/03 23:00:00 30.25716811
01/03 24:00:00 30.24966797
01/04 01:00:00 30.21966982
01/04 02:00:00 30.20842041
01/04 03:00:00 30.22716985
01/04 04:00:00 30.21966954
01/04 05:00:00 30.20842041
01/04 06:00:00 30.20842015
01/04 07:00:00 30.20842097
01/04 08:00:00 30.22716957
01/04 09:00:00 30.23841916
01/04 10:00:00 30.23841969
01/04 11:00:00 30.21967067
01/04 12:00:00 30.17092321
01/04 13:00:00 30.12967537
01/04 14:00:00 30.09967694
01/04 15:00:00 30.06967851
01/04 16:00:00 30.05842909
01/04 17:00:00 30.05842853
01/04 18:00:00 30.05842909
01/04 19:00:00 30.05842909
01/04 20:00:00 30.03968007
01/04 21:00:00 30.02843066
01/04 22:00:00 30.02843052
01/04 23:00:00 30.02843066
01/04 24:00:00 30.00968136
01/05 01:00:00 29.97968279
01/05 02:00:00 29.9684338
01/05 03:00:00 29.96843324
01/05 04:00:00 29.94968478
01/05 05:00:00 29.93843508
01/05 06:00:00 29.93843508
01/05 07:00:00 29.93843515
01/05 08:00:00 29.9571841
01/05 09:00:00 29.98718282
01/05 10:00:00 29.99843139
01/05 11:00:00 29.97968293
01/05 12:00:00 29.94968436
01/05 13:00:00 29.9196862
01/05 14:00:00 29.90843651
01/05 15:00:00 29.90843665
01/05 16:00:00 29.92718539
01/05 17:00:00 29.93843467
01/05 18:00:00 29.93843439
01/05 19:00:00 29.95718397
01/05 20:00:00 29.9684331
01/05 21:00:00 29.98718268
01/05 22:00:00 29.99843181
01/05 23:00:00 30.01718083
01/05 24:00:00 30.02842996
01/06 01:00:00 30.02843024
01/06 02:00:00 30.04717926
01/06 03:00:00 30.05842867
01/06 04:00:00 30.05842881
01/06 05:00:00 30.07717797
01/06 06:00:00 30.10717598
01/06 07:00:00 30.11842544
01/06 08:00:00 30.13717427
01/06 09:00:00 30.16717285
01/06 10:00:00 30.19717184
01/06 11:00:00 30.18967153
01/06 12:00:00 30.1784224
01/06 13:00:00 30.15967338
01/06 14:00:00 30.14842383
01/06 15:00:00 30.1484234
01/06 16:00:00 30.14842355
01/06 17:00:00 30.14842298
01/06 18:00:00 30.16717285
01/06 19:00:00 30.1784217
01/06 20:00:00 30.17842184
01/06 21:00:00 30.1784224
01/06 22:00:00 30.17842212
01/06 23:00:00 30.17842215
01/06 24:00:00 30.15967338
01/07 01:00:00 30.14842411
01/07 02:00:00 30.12967424
01/07 03:00:00 30.11842582
01/07 04:00:00 30.13717456
01/07 05:00:00 30.12967481
01/07 06:00:00 30.13717385
01/07 07:00:00 30.14842386
01/07 08:00:00 30.14842425
01/07 09:00:00 30.16717228
01/07 10:00:00 30.17842254
01/07 11:00:00 30.17842226
01/07 12:00:00 30.15967296
01/07 13:00:00 30.12967509
01/07 14:00:00 30.0996768
01/07 15:00:00 30.08842668
01/07 16:00:00 30.0884271
01/07 17:00:00 30.08842668
01/07 18:00:00 30.08842668
01/07 19:00:00 30.08842696
01/07 20:00:00 30.08842626
01/07 21:00:00 30.08842696
01/07 22:00:00 30.0884271
01/07 23:00:00 30.08842724
01/07 24:00:00 30.06967808
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
07/02 01:00:00 36.12686096
07/02 02:00:00 36.12686096
07/02 03:00:00 36.12686096
07/02 04:00:00 36.12685995
07/02 05:00:00 36.12685978
07/02 06:00:00 36.1268608
07/02 07:00:00 36.14955326
07/02 08:00:00 36.16316861
07/02 09:00:00 36.16316949
07/02 10:00:00 36.16316884
07/02 11:00:00 36.16316894
07/02 12:00:00 36.16316904
07/02 13:00:00 36.16316886
07/02 14:00:00 36.14047618
07/02 15:00:00 36.12686033
07/02 16:00:00 36.12686028
07/02 17:00:00 36.12686031
07/02 18:00:00 36.12686061
07/02 19:00:00 36.12686033
07/02 20:00:00 36.1268608
07/02 21:00:00 36.13981066
07/02 22:00:00 36.12534957
07/02 23:00:00 36.11940171
07/02 24:00:00 36.1194112
07/03 01:00:00 36.11941053
07/03 02:00:00 36.09674591
07/03 03:00:00 36.08314589
07/03 04:00:00 36.08314577
07/03 05:00:00 36.10581127
07/03 06:00:00 36.11941074
07/03 07:00:00 36.14207582
07/03 08:00:00 36.15567466
07/03 09:00:00 36.15567516
07/03 10:00:00 36.15567533
07/03 11:00:00 36.15567525
07/03 12:00:00 36.15567491
07/03 13:00:00 36.13300987
07/03 14:00:00 36.11941095
07/03 15:00:00 36.1194112
07/03 16:00:00 36.11941069
07/03 17:00:00 36.0967449
07/03 18:00:00 36.08314572
07/03 19:00:00 36.08314648
07/03 20:00:00 36.10581101
07/03 21:00:00 36.11941069
07/03 22:00:00 36.11940994
07/03 23:00:00 36.11941019
07/03 24:00:00 36.11941036
07/04 01:00:00 36.11941086
07/04 02:00:00 36.11941086
07/04 03:00:00 36.11941002
07/04 04:00:00 36.11940985
07/04 05:00:00 36.11933984
07/04 06:00:00 36.12153371
07/04 07:00:00 36.11364399
07/04 08:00:00 36.11369359
07/04 09:00:00 36.1136946
07/04 10:00:00 36.11369446
07/04 11:00:00 36.11369484
07/04 12:00:00 36.11369441
07/04 13:00:00 36.09105561
07/04 14:00:00 36.07747228
07/04 15:00:00 36.07747258
07/04 16:00:00 36.05483345
07/04 17:00:00 36.04125009
07/04 18:00:00 36.0412497
07/04 19:00:00 36.04124935
07/04 20:00:00 36.04124957
07/04 21:00:00 36.0412502
07/04 22:00:00 36.04125004
07/04 23:00:00 36.04124987
07/04 24:00:00 36.04125004
07/05 01:00:00 36.04124987
07/05 02:00:00 36.04125037
07/05 03:00:00 36.0412497
07/05 04:00:00 36.04124936
07/05 05:00:00 36.0412497
07/05 06:00:00 36.04124991
07/05 07:00:00 36.04125004
07/05 08:00:00 36.0412502
07/05 09:00:00 36.04124953
07/05 10:00:00 36.06388884
07/05 11:00:00 36.05483292
07/05 12:00:00 36.04124945
07/05 13:00:00 36.04125004
07/05 14:00:00 36.04125054
07/05 15:00:00 36.01861106
07/05 16:00:00 36.00502667
07/05 17:00:00 35.9823887
07/05 18:00:00 35.96880431
07/05 19:00:00 35.96880506
07/05 20:00:00 35.96880481
07/05 21:00:00 35.99144379
07/05 22:00:00 35.99912995
07/05 23:00:00 35.95881037
07/05 24:00:00 35.94770478
07/06 01:00:00 35.81016103
07/06 02:00:00 35.57496488
07/06 03:00:00 35.55758753
07/06 04:00:00 35.55241445
07/06 05:00:00 35.55244833
07/06 06:00:00 35.57480237
07/06 07:00:00 35.58821505
07/06 08:00:00 35.61056912
07/06 09:00:00 35.60162753
07/06 10:00:00 35.58821455
07/06 11:00:00 35.58821439
07/06 12:00:00 35.58821513
07/06 13:00:00 35.58821488
07/06 14:00:00 35.58821538
07/06 15:00:00 35.58821513
07/06 16:00:00 35.58821463
07/06 17:00:00 35.56585973
07/06 18:00:00 35.55244734
07/06 19:00:00 35.55244758
07/06 20:00:00 35.57480174
07/06 21:00:00 35.58821513
07/06 22:00:00 35.5882148
07/06 23:00:00 35.58821472
07/06 24:00:00 35.58821488
07/07 01:00:00 35.58821522
07/07 02:00:00 35.58821522
07/07 03:00:00 35.58821505
07/07 04:00:00 35.58821434
07/07 05:00:00 35.58821452
07/07 06:00:00 35.58821443
07/07 07:00:00 35.61056929
07/07 08:00:00 35.62398143
07/07 09:00:00 35.62398177
07/07 10:00:00 35.6239821
07/07 11:00:00 35.6239816
07/07 12:00:00 35.62398177
07/07 13:00:00 35.62398193
07/07 14:00:00 35.62398094
07/07 15:00:00 35.62398218
07/07 16:00:00 35.62398168
07/07 17:00:00 35.60162753
07/07 18:00:00 35.58821463
07/07 19:00:00 35.58821463
07/07 20:00:00 35.61056929
07/07 21:00:00 35.62398193
07/07 22:00:00 35.64633584
07/07 23:00:00 35.63739458
07/07 24:00:00 35.62398127
POST POST SCRIPT
I tried using
Date/Time PLENUM-1:Zone Air Relative Humidity % SPACE1-1:Zone Air Relative Humidity % SPACE2-1:Zone Air Relative Humidity % SPACE3-1:Zone Air Relative Humidity % SPACE4-1:Zone Air Relative Humidity % SPACE5-1:Zone Air Relative Humidity % 01/01 01:00:00 51.39308405 50.6227215 50.31020329 50.61366559 50.35114189 47.38838323 01/01 02:00:00 51.12060459 50.40345454 49.92701608 50.38874014 49.95193632 46.49975974 01/01 03:00:00 51.66171635 50.39599998 49.97986723 50.38034475 49.99369154 46.17197987 01/01 04:00:00 52.40099555 50.33545801 49.99523801 50.30872292 50.01148337 45.83114765 01/01 05:00:00 53.03153832 50.31376554 49.99736479 50.2880775 50.00119 45.63775258 01/01 06:00:00 53.83007585 51.37589648 51.56680174 51.27313333 51.71770193 46.07728109 01/01 07:00:00 55.53692081 51.30309017 50.96907893 51.24080992 50.89709363 46.13626085 01/01 08:00:00 46.77669324 37.02046711 35.96658755 37.13803451 36.23723534 36.46840133 01/01 09:00:00 37.61503947 25.91919628 24.0836249 26.11045698 23.14873182 28.06367736 01/01 10:00:00 29.12824759 25.59864662 23.85472994 25.90522004 23.38431776 28.2954232 01/01 11:00:00 31.42517646 28.77039136 26.63164767 29.15415538 26.07282762 30.47431895 01/01 12:00:00 32.71248513 30.73082964 28.20424186 30.86736715 27.69516957 32.93819554 01/01 13:00:00 33.85435971 32.13633206 30.04195625 32.22851721 29.61738946 34.64025291 01/01 14:00:00 34.28482617 32.3589479 30.61109958 32.69990127 30.25084454 34.46706795 01/01 15:00:00 33.66819838 33.5351735 32.00336106 33.56496003 31.62344188 34.44557616 01/01 16:00:00 35.58122318 35.92777043 33.84653395 36.03023589 33.29161425 36.7888955 01/01 17:00:00 37.40854954 37.6911575 35.05209601 38.04793719 34.40210631 38.80756144 01/01 18:00:00 38.26087009 35.0609164 32.76993293 35.64694696 32.3067546 39.85674924 01/01 19:00:00 35.72110369 32.49592986 32.0742514 32.69962573 32.10213095 35.24884022 01/01 20:00:00 39.727088 42.64774329 45.01971647 42.29182268 45.93530245 40.04584019 01/01 21:00:00 47.67904603 49.71823512 50.67298555 49.40052883 50.91021943 45.62798205 01/01 22:00:00 49.58229555 50.41738831 50.47234605 50.30630984 50.58180247 47.03459938 01/01 23:00:00 50.21743229 50.3479494 50.30046068 50.30671967 50.39972228 47.41683987 01/01 24:00:00 50.74098158 50.31928614 50.29144461 50.30001159 50.38965699 47.52951122 01/02 01:00:00 51.13415178 50.26511235 50.26092975 50.2635493 50.35104876 47.52464572 01/02 02:00:00 51.47822739 50.24476058 50.25360056 50.24246213 50.33504975 47.52701143 01/02 03:00:00 51.72909715 50.26237803 50.25514405 50.2420259 50.32923089 47.50837155 01/02 04:00:00 51.91690795 50.28722272 50.21914945 50.2532367 50.2810871 47.42089376 01/02 05:00:00 52.04488289 50.28251704 50.17635341 50.24307993 50.23229676 47.26329943 01/02 06:00:00 52.26367004 50.28497846 50.14073327 50.24473774 50.18572794 47.13992804 01/02 07:00:00 52.45569679 50.31800465 50.16988659 50.27062143 50.21790398 47.02284795 01/02 08:00:00 49.38784131 41.09368535 41.18245885 41.12173625 41.31010183 41.15733228 01/02 09:00:00 45.1237594 35.7597072 34.85030557 35.87167349 34.59530378 36.81685865 01/02 10:00:00 42.820671 40.06123682 39.29832054 40.19953026 39.14992465 40.62499252 01/02 11:00:00 46.97931123 43.95837973 41.69509082 44.59625946 43.96557754 44.48096249 01/02 12:00:00 50.1055416 48.30247887 46.13222992 48.61962593 47.74941523 48.78539509 01/02 13:00:00 51.30550279 50.15168521 48.00397513 50.17680899 48.88402522 49.90675728 01/02 14:00:00 50.56743525 50.60865407 49.26524944 50.45544831 49.21371435 49.92138128 01/02 15:00:00 49.35639757 49.83650488 48.64463441 49.68659356 48.64971118 49.60759338 01/02 16:00:00 49.27766176 49.92733921 48.06844882 50.02092702 47.98211615 49.65390461 01/02 17:00:00 48.74556763 49.92231333 47.77257505 50.21587023 47.5436416 49.58829947 01/02 18:00:00 47.90582432 47.52370716 44.25562182 48.25030573 43.59509287 50.80182338 01/02 19:00:00 48.91504786 49.25865325 49.49156578 49.37649533 49.67616598 50.49021899 01/02 20:00:00 49.7593146 49.83401441 47.96697712 50.06146309 47.49251668 50.92475392 01/02 21:00:00 47.38403617 49.70572408 49.14170206 49.85353963 49.29053758 50.5284427 01/02 22:00:00 48.56880341 50.3528305 50.34383467 50.40375975 50.4962747 50.11439835 01/02 23:00:00 48.9481086 50.3519565 50.31633866 50.40004204 50.44230291 49.64431516 01/02 24:00:00 49.22964463 50.34633727 50.36014882 50.37680203 50.49115614 49.1490971 01/03 01:00:00 49.52405212 50.3663872 50.41269764 50.37012708 50.54200913 48.67372673 01/03 02:00:00 49.85447939 50.33211716 50.34413784 50.33242188 50.45512709 48.30361397 01/03 03:00:00 50.2733306 50.33955643 50.36132146 50.32606986 50.46970251 47.98471348 01/03 04:00:00 50.65423366 50.32744876 50.35000375 50.30136713 50.4536274 47.67656096 01/03 05:00:00 51.04300146 50.34843968 50.30721832 50.30913968 50.39197762 47.42116102 01/03 06:00:00 51.37343891 50.33418302 50.25012965 50.28500685 50.32839959 47.18244338 01/03 07:00:00 51.73339373 50.27832799 50.25533954 50.22622356 50.3354283 46.95040658 01/03 08:00:00 48.39947559 40.28834389 40.0738331 40.35422389 40.24102514 40.45009337 01/03 09:00:00 42.04456508 32.57663881 30.94188608 32.8426382 30.55122811 34.26384162 01/03 10:00:00 36.55992247 33.47531475 31.62691472 33.80157282 31.30844742 35.39863127 01/03 11:00:00 36.64619939 34.17284115 30.97245131 34.46246543 30.77043074 35.78961971 01/03 12:00:00 35.35971848 33.17789904 30.04347027 33.43339709 29.90627855 36.01525483 01/03 13:00:00 33.80133171 32.00511653 29.12661421 32.27536512 28.51610195 34.52639818 01/03 14:00:00 31.15874535 29.11358099 26.74093144 29.68706103 26.25470815 31.88877418 01/03 15:00:00 28.78715195 28.32609158 26.33779208 28.69426791 25.87157593 30.38568184 01/03 16:00:00 29.24007901 29.29823925 26.86577943 29.77871206 26.26494648 31.45040799 01/03 17:00:00 30.46171277 30.2191304 27.3264928 30.8145546 26.61791156 32.76201024 01/03 18:00:00 30.31364188 26.79359784 24.15816405 27.35177691 23.62195784 32.55654065 01/03 19:00:00 26.71518831 22.72524661 21.72948839 23.00409185 21.6169623 26.44541519 01/03 20:00:00 30.86136054 34.80072493 38.28670554 34.32462336 39.62993627 31.57170738 01/03 21:00:00 45.16952238 48.25862169 50.44738624 47.62796031 50.88859467 41.03364406 01/03 22:00:00 49.84715807 50.46012076 50.65378598 50.16645938 50.76507 44.25960597 01/03 23:00:00 51.92924103 51.63452077 51.85217806 51.39678356 52.0130334 45.69132148 01/03 24:00:00 53.09705762 51.81093101 51.95861708 51.61481454 52.12119011 46.0682922 01/04 01:00:00 53.74251435 51.59780603 51.7585093 51.41487561 51.88373148 45.98676962 01/04 02:00:00 54.38026917 51.28744599 51.26515826 51.13402264 51.30524077 45.85027173 01/04 03:00:00 54.60974435 51.66260521 51.86909963 51.48603912 52.01287296 46.01513813 01/04 04:00:00 54.8366233 51.47811576 51.69539432 51.29139554 51.81249056 45.76314778 01/04 05:00:00 55.23568151 51.1164313 51.09110839 50.96289194 51.11116088 45.63629234 01/04 06:00:00 55.31490669 51.47283985 51.78007887 51.28909592 51.92061888 45.86862371 01/04 07:00:00 55.55631633 51.40002055 51.61360782 51.226966 51.70841358 45.8662873 01/04 08:00:00 47.72200656 38.05891823 37.49430361 38.09356806 37.91873551 37.19106924 01/04 09:00:00 39.41610511 28.26431752 27.15372257 28.38161489 26.499099 29.43774683 01/04 10:00:00 31.10601151 26.36310989 24.38599072 26.68321567 23.7812686 28.99481388 01/04 11:00:00 30.68680265 27.19847584 24.65339097 27.67643806 24.0079913 29.60239506 01/04 12:00:00 30.70867444 27.93697226 25.26468678 28.4819997 24.62280576 30.71312732 01/04 13:00:00 30.62586463 27.62413488 25.01662638 28.16419849 24.40850489 30.95315434 01/04 14:00:00 28.89118162 25.54631867 23.59512992 25.9794381 23.19469379 28.88494101 01/04 15:00:00 27.27448748 25.82400799 24.20650819 26.17169816 23.80658575 27.91590431 01/04 16:00:00 27.99471657 26.80280852 24.45679045 27.25893539 23.84848236 29.3298183 01/04 17:00:00 28.54407623 27.01164171 24.20524047 27.56319247 23.51376694 30.55921558 01/04 18:00:00 28.1655107 23.76527103 21.35775893 24.26637304 20.86859451 29.40841728 01/04 19:00:00 24.61191169 20.46624893 19.78082302 20.67372163 19.73040101 23.57826903 01/04 20:00:00 29.59051114 33.25675906 36.82056144 32.71132256 38.1598057 29.36915867 01/04 21:00:00 45.14234594 48.99043016 51.47816441 48.15801544 52.07769497 39.93001645 01/04 22:00:00 51.31958452 51.88978509 51.93910738 51.42857317 52.07126274 43.83921512 01/04 23:00:00 52.66072204 51.66312563 51.71637583 51.40252871 51.85404179 45.04636645 01/04 24:00:00 53.95676286 51.32628518 51.10633494 51.1469446 51.12270557 45.36887491 01/05 01:00:00 54.42221281 51.45255952 51.64840242 51.24547727 51.7996283 45.40826689 01/05 02:00:00 55.25539412 51.45334199 51.52222943 51.26626016 51.59730843 45.53922425 01/05 03:00:00 55.77759158 51.16187073 50.9627197 51.0194747 50.95430346 45.57549275 01/05 04:00:00 55.91200598 51.59331023 51.66612149 51.41753102 51.77582064 45.80695321 01/05 05:00:00 56.02269581 51.49801341 51.52728455 51.30968471 51.61514379 45.54661472 01/05 06:00:00 56.12243038 51.15709515 51.07693917 50.97041812 51.10982332 45.10002841 01/05 07:00:00 56.17134935 51.52743072 51.61924504 51.32094228 51.72442503 45.20439928 01/05 08:00:00 55.26921044 46.13334412 47.75349274 46.00762761 48.32693519 44.13370542 01/05 09:00:00 61.71186632 49.22068817 50.37629212 49.05489075 50.71915515 46.89988521 01/05 10:00:00 63.36276468 50.32082786 51.13227095 50.13677618 51.32471733 48.08832902 01/05 11:00:00 62.31680578 50.35822285 51.24223309 50.18757903 51.42447763 48.53998537 01/05 12:00:00 60.72016579 50.46508525 51.31618668 50.30358166 51.48654284 48.83581703 01/05 13:00:00 59.03156482 50.59517171 51.43428631 50.44011093 51.60128112 49.04954958 01/05 14:00:00 58.09977033 50.71106788 51.5094715 50.55851658 51.66783586 49.2423756 01/05 15:00:00 54.60140814 45.87491911 48.27301247 51.48685106 48.34231311 48.98302312 01/05 16:00:00 50.53928166 42.70547625 50.38275829 51.77103538 49.98790757 47.63318137 01/05 17:00:00 49.83854032 44.67346962 49.49296908 50.98898153 48.6971274 45.70843306 01/05 18:00:00 51.02505702 48.31353757 51.38324212 51.60239887 51.18420281 44.97032961 01/05 19:00:00 53.00163348 49.66645455 51.10509737 51.41771613 50.89284771 44.34871656 01/05 20:00:00 53.90755643 50.83345621 51.73161805 51.70153823 51.71197641 44.14958601 01/05 21:00:00 54.92152971 51.1863073 51.51299849 51.57613498 51.49545223 43.78723585 01/05 22:00:00 55.82093036 51.09929315 51.04061424 51.23188795 50.98952417 43.30052371 01/05 23:00:00 56.68863179 51.75910479 51.76553084 51.71045576 51.80679082 43.37996508 01/05 24:00:00 57.7737843 52.03834405 51.84517213 51.90984294 51.85590634 43.37303976 01/06 01:00:00 58.28559157 51.67849196 51.3909822 51.49903775 51.37484802 42.77486375 01/06 02:00:00 58.82772194 51.65308573 51.24553463 51.4500714 51.19014705 42.515803 01/06 03:00:00 58.81292886 51.43904222 51.08932827 51.2241344 51.07252983 42.19391786 01/06 04:00:00 59.36150962 51.48446264 51.1237746 51.25847831 51.09349487 42.09364421 01/06 05:00:00 59.89038831 51.57884219 51.20351156 51.34273731 51.16882173 42.03767561 01/06 06:00:00 60.27836741 51.57279637 51.22581039 51.32458282 51.19332161 41.93299284 01/06 07:00:00 60.67337417 51.69640307 51.33375697 51.44384898 51.2875744 41.94645567 01/06 08:00:00 57.821632 45.45256399 45.06865682 45.36372096 46.68043736 40.87732556 01/06 09:00:00 61.7104814 47.68272405 45.70788454 47.8633959 49.84117466 45.28658468 01/06 10:00:00 65.0268819 48.53467446 48.48827181 49.23901008 50.80131387 46.94559212 01/06 11:00:00 65.22575265 48.84410841 50.09005977 49.84299882 51.05197629 46.87810616 01/06 12:00:00 64.12832722 49.21292809 50.64349906 49.95924864 50.98216029 46.91984674 01/06 13:00:00 62.34543228 49.12591058 50.66533406 49.69925778 51.00111789 46.62445212 01/06 14:00:00 60.96951578 49.21055652 50.7498321 49.60933582 51.07004927 46.61868903 01/06 15:00:00 57.210825 42.99485008 48.49668694 52.39036978 48.85771183 47.018713 01/06 16:00:00 51.60429329 40.67475113 50.4321132 51.98732886 50.3590985 45.22628144 01/06 17:00:00 51.39706511 43.47619197 49.51971535 50.92272641 48.91924947 43.51095892 01/06 18:00:00 52.41491836 47.39554909 51.20312998 51.29068642 51.08106708 42.91588573 01/06 19:00:00 54.37145511 49.04828362 50.91121369 51.14369675 50.75056778 42.65537806 01/06 20:00:00 55.26884865 50.28987159 51.4740138 51.3405798 51.48480706 42.72336537 01/06 21:00:00 56.23860071 50.74759365 51.3637434 51.22431498 51.38256297 42.66855702 01/06 22:00:00 57.11907813 50.79022158 50.94160457 50.96877258 50.9111128 42.58776439 01/06 23:00:00 57.64849023 51.26777835 51.47087474 51.25312028 51.52318172 42.78433689 01/06 24:00:00 58.47763965 51.55910555 51.54286769 51.46709515 51.54911059 43.08743724 01/07 01:00:00 59.07849927 51.82659426 51.53242499 51.70835264 51.47723888 43.4512721 01/07 02:00:00 58.68047172 51.43317013 51.04185453 51.30606964 50.99794356 43.2015311 01/07 03:00:00 58.7849193 51.37101205 51.05487783 51.2141389 51.01939431 43.04445225 01/07 04:00:00 59.0002911 51.36202475 51.04568386 51.19090317 51.00512442 42.97902712 01/07 05:00:00 59.09992214 51.30809402 51.0322987 51.12594914 50.99655461 42.86723987 01/07 06:00:00 59.4950424 51.5750809 51.21834763 51.40281938 51.15245905 43.09483771 01/07 07:00:00 60.04466769 51.87210084 51.39121004 51.71389686 51.30605278 43.39767531 01/07 08:00:00 45.69579818 33.3408966 30.7387181 33.47162707 31.80419565 31.24580893 01/07 09:00:00 29.49465296 21.8500391 19.86143413 22.05309121 22.32771011 21.9330526 01/07 10:00:00 24.55798704 18.66346912 16.92303739 18.1982633 15.41880932 20.18764515 01/07 11:00:00 20.56248665 16.74348931 13.21279258 16.84122088 11.63180548 20.53422739 01/07 12:00:00 18.61782979 15.78123974 12.45637874 16.34566076 11.91729842 20.48863725 01/07 13:00:00 17.95027807 15.24992298 12.95436009 16.14077162 12.24346501 20.20045735 01/07 14:00:00 16.63333098 14.11498474 11.95111384 14.52162011 11.45952685 18.46912723 01/07 15:00:00 15.41560633 14.08857196 12.89280682 14.93494501 12.50434477 17.84552259 01/07 16:00:00 17.16620944 16.2488238 14.5087669 17.32098312 13.89627001 20.30938367 01/07 17:00:00 18.70682868 18.21542132 14.98249365 18.28276699 14.29972769 22.00349114 01/07 18:00:00 18.1198257 14.80579025 12.49290632 14.95290313 12.23320689 19.54113459 01/07 19:00:00 15.68688534 13.66012828 14.00337847 13.73396904 14.20073201 15.599075 01/07 20:00:00 23.2977999 27.0470568 31.83470437 26.67989055 33.19092007 22.27472946 01/07 21:00:00 41.62680662 46.0516102 50.10349869 45.40013091 50.88677435 35.68341008 01/07 22:00:00 51.72828731 51.16115008 51.80414405 50.91415797 51.8353747 42.2956356 01/07 23:00:00 53.97037294 52.01163736 51.97478522 51.9305533 52.03055755 44.68559869 01/07 24:00:00 55.02033179 51.98006166 51.71995613 51.92566982 51.73815073 45.41591241 07/01 01:00:00 49.36715381 50.76484674 46.33591652 50.49925879 45.36735544 54.34325158 07/01 02:00:00 50.12665648 49.98573344 45.85390796 49.78620976 44.8978599 54.48034353 07/01 03:00:00 50.43239771 49.99871311 45.83639027 49.8066942 44.88206654 54.57827623 07/01 04:00:00 50.62542065 50.26111735 46.01406725 50.06799555 45.05681466 54.67912 07/01 05:00:00 50.80704473 50.59448006 45.84379207 49.6078206 45.26855698 54.76764263 07/01 06:00:00 50.54770647 50.22353541 42.85281703 45.48464493 44.66710283 54.60205301 07/01 07:00:00 49.67116857 48.94354273 37.90633251 40.82639152 43.25942157 53.98251632 07/01 08:00:00 46.5184492 47.43032571 43.31965934 43.9220089 45.90316374 49.56790305 07/01 09:00:00 47.12040732 49.52100073 45.80833789 47.41102894 49.86837508 50.11886051 07/01 10:00:00 43.90464917 47.90010928 41.12565077 45.51847886 46.27719982 49.83366702 07/01 11:00:00 41.50336468 46.36534337 42.58446378 45.76409657 46.90355755 49.74148526 07/01 12:00:00 40.72327796 46.64340531 43.57519621 45.60688444 46.76131148 50.08429307 07/01 13:00:00 40.4022739 47.03723515 45.26842474 46.32977347 47.69108484 50.16951348 07/01 14:00:00 40.2566871 47.62739055 47.4660684 47.15944498 49.36295117 50.17143473 07/01 15:00:00 40.23242907 47.57790708 47.09151596 46.91776545 48.00386876 50.04112883 07/01 16:00:00 39.97820389 47.51846474 46.58557632 46.59082953 46.76591782 50.12140789 07/01 17:00:00 39.99242869 47.69358009 46.81683033 46.66148402 46.68918269 50.17932983 07/01 18:00:00 40.6531965 47.29532325 43.62628617 46.56426115 42.69694805 50.99034078 07/01 19:00:00 39.50913646 45.95722102 41.82965053 45.32876312 40.95425515 50.32836329 07/01 20:00:00 41.10976146 47.30441958 42.81176878 46.75111331 41.83772168 51.26382307 07/01 21:00:00 42.97239407 48.55081017 44.01306324 48.10843009 43.04688212 52.13876394 07/01 22:00:00 44.86467555 49.55983614 44.9922713 49.18011222 44.02676491 52.91679073 07/01 23:00:00 46.62458547 50.331047 45.76207315 50.00579528 44.79351285 53.56442662 07/01 24:00:00 48.2001363 50.98974698 46.39585662 50.68791436 45.42166784 54.10581527 07/02 01:00:00 49.60598136 51.53464378 46.95222249 51.23656416 45.97089242 54.5627189 07/02 02:00:00 50.87248787 51.88035567 47.30405656 51.59813603 46.31795496 54.95104083 07/02 03:00:00 51.97130524 52.15723504 47.57858928 51.88381191 46.5880851 55.27008857 07/02 04:00:00 52.85391267 52.460252 47.8558408 52.18276792 46.86031547 55.57712117 07/02 05:00:00 53.52683652 52.5768996 47.60898786 51.59809626 46.95194948 55.8199301 07/02 06:00:00 53.64167079 52.08706935 44.76761456 47.65661465 46.29837049 55.79116262 07/02 07:00:00 52.90702561 51.03617155 39.95096778 43.13446166 44.98488394 55.29272925 07/02 08:00:00 48.99081421 47.12289949 44.03895041 45.11270622 45.49626969 50.09619172 07/02 09:00:00 48.6164662 49.30044092 46.39869866 48.27119986 49.74645746 50.11612055 07/02 10:00:00 45.31797484 48.67884462 41.64775609 46.41145955 46.50404996 50.08944736 07/02 11:00:00 42.34976915 46.75436942 42.31513213 46.03137132 47.17069102 49.82295047 07/02 12:00:00 41.18245227 46.91714718 43.16272363 46.08527199 47.19709145 50.06202126 07/02 13:00:00 40.20737594 47.17798111 45.16579452 46.76162008 48.35730836 50.15944367 07/02 14:00:00 39.45670703 47.61614292 47.79113124 47.48532348 49.62224276 50.16675271 07/02 15:00:00 38.83266795 47.3048354 47.35714931 47.31573457 46.27285474 50.10223458 07/02 16:00:00 38.09128008 46.836115 46.97828518 47.04882507 44.29193526 50.1200371 07/02 17:00:00 37.79064856 46.7985617 47.21858721 47.06997189 43.49399714 50.17634566 07/02 18:00:00 37.61240715 46.13962473 44.26409858 46.47379138 39.59513027 50.72819354 07/02 19:00:00 35.25527429 43.80798559 41.95260447 44.34139685 34.65960515 48.94985335 07/02 20:00:00 36.08736936 44.70316521 42.79267936 45.27837794 36.40007889 49.2151386 07/02 21:00:00 38.05865631 46.16076531 44.06187086 46.7178784 39.78185764 50.07145376 07/02 22:00:00 40.1609215 47.24618615 45.04853066 47.80044449 42.15330427 50.90974595 07/02 23:00:00 42.14217078 48.11864325 45.84401858 48.66279871 43.82085658 51.65147191 07/02 24:00:00 43.91315742 48.79620957 46.48549366 49.35129054 44.98620333 52.28361501 07/03 01:00:00 45.45880287 49.41793303 47.06870555 49.99014146 45.87330416 52.8112934 07/03 02:00:00 46.79215098 49.99486244 47.5937473 50.57462428 46.57127805 53.2268946 07/03 03:00:00 48.01168989 50.44645207 48.03216373 50.99483089 47.10988407 53.59669737 07/03 04:00:00 49.16664596 50.81334256 48.38736134 51.36047141 47.52165635 53.96691555 07/03 05:00:00 50.07988123 51.02761838 48.18341323 50.79747848 47.73882918 54.25166451 07/03 06:00:00 50.2781383 50.59505932 45.07631078 46.60733429 47.12121138 54.22739289 07/03 07:00:00 49.57480364 49.15440535 39.76955587 41.66716758 45.50918971 53.69275391 07/03 08:00:00 47.57061497 47.01971324 44.17514087 44.27263183 46.51583622 49.64830935 07/03 09:00:00 47.6587725 49.3717804 45.87884705 47.37654264 49.85131709 50.10508655 07/03 10:00:00 43.78618553 47.56200703 40.96799676 45.28436127 46.1651587 49.80320867 07/03 11:00:00 41.38099127 46.21894812 42.5090513 45.62587594 46.83780217 49.73944342 07/03 12:00:00 40.30234648 46.115151 43.28091156 45.46486681 46.5945661 50.07617466 07/03 13:00:00 39.47036206 46.47142942 45.08332289 46.19336828 47.41229806 50.16802679 07/03 14:00:00 38.75853516 47.1882219 46.76087438 47.0783973 48.37611198 50.16754657 07/03 15:00:00 38.2846002 46.80673405 46.41681422 46.73394321 45.8936192 50.12289221 07/03 16:00:00 37.62395328 46.42393554 46.05903473 46.29358299 44.84964521 50.12974205 07/03 17:00:00 37.4838845 46.20736935 46.20156224 46.1637844 43.83870207 50.18018816 07/03 18:00:00 37.14995116 44.93856878 44.54019929 44.98295236 39.09921248 50.83571652 07/03 19:00:00 34.37619522 41.78363789 40.68032689 42.08112173 33.57705785 48.83202922 07/03 20:00:00 34.53134347 41.73544895 40.62620647 42.15903438 34.38326258 48.6475291 07/03 21:00:00 35.81325622 42.70785771 41.44939646 43.14131465 37.39360458 49.18152044 07/03 22:00:00 37.25085211 43.56774414 42.18516341 43.97863638 39.48311447 49.82355075 07/03 23:00:00 38.67115182 44.40035159 42.89738572 44.77766986 41.01814868 50.4378393 07/03 24:00:00 40.00367076 45.20774177 43.59770759 45.56763365 42.19866065 50.97195026 07/04 01:00:00 41.23535485 45.72135572 44.09081538 46.08725647 42.97027475 51.40460476 07/04 02:00:00 42.3264327 46.1848116 44.53298739 46.5650773 43.56969768 51.75168237 07/04 03:00:00 43.31843718 46.55423092 44.89184849 46.93681501 44.01718825 52.07985815 07/04 04:00:00 44.19050417 46.71394967 45.08602231 47.10062123 44.26253279 52.36644017 07/04 05:00:00 44.88196453 46.93310822 45.28068911 47.30706056 44.48509338 52.58682425 07/04 06:00:00 45.37482844 46.96215073 45.09845877 47.10448851 44.35040903 52.73557617 07/04 07:00:00 45.61667253 46.56602453 44.31580852 46.24887947 43.70602083 52.77329313 07/04 08:00:00 45.80486686 47.12928417 47.21744447 47.17994891 47.28357438 48.77656974 07/04 09:00:00 47.67869725 49.80110336 50.30012254 49.72194835 50.37889257 49.57726534 07/04 10:00:00 45.11974278 48.17826709 45.08546225 47.01988556 47.77338544 50.13634265 07/04 11:00:00 42.2801224 45.84988349 43.21864145 45.62342097 45.82057614 49.7352672 07/04 12:00:00 40.52024684 45.482616 43.5045931 44.981331 45.55528986 50.06928621 07/04 13:00:00 39.58902835 46.18191772 45.10420814 45.86622484 46.69204388 50.17397305 07/04 14:00:00 39.31791167 47.22804891 47.66466541 46.92191378 49.61434568 50.11363683 07/04 15:00:00 39.86054221 47.66009827 47.43388449 47.0620277 48.41835716 50.04108946 07/04 16:00:00 39.9416231 47.3656779 46.60842606 46.56847248 46.35767521 50.11864411 07/04 17:00:00 39.99409269 47.57413673 47.13008554 46.83102425 47.03958147 50.18179666 07/04 18:00:00 40.67166066 47.26478096 43.60506435 46.86299792 42.67138453 51.02524128 07/04 19:00:00 39.44623861 45.65632858 41.75859029 45.39512317 40.92032444 50.38308943 07/04 20:00:00 40.87618455 46.50439233 42.32069232 46.29988824 41.38595898 51.25627357 07/04 21:00:00 42.39096856 47.37725912 43.13383132 47.22627363 42.20657391 51.9939237 07/04 22:00:00 43.85002269 48.28481151 43.90516891 48.13016788 42.97818297 52.59282432 07/04 23:00:00 45.3356256 49.05843134 44.59688361 48.91081593 43.66620986 53.12461495 07/04 24:00:00 46.73639654 49.34935231 44.99761383 49.26882592 44.06483585 53.59915391 07/05 01:00:00 47.79077507 48.98527591 44.77577755 48.94246172 43.85102166 53.0324692 07/05 02:00:00 48.5523186 49.06514782 44.86490812 49.04706831 43.94021797 52.9070951 07/05 03:00:00 49.24905609 49.42476803 45.15349766 49.41235117 44.22392401 53.00620992 07/05 04:00:00 49.96641066 49.75174397 45.43134922 49.7370891 44.49666054 53.16882208 07/05 05:00:00 50.60337345 50.03282286 45.34568011 49.38651997 44.71416389 53.34238354 07/05 06:00:00 50.67131493 49.42602688 42.44472415 45.3347319 43.98609802 53.28508867 07/05 07:00:00 49.86963065 47.890475 37.48484369 40.50759961 42.40818549 52.75581248 07/05 08:00:00 48.01859044 45.905589 32.72550352 37.45397959 40.53696115 51.82569892 07/05 09:00:00 45.32438474 43.72316981 29.05461353 36.36125202 38.68822252 50.71246741 07/05 10:00:00 42.18997421 41.79536467 27.17249692 36.77306673 37.0810972 49.67210634 07/05 11:00:00 39.12119136 40.19666348 26.95313559 37.20652718 35.77319078 48.73842181 07/05 12:00:00 36.5270961 38.81018369 27.96941735 36.98426838 34.59125932 47.8857491 07/05 13:00:00 34.11587739 37.96125076 29.81136235 36.85259643 33.82156017 47.2212901 07/05 14:00:00 31.95153465 37.19818238 31.0696889 36.47183329 32.33151724 46.62980348 07/05 15:00:00 30.46784722 36.95583042 31.7439856 36.17021709 30.78988555 46.08485931 07/05 16:00:00 29.99424909 37.55899405 32.61924946 36.56487452 30.80161788 45.80791385 07/05 17:00:00 30.64418101 39.14962547 34.29444407 38.16460701 32.65891305 45.97170684 07/05 18:00:00 32.10842025 40.94714934 36.1650398 40.0670321 34.79169123 46.60423158 07/05 19:00:00 33.98400503 42.32811244 37.75562828 41.65245339 36.55012309 47.37887902 07/05 20:00:00 35.98903824 43.84891202 39.43025731 43.43443642 38.3611433 48.1916578 07/05 21:00:00 38.09371056 45.22556038 40.87761134 44.9715398 39.88819589 49.05005247 07/05 22:00:00 40.19252404 46.25533716 41.95065627 46.07178598 41.00269004 49.83238376 07/05 23:00:00 42.14737825 47.07254937 42.78848822 46.93381596 41.85986617 50.49774357 07/05 24:00:00 43.87745697 47.73435931 43.44868299 47.62146731 42.52745763 51.06157656 07/06 01:00:00 45.4589899 48.37394318 44.05880107 48.27460134 43.13698635 51.62405697 07/06 02:00:00 46.87963324 48.86065773 44.54773763 48.78695863 43.62274286 52.12640217 07/06 03:00:00 48.1034616 49.26510163 44.96324095 49.23497949 44.03365014 52.54133238 07/06 04:00:00 49.11348471 49.54130079 45.24785525 49.53352682 44.31468899 52.86102627 07/06 05:00:00 49.87446885 49.67134788 45.05042418 49.03121434 44.41889446 53.1142455 07/06 06:00:00 50.01348817 49.12416687 42.38454217 45.29786724 43.70091701 53.135471 07/06 07:00:00 49.48565491 47.9145455 39.43115729 42.58800514 42.21008666 52.74226433 07/06 08:00:00 48.20470787 46.22145585 36.51246175 40.56532877 40.31140073 52.12382196 07/06 09:00:00 46.31972483 44.44915347 34.06664265 39.27342432 38.44444015 51.35208874 07/06 10:00:00 44.11073039 42.95006811 32.21808061 38.89414337 37.02962038 50.5458936 07/06 11:00:00 41.75724753 41.53151318 30.63200556 38.97205625 36.14251786 49.76953913 07/06 12:00:00 39.14409211 40.36893868 30.6836707 38.79293109 35.45897698 48.99093825 07/06 13:00:00 36.51261409 39.52057344 32.06652942 38.61417444 34.92067098 48.20583334 07/06 14:00:00 34.46320184 38.96714138 33.21128296 38.49899355 33.77742078 47.66790495 07/06 15:00:00 32.84727399 38.38214677 33.87882024 38.31332245 31.24281457 47.18631063 07/06 16:00:00 31.80282668 38.19138142 34.50773367 38.47689519 28.70609532 46.75913914 07/06 17:00:00 31.44793355 38.60210979 35.28866159 39.03775185 27.20647904 46.51434696 07/06 18:00:00 31.85558448 39.58867617 36.31836701 39.95959376 26.8980779 46.54266197 07/06 19:00:00 32.94551981 41.03213388 37.65029503 41.27016457 28.23872385 46.87257187 07/06 20:00:00 34.70609459 42.83731243 39.28388941 42.99969336 32.04678333 47.5243984 07/06 21:00:00 36.92284663 44.50330301 40.74225682 44.59835721 35.98604735 48.46453084 07/06 22:00:00 39.1836342 45.78236439 41.85315147 45.82222419 38.66329599 49.3848796 07/06 23:00:00 41.28369293 46.75802612 42.71069656 46.76283033 40.46044915 50.1668643 07/06 24:00:00 43.15544277 47.36361803 43.27570513 47.34465384 41.59173407 50.81987885 07/07 01:00:00 44.79039628 48.48660283 44.25865088 48.46369371 42.88601313 52.25239856 07/07 02:00:00 46.2246567 49.28884203 44.97881007 49.28477608 43.78595399 53.27905853 07/07 03:00:00 47.40670522 49.66705703 45.36261192 49.67594192 44.27596353 53.81842346 07/07 04:00:00 48.39175897 50.09123169 45.75156373 50.11505291 44.72245966 54.20354552 07/07 05:00:00 49.21242418 50.35302002 45.69409481 49.79320156 44.99353003 54.53815369 07/07 06:00:00 49.30276499 49.79704119 42.87891989 45.86858088 44.29886054 54.52568568 07/07 07:00:00 48.65249349 48.61609749 38.89256591 42.08960781 42.87725456 53.98235389 07/07 08:00:00 46.27350026 47.39351843 45.26630502 46.0674108 45.48904498 49.49845762 07/07 09:00:00 47.03117245 49.60578484 48.71980101 49.03475013 49.95825341 50.09659272 07/07 10:00:00 44.21980328 48.47021588 43.84233529 46.61021216 47.97782698 50.07586228 07/07 11:00:00 42.29641112 46.88310623 43.3091445 46.31031398 47.44298637 49.74264206 07/07 12:00:00 40.59469645 46.40379438 43.44198888 45.75331799 46.68319555 50.07387296 07/07 13:00:00 39.76767718 46.65842922 45.16701529 46.34760103 47.60400113 50.16461526 07/07 14:00:00 39.2521288 47.32550896 47.30999995 47.20248714 48.82848643 50.17415121 07/07 15:00:00 38.75127866 46.95151303 46.94214081 46.97979355 45.87426605 50.10348501 07/07 16:00:00 37.9913074 46.46124287 46.72841023 46.73900999 44.10651414 50.12409538 07/07 17:00:00 37.55625979 46.27755417 46.91831467 46.73618237 43.08766946 50.17779805 07/07 18:00:00 37.20579695 45.4570746 44.56519713 46.10736199 38.37817634 50.84516847 07/07 19:00:00 34.60378591 42.93350943 41.58816543 43.71525937 33.4391561 48.96420485 07/07 20:00:00 35.18236343 43.37209058 42.04501207 44.20063842 34.83680552 48.96034785 07/07 21:00:00 37.01094936 44.69387288 43.15791367 45.47251239 38.37297964 49.68570973 07/07 22:00:00 38.95616995 45.80171911 44.10188512 46.53480463 40.86668568 50.47212671 07/07 23:00:00 40.79868195 46.62390553 44.83946479 47.33729346 42.55221316 51.18011803 07/07 24:00:00 42.45468224 47.33871566 45.48621685 48.04409856 43.76077976 51.78827797
Meeting Humidity Setpoint in a Computer RoomSetpoint
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the two design days, the first week of January, and the first week of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
12/21 01:00:00 22.48504471
12/21 02:00:00 22.48504471
12/21 03:00:00 22.48504482
12/21 04:00:00 22.4850445
12/21 05:00:00 22.48504492
12/21 06:00:00 22.48504441
12/21 07:00:00 22.4850446
12/21 08:00:00 22.48504482
12/21 09:00:00 22.48504492
12/21 10:00:00 22.48504482
12/21 11:00:00 22.48504482
12/21 12:00:00 22.48504461
12/21 13:00:00 22.4850445
12/21 14:00:00 22.48504503
12/21 15:00:00 22.48504482
12/21 16:00:00 22.48504482
12/21 17:00:00 22.48504461
12/21 18:00:00 22.48504471
12/21 19:00:00 22.48504466
12/21 20:00:00 22.48504469
12/21 21:00:00 22.48504481
12/21 22:00:00 22.48504482
12/21 23:00:00 22.48504455
12/21 24:00:00 22.48504461
08/21 01:00:00 35.83543615
08/21 02:00:00 35.835436
08/21 03:00:00 35.8354359
08/21 04:00:00 35.83543573
08/21 05:00:00 35.83543556
08/21 06:00:00 35.83543589
08/21 07:00:00 35.83543569
08/21 08:00:00 35.83543565
08/21 09:00:00 35.83543556
08/21 10:00:00 35.83543556
08/21 11:00:00 35.83543506
08/21 12:00:00 35.83543556
08/21 13:00:00 35.83543556
08/21 14:00:00 35.83543606
08/21 15:00:00 35.83543456
08/21 16:00:00 35.83543556
08/21 17:00:00 35.83543606
08/21 18:00:00 35.83543506
08/21 19:00:00 35.83543456
08/21 20:00:00 35.83543506
08/21 21:00:00 35.83543506
08/21 22:00:00 35.83543556
08/21 23:00:00 35.83543572
08/21 24:00:00 35.83543569
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
01/02 01:00:00 29.99843125
01/02 02:00:00 29.99843139
01/02 03:00:00 29.99843139
01/02 04:00:00 29.99843111
01/02 05:00:00 29.99843111
01/02 06:00:00 29.99843152
01/02 07:00:00 30.01718048
01/02 08:00:00 30.0471794
01/02 09:00:00 30.07717699
01/02 10:00:00 30.10717556
01/02 11:00:00 30.11842511
01/02 12:00:00 30.09967666
01/02 13:00:00 30.08842654
01/02 14:00:00 30.0696778
01/02 15:00:00 30.07717741
01/02 16:00:00 30.0884264
01/02 17:00:00 30.08842696
01/02 18:00:00 30.08842724
01/02 19:00:00 30.1071757
01/02 20:00:00 30.11842511
01/02 21:00:00 30.11842511
01/02 22:00:00 30.13717442
01/02 23:00:00 30.12967488
01/02 24:00:00 30.13717371
01/03 01:00:00 30.12967467
01/03 02:00:00 30.11842525
01/03 03:00:00 30.11842554
01/03 04:00:00 30.11842525
01/03 05:00:00 30.13717413
01/03 06:00:00 30.16717209
01/03 07:00:00 30.17842206
01/03 08:00:00 30.19717142
01/03 09:00:00 30.20842041
01/03 10:00:00 30.22716915
01/03 11:00:00 30.23841898
01/03 12:00:00 30.21967038
01/03 13:00:00 30.20842069
01/03 14:00:00 30.18967181
01/03 15:00:00 30.17842254
01/03 16:00:00 30.1784217
01/03 17:00:00 30.17842113
01/03 18:00:00 30.19717156
01/03 19:00:00 30.20842027
01/03 20:00:00 30.22716943
01/03 21:00:00 30.23841828
01/03 22:00:00 30.23841828
01/03 23:00:00 30.25716811
01/03 24:00:00 30.24966797
01/04 01:00:00 30.21966982
01/04 02:00:00 30.20842041
01/04 03:00:00 30.22716985
01/04 04:00:00 30.21966954
01/04 05:00:00 30.20842041
01/04 06:00:00 30.20842015
01/04 07:00:00 30.20842097
01/04 08:00:00 30.22716957
01/04 09:00:00 30.23841916
01/04 10:00:00 30.23841969
01/04 11:00:00 30.21967067
01/04 12:00:00 30.17092321
01/04 13:00:00 30.12967537
01/04 14:00:00 30.09967694
01/04 15:00:00 30.06967851
01/04 16:00:00 30.05842909
01/04 17:00:00 30.05842853
01/04 18:00:00 30.05842909
01/04 19:00:00 30.05842909
01/04 20:00:00 30.03968007
01/04 21:00:00 30.02843066
01/04 22:00:00 30.02843052
01/04 23:00:00 30.02843066
01/04 24:00:00 30.00968136
01/05 01:00:00 29.97968279
01/05 02:00:00 29.9684338
01/05 03:00:00 29.96843324
01/05 04:00:00 29.94968478
01/05 05:00:00 29.93843508
01/05 06:00:00 29.93843508
01/05 07:00:00 29.93843515
01/05 08:00:00 29.9571841
01/05 09:00:00 29.98718282
01/05 10:00:00 29.99843139
01/05 11:00:00 29.97968293
01/05 12:00:00 29.94968436
01/05 13:00:00 29.9196862
01/05 14:00:00 29.90843651
01/05 15:00:00 29.90843665
01/05 16:00:00 29.92718539
01/05 17:00:00 29.93843467
01/05 18:00:00 29.93843439
01/05 19:00:00 29.95718397
01/05 20:00:00 29.9684331
01/05 21:00:00 29.98718268
01/05 22:00:00 29.99843181
01/05 23:00:00 30.01718083
01/05 24:00:00 30.02842996
01/06 01:00:00 30.02843024
01/06 02:00:00 30.04717926
01/06 03:00:00 30.05842867
01/06 04:00:00 30.05842881
01/06 05:00:00 30.07717797
01/06 06:00:00 30.10717598
01/06 07:00:00 30.11842544
01/06 08:00:00 30.13717427
01/06 09:00:00 30.16717285
01/06 10:00:00 30.19717184
01/06 11:00:00 30.18967153
01/06 12:00:00 30.1784224
01/06 13:00:00 30.15967338
01/06 14:00:00 30.14842383
01/06 15:00:00 30.1484234
01/06 16:00:00 30.14842355
01/06 17:00:00 30.14842298
01/06 18:00:00 30.16717285
01/06 19:00:00 30.1784217
01/06 20:00:00 30.17842184
01/06 21:00:00 30.1784224
01/06 22:00:00 30.17842212
01/06 23:00:00 30.17842215
01/06 24:00:00 30.15967338
01/07 01:00:00 30.14842411
01/07 02:00:00 30.12967424
01/07 03:00:00 30.11842582
01/07 04:00:00 30.13717456
01/07 05:00:00 30.12967481
01/07 06:00:00 30.13717385
01/07 07:00:00 30.14842386
01/07 08:00:00 30.14842425
01/07 09:00:00 30.16717228
01/07 10:00:00 30.17842254
01/07 11:00:00 30.17842226
01/07 12:00:00 30.15967296
01/07 13:00:00 30.12967509
01/07 14:00:00 30.0996768
01/07 15:00:00 30.08842668
01/07 16:00:00 30.0884271
01/07 17:00:00 30.08842668
01/07 18:00:00 30.08842668
01/07 19:00:00 30.08842696
01/07 20:00:00 30.08842626
01/07 21:00:00 30.08842696
01/07 22:00:00 30.0884271
01/07 23:00:00 30.08842724
01/07 24:00:00 30.06967808
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
07/02 01:00:00 36.12686096
07/02 02:00:00 36.12686096
07/02 03:00:00 36.12686096
07/02 04:00:00 36.12685995
07/02 05:00:00 36.12685978
07/02 06:00:00 36.1268608
07/02 07:00:00 36.14955326
07/02 08:00:00 36.16316861
07/02 09:00:00 36.16316949
07/02 10:00:00 36.16316884
07/02 11:00:00 36.16316894
07/02 12:00:00 36.16316904
07/02 13:00:00 36.16316886
07/02 14:00:00 36.14047618
07/02 15:00:00 36.12686033
07/02 16:00:00 36.12686028
07/02 17:00:00 36.12686031
07/02 18:00:00 36.12686061
07/02 19:00:00 36.12686033
07/02 20:00:00 36.1268608
07/02 21:00:00 36.13981066
07/02 22:00:00 36.12534957
07/02 23:00:00 36.11940171
07/02 24:00:00 36.1194112
07/03 01:00:00 36.11941053
07/03 02:00:00 36.09674591
07/03 03:00:00 36.08314589
07/03 04:00:00 36.08314577
07/03 05:00:00 36.10581127
07/03 06:00:00 36.11941074
07/03 07:00:00 36.14207582
07/03 08:00:00 36.15567466
07/03 09:00:00 36.15567516
07/03 10:00:00 36.15567533
07/03 11:00:00 36.15567525
07/03 12:00:00 36.15567491
07/03 13:00:00 36.13300987
07/03 14:00:00 36.11941095
07/03 15:00:00 36.1194112
07/03 16:00:00 36.11941069
07/03 17:00:00 36.0967449
07/03 18:00:00 36.08314572
07/03 19:00:00 36.08314648
07/03 20:00:00 36.10581101
07/03 21:00:00 36.11941069
07/03 22:00:00 36.11940994
07/03 23:00:00 36.11941019
07/03 24:00:00 36.11941036
07/04 01:00:00 36.11941086
07/04 02:00:00 36.11941086
07/04 03:00:00 36.11941002
07/04 04:00:00 36.11940985
07/04 05:00:00 36.11933984
07/04 06:00:00 36.12153371
07/04 07:00:00 36.11364399
07/04 08:00:00 36.11369359
07/04 09:00:00 36.1136946
07/04 10:00:00 36.11369446
07/04 11:00:00 36.11369484
07/04 12:00:00 36.11369441
07/04 13:00:00 36.09105561
07/04 14:00:00 36.07747228
07/04 15:00:00 36.07747258
07/04 16:00:00 36.05483345
07/04 17:00:00 36.04125009
07/04 18:00:00 36.0412497
07/04 19:00:00 36.04124935
07/04 20:00:00 36.04124957
07/04 21:00:00 36.0412502
07/04 22:00:00 36.04125004
07/04 23:00:00 36.04124987
07/04 24:00:00 36.04125004
07/05 01:00:00 36.04124987
07/05 02:00:00 36.04125037
07/05 03:00:00 36.0412497
07/05 04:00:00 36.04124936
07/05 05:00:00 36.0412497
07/05 06:00:00 36.04124991
07/05 07:00:00 36.04125004
07/05 08:00:00 36.0412502
07/05 09:00:00 36.04124953
07/05 10:00:00 36.06388884
07/05 11:00:00 36.05483292
07/05 12:00:00 36.04124945
07/05 13:00:00 36.04125004
07/05 14:00:00 36.04125054
07/05 15:00:00 36.01861106
07/05 16:00:00 36.00502667
07/05 17:00:00 35.9823887
07/05 18:00:00 35.96880431
07/05 19:00:00 35.96880506
07/05 20:00:00 35.96880481
07/05 21:00:00 35.99144379
07/05 22:00:00 35.99912995
07/05 23:00:00 35.95881037
07/05 24:00:00 35.94770478
07/06 01:00:00 35.81016103
07/06 02:00:00 35.57496488
07/06 03:00:00 35.55758753
07/06 04:00:00 35.55241445
07/06 05:00:00 35.55244833
07/06 06:00:00 35.57480237
07/06 07:00:00 35.58821505
07/06 08:00:00 35.61056912
07/06 09:00:00 35.60162753
07/06 10:00:00 35.58821455
07/06 11:00:00 35.58821439
07/06 12:00:00 35.58821513
07/06 13:00:00 35.58821488
07/06 14:00:00 35.58821538
07/06 15:00:00 35.58821513
07/06 16:00:00 35.58821463
07/06 17:00:00 35.56585973
07/06 18:00:00 35.55244734
07/06 19:00:00 35.55244758
07/06 20:00:00 35.57480174
07/06 21:00:00 35.58821513
07/06 22:00:00 35.5882148
07/06 23:00:00 35.58821472
07/06 24:00:00 35.58821488
07/07 01:00:00 35.58821522
07/07 02:00:00 35.58821522
07/07 03:00:00 35.58821505
07/07 04:00:00 35.58821434
07/07 05:00:00 35.58821452
07/07 06:00:00 35.58821443
07/07 07:00:00 35.61056929
07/07 08:00:00 35.62398143
07/07 09:00:00 35.62398177
07/07 10:00:00 35.6239821
07/07 11:00:00 35.6239816
07/07 12:00:00 35.62398177
07/07 13:00:00 35.62398193
07/07 14:00:00 35.62398094
07/07 15:00:00 35.62398218
07/07 16:00:00 35.62398168
07/07 17:00:00 35.60162753
07/07 18:00:00 35.58821463
07/07 19:00:00 35.58821463
07/07 20:00:00 35.61056929
07/07 21:00:00 35.62398193
07/07 22:00:00 35.64633584
07/07 23:00:00 35.63739458
07/07 24:00:00 35.62398127
Meeting Humidity SetpointSetpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the two design days, the first week of January, and the first week of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
12/21 01:00:00 22.48504471
12/21 02:00:00 22.48504471
12/21 03:00:00 22.48504482
12/21 04:00:00 22.4850445
12/21 05:00:00 22.48504492
12/21 06:00:00 22.48504441
12/21 07:00:00 22.4850446
12/21 08:00:00 22.48504482
12/21 09:00:00 22.48504492
12/21 10:00:00 22.48504482
12/21 11:00:00 22.48504482
12/21 12:00:00 22.48504461
12/21 13:00:00 22.4850445
12/21 14:00:00 22.48504503
12/21 15:00:00 22.48504482
12/21 16:00:00 22.48504482
12/21 17:00:00 22.48504461
12/21 18:00:00 22.48504471
12/21 19:00:00 22.48504466
12/21 20:00:00 22.48504469
12/21 21:00:00 22.48504481
12/21 22:00:00 22.48504482
12/21 23:00:00 22.48504455
12/21 24:00:00 22.48504461
08/21 01:00:00 35.83543615
08/21 02:00:00 35.835436
08/21 03:00:00 35.8354359
08/21 04:00:00 35.83543573
08/21 05:00:00 35.83543556
08/21 06:00:00 35.83543589
08/21 07:00:00 35.83543569
08/21 08:00:00 35.83543565
08/21 09:00:00 35.83543556
08/21 10:00:00 35.83543556
08/21 11:00:00 35.83543506
08/21 12:00:00 35.83543556
08/21 13:00:00 35.83543556
08/21 14:00:00 35.83543606
08/21 15:00:00 35.83543456
08/21 16:00:00 35.83543556
08/21 17:00:00 35.83543606
08/21 18:00:00 35.83543506
08/21 19:00:00 35.83543456
08/21 20:00:00 35.83543506
08/21 21:00:00 35.83543506
08/21 22:00:00 35.83543556
08/21 23:00:00 35.83543572
08/21 24:00:00 35.83543569
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
01/02 01:00:00 29.99843125
01/02 02:00:00 29.99843139
01/02 03:00:00 29.99843139
01/02 04:00:00 29.99843111
01/02 05:00:00 29.99843111
01/02 06:00:00 29.99843152
01/02 07:00:00 30.01718048
01/02 08:00:00 30.0471794
01/02 09:00:00 30.07717699
01/02 10:00:00 30.10717556
01/02 11:00:00 30.11842511
01/02 12:00:00 30.09967666
01/02 13:00:00 30.08842654
01/02 14:00:00 30.0696778
01/02 15:00:00 30.07717741
01/02 16:00:00 30.0884264
01/02 17:00:00 30.08842696
01/02 18:00:00 30.08842724
01/02 19:00:00 30.1071757
01/02 20:00:00 30.11842511
01/02 21:00:00 30.11842511
01/02 22:00:00 30.13717442
01/02 23:00:00 30.12967488
01/02 24:00:00 30.13717371
01/03 01:00:00 30.12967467
01/03 02:00:00 30.11842525
01/03 03:00:00 30.11842554
01/03 04:00:00 30.11842525
01/03 05:00:00 30.13717413
01/03 06:00:00 30.16717209
01/03 07:00:00 30.17842206
01/03 08:00:00 30.19717142
01/03 09:00:00 30.20842041
01/03 10:00:00 30.22716915
01/03 11:00:00 30.23841898
01/03 12:00:00 30.21967038
01/03 13:00:00 30.20842069
01/03 14:00:00 30.18967181
01/03 15:00:00 30.17842254
01/03 16:00:00 30.1784217
01/03 17:00:00 30.17842113
01/03 18:00:00 30.19717156
01/03 19:00:00 30.20842027
01/03 20:00:00 30.22716943
01/03 21:00:00 30.23841828
01/03 22:00:00 30.23841828
01/03 23:00:00 30.25716811
01/03 24:00:00 30.24966797
01/04 01:00:00 30.21966982
01/04 02:00:00 30.20842041
01/04 03:00:00 30.22716985
01/04 04:00:00 30.21966954
01/04 05:00:00 30.20842041
01/04 06:00:00 30.20842015
01/04 07:00:00 30.20842097
01/04 08:00:00 30.22716957
01/04 09:00:00 30.23841916
01/04 10:00:00 30.23841969
01/04 11:00:00 30.21967067
01/04 12:00:00 30.17092321
01/04 13:00:00 30.12967537
01/04 14:00:00 30.09967694
01/04 15:00:00 30.06967851
01/04 16:00:00 30.05842909
01/04 17:00:00 30.05842853
01/04 18:00:00 30.05842909
01/04 19:00:00 30.05842909
01/04 20:00:00 30.03968007
01/04 21:00:00 30.02843066
01/04 22:00:00 30.02843052
01/04 23:00:00 30.02843066
01/04 24:00:00 30.00968136
01/05 01:00:00 29.97968279
01/05 02:00:00 29.9684338
01/05 03:00:00 29.96843324
01/05 04:00:00 29.94968478
01/05 05:00:00 29.93843508
01/05 06:00:00 29.93843508
01/05 07:00:00 29.93843515
01/05 08:00:00 29.9571841
01/05 09:00:00 29.98718282
01/05 10:00:00 29.99843139
01/05 11:00:00 29.97968293
01/05 12:00:00 29.94968436
01/05 13:00:00 29.9196862
01/05 14:00:00 29.90843651
01/05 15:00:00 29.90843665
01/05 16:00:00 29.92718539
01/05 17:00:00 29.93843467
01/05 18:00:00 29.93843439
01/05 19:00:00 29.95718397
01/05 20:00:00 29.9684331
01/05 21:00:00 29.98718268
01/05 22:00:00 29.99843181
01/05 23:00:00 30.01718083
01/05 24:00:00 30.02842996
01/06 01:00:00 30.02843024
01/06 02:00:00 30.04717926
01/06 03:00:00 30.05842867
01/06 04:00:00 30.05842881
01/06 05:00:00 30.07717797
01/06 06:00:00 30.10717598
01/06 07:00:00 30.11842544
01/06 08:00:00 30.13717427
01/06 09:00:00 30.16717285
01/06 10:00:00 30.19717184
01/06 11:00:00 30.18967153
01/06 12:00:00 30.1784224
01/06 13:00:00 30.15967338
01/06 14:00:00 30.14842383
01/06 15:00:00 30.1484234
01/06 16:00:00 30.14842355
01/06 17:00:00 30.14842298
01/06 18:00:00 30.16717285
01/06 19:00:00 30.1784217
01/06 20:00:00 30.17842184
01/06 21:00:00 30.1784224
01/06 22:00:00 30.17842212
01/06 23:00:00 30.17842215
01/06 24:00:00 30.15967338
01/07 01:00:00 30.14842411
01/07 02:00:00 30.12967424
01/07 03:00:00 30.11842582
01/07 04:00:00 30.13717456
01/07 05:00:00 30.12967481
01/07 06:00:00 30.13717385
01/07 07:00:00 30.14842386
01/07 08:00:00 30.14842425
01/07 09:00:00 30.16717228
01/07 10:00:00 30.17842254
01/07 11:00:00 30.17842226
01/07 12:00:00 30.15967296
01/07 13:00:00 30.12967509
01/07 14:00:00 30.0996768
01/07 15:00:00 30.08842668
01/07 16:00:00 30.0884271
01/07 17:00:00 30.08842668
01/07 18:00:00 30.08842668
01/07 19:00:00 30.08842696
01/07 20:00:00 30.08842626
01/07 21:00:00 30.08842696
01/07 22:00:00 30.0884271
01/07 23:00:00 30.08842724
01/07 24:00:00 30.06967808
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
07/02 01:00:00 36.12686096
07/02 02:00:00 36.12686096
07/02 03:00:00 36.12686096
07/02 04:00:00 36.12685995
07/02 05:00:00 36.12685978
07/02 06:00:00 36.1268608
07/02 07:00:00 36.14955326
07/02 08:00:00 36.16316861
07/02 09:00:00 36.16316949
07/02 10:00:00 36.16316884
07/02 11:00:00 36.16316894
07/02 12:00:00 36.16316904
07/02 13:00:00 36.16316886
07/02 14:00:00 36.14047618
07/02 15:00:00 36.12686033
07/02 16:00:00 36.12686028
07/02 17:00:00 36.12686031
07/02 18:00:00 36.12686061
07/02 19:00:00 36.12686033
07/02 20:00:00 36.1268608
07/02 21:00:00 36.13981066
07/02 22:00:00 36.12534957
07/02 23:00:00 36.11940171
07/02 24:00:00 36.1194112
07/03 01:00:00 36.11941053
07/03 02:00:00 36.09674591
07/03 03:00:00 36.08314589
07/03 04:00:00 36.08314577
07/03 05:00:00 36.10581127
07/03 06:00:00 36.11941074
07/03 07:00:00 36.14207582
07/03 08:00:00 36.15567466
07/03 09:00:00 36.15567516
07/03 10:00:00 36.15567533
07/03 11:00:00 36.15567525
07/03 12:00:00 36.15567491
07/03 13:00:00 36.13300987
07/03 14:00:00 36.11941095
07/03 15:00:00 36.1194112
07/03 16:00:00 36.11941069
07/03 17:00:00 36.0967449
07/03 18:00:00 36.08314572
07/03 19:00:00 36.08314648
07/03 20:00:00 36.10581101
07/03 21:00:00 36.11941069
07/03 22:00:00 36.11940994
07/03 23:00:00 36.11941019
07/03 24:00:00 36.11941036
07/04 01:00:00 36.11941086
07/04 02:00:00 36.11941086
07/04 03:00:00 36.11941002
07/04 04:00:00 36.11940985
07/04 05:00:00 36.11933984
07/04 06:00:00 36.12153371
07/04 07:00:00 36.11364399
07/04 08:00:00 36.11369359
07/04 09:00:00 36.1136946
07/04 10:00:00 36.11369446
07/04 11:00:00 36.11369484
07/04 12:00:00 36.11369441
07/04 13:00:00 36.09105561
07/04 14:00:00 36.07747228
07/04 15:00:00 36.07747258
07/04 16:00:00 36.05483345
07/04 17:00:00 36.04125009
07/04 18:00:00 36.0412497
07/04 19:00:00 36.04124935
07/04 20:00:00 36.04124957
07/04 21:00:00 36.0412502
07/04 22:00:00 36.04125004
07/04 23:00:00 36.04124987
07/04 24:00:00 36.04125004
07/05 01:00:00 36.04124987
07/05 02:00:00 36.04125037
07/05 03:00:00 36.0412497
07/05 04:00:00 36.04124936
07/05 05:00:00 36.0412497
07/05 06:00:00 36.04124991
07/05 07:00:00 36.04125004
07/05 08:00:00 36.0412502
07/05 09:00:00 36.04124953
07/05 10:00:00 36.06388884
07/05 11:00:00 36.05483292
07/05 12:00:00 36.04124945
07/05 13:00:00 36.04125004
07/05 14:00:00 36.04125054
07/05 15:00:00 36.01861106
07/05 16:00:00 36.00502667
07/05 17:00:00 35.9823887
07/05 18:00:00 35.96880431
07/05 19:00:00 35.96880506
07/05 20:00:00 35.96880481
07/05 21:00:00 35.99144379
07/05 22:00:00 35.99912995
07/05 23:00:00 35.95881037
07/05 24:00:00 35.94770478
07/06 01:00:00 35.81016103
07/06 02:00:00 35.57496488
07/06 03:00:00 35.55758753
07/06 04:00:00 35.55241445
07/06 05:00:00 35.55244833
07/06 06:00:00 35.57480237
07/06 07:00:00 35.58821505
07/06 08:00:00 35.61056912
07/06 09:00:00 35.60162753
07/06 10:00:00 35.58821455
07/06 11:00:00 35.58821439
07/06 12:00:00 35.58821513
07/06 13:00:00 35.58821488
07/06 14:00:00 35.58821538
07/06 15:00:00 35.58821513
07/06 16:00:00 35.58821463
07/06 17:00:00 35.56585973
07/06 18:00:00 35.55244734
07/06 19:00:00 35.55244758
07/06 20:00:00 35.57480174
07/06 21:00:00 35.58821513
07/06 22:00:00 35.5882148
07/06 23:00:00 35.58821472
07/06 24:00:00 35.58821488
07/07 01:00:00 35.58821522
07/07 02:00:00 35.58821522
07/07 03:00:00 35.58821505
07/07 04:00:00 35.58821434
07/07 05:00:00 35.58821452
07/07 06:00:00 35.58821443
07/07 07:00:00 35.61056929
07/07 08:00:00 35.62398143
07/07 09:00:00 35.62398177
07/07 10:00:00 35.6239821
07/07 11:00:00 35.6239816
07/07 12:00:00 35.62398177
07/07 13:00:00 35.62398193
07/07 14:00:00 35.62398094
07/07 15:00:00 35.62398218
07/07 16:00:00 35.62398168
07/07 17:00:00 35.60162753
07/07 18:00:00 35.58821463
07/07 19:00:00 35.58821463
07/07 20:00:00 35.61056929
07/07 21:00:00 35.62398193
07/07 22:00:00 35.64633584
07/07 23:00:00 35.63739458
07/07 24:00:00 35.62398127
Meeting Humidity Setpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the two design days, the first week of January, and the first week of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
12/21 01:00:00 22.48504471
12/21 02:00:00 22.48504471
12/21 03:00:00 22.48504482
12/21 04:00:00 22.4850445
12/21 05:00:00 22.48504492
12/21 06:00:00 22.48504441
12/21 07:00:00 22.4850446
12/21 08:00:00 22.48504482
12/21 09:00:00 22.48504492
12/21 10:00:00 22.48504482
12/21 11:00:00 22.48504482
12/21 12:00:00 22.48504461
12/21 13:00:00 22.4850445
12/21 14:00:00 22.48504503
12/21 15:00:00 22.48504482
12/21 16:00:00 22.48504482
12/21 17:00:00 22.48504461
12/21 18:00:00 22.48504471
12/21 19:00:00 22.48504466
12/21 20:00:00 22.48504469
12/21 21:00:00 22.48504481
12/21 22:00:00 22.48504482
12/21 23:00:00 22.48504455
12/21 24:00:00 22.48504461
08/21 01:00:00 35.83543615
08/21 02:00:00 35.835436
08/21 03:00:00 35.8354359
08/21 04:00:00 35.83543573
08/21 05:00:00 35.83543556
08/21 06:00:00 35.83543589
08/21 07:00:00 35.83543569
08/21 08:00:00 35.83543565
08/21 09:00:00 35.83543556
08/21 10:00:00 35.83543556
08/21 11:00:00 35.83543506
08/21 12:00:00 35.83543556
08/21 13:00:00 35.83543556
08/21 14:00:00 35.83543606
08/21 15:00:00 35.83543456
08/21 16:00:00 35.83543556
08/21 17:00:00 35.83543606
08/21 18:00:00 35.83543506
08/21 19:00:00 35.83543456
08/21 20:00:00 35.83543506
08/21 21:00:00 35.83543506
08/21 22:00:00 35.83543556
08/21 23:00:00 35.83543572
08/21 24:00:00 35.83543569
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
01/02 01:00:00 29.99843125
01/02 02:00:00 29.99843139
01/02 03:00:00 29.99843139
01/02 04:00:00 29.99843111
01/02 05:00:00 29.99843111
01/02 06:00:00 29.99843152
01/02 07:00:00 30.01718048
01/02 08:00:00 30.0471794
01/02 09:00:00 30.07717699
01/02 10:00:00 30.10717556
01/02 11:00:00 30.11842511
01/02 12:00:00 30.09967666
01/02 13:00:00 30.08842654
01/02 14:00:00 30.0696778
01/02 15:00:00 30.07717741
01/02 16:00:00 30.0884264
01/02 17:00:00 30.08842696
01/02 18:00:00 30.08842724
01/02 19:00:00 30.1071757
01/02 20:00:00 30.11842511
01/02 21:00:00 30.11842511
01/02 22:00:00 30.13717442
01/02 23:00:00 30.12967488
01/02 24:00:00 30.13717371
01/03 01:00:00 30.12967467
01/03 02:00:00 30.11842525
01/03 03:00:00 30.11842554
01/03 04:00:00 30.11842525
01/03 05:00:00 30.13717413
01/03 06:00:00 30.16717209
01/03 07:00:00 30.17842206
01/03 08:00:00 30.19717142
01/03 09:00:00 30.20842041
01/03 10:00:00 30.22716915
01/03 11:00:00 30.23841898
01/03 12:00:00 30.21967038
01/03 13:00:00 30.20842069
01/03 14:00:00 30.18967181
01/03 15:00:00 30.17842254
01/03 16:00:00 30.1784217
01/03 17:00:00 30.17842113
01/03 18:00:00 30.19717156
01/03 19:00:00 30.20842027
01/03 20:00:00 30.22716943
01/03 21:00:00 30.23841828
01/03 22:00:00 30.23841828
01/03 23:00:00 30.25716811
01/03 24:00:00 30.24966797
01/04 01:00:00 30.21966982
01/04 02:00:00 30.20842041
01/04 03:00:00 30.22716985
01/04 04:00:00 30.21966954
01/04 05:00:00 30.20842041
01/04 06:00:00 30.20842015
01/04 07:00:00 30.20842097
01/04 08:00:00 30.22716957
01/04 09:00:00 30.23841916
01/04 10:00:00 30.23841969
01/04 11:00:00 30.21967067
01/04 12:00:00 30.17092321
01/04 13:00:00 30.12967537
01/04 14:00:00 30.09967694
01/04 15:00:00 30.06967851
01/04 16:00:00 30.05842909
01/04 17:00:00 30.05842853
01/04 18:00:00 30.05842909
01/04 19:00:00 30.05842909
01/04 20:00:00 30.03968007
01/04 21:00:00 30.02843066
01/04 22:00:00 30.02843052
01/04 23:00:00 30.02843066
01/04 24:00:00 30.00968136
01/05 01:00:00 29.97968279
01/05 02:00:00 29.9684338
01/05 03:00:00 29.96843324
01/05 04:00:00 29.94968478
01/05 05:00:00 29.93843508
01/05 06:00:00 29.93843508
01/05 07:00:00 29.93843515
01/05 08:00:00 29.9571841
01/05 09:00:00 29.98718282
01/05 10:00:00 29.99843139
01/05 11:00:00 29.97968293
01/05 12:00:00 29.94968436
01/05 13:00:00 29.9196862
01/05 14:00:00 29.90843651
01/05 15:00:00 29.90843665
01/05 16:00:00 29.92718539
01/05 17:00:00 29.93843467
01/05 18:00:00 29.93843439
01/05 19:00:00 29.95718397
01/05 20:00:00 29.9684331
01/05 21:00:00 29.98718268
01/05 22:00:00 29.99843181
01/05 23:00:00 30.01718083
01/05 24:00:00 30.02842996
01/06 01:00:00 30.02843024
01/06 02:00:00 30.04717926
01/06 03:00:00 30.05842867
01/06 04:00:00 30.05842881
01/06 05:00:00 30.07717797
01/06 06:00:00 30.10717598
01/06 07:00:00 30.11842544
01/06 08:00:00 30.13717427
01/06 09:00:00 30.16717285
01/06 10:00:00 30.19717184
01/06 11:00:00 30.18967153
01/06 12:00:00 30.1784224
01/06 13:00:00 30.15967338
01/06 14:00:00 30.14842383
01/06 15:00:00 30.1484234
01/06 16:00:00 30.14842355
01/06 17:00:00 30.14842298
01/06 18:00:00 30.16717285
01/06 19:00:00 30.1784217
01/06 20:00:00 30.17842184
01/06 21:00:00 30.1784224
01/06 22:00:00 30.17842212
01/06 23:00:00 30.17842215
01/06 24:00:00 30.15967338
01/07 01:00:00 30.14842411
01/07 02:00:00 30.12967424
01/07 03:00:00 30.11842582
01/07 04:00:00 30.13717456
01/07 05:00:00 30.12967481
01/07 06:00:00 30.13717385
01/07 07:00:00 30.14842386
01/07 08:00:00 30.14842425
01/07 09:00:00 30.16717228
01/07 10:00:00 30.17842254
01/07 11:00:00 30.17842226
01/07 12:00:00 30.15967296
01/07 13:00:00 30.12967509
01/07 14:00:00 30.0996768
01/07 15:00:00 30.08842668
01/07 16:00:00 30.0884271
01/07 17:00:00 30.08842668
01/07 18:00:00 30.08842668
01/07 19:00:00 30.08842696
01/07 20:00:00 30.08842626
01/07 21:00:00 30.08842696
01/07 22:00:00 30.0884271
01/07 23:00:00 30.08842724
01/07 24:00:00 30.06967808
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
07/02 01:00:00 36.12686096
07/02 02:00:00 36.12686096
07/02 03:00:00 36.12686096
07/02 04:00:00 36.12685995
07/02 05:00:00 36.12685978
07/02 06:00:00 36.1268608
07/02 07:00:00 36.14955326
07/02 08:00:00 36.16316861
07/02 09:00:00 36.16316949
07/02 10:00:00 36.16316884
07/02 11:00:00 36.16316894
07/02 12:00:00 36.16316904
07/02 13:00:00 36.16316886
07/02 14:00:00 36.14047618
07/02 15:00:00 36.12686033
07/02 16:00:00 36.12686028
07/02 17:00:00 36.12686031
07/02 18:00:00 36.12686061
07/02 19:00:00 36.12686033
07/02 20:00:00 36.1268608
07/02 21:00:00 36.13981066
07/02 22:00:00 36.12534957
07/02 23:00:00 36.11940171
07/02 24:00:00 36.1194112
07/03 01:00:00 36.11941053
07/03 02:00:00 36.09674591
07/03 03:00:00 36.08314589
07/03 04:00:00 36.08314577
07/03 05:00:00 36.10581127
07/03 06:00:00 36.11941074
07/03 07:00:00 36.14207582
07/03 08:00:00 36.15567466
07/03 09:00:00 36.15567516
07/03 10:00:00 36.15567533
07/03 11:00:00 36.15567525
07/03 12:00:00 36.15567491
07/03 13:00:00 36.13300987
07/03 14:00:00 36.11941095
07/03 15:00:00 36.1194112
07/03 16:00:00 36.11941069
07/03 17:00:00 36.0967449
07/03 18:00:00 36.08314572
07/03 19:00:00 36.08314648
07/03 20:00:00 36.10581101
07/03 21:00:00 36.11941069
07/03 22:00:00 36.11940994
07/03 23:00:00 36.11941019
07/03 24:00:00 36.11941036
07/04 01:00:00 36.11941086
07/04 02:00:00 36.11941086
07/04 03:00:00 36.11941002
07/04 04:00:00 36.11940985
07/04 05:00:00 36.11933984
07/04 06:00:00 36.12153371
07/04 07:00:00 36.11364399
07/04 08:00:00 36.11369359
07/04 09:00:00 36.1136946
07/04 10:00:00 36.11369446
07/04 11:00:00 36.11369484
07/04 12:00:00 36.11369441
07/04 13:00:00 36.09105561
07/04 14:00:00 36.07747228
07/04 15:00:00 36.07747258
07/04 16:00:00 36.05483345
07/04 17:00:00 36.04125009
07/04 18:00:00 36.0412497
07/04 19:00:00 36.04124935
07/04 20:00:00 36.04124957
07/04 21:00:00 36.0412502
07/04 22:00:00 36.04125004
07/04 23:00:00 36.04124987
07/04 24:00:00 36.04125004
07/05 01:00:00 36.04124987
07/05 02:00:00 36.04125037
07/05 03:00:00 36.0412497
07/05 04:00:00 36.04124936
07/05 05:00:00 36.0412497
07/05 06:00:00 36.04124991
07/05 07:00:00 36.04125004
07/05 08:00:00 36.0412502
07/05 09:00:00 36.04124953
07/05 10:00:00 36.06388884
07/05 11:00:00 36.05483292
07/05 12:00:00 36.04124945
07/05 13:00:00 36.04125004
07/05 14:00:00 36.04125054
07/05 15:00:00 36.01861106
07/05 16:00:00 36.00502667
07/05 17:00:00 35.9823887
07/05 18:00:00 35.96880431
07/05 19:00:00 35.96880506
07/05 20:00:00 35.96880481
07/05 21:00:00 35.99144379
07/05 22:00:00 35.99912995
07/05 23:00:00 35.95881037
07/05 24:00:00 35.94770478
07/06 01:00:00 35.81016103
07/06 02:00:00 35.57496488
07/06 03:00:00 35.55758753
07/06 04:00:00 35.55241445
07/06 05:00:00 35.55244833
07/06 06:00:00 35.57480237
07/06 07:00:00 35.58821505
07/06 08:00:00 35.61056912
07/06 09:00:00 35.60162753
07/06 10:00:00 35.58821455
07/06 11:00:00 35.58821439
07/06 12:00:00 35.58821513
07/06 13:00:00 35.58821488
07/06 14:00:00 35.58821538
07/06 15:00:00 35.58821513
07/06 16:00:00 35.58821463
07/06 17:00:00 35.56585973
07/06 18:00:00 35.55244734
07/06 19:00:00 35.55244758
07/06 20:00:00 35.57480174
07/06 21:00:00 35.58821513
07/06 22:00:00 35.5882148
07/06 23:00:00 35.58821472
07/06 24:00:00 35.58821488
07/07 01:00:00 35.58821522
07/07 02:00:00 35.58821522
07/07 03:00:00 35.58821505
07/07 04:00:00 35.58821434
07/07 05:00:00 35.58821452
07/07 06:00:00 35.58821443
07/07 07:00:00 35.61056929
07/07 08:00:00 35.62398143
07/07 09:00:00 35.62398177
07/07 10:00:00 35.6239821
07/07 11:00:00 35.6239816
07/07 12:00:00 35.62398177
07/07 13:00:00 35.62398193
07/07 14:00:00 35.62398094
07/07 15:00:00 35.62398218
07/07 16:00:00 35.62398168
07/07 17:00:00 35.60162753
07/07 18:00:00 35.58821463
07/07 19:00:00 35.58821463
07/07 20:00:00 35.61056929
07/07 21:00:00 35.62398193
07/07 22:00:00 35.64633584
07/07 23:00:00 35.63739458
07/07 24:00:00 35.62398127
Meeting Humidity Setpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses much of all the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the two design days, the first week of January, and the first week of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
12/21 01:00:00 22.48504471
12/21 02:00:00 22.48504471
12/21 03:00:00 22.48504482
12/21 04:00:00 22.4850445
12/21 05:00:00 22.48504492
12/21 06:00:00 22.48504441
12/21 07:00:00 22.4850446
12/21 08:00:00 22.48504482
12/21 09:00:00 22.48504492
12/21 10:00:00 22.48504482
12/21 11:00:00 22.48504482
12/21 12:00:00 22.48504461
12/21 13:00:00 22.4850445
12/21 14:00:00 22.48504503
12/21 15:00:00 22.48504482
12/21 16:00:00 22.48504482
12/21 17:00:00 22.48504461
12/21 18:00:00 22.48504471
12/21 19:00:00 22.48504466
12/21 20:00:00 22.48504469
12/21 21:00:00 22.48504481
12/21 22:00:00 22.48504482
12/21 23:00:00 22.48504455
12/21 24:00:00 22.48504461
08/21 01:00:00 35.83543615
08/21 02:00:00 35.835436
08/21 03:00:00 35.8354359
08/21 04:00:00 35.83543573
08/21 05:00:00 35.83543556
08/21 06:00:00 35.83543589
08/21 07:00:00 35.83543569
08/21 08:00:00 35.83543565
08/21 09:00:00 35.83543556
08/21 10:00:00 35.83543556
08/21 11:00:00 35.83543506
08/21 12:00:00 35.83543556
08/21 13:00:00 35.83543556
08/21 14:00:00 35.83543606
08/21 15:00:00 35.83543456
08/21 16:00:00 35.83543556
08/21 17:00:00 35.83543606
08/21 18:00:00 35.83543506
08/21 19:00:00 35.83543456
08/21 20:00:00 35.83543506
08/21 21:00:00 35.83543506
08/21 22:00:00 35.83543556
08/21 23:00:00 35.83543572
08/21 24:00:00 35.83543569
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
01/02 01:00:00 29.99843125
01/02 02:00:00 29.99843139
01/02 03:00:00 29.99843139
01/02 04:00:00 29.99843111
01/02 05:00:00 29.99843111
01/02 06:00:00 29.99843152
01/02 07:00:00 30.01718048
01/02 08:00:00 30.0471794
01/02 09:00:00 30.07717699
01/02 10:00:00 30.10717556
01/02 11:00:00 30.11842511
01/02 12:00:00 30.09967666
01/02 13:00:00 30.08842654
01/02 14:00:00 30.0696778
01/02 15:00:00 30.07717741
01/02 16:00:00 30.0884264
01/02 17:00:00 30.08842696
01/02 18:00:00 30.08842724
01/02 19:00:00 30.1071757
01/02 20:00:00 30.11842511
01/02 21:00:00 30.11842511
01/02 22:00:00 30.13717442
01/02 23:00:00 30.12967488
01/02 24:00:00 30.13717371
01/03 01:00:00 30.12967467
01/03 02:00:00 30.11842525
01/03 03:00:00 30.11842554
01/03 04:00:00 30.11842525
01/03 05:00:00 30.13717413
01/03 06:00:00 30.16717209
01/03 07:00:00 30.17842206
01/03 08:00:00 30.19717142
01/03 09:00:00 30.20842041
01/03 10:00:00 30.22716915
01/03 11:00:00 30.23841898
01/03 12:00:00 30.21967038
01/03 13:00:00 30.20842069
01/03 14:00:00 30.18967181
01/03 15:00:00 30.17842254
01/03 16:00:00 30.1784217
01/03 17:00:00 30.17842113
01/03 18:00:00 30.19717156
01/03 19:00:00 30.20842027
01/03 20:00:00 30.22716943
01/03 21:00:00 30.23841828
01/03 22:00:00 30.23841828
01/03 23:00:00 30.25716811
01/03 24:00:00 30.24966797
01/04 01:00:00 30.21966982
01/04 02:00:00 30.20842041
01/04 03:00:00 30.22716985
01/04 04:00:00 30.21966954
01/04 05:00:00 30.20842041
01/04 06:00:00 30.20842015
01/04 07:00:00 30.20842097
01/04 08:00:00 30.22716957
01/04 09:00:00 30.23841916
01/04 10:00:00 30.23841969
01/04 11:00:00 30.21967067
01/04 12:00:00 30.17092321
01/04 13:00:00 30.12967537
01/04 14:00:00 30.09967694
01/04 15:00:00 30.06967851
01/04 16:00:00 30.05842909
01/04 17:00:00 30.05842853
01/04 18:00:00 30.05842909
01/04 19:00:00 30.05842909
01/04 20:00:00 30.03968007
01/04 21:00:00 30.02843066
01/04 22:00:00 30.02843052
01/04 23:00:00 30.02843066
01/04 24:00:00 30.00968136
01/05 01:00:00 29.97968279
01/05 02:00:00 29.9684338
01/05 03:00:00 29.96843324
01/05 04:00:00 29.94968478
01/05 05:00:00 29.93843508
01/05 06:00:00 29.93843508
01/05 07:00:00 29.93843515
01/05 08:00:00 29.9571841
01/05 09:00:00 29.98718282
01/05 10:00:00 29.99843139
01/05 11:00:00 29.97968293
01/05 12:00:00 29.94968436
01/05 13:00:00 29.9196862
01/05 14:00:00 29.90843651
01/05 15:00:00 29.90843665
01/05 16:00:00 29.92718539
01/05 17:00:00 29.93843467
01/05 18:00:00 29.93843439
01/05 19:00:00 29.95718397
01/05 20:00:00 29.9684331
01/05 21:00:00 29.98718268
01/05 22:00:00 29.99843181
01/05 23:00:00 30.01718083
01/05 24:00:00 30.02842996
01/06 01:00:00 30.02843024
01/06 02:00:00 30.04717926
01/06 03:00:00 30.05842867
01/06 04:00:00 30.05842881
01/06 05:00:00 30.07717797
01/06 06:00:00 30.10717598
01/06 07:00:00 30.11842544
01/06 08:00:00 30.13717427
01/06 09:00:00 30.16717285
01/06 10:00:00 30.19717184
01/06 11:00:00 30.18967153
01/06 12:00:00 30.1784224
01/06 13:00:00 30.15967338
01/06 14:00:00 30.14842383
01/06 15:00:00 30.1484234
01/06 16:00:00 30.14842355
01/06 17:00:00 30.14842298
01/06 18:00:00 30.16717285
01/06 19:00:00 30.1784217
01/06 20:00:00 30.17842184
01/06 21:00:00 30.1784224
01/06 22:00:00 30.17842212
01/06 23:00:00 30.17842215
01/06 24:00:00 30.15967338
01/07 01:00:00 30.14842411
01/07 02:00:00 30.12967424
01/07 03:00:00 30.11842582
01/07 04:00:00 30.13717456
01/07 05:00:00 30.12967481
01/07 06:00:00 30.13717385
01/07 07:00:00 30.14842386
01/07 08:00:00 30.14842425
01/07 09:00:00 30.16717228
01/07 10:00:00 30.17842254
01/07 11:00:00 30.17842226
01/07 12:00:00 30.15967296
01/07 13:00:00 30.12967509
01/07 14:00:00 30.0996768
01/07 15:00:00 30.08842668
01/07 16:00:00 30.0884271
01/07 17:00:00 30.08842668
01/07 18:00:00 30.08842668
01/07 19:00:00 30.08842696
01/07 20:00:00 30.08842626
01/07 21:00:00 30.08842696
01/07 22:00:00 30.0884271
01/07 23:00:00 30.08842724
01/07 24:00:00 30.06967808
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
07/02 01:00:00 36.12686096
07/02 02:00:00 36.12686096
07/02 03:00:00 36.12686096
07/02 04:00:00 36.12685995
07/02 05:00:00 36.12685978
07/02 06:00:00 36.1268608
07/02 07:00:00 36.14955326
07/02 08:00:00 36.16316861
07/02 09:00:00 36.16316949
07/02 10:00:00 36.16316884
07/02 11:00:00 36.16316894
07/02 12:00:00 36.16316904
07/02 13:00:00 36.16316886
07/02 14:00:00 36.14047618
07/02 15:00:00 36.12686033
07/02 16:00:00 36.12686028
07/02 17:00:00 36.12686031
07/02 18:00:00 36.12686061
07/02 19:00:00 36.12686033
07/02 20:00:00 36.1268608
07/02 21:00:00 36.13981066
07/02 22:00:00 36.12534957
07/02 23:00:00 36.11940171
07/02 24:00:00 36.1194112
07/03 01:00:00 36.11941053
07/03 02:00:00 36.09674591
07/03 03:00:00 36.08314589
07/03 04:00:00 36.08314577
07/03 05:00:00 36.10581127
07/03 06:00:00 36.11941074
07/03 07:00:00 36.14207582
07/03 08:00:00 36.15567466
07/03 09:00:00 36.15567516
07/03 10:00:00 36.15567533
07/03 11:00:00 36.15567525
07/03 12:00:00 36.15567491
07/03 13:00:00 36.13300987
07/03 14:00:00 36.11941095
07/03 15:00:00 36.1194112
07/03 16:00:00 36.11941069
07/03 17:00:00 36.0967449
07/03 18:00:00 36.08314572
07/03 19:00:00 36.08314648
07/03 20:00:00 36.10581101
07/03 21:00:00 36.11941069
07/03 22:00:00 36.11940994
07/03 23:00:00 36.11941019
07/03 24:00:00 36.11941036
07/04 01:00:00 36.11941086
07/04 02:00:00 36.11941086
07/04 03:00:00 36.11941002
07/04 04:00:00 36.11940985
07/04 05:00:00 36.11933984
07/04 06:00:00 36.12153371
07/04 07:00:00 36.11364399
07/04 08:00:00 36.11369359
07/04 09:00:00 36.1136946
07/04 10:00:00 36.11369446
07/04 11:00:00 36.11369484
07/04 12:00:00 36.11369441
07/04 13:00:00 36.09105561
07/04 14:00:00 36.07747228
07/04 15:00:00 36.07747258
07/04 16:00:00 36.05483345
07/04 17:00:00 36.04125009
07/04 18:00:00 36.0412497
07/04 19:00:00 36.04124935
07/04 20:00:00 36.04124957
07/04 21:00:00 36.0412502
07/04 22:00:00 36.04125004
07/04 23:00:00 36.04124987
07/04 24:00:00 36.04125004
07/05 01:00:00 36.04124987
07/05 02:00:00 36.04125037
07/05 03:00:00 36.0412497
07/05 04:00:00 36.04124936
07/05 05:00:00 36.0412497
07/05 06:00:00 36.04124991
07/05 07:00:00 36.04125004
07/05 08:00:00 36.0412502
07/05 09:00:00 36.04124953
07/05 10:00:00 36.06388884
07/05 11:00:00 36.05483292
07/05 12:00:00 36.04124945
07/05 13:00:00 36.04125004
07/05 14:00:00 36.04125054
07/05 15:00:00 36.01861106
07/05 16:00:00 36.00502667
07/05 17:00:00 35.9823887
07/05 18:00:00 35.96880431
07/05 19:00:00 35.96880506
07/05 20:00:00 35.96880481
07/05 21:00:00 35.99144379
07/05 22:00:00 35.99912995
07/05 23:00:00 35.95881037
07/05 24:00:00 35.94770478
07/06 01:00:00 35.81016103
07/06 02:00:00 35.57496488
07/06 03:00:00 35.55758753
07/06 04:00:00 35.55241445
07/06 05:00:00 35.55244833
07/06 06:00:00 35.57480237
07/06 07:00:00 35.58821505
07/06 08:00:00 35.61056912
07/06 09:00:00 35.60162753
07/06 10:00:00 35.58821455
07/06 11:00:00 35.58821439
07/06 12:00:00 35.58821513
07/06 13:00:00 35.58821488
07/06 14:00:00 35.58821538
07/06 15:00:00 35.58821513
07/06 16:00:00 35.58821463
07/06 17:00:00 35.56585973
07/06 18:00:00 35.55244734
07/06 19:00:00 35.55244758
07/06 20:00:00 35.57480174
07/06 21:00:00 35.58821513
07/06 22:00:00 35.5882148
07/06 23:00:00 35.58821472
07/06 24:00:00 35.58821488
07/07 01:00:00 35.58821522
07/07 02:00:00 35.58821522
07/07 03:00:00 35.58821505
07/07 04:00:00 35.58821434
07/07 05:00:00 35.58821452
07/07 06:00:00 35.58821443
07/07 07:00:00 35.61056929
07/07 08:00:00 35.62398143
07/07 09:00:00 35.62398177
07/07 10:00:00 35.6239821
07/07 11:00:00 35.6239816
07/07 12:00:00 35.62398177
07/07 13:00:00 35.62398193
07/07 14:00:00 35.62398094
07/07 15:00:00 35.62398218
07/07 16:00:00 35.62398168
07/07 17:00:00 35.60162753
07/07 18:00:00 35.58821463
07/07 19:00:00 35.58821463
07/07 20:00:00 35.61056929
07/07 21:00:00 35.62398193
07/07 22:00:00 35.64633584
07/07 23:00:00 35.63739458
07/07 24:00:00 35.62398127
Meeting Humidity Setpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses all the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What object objecta would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.
POST SCRIPT
Providing some data from the simulation, the humidity can get quite low if there is there is no humidifier present. These are the relative humidity values for the two design days, the first week of January, and the first week of July in a data center that does not possess a humidifier.
Date/Time DATACENTER_MID_ZN_6:Zone Air Relative Humidity [%](Hourly)
12/21 01:00:00 22.48504471
12/21 02:00:00 22.48504471
12/21 03:00:00 22.48504482
12/21 04:00:00 22.4850445
12/21 05:00:00 22.48504492
12/21 06:00:00 22.48504441
12/21 07:00:00 22.4850446
12/21 08:00:00 22.48504482
12/21 09:00:00 22.48504492
12/21 10:00:00 22.48504482
12/21 11:00:00 22.48504482
12/21 12:00:00 22.48504461
12/21 13:00:00 22.4850445
12/21 14:00:00 22.48504503
12/21 15:00:00 22.48504482
12/21 16:00:00 22.48504482
12/21 17:00:00 22.48504461
12/21 18:00:00 22.48504471
12/21 19:00:00 22.48504466
12/21 20:00:00 22.48504469
12/21 21:00:00 22.48504481
12/21 22:00:00 22.48504482
12/21 23:00:00 22.48504455
12/21 24:00:00 22.48504461
08/21 01:00:00 35.83543615
08/21 02:00:00 35.835436
08/21 03:00:00 35.8354359
08/21 04:00:00 35.83543573
08/21 05:00:00 35.83543556
08/21 06:00:00 35.83543589
08/21 07:00:00 35.83543569
08/21 08:00:00 35.83543565
08/21 09:00:00 35.83543556
08/21 10:00:00 35.83543556
08/21 11:00:00 35.83543506
08/21 12:00:00 35.83543556
08/21 13:00:00 35.83543556
08/21 14:00:00 35.83543606
08/21 15:00:00 35.83543456
08/21 16:00:00 35.83543556
08/21 17:00:00 35.83543606
08/21 18:00:00 35.83543506
08/21 19:00:00 35.83543456
08/21 20:00:00 35.83543506
08/21 21:00:00 35.83543506
08/21 22:00:00 35.83543556
08/21 23:00:00 35.83543572
08/21 24:00:00 35.83543569
01/01 01:00:00 29.96093349
01/01 02:00:00 29.95718355
01/01 03:00:00 29.9684331
01/01 04:00:00 29.96843366
01/01 05:00:00 29.98718226
01/01 06:00:00 29.97968237
01/01 07:00:00 29.98718184
01/01 08:00:00 30.01718079
01/01 09:00:00 30.04717912
01/01 10:00:00 30.07717769
01/01 11:00:00 30.0884264
01/01 12:00:00 30.06967808
01/01 13:00:00 30.03967937
01/01 14:00:00 30.0284301
01/01 15:00:00 30.02842996
01/01 16:00:00 30.02842954
01/01 17:00:00 30.0096808
01/01 18:00:00 29.99843139
01/01 19:00:00 29.99843181
01/01 20:00:00 29.99843125
01/01 21:00:00 29.99843167
01/01 22:00:00 30.01718055
01/01 23:00:00 30.00968108
01/01 24:00:00 29.99843153
01/02 01:00:00 29.99843125
01/02 02:00:00 29.99843139
01/02 03:00:00 29.99843139
01/02 04:00:00 29.99843111
01/02 05:00:00 29.99843111
01/02 06:00:00 29.99843152
01/02 07:00:00 30.01718048
01/02 08:00:00 30.0471794
01/02 09:00:00 30.07717699
01/02 10:00:00 30.10717556
01/02 11:00:00 30.11842511
01/02 12:00:00 30.09967666
01/02 13:00:00 30.08842654
01/02 14:00:00 30.0696778
01/02 15:00:00 30.07717741
01/02 16:00:00 30.0884264
01/02 17:00:00 30.08842696
01/02 18:00:00 30.08842724
01/02 19:00:00 30.1071757
01/02 20:00:00 30.11842511
01/02 21:00:00 30.11842511
01/02 22:00:00 30.13717442
01/02 23:00:00 30.12967488
01/02 24:00:00 30.13717371
01/03 01:00:00 30.12967467
01/03 02:00:00 30.11842525
01/03 03:00:00 30.11842554
01/03 04:00:00 30.11842525
01/03 05:00:00 30.13717413
01/03 06:00:00 30.16717209
01/03 07:00:00 30.17842206
01/03 08:00:00 30.19717142
01/03 09:00:00 30.20842041
01/03 10:00:00 30.22716915
01/03 11:00:00 30.23841898
01/03 12:00:00 30.21967038
01/03 13:00:00 30.20842069
01/03 14:00:00 30.18967181
01/03 15:00:00 30.17842254
01/03 16:00:00 30.1784217
01/03 17:00:00 30.17842113
01/03 18:00:00 30.19717156
01/03 19:00:00 30.20842027
01/03 20:00:00 30.22716943
01/03 21:00:00 30.23841828
01/03 22:00:00 30.23841828
01/03 23:00:00 30.25716811
01/03 24:00:00 30.24966797
01/04 01:00:00 30.21966982
01/04 02:00:00 30.20842041
01/04 03:00:00 30.22716985
01/04 04:00:00 30.21966954
01/04 05:00:00 30.20842041
01/04 06:00:00 30.20842015
01/04 07:00:00 30.20842097
01/04 08:00:00 30.22716957
01/04 09:00:00 30.23841916
01/04 10:00:00 30.23841969
01/04 11:00:00 30.21967067
01/04 12:00:00 30.17092321
01/04 13:00:00 30.12967537
01/04 14:00:00 30.09967694
01/04 15:00:00 30.06967851
01/04 16:00:00 30.05842909
01/04 17:00:00 30.05842853
01/04 18:00:00 30.05842909
01/04 19:00:00 30.05842909
01/04 20:00:00 30.03968007
01/04 21:00:00 30.02843066
01/04 22:00:00 30.02843052
01/04 23:00:00 30.02843066
01/04 24:00:00 30.00968136
01/05 01:00:00 29.97968279
01/05 02:00:00 29.9684338
01/05 03:00:00 29.96843324
01/05 04:00:00 29.94968478
01/05 05:00:00 29.93843508
01/05 06:00:00 29.93843508
01/05 07:00:00 29.93843515
01/05 08:00:00 29.9571841
01/05 09:00:00 29.98718282
01/05 10:00:00 29.99843139
01/05 11:00:00 29.97968293
01/05 12:00:00 29.94968436
01/05 13:00:00 29.9196862
01/05 14:00:00 29.90843651
01/05 15:00:00 29.90843665
01/05 16:00:00 29.92718539
01/05 17:00:00 29.93843467
01/05 18:00:00 29.93843439
01/05 19:00:00 29.95718397
01/05 20:00:00 29.9684331
01/05 21:00:00 29.98718268
01/05 22:00:00 29.99843181
01/05 23:00:00 30.01718083
01/05 24:00:00 30.02842996
01/06 01:00:00 30.02843024
01/06 02:00:00 30.04717926
01/06 03:00:00 30.05842867
01/06 04:00:00 30.05842881
01/06 05:00:00 30.07717797
01/06 06:00:00 30.10717598
01/06 07:00:00 30.11842544
01/06 08:00:00 30.13717427
01/06 09:00:00 30.16717285
01/06 10:00:00 30.19717184
01/06 11:00:00 30.18967153
01/06 12:00:00 30.1784224
01/06 13:00:00 30.15967338
01/06 14:00:00 30.14842383
01/06 15:00:00 30.1484234
01/06 16:00:00 30.14842355
01/06 17:00:00 30.14842298
01/06 18:00:00 30.16717285
01/06 19:00:00 30.1784217
01/06 20:00:00 30.17842184
01/06 21:00:00 30.1784224
01/06 22:00:00 30.17842212
01/06 23:00:00 30.17842215
01/06 24:00:00 30.15967338
01/07 01:00:00 30.14842411
01/07 02:00:00 30.12967424
01/07 03:00:00 30.11842582
01/07 04:00:00 30.13717456
01/07 05:00:00 30.12967481
01/07 06:00:00 30.13717385
01/07 07:00:00 30.14842386
01/07 08:00:00 30.14842425
01/07 09:00:00 30.16717228
01/07 10:00:00 30.17842254
01/07 11:00:00 30.17842226
01/07 12:00:00 30.15967296
01/07 13:00:00 30.12967509
01/07 14:00:00 30.0996768
01/07 15:00:00 30.08842668
01/07 16:00:00 30.0884271
01/07 17:00:00 30.08842668
01/07 18:00:00 30.08842668
01/07 19:00:00 30.08842696
01/07 20:00:00 30.08842626
01/07 21:00:00 30.08842696
01/07 22:00:00 30.0884271
01/07 23:00:00 30.08842724
01/07 24:00:00 30.06967808
07/01 01:00:00 36.12686063
07/01 02:00:00 36.1041672
07/01 03:00:00 36.09055239
07/01 04:00:00 36.11324487
07/01 05:00:00 36.12685991
07/01 06:00:00 36.14955376
07/01 07:00:00 36.16316903
07/01 08:00:00 36.1631692
07/01 09:00:00 36.16316869
07/01 10:00:00 36.1631692
07/01 11:00:00 36.18586136
07/01 12:00:00 36.1767846
07/01 13:00:00 36.1631692
07/01 14:00:00 36.14047543
07/01 15:00:00 36.12686105
07/01 16:00:00 36.12686054
07/01 17:00:00 36.12686069
07/01 18:00:00 36.12686059
07/01 19:00:00 36.12686069
07/01 20:00:00 36.1268608
07/01 21:00:00 36.12686046
07/01 22:00:00 36.12686046
07/01 23:00:00 36.12686063
07/01 24:00:00 36.12686046
07/02 01:00:00 36.12686096
07/02 02:00:00 36.12686096
07/02 03:00:00 36.12686096
07/02 04:00:00 36.12685995
07/02 05:00:00 36.12685978
07/02 06:00:00 36.1268608
07/02 07:00:00 36.14955326
07/02 08:00:00 36.16316861
07/02 09:00:00 36.16316949
07/02 10:00:00 36.16316884
07/02 11:00:00 36.16316894
07/02 12:00:00 36.16316904
07/02 13:00:00 36.16316886
07/02 14:00:00 36.14047618
07/02 15:00:00 36.12686033
07/02 16:00:00 36.12686028
07/02 17:00:00 36.12686031
07/02 18:00:00 36.12686061
07/02 19:00:00 36.12686033
07/02 20:00:00 36.1268608
07/02 21:00:00 36.13981066
07/02 22:00:00 36.12534957
07/02 23:00:00 36.11940171
07/02 24:00:00 36.1194112
07/03 01:00:00 36.11941053
07/03 02:00:00 36.09674591
07/03 03:00:00 36.08314589
07/03 04:00:00 36.08314577
07/03 05:00:00 36.10581127
07/03 06:00:00 36.11941074
07/03 07:00:00 36.14207582
07/03 08:00:00 36.15567466
07/03 09:00:00 36.15567516
07/03 10:00:00 36.15567533
07/03 11:00:00 36.15567525
07/03 12:00:00 36.15567491
07/03 13:00:00 36.13300987
07/03 14:00:00 36.11941095
07/03 15:00:00 36.1194112
07/03 16:00:00 36.11941069
07/03 17:00:00 36.0967449
07/03 18:00:00 36.08314572
07/03 19:00:00 36.08314648
07/03 20:00:00 36.10581101
07/03 21:00:00 36.11941069
07/03 22:00:00 36.11940994
07/03 23:00:00 36.11941019
07/03 24:00:00 36.11941036
07/04 01:00:00 36.11941086
07/04 02:00:00 36.11941086
07/04 03:00:00 36.11941002
07/04 04:00:00 36.11940985
07/04 05:00:00 36.11933984
07/04 06:00:00 36.12153371
07/04 07:00:00 36.11364399
07/04 08:00:00 36.11369359
07/04 09:00:00 36.1136946
07/04 10:00:00 36.11369446
07/04 11:00:00 36.11369484
07/04 12:00:00 36.11369441
07/04 13:00:00 36.09105561
07/04 14:00:00 36.07747228
07/04 15:00:00 36.07747258
07/04 16:00:00 36.05483345
07/04 17:00:00 36.04125009
07/04 18:00:00 36.0412497
07/04 19:00:00 36.04124935
07/04 20:00:00 36.04124957
07/04 21:00:00 36.0412502
07/04 22:00:00 36.04125004
07/04 23:00:00 36.04124987
07/04 24:00:00 36.04125004
07/05 01:00:00 36.04124987
07/05 02:00:00 36.04125037
07/05 03:00:00 36.0412497
07/05 04:00:00 36.04124936
07/05 05:00:00 36.0412497
07/05 06:00:00 36.04124991
07/05 07:00:00 36.04125004
07/05 08:00:00 36.0412502
07/05 09:00:00 36.04124953
07/05 10:00:00 36.06388884
07/05 11:00:00 36.05483292
07/05 12:00:00 36.04124945
07/05 13:00:00 36.04125004
07/05 14:00:00 36.04125054
07/05 15:00:00 36.01861106
07/05 16:00:00 36.00502667
07/05 17:00:00 35.9823887
07/05 18:00:00 35.96880431
07/05 19:00:00 35.96880506
07/05 20:00:00 35.96880481
07/05 21:00:00 35.99144379
07/05 22:00:00 35.99912995
07/05 23:00:00 35.95881037
07/05 24:00:00 35.94770478
07/06 01:00:00 35.81016103
07/06 02:00:00 35.57496488
07/06 03:00:00 35.55758753
07/06 04:00:00 35.55241445
07/06 05:00:00 35.55244833
07/06 06:00:00 35.57480237
07/06 07:00:00 35.58821505
07/06 08:00:00 35.61056912
07/06 09:00:00 35.60162753
07/06 10:00:00 35.58821455
07/06 11:00:00 35.58821439
07/06 12:00:00 35.58821513
07/06 13:00:00 35.58821488
07/06 14:00:00 35.58821538
07/06 15:00:00 35.58821513
07/06 16:00:00 35.58821463
07/06 17:00:00 35.56585973
07/06 18:00:00 35.55244734
07/06 19:00:00 35.55244758
07/06 20:00:00 35.57480174
07/06 21:00:00 35.58821513
07/06 22:00:00 35.5882148
07/06 23:00:00 35.58821472
07/06 24:00:00 35.58821488
07/07 01:00:00 35.58821522
07/07 02:00:00 35.58821522
07/07 03:00:00 35.58821505
07/07 04:00:00 35.58821434
07/07 05:00:00 35.58821452
07/07 06:00:00 35.58821443
07/07 07:00:00 35.61056929
07/07 08:00:00 35.62398143
07/07 09:00:00 35.62398177
07/07 10:00:00 35.6239821
07/07 11:00:00 35.6239816
07/07 12:00:00 35.62398177
07/07 13:00:00 35.62398193
07/07 14:00:00 35.62398094
07/07 15:00:00 35.62398218
07/07 16:00:00 35.62398168
07/07 17:00:00 35.60162753
07/07 18:00:00 35.58821463
07/07 19:00:00 35.58821463
07/07 20:00:00 35.61056929
07/07 21:00:00 35.62398193
07/07 22:00:00 35.64633584
07/07 23:00:00 35.63739458
07/07 24:00:00 35.62398127
Meeting Humidity Setpoint with Evaporative Media
I am setting up an HVAC system for a computer room. The person density in the computer room is 0 and the computers are always on generating much heat. There is no outdoor airflow due to fear of particles, and the cooling coil is always on, day and night, which condenses all the water out of the air. Low humidity is bad for computers since static charge can build up and damage components, so water must be added to the air in the loop.
The best objects I've found is either of the EvaporativeCooler:Direct:CelDekPad or EvaporativeCooler:Direct:ResearchSpecial as opposed to the humidifies which heat the water. There is no reason to add heat to the airloop serving the computer equipment as the computer room never, ever needs heating.
However, I've run into a problem on how to control the direct evaporative coolers based on humidity. The ideal relative humidity for computer equipment is 45% - 55% and I don't see an easy way for the EvaporativeCooler:Direct to be turned on and off based on the humidity. What objecta would you recommend that are smart enough to control the fan, cooling coil, heating coil that is in in the airloop but is never used, and evaporative cooler to meet a temperature of 28C and relative humidity kept between 45% - 55%?
A possible alternative is to use a Humidifier:Steam:Electric object and specify the parameters in such a way that it evaporates water but generates zero heat. Then there are appropriate objects for controlling the equipment in the airloop based on temperature and humidity while not unnecessarily heating the computer equipment with a kluge parameter choice of the Humidifier:Steam:Electric object.