How to use HVACTemplate:Plant:Chiller:ObjectReference?
I wanted to input actual chiller performance curve using HVACTemplate. That's why I used HVACTemplate:Plant:Chiller:ObjectReference
with HVACTemplate:ChillerWaterLoop
and Chiller:Electric:EIR
. Howerver, I got fatal error because I didnt fill in Chilled Water Inlet Node Name
and Chilled Water Outlet Node Name
. However, I expected that I dont have to worry about Inlet and Outlet because HVACTemplate will take care of it. Does anyone know how I can use HVACTemplate:Plant:Chiller:ObjectReference
with Chiller:Electric:EIR
?
I added corresponding part in idf as below.
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:PLANT:CHILLEDWATERLOOP ===========
HVACTemplate:Plant:ChilledWaterLoop,
CHWloop, !- Name
ALWAYS ON, !- Pump Schedule Name
Intermittent, !- Pump Control Type
Default, !- Chiller Plant Operation Scheme Type
, !- Chiller Plant Equipment Operation Schemes Name
, !- Chilled Water Setpoint Schedule Name
6.7, !- Chilled Water Design Setpoint {C}
VariablePrimaryNoSecondary, !- Chilled Water Pump Configuration
116300.0, !- Primary Chilled Water Pump Rated Head {Pa}
232700.0, !- Secondary Chilled Water Pump Rated Head {Pa}
Default, !- Condenser Plant Operation Scheme Type
, !- Condenser Equipment Operation Schemes Name
, !- Condenser Water Temperature Control Type
, !- Condenser Water Setpoint Schedule Name
28.3, !- Condenser Water Design Setpoint {C}
310000.0, !- Condenser Water Pump Rated Head {Pa}
OutdoorAirTemperatureReset, !- Chilled Water Setpoint Reset Type
12, !- Chilled Water Setpoint at Outdoor Dry-Bulb Low {C}
16, !- Chilled Water Reset Outdoor Dry-Bulb Low {C}
7, !- Chilled Water Setpoint at Outdoor Dry-Bulb High {C}
27, !- Chilled Water Reset Outdoor Dry-Bulb High {C}
PumpPerChiller, !- Chilled Water Primary Pump Type
SinglePump, !- Chilled Water Secondary Pump Type
SinglePump, !- Condenser Water Pump Type
Yes, !- Chilled Water Supply Side Bypass Pipe
Yes, !- Chilled Water Demand Side Bypass Pipe
Yes, !- Condenser Water Supply Side Bypass Pipe
Yes, !- Condenser Water Demand Side Bypass Pipe
Water, !- Fluid Type
6.67, !- Loop Design Delta Temperature {deltaC}
, !- Minimum Outdoor Dry Bulb Temperature {C}
SequentialLoad, !- Chilled Water Load Distribution Scheme
SequentialLoad; !- Condenser Water Load Distribution Scheme
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:PLANT:CHILLER:OBJECTREFERENCE ===========
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller1, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller1, !- Chiller Name
; !- Priority
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller2, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller2, !- Chiller Name
; !- Priority
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller3, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller3, !- Chiller Name
; !- Priority
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller4, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller4, !- Chiller Name
; !- Priority
!- =========== ALL OBJECTS IN CLASS: CHILLER:ELECTRIC:EIR ===========
Chiller:Electric:EIR,
OilFreeChiller1, !- Name
2461800, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory
Chiller:Electric:EIR,
OilFreeChiller2, !- Name
2461800, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory
Chiller:Electric:EIR,
OilFreeChiller3, !- Name
2461800, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory
Chiller:Electric:EIR,
OilFreeChiller4, !- Name
527528, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory
How to use HVACTemplate:Plant:Chiller:ObjectReference?
I wanted to input actual chiller performance curve using HVACTemplate. That's why I used HVACTemplate:Plant:Chiller:ObjectReference
with HVACTemplate:ChillerWaterLoop
and Chiller:Electric:EIR
. Howerver, I got fatal error because I didnt fill in Chilled Water Inlet Node Name
and Chilled Water Outlet Node Name
. However, I expected that I dont have to worry about Inlet and Outlet because HVACTemplate will take care of it. Does anyone know how I can use HVACTemplate:Plant:Chiller:ObjectReference
with Chiller:Electric:EIR
?
I added corresponding part in idf as below.
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:PLANT:CHILLEDWATERLOOP ===========
HVACTemplate:Plant:ChilledWaterLoop,
CHWloop, !- Name
ALWAYS ON, !- Pump Schedule Name
Intermittent, !- Pump Control Type
Default, !- Chiller Plant Operation Scheme Type
, !- Chiller Plant Equipment Operation Schemes Name
, !- Chilled Water Setpoint Schedule Name
6.7, !- Chilled Water Design Setpoint {C}
VariablePrimaryNoSecondary, !- Chilled Water Pump Configuration
116300.0, !- Primary Chilled Water Pump Rated Head {Pa}
232700.0, !- Secondary Chilled Water Pump Rated Head {Pa}
Default, !- Condenser Plant Operation Scheme Type
, !- Condenser Equipment Operation Schemes Name
, !- Condenser Water Temperature Control Type
, !- Condenser Water Setpoint Schedule Name
28.3, !- Condenser Water Design Setpoint {C}
310000.0, !- Condenser Water Pump Rated Head {Pa}
OutdoorAirTemperatureReset, !- Chilled Water Setpoint Reset Type
12, !- Chilled Water Setpoint at Outdoor Dry-Bulb Low {C}
16, !- Chilled Water Reset Outdoor Dry-Bulb Low {C}
7, !- Chilled Water Setpoint at Outdoor Dry-Bulb High {C}
27, !- Chilled Water Reset Outdoor Dry-Bulb High {C}
PumpPerChiller, !- Chilled Water Primary Pump Type
SinglePump, !- Chilled Water Secondary Pump Type
SinglePump, !- Condenser Water Pump Type
Yes, !- Chilled Water Supply Side Bypass Pipe
Yes, !- Chilled Water Demand Side Bypass Pipe
Yes, !- Condenser Water Supply Side Bypass Pipe
Yes, !- Condenser Water Demand Side Bypass Pipe
Water, !- Fluid Type
6.67, !- Loop Design Delta Temperature {deltaC}
, !- Minimum Outdoor Dry Bulb Temperature {C}
SequentialLoad, !- Chilled Water Load Distribution Scheme
SequentialLoad; !- Condenser Water Load Distribution Scheme
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:PLANT:CHILLER:OBJECTREFERENCE ===========
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller1, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller1, !- Chiller Name
; !- Priority
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller2, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller2, !- Chiller Name
; !- Priority
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller3, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller3, !- Chiller Name
; !- Priority
HVACTemplate:Plant:Chiller:ObjectReference,
OilFreeChiller4, !- Name
Chiller:Electric:EIR, !- Chiller Object Type
OilFreeChiller4, !- Chiller Name
; !- Priority
!- =========== ALL OBJECTS IN CLASS: CHILLER:ELECTRIC:EIR ===========
Chiller:Electric:EIR,
OilFreeChiller1, !- Name
2461800, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory
Chiller:Electric:EIR,
OilFreeChiller2, !- Name
2461800, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory
Chiller:Electric:EIR,
OilFreeChiller3, !- Name
2461800, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory
Chiller:Electric:EIR,
OilFreeChiller4, !- Name
527528, !- Reference Capacity {W}
5.8, !- Reference COP {W/W}
6.67, !- Reference Leaving Chilled Water Temperature {C}
29.4, !- Reference Entering Condenser Fluid Temperature {C}
, !- Reference Chilled Water Flow Rate {m3/s}
, !- Reference Condenser Fluid Flow Rate {m3/s}
OilFreeChiller_CAPFT, !- Cooling Capacity Function of Temperature Curve Name
OilFreeChiller_EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
OilFree_EIRPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.1, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.2, !- Minimum Unloading Ratio
, !- Chilled Water Inlet Node Name
, !- Chilled Water Outlet Node Name
, !- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
, !- Condenser Fan Power Ratio {W/W}
1, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2, !- Leaving Chilled Water Lower Temperature Limit {C}
NotModulated, !- Chiller Flow Mode
, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1, !- Sizing Factor
, !- Basin Heater Capacity {W/K}
2, !- Basin Heater Setpoint Temperature {C}
, !- Basin Heater Operating Schedule Name
, !- Condenser Heat Recovery Relative Capacity Fraction
, !- Heat Recovery Inlet High Temperature Limit Schedule Name
, !- Heat Recovery Leaving Temperature Setpoint Node Name
General; !- End-Use Subcategory