Revision history [back]
How to fix the node connection error
eplusout.err:
Program Version,EnergyPlus 6.0.0.023, 19-12-2018 11:38,IDD_Version 6.0.0.023
************* Beginning Zone Sizing Calculations
** Warning ** SizingPeriod:DesignDay: AHMEDABAD:1.0% WINTER
** ~~~ ** Humidity Indicator Temperature at Max Temp=12.8 > Max DryBulb=12.2
** ~~~ ** Humidity Indicating Type=WETBULB
** ~~~ ** Conditions for day will be set to Relative Humidity = 100%
** Warning ** Zone areas*inside surface emissivities are summing to zero, for Zone="Z1"
** ~~~ ** As a result, MRT will be set to MAT for that zone
************* Beginning System Sizing Calculations
** Warning ** Could not find chilled water coil with name SYSFANPWRVAV_SYS 1 COOLING COIL on any plant loop
** ~~~ ** Autosizing of water coil requires a cooling loop Sizing:Plant object
** ~~~ ** Occurs in water coil object= SYSFANPWRVAV_SYS 1 COOLING COIL
** Fatal ** Preceeding water coil sizing errors cause program termination
...Summary of Errors that led to program termination:
..... Reference severe error count=0
..... Last severe error=
************* Fatal error -- final processing. More error messages may appear.
************* Testing Individual Branch Integrity
** Warning ** There are orphaned Branches in input
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 COOLING COIL CHW BRANCH
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 HEATING COIL HW BRANCH
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=COIL:HEATING:WATER, Name=SYSFANPWRVAV_SYS 1 HEATING COIL
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=COIL:COOLING:WATER, Name=SYSFANPWRVAV_SYS 1 COOLING COIL
************* There were 4 node connection errors noted.
*************
************* ===== Final Error Summary =====
************* The following error categories occurred. Consider correcting or noting.
************* Node Connection Errors
************* ..Node connection errors are often caused by spelling mistakes in a node name field.
************* ..To track down the problem, search the idf file for each node name listed to see if it
************* ..occurs in the expected input fields.
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 2 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 4 Warning; 4 Severe Errors; Elapsed Time=00hr 00min 2.42sec
How to fix the node connection error
eplusout.err:
Program Version,EnergyPlus 6.0.0.023, 19-12-2018 11:38,IDD_Version 6.0.0.023
************* Beginning Zone Sizing Calculations
** Warning ** SizingPeriod:DesignDay: AHMEDABAD:1.0% WINTER
** ~~~ ** Humidity Indicator Temperature at Max Temp=12.8 > Max DryBulb=12.2
** ~~~ ** Humidity Indicating Type=WETBULB
** ~~~ ** Conditions for day will be set to Relative Humidity = 100%
** Warning ** Zone areas*inside surface emissivities are summing to zero, for Zone="Z1"
** ~~~ ** As a result, MRT will be set to MAT for that zone
************* Beginning System Sizing Calculations
** Warning ** Could not find chilled water coil with name SYSFANPWRVAV_SYS 1 COOLING COIL on any plant loop
** ~~~ ** Autosizing of water coil requires a cooling loop Sizing:Plant object
** ~~~ ** Occurs in water coil object= SYSFANPWRVAV_SYS 1 COOLING COIL
** Fatal ** Preceeding water coil sizing errors cause program termination
...Summary of Errors that led to program termination:
..... Reference severe error count=0
..... Last severe error=
************* Fatal error -- final processing. More error messages may appear.
************* Testing Individual Branch Integrity
** Warning ** There are orphaned Branches in input
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 COOLING COIL CHW BRANCH
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 HEATING COIL HW BRANCH
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=COIL:HEATING:WATER, Name=SYSFANPWRVAV_SYS 1 HEATING COIL
** Severe ** Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=COIL:COOLING:WATER, Name=SYSFANPWRVAV_SYS 1 COOLING COIL
************* There were 4 node connection errors noted.
*************
************* ===== Final Error Summary =====
************* The following error categories occurred. Consider correcting or noting.
************* Node Connection Errors
************* ..Node connection errors are often caused by spelling mistakes in a node name field.
************* ..To track down the problem, search the idf file for each node name listed to see if it
************* ..occurs in the expected input fields.
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 2 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 4 Warning; 4 Severe Errors; Elapsed Time=00hr 00min 2.42sec
How to fix the node connection error
eplusout.err:
Program Version,EnergyPlus 6.0.0.023, 19-12-2018 11:38,IDD_Version 6.0.0.023
************* *** Beginning Zone Sizing Calculations
** * Warning ** * SizingPeriod:DesignDay: AHMEDABAD:1.0% WINTER
** ~~~ ** * ~~~ * Humidity Indicator Temperature at Max Temp=12.8 > Max DryBulb=12.2
** ~~~ ** * ~~~ * Humidity Indicating Type=WETBULB
** ~~~ ** * ~~~ * Conditions for day will be set to Relative Humidity = 100%
** * Warning ** * Zone areas*inside areasinside surface emissivities are summing to zero, for Zone="Z1"
** ~~~ ** * ~~~ * As a result, MRT will be set to MAT for that zone
************* *** Beginning System Sizing Calculations
** * Warning ** * Could not find chilled water coil with name SYSFANPWRVAV_SYS 1 COOLING COIL on any plant loop
** ~~~ ** * ~~~ * Autosizing of water coil requires a cooling loop Sizing:Plant object
** ~~~ ** * ~~~ * Occurs in water coil object= SYSFANPWRVAV_SYS 1 COOLING COIL
** * Fatal ** * Preceeding water coil sizing errors cause program termination
...Summary of Errors that led to program termination:
..... Reference severe error count=0
..... Last severe error=
************* *** Fatal error -- final processing. More error messages may appear.
************* *** Testing Individual Branch Integrity
** * Warning ** * There are orphaned Branches in input
************* *** All Branches passed integrity testing
************* *** Testing Individual Supply Air Path Integrity
************* *** All Supply Air Paths passed integrity testing
************* *** Testing Individual Return Air Path Integrity
************* *** All Return Air Paths passed integrity testing
** * Severe ** * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** * ~~~ * Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 COOLING COIL CHW BRANCH
** * Severe ** * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** * ~~~ * Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 HEATING COIL HW BRANCH
** * Severe ** * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** * ~~~ * Reference Object=COIL:HEATING:WATER, Name=SYSFANPWRVAV_SYS 1 HEATING COIL
** * Severe ** * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** * ~~~ * Reference Object=COIL:COOLING:WATER, Name=SYSFANPWRVAV_SYS 1 COOLING COIL
************* *** There were 4 node connection errors noted.
*************
************* *** *** ===== Final Error Summary =====
************* *** The following error categories occurred. Consider correcting or noting.
************* *** Node Connection Errors
************* *** ..Node connection errors are often caused by spelling mistakes in a node name field.
************* *** ..To track down the problem, search the idf file for each node name listed to see if it
************* *** ..occurs in the expected input fields.
*************
************* *** *** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* *** EnergyPlus Sizing Error Summary. During Sizing: 2 Warning; 0 Severe Errors.
************* **** EnergyPlus Terminated--Fatal Error Detected. 4 Warning; 4 Severe Errors; Elapsed Time=00hr 00min 2.42sec
2.42sec How to fix the node connection error
Program Version,EnergyPlus 6.0.0.023, 19-12-2018 11:38,IDD_Version 6.0.0.023 *** Beginning Zone Sizing Calculations * Warning * SizingPeriod:DesignDay: AHMEDABAD:1.0% WINTER * ~~~ * Humidity Indicator Temperature at Max Temp=12.8 > Max DryBulb=12.2 * ~~~ * Humidity Indicating Type=WETBULB * ~~~ * Conditions for day will be set to Relative Humidity = 100% * Warning * Zone areasinside surface emissivities are summing to zero, for Zone="Z1" * ~~~ * As a result, MRT will be set to MAT for that zone *** Beginning System Sizing Calculations * Warning * Could not find chilled water coil with name SYSFANPWRVAV_SYS 1 COOLING COIL on any plant loop * ~~~ * Autosizing of water coil requires a cooling loop Sizing:Plant object * ~~~ * Occurs in water coil object= SYSFANPWRVAV_SYS 1 COOLING COIL * Fatal * Preceeding water coil sizing errors cause program termination ...Summary of Errors that led to program termination: ..... Reference severe error count=0 ..... Last severe error= *** Fatal error -- final processing. More error messages may appear. *** Testing Individual Branch Integrity * Warning * There are orphaned Branches in input *** All Branches passed integrity testing *** Testing Individual Supply Air Path Integrity *** All Supply Air Paths passed integrity testing *** Testing Individual Return Air Path Integrity *** All Return Air Paths passed integrity testing * Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node. * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object. * ~~~ * Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 COOLING COIL CHW BRANCH * Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node. * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object. * ~~~ * Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 HEATING COIL HW BRANCH * Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node. * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object. * ~~~ * Reference Object=COIL:HEATING:WATER, Name=SYSFANPWRVAV_SYS 1 HEATING COIL * Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node. * ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object. * ~~~ * Reference Object=COIL:COOLING:WATER, Name=SYSFANPWRVAV_SYS 1 COOLING COIL *** There were 4 node connection errors noted. *** *** ===== Final Error Summary ===== *** The following error categories occurred. Consider correcting or noting. *** Node Connection Errors *** ..Node connection errors are often caused by spelling mistakes in a node name field. *** ..To track down the problem, search the idf file for each node name listed to see if it *** ..occurs in the expected input fields. *** *** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors. *** EnergyPlus Sizing Error Summary. During Sizing: 2 Warning; 0 Severe Errors. **** EnergyPlus Terminated--Fatal Error Detected. 4 Warning; 4 Severe Errors; Elapsed Time=00hr 00min 2.42sec
How to fix the node connection error
Program Version,EnergyPlus 6.0.0.023, 19-12-2018 11:38,IDD_Version 6.0.0.023
*** Beginning Zone Sizing Calculations
* Warning * SizingPeriod:DesignDay: AHMEDABAD:1.0% WINTER
* ~~~ * Humidity Indicator Temperature at Max Temp=12.8 > Max DryBulb=12.2
* ~~~ * Humidity Indicating Type=WETBULB
* ~~~ * Conditions for day will be set to Relative Humidity = 100%
* Warning * Zone areasinside surface emissivities are summing to zero, for Zone="Z1"
* ~~~ * As a result, MRT will be set to MAT for that zone
*** Beginning System Sizing Calculations
* Warning * Could not find chilled water coil with name SYSFANPWRVAV_SYS 1 COOLING COIL on any plant loop
* ~~~ * Autosizing of water coil requires a cooling loop Sizing:Plant object
* ~~~ * Occurs in water coil object= SYSFANPWRVAV_SYS 1 COOLING COIL
* Fatal * Preceeding water coil sizing errors cause program termination
...Summary of Errors that led to program termination:
..... Reference severe error count=0
..... Last severe error=
*** Fatal error -- final processing. More error messages may appear.
*** Testing Individual Branch Integrity
* Warning * There are orphaned Branches in input
*** All Branches passed integrity testing
*** Testing Individual Supply Air Path Integrity
*** All Supply Air Paths passed integrity testing
*** Testing Individual Return Air Path Integrity
*** All Return Air Paths passed integrity testing
* Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
* ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
* ~~~ * Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 COOLING COIL CHW BRANCH
* Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
* ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
* ~~~ * Reference Object=BRANCH, Name=SYSFANPWRVAV_SYS 1 HEATING COIL HW BRANCH
* Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
* ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
* ~~~ * Reference Object=COIL:HEATING:WATER, Name=SYSFANPWRVAV_SYS 1 HEATING COIL
* Severe * Node Connection Error, Node="SYSFANPWRVAV_SYS 1 COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
* ~~~ * If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
* ~~~ * Reference Object=COIL:COOLING:WATER, Name=SYSFANPWRVAV_SYS 1 COOLING COIL
******* There were 4 node connection errors noted.
***noted.
***
===== Final Error Summary =====***
EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.