Error while modeling radiant underfloor cooling system
Hello guys! I'm a student in Technical University in Crete and I've been struggling a couple of weeks in a project, in which I would like to model a radiant floor cooling system using "Low Temperature Radiant Variable Flow" and I'm getting the following warnings every time:
Error file results:
Program Version,EnergyPlus, Version 9.0.1-bb7ca4f0da, YMD=2019.01.18 18:50, ************* Beginning Zone Sizing Calculations ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS ON DISCRETE", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input. ** ~~~ ** Found first in surface=SURFACE 16 ** ~~~ ** Defaults, constant throughout the year of (18.0) will be used. ** Warning ** CheckUsedConstructions: There are 1 nominally unused constructions in input. ** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings; ** Warning ** Calculated design heating load for zone=THERMAL ZONE 4 is zero. ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs. ** Warning ** Calculated design heating load for zone=THERMAL ZONE 8 is zero. ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs. ************* Beginning Plant Sizing Calculations ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="CHILLER - AIR COOLED" ** ~~~ ** Adding OutdoorAir:Node=CHILLER - AIR COOLED INLET NODE FOR CONDENSER ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="CHILLER - AIR COOLED" ** ~~~ ** Energy input ratio as a function of temperature curve output is not equal to 1.0 (+ or - 10%) at reference conditions. ** ~~~ ** Curve output at reference conditions = 0.850 ** Warning ** Output:Meter:MeterFileOnly requested for "Electricity:Facility" (TimeStep), already on "Output:Meter". Will report to both eplusout.eso and eplusout.mtr ************* Testing Individual Branch Integrity ************* All Branches passed integrity testing ************* Testing Individual Supply Air Path Integrity ************* All Supply Air Paths passed integrity testing ************* Testing Individual Return Air Path Integrity ************* All Return Air Paths passed integrity testing ************* No node connection errors were found. ************* Beginning Simulation ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 1] ** ~~~ ** Surface [SURFACE 28] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 33.33 ** ~~~ ** Zone dew-point temperature + safety delta T= 33.79 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 6] ** ~~~ ** Surface [SURFACE 49] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 32.67 ** ~~~ ** Zone dew-point temperature + safety delta T= 38.23 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 7] ** ~~~ ** Surface [SURFACE 42] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 33.01 ** ~~~ ** Zone dew-point temperature + safety delta T= 35.55 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ** ~~~ ** Routine=CorrectZoneHumRat, Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 14:20 - 14:30 ** ~~~ ** Input Temperature=200.11 ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 5] ** ~~~ ** Surface [SURFACE 35] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 28.09 ** ~~~ ** Zone dew-point temperature + safety delta T= 28.16 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS ENTH=>MDB, at Simulation time=07/21 15:30 - 15:40 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-ELECTRICITY" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-DISTILLATE OIL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-RESIDUAL OIL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-NATURAL GAS" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-COAL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ************* Simulation Error Summary ************* ************* There are 3 unused schedules in input. ************* There are 3 unused week schedules in input. ************* There are 6 unused day schedules in input. ************* Use Output:Diagnostics,DisplayUnusedSchedules; to see them. ************* ************* ===== Recurring Error Summary ===== ************* The following recurring error messages occurred. ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 1] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 53532 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=35.882518 C Min=25.368306 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 6] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 124007 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=37.290586 C Min=21.089111 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 7] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 83808 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=36.035267 C Min=24.842032 C ************* ************* ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ************* ** ~~~ ** This error occurred 419 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=237.325226 C Min=200.115784 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 5] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 110 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=27.4445 C Min=27.085091 C ************* ************* ************* ===== Final Error Summary ===== ************* The following error categories occurred. Consider correcting or noting. ************* Nominally Unused Constructions ************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause ************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm ************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option). ************* ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors. ************* EnergyPlus Sizing Error Summary. During Sizing: 7 Warning; 0 Severe Errors. ************* EnergyPlus Completed Successfully-- 261891 Warning; 0 Severe Errors; Elapsed Time=00hr 00min 48.82sec
I have already seen these posts:
- https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/
- https://unmethours.com/question/17175/calculated-design-cooling-load-is-zero/
- https://unmethours.com/question/9399/energyplus-design-cooling-load-is-zero/
- https://unmethours.com/question/23927/many-unmet-cooling-hours-with-radiant-floor-with-doas-possibly-due-to-condensation-shutoff/
but I couldn't solve my warnings. Could somebody help me please?
The major problem is when I try to export my results to .csv I get "0" Ideal Loads so I can't compare anything. The measure that I use to export to .csv file is:
OpenStudio Measures
- AddOutputVariable with variable name Zone Air System Sensible Heating Energy
- AddOutputVariable 1 with variable name Zone Air System Sensible Cooling Energy
Reporting Measures
- ExportOutputVariabletoCSV with variable name Zone Air System Sensible Heating Energy
- ExportOutputVariabletoCSV 1 with variable name Zone Air System Sensible Cooling Energy
I'm attaching my updated .osm and weather file .epw in a .zip here: http://www.mediafire.com/file/wnc6z4uy8084bcc/radiant_model.zip/file
Thank's in advance!
Error while modeling radiant underfloor cooling system
Hello guys! I'm a student in Technical University in Crete and I've been struggling a couple of weeks in a project, in which I would like to model a radiant floor cooling system using "Low Temperature Radiant Variable Flow" and I'm getting the following warnings every time:
Error file results:
Program Version,EnergyPlus, Version 9.0.1-bb7ca4f0da, YMD=2019.01.18 18:50, ************* Beginning Zone Sizing Calculations ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS ON DISCRETE", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input. ** ~~~ ** Found first in surface=SURFACE 16 ** ~~~ ** Defaults, constant throughout the year of (18.0) will be used. ** Warning ** CheckUsedConstructions: There are 1 nominally unused constructions in input. ** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings; ** Warning ** Calculated design heating load for zone=THERMAL ZONE 4 is zero. ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs. ** Warning ** Calculated design heating load for zone=THERMAL ZONE 8 is zero. ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs. ************* Beginning Plant Sizing Calculations ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="CHILLER - AIR COOLED" ** ~~~ ** Adding OutdoorAir:Node=CHILLER - AIR COOLED INLET NODE FOR CONDENSER ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="CHILLER - AIR COOLED" ** ~~~ ** Energy input ratio as a function of temperature curve output is not equal to 1.0 (+ or - 10%) at reference conditions. ** ~~~ ** Curve output at reference conditions = 0.850 ** Warning ** Output:Meter:MeterFileOnly requested for "Electricity:Facility" (TimeStep), already on "Output:Meter". Will report to both eplusout.eso and eplusout.mtr ************* Testing Individual Branch Integrity ************* All Branches passed integrity testing ************* Testing Individual Supply Air Path Integrity ************* All Supply Air Paths passed integrity testing ************* Testing Individual Return Air Path Integrity ************* All Return Air Paths passed integrity testing ************* No node connection errors were found. ************* Beginning Simulation ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 1] ** ~~~ ** Surface [SURFACE 28] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 33.33 ** ~~~ ** Zone dew-point temperature + safety delta T= 33.79 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 6] ** ~~~ ** Surface [SURFACE 49] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 32.67 ** ~~~ ** Zone dew-point temperature + safety delta T= 38.23 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 7] ** ~~~ ** Surface [SURFACE 42] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 33.01 ** ~~~ ** Zone dew-point temperature + safety delta T= 35.55 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ** ~~~ ** Routine=CorrectZoneHumRat, Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 14:20 - 14:30 ** ~~~ ** Input Temperature=200.11 ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 5] ** ~~~ ** Surface [SURFACE 35] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 28.09 ** ~~~ ** Zone dew-point temperature + safety delta T= 28.16 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS ENTH=>MDB, at Simulation time=07/21 15:30 - 15:40 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-ELECTRICITY" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-DISTILLATE OIL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-RESIDUAL OIL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-NATURAL GAS" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-COAL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ************* Simulation Error Summary ************* ************* There are 3 unused schedules in input. ************* There are 3 unused week schedules in input. ************* There are 6 unused day schedules in input. ************* Use Output:Diagnostics,DisplayUnusedSchedules; to see them. ************* ************* ===== Recurring Error Summary ===== ************* The following recurring error messages occurred. ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 1] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 53532 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=35.882518 C Min=25.368306 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 6] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 124007 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=37.290586 C Min=21.089111 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 7] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 83808 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=36.035267 C Min=24.842032 C ************* ************* ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ************* ** ~~~ ** This error occurred 419 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=237.325226 C Min=200.115784 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 5] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 110 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=27.4445 C Min=27.085091 C ************* ************* ************* ===== Final Error Summary ===== ************* The following error categories occurred. Consider correcting or noting. ************* Nominally Unused Constructions ************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause ************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm ************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option). ************* ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors. ************* EnergyPlus Sizing Error Summary. During Sizing: 7 Warning; 0 Severe Errors. ************* EnergyPlus Completed Successfully-- 261891 Warning; 0 Severe Errors; Elapsed Time=00hr 00min 48.82sec
I have already seen these posts:
- https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/
- https://unmethours.com/question/17175/calculated-design-cooling-load-is-zero/
- https://unmethours.com/question/9399/energyplus-design-cooling-load-is-zero/
- https://unmethours.com/question/23927/many-unmet-cooling-hours-with-radiant-floor-with-doas-possibly-due-to-condensation-shutoff/
but I couldn't solve my warnings. Could somebody help me please?
The major problem is when I try to export my results to .csv I get "0" Ideal Loads so I can't compare anything. The measure that I use to export to .csv file is:
OpenStudio Measures
- AddOutputVariable with variable name Zone Air System Sensible Heating Energy
- AddOutputVariable 1 with variable name Zone Air System Sensible Cooling Energy
Reporting Measures
- ExportOutputVariabletoCSV with variable name Zone Air System Sensible Heating Energy
- ExportOutputVariabletoCSV 1 with variable name Zone Air System Sensible Cooling Energy
I'm attaching my updated .osm and weather file .epw in a .zip here: http://www.mediafire.com/file/wnc6z4uy8084bcc/radiant_model.zip/file
Thank's in advance!
Error while modeling radiant underfloor cooling system
Hello guys! I'm a student in Technical University in Crete and I've been struggling a couple of weeks in a project, in which I would like to model a radiant floor cooling system using "Low Temperature Radiant Variable Flow" and I'm getting the following warnings error every time:
Error file results:
Program Version,EnergyPlus, Version 9.0.1-bb7ca4f0da, YMD=2019.01.18 18:50, ************* Beginning Zone Sizing Calculations ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS ON DISCRETE", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS ON CONTINUOUS", Blank Schedule Type Limits Name input -- will not be validated. ** Warning ** GetHTSurfaceData: Surfaces with interface** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW ** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 1 ** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 2 ** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 3 ** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 4 ** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 5 ** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 6 ** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ ** Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 7 ** Fatal ** GetLowTempRadiantSystem: Errors found in input. Preceding conditions cause termination. ...Summary of Errors that led toGround found but no "Ground Temperatures" were input. ** ~~~ ** Found first in surface=SURFACE 16 ** ~~~ ** Defaults, constant throughout the year of (18.0) will be used. ** Warning ** CheckUsedConstructions: There are 1 nominally unused constructions in input. ** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings; ** Warning ** Calculated design heating load for zone=THERMAL ZONE 4 is zero. ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs. ** Warning ** Calculated design heating load for zone=THERMAL ZONE 8 is zero. ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs. ************* Beginning Plant Sizing Calculations ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="CHILLER - AIR COOLED" ** ~~~ ** Adding OutdoorAir:Node=CHILLER - AIR COOLED INLET NODE FOR CONDENSER ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="CHILLER - AIR COOLED" ** ~~~ ** Energy input ratio as a function of temperature curve output is not equal to 1.0 (+ or - 10%) at reference conditions. ** ~~~ ** Curve output at reference conditions = 0.850 ** Warning ** Output:Meter:MeterFileOnly requested for "Electricity:Facility" (TimeStep), already on "Output:Meter". Will report to both eplusout.eso and eplusout.mtr ************* Testing Individual Branch Integrity ************* All Branches passed integrity testing ************* Testing Individual Supply Air Path Integrity ************* All Supply Air Paths passed integrity testing ************* Testing Individual Return Air Path Integrity ************* All Return Air Paths passed integrity testing ************* No node connection errors were found. ************* Beginning Simulation ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 1] ** ~~~ ** Surface [SURFACE 28] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 33.33 ** ~~~ ** Zone dew-point temperature + safety delta T= 33.79 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 6] ** ~~~ ** Surface [SURFACE 49] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 32.67 ** ~~~ ** Zone dew-point temperature + safety delta T= 38.23 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 7] ** ~~~ ** Surface [SURFACE 42] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 33.01 ** ~~~ ** Zone dew-point temperature + safety delta T= 35.55 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 00:10 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ** ~~~ ** Routine=CorrectZoneHumRat, Environment=SOUDA/KHANIA ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 14:20 - 14:30 ** ~~~ ** Input Temperature=200.11 ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 5] ** ~~~ ** Surface [SURFACE 35] temperature below dew-point temperature--potential for condensation exists ** ~~~ ** Flow to the radiant system will be shut-off to avoid condensation ** ~~~ ** Predicted radiant system surface temperature = 28.09 ** ~~~ ** Zone dew-point temperature + safety delta T= 28.16 ** ~~~ ** Environment=SOUDA/KHANIA ANN CLG .4% CONDNS ENTH=>MDB, at Simulation time=07/21 15:30 - 15:40 ** ~~~ ** Note that a 1.0000 C safety was chosen in the input for the shut-off criteria ** ~~~ ** Note also that this affects all surfaces that are part of this radiant system ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-ELECTRICITY" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-DISTILLATE OIL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-RESIDUAL OIL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-NATURAL GAS" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ** Warning ** The resource referenced by LifeCycleCost:UsePriceEscalation= "U.S. AVG COMMERCIAL-COAL" has no energy cost. ** ~~~ ** ... It is likely that the wrong resource is used. The resource should match the meter used in Utility:Tariff. ************* Simulation Error Summary ************* ************* There are 3 unused schedules in input. ************* There are 3 unused week schedules in input. ************* There are 6 unused day schedules in input. ************* Use Output:Diagnostics,DisplayUnusedSchedules; to see them. ************* ************* ===== Recurring Error Summary ===== ************* The following recurringprogram termination: ..... Reference severe errormessages occurred. ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 1] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 53532 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=35.882518 C Min=25.368306 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 6] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 124007 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=37.290586 C Min=21.089111 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 7] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 83808 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=36.035267 C Min=24.842032 C ************* ************* ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ************* ** ~~~ ** This error occurred 419 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=237.325226 C Min=200.115784 C ************* ************* ** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [LOW TEMP RADIANT VAR FLOW 5] condensation shut-off occurrence continues. ************* ** ~~~ ** This error occurred 110 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=27.4445 C Min=27.085091 C ************* ************* ************* ===== Final Error Summary ===== ************* The following error categories occurred. Consider correcting or noting. ************* Nominally Unused Constructions ************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause ************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm ************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option). ************* ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors. ************* EnergyPlus Sizing Error Summary. During Sizing: 7 Warning; 0 Severe Errors. ************* EnergyPlus Completed Successfully-- 261891 Warning; 0 Severe Errors; Elapsed Time=00hr 00min 48.82seccount=8 ..... Last severe error=Hydronic radiant systems may not be autosized without specification of nodes or schedules.
I have already seen these posts:
- https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/
- https://unmethours.com/question/17175/calculated-design-cooling-load-is-zero/
- https://unmethours.com/question/9399/energyplus-design-cooling-load-is-zero/
- https://unmethours.com/question/23927/many-unmet-cooling-hours-with-radiant-floor-with-doas-possibly-due-to-condensation-shutoff/
this post: https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/ but I couldn't solve my warnings. error. Could somebody help me please?
The major problem is when I try to export my results to .csv I get "0" Ideal Loads so I can't compare anything. The measure that I use to export to .csv file is:
OpenStudio Measures
- AddOutputVariable with variable name Zone Air System Sensible Heating Energy
- AddOutputVariable 1 with variable name Zone Air System Sensible Cooling Energy
Reporting Measures
- ExportOutputVariabletoCSV with variable name Zone Air System Sensible Heating Energy
- ExportOutputVariabletoCSV 1 with variable name Zone Air System Sensible Cooling Energy
I'm attaching my updated .osm and weather file .epw in a .zip here: http://www.mediafire.com/file/wnc6z4uy8084bcc/radiant_model.zip/filehttp://www.mediafire.com/file/281lrnz1tnqhgkg/radiant_model.zip/file
Thank's in advance!
Error while modeling radiant underfloor cooling system
Hello guys! I'm a student in Technical University in Crete and I've been struggling a couple of weeks in a project, in which I would like to model a radiant floor cooling system using "Low Temperature Radiant Variable Flow" and I'm getting the following error every time:
** Severe ** Hydronic radiant systems may not be autosized without specification of nodes or schedules. ** ~~~ **
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ *
I have already seen this post: https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/ but I couldn't solve my error. Could somebody help me please?
I'm attaching my .osm and weather file .epw in a .zip here: http://www.mediafire.com/file/281lrnz1tnqhgkg/radiant_model.zip/file
Thank's in advance!
Error while modeling radiant underfloor cooling system
Hello guys! I'm a student in Technical University in Crete and I've been struggling a couple of weeks in a project, in which I would like to model a radiant floor cooling system using "Low Temperature Radiant Variable Flow" and I'm getting the following error every time:
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 1
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 2
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 3
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 4
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 5
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 6
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules.
* ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 7
* Fatal * GetLowTempRadiantSystem: Errors found in input. Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=8
..... Last severe error=Hydronic radiant systems may not be autosized without specification of nodes or
schedules.
schedules.
I have already seen this post: https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/ but I couldn't solve my error. Could somebody help me please?
I'm attaching my .osm and weather file .epw in a .zip here: http://www.mediafire.com/file/281lrnz1tnqhgkg/radiant_model.zip/file
Thank's in advance!
Error while modeling radiant underfloor cooling system
Hello guys! I'm a student in Technical University in Crete and I've been struggling a couple of weeks in a project, in which I would like to model a radiant floor cooling system using "Low Temperature Radiant Variable Flow" and I'm getting the following error every time:
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 1 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 2 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 3 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 4 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 5 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 6 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 7 * Fatal * GetLowTempRadiantSystem: Errors found in input. Preceding conditions cause termination. ...Summary of Errors that led to program termination: ..... Reference severe error count=8 ..... Last severe error=Hydronic radiant systems may not be autosized without specification of nodes or schedules.
I have already seen this post: https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/ but I couldn't solve my error. Could somebody help me please?
I'm attaching my .osm and weather file .epw in a .zip here: http://www.mediafire.com/file/281lrnz1tnqhgkg/radiant_model.zip/file
Thank's in advance!
Error while modeling radiant underfloor cooling system
Hello guys! I'm a student in Technical University in Crete and I've been struggling a couple of weeks in a project, in which I would like to model a radiant floor cooling system using "Low Temperature Radiant Variable Flow" and I'm getting the following error every time:
* Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 1 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 2 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 3 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 4 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 5 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 6 * Severe * Hydronic radiant systems may not be autosized without specification of nodes or schedules. * ~~~ * Occurs in ZoneHVAC:LowTemperatureRadiant:VariableFlow (heating input) = LOW TEMP RADIANT VAR FLOW 7 * Fatal * GetLowTempRadiantSystem: Errors found in input. Preceding conditions cause termination. ...Summary of Errors that led to program termination: ..... Reference severe error count=8 ..... Last severe error=Hydronic radiant systems may not be autosized without specification of nodes or schedules.
I have already seen this post: https://unmethours.com/question/19482/error-when-controling-a-low-temperature-radiant-floor/ but I couldn't solve my error. Could somebody help me please?
I'm attaching my .osm and weather file .epw in a .zip here: http://www.mediafire.com/file/281lrnz1tnqhgkg/radiant_model.zip/file
Thank's in advance!