Revision history [back]
Why using warmest sp manager undersize cooling capacity for VAV reheat system?
Hi All,
I am a new user of openstudio. I am trying to model a 90.1 baseline for a hotel using a central VAV system with electric parallel fan box reheat. But I am getting too much over heating. I use the warmest setpoint to in my air loop. However when I plot the warmest zone, I see that the autosize capacity cannot lower the air temperature to setpoint level. I also checked that the reheat is not active as well. I thought using the warmest set point manager would resolve this. Why is the autosizing algorithm under sizing the cooling capacity? Thanks
Why using warmest sp manager undersize cooling capacity for VAV reheat system?
Hi All,
I am a new user of openstudio. I am trying to model a 90.1 baseline for a hotel using a central VAV system with electric parallel fan box reheat. But I am getting too much over heating. I use the warmest setpoint to in my air loop. However when I plot the warmest zone, I see that the autosize capacity cannot lower the air temperature to setpoint level. I also checked that the reheat is not active as well. I thought using the warmest set point manager would resolve this. Why is the autosizing algorithm under sizing the cooling capacity? Thanks
Why using warmest sp manager undersize cooling capacity for VAV reheat system?
Hi All,
I am a new user of openstudio. I am trying to model a 90.1 baseline for a hotel using a central VAV system with electric parallel fan box reheat. But I am getting too much over heating. I use the warmest setpoint to in my air loop. However when I plot the warmest zone, I see that the autosize capacity cannot lower the air temperature to setpoint level. I also checked that the reheat is not active as well. I thought using the warmest set point manager would resolve this. Why is the autosizing algorithm under sizing the cooling capacity? Thanks