Revision history [back]
Zone Ideal Loads mismatch
Hi guys
I can't get the following equation (for both heating and cooling) to match in my simulations (example file idf):
Zone Ideal Loads Supply Air Total Cooling Energy + Zone Ideal Loads Heat Recovery Total Cooling Energy
= Zone Ideal Loads Zone Total Cooling Energy+ Zone Ideal Loads Outdoor Air Total Cooling Energy
<=>
2312.1212797468634 + 0 = 8598.715438236986 + 77.11803171210939 [kWh/year]
EnergyPlus version 8.5
----- Update ----
Have the same issue in version 8.9, also for both heating and cooling
+++++ Info +++++
HVAC objects from expanded idf:
ZoneHVAC:IdealLoadsAirSystem,
ZONENAME Ideal Loads Air System, !- Name
, !- Availability Schedule Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Supply Air Node Name
, !- Zone Exhaust Air Node Name
40, !- Maximum Heating Supply Air Temperature [C]
13, !- Minimum Cooling Supply Air Temperature [C]
0.008, !- Maximum Heating Supply Air Humidity Ratio [kg-H20/kg-air]
0.0085, !- Minimum Cooling Supply Air Humidity Ratio [kg-H20/kg-air]
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, !- Maximum Sensible Heating Capacity {m3/s}
LimitFlowRate, !- Cooling Limit
autosize, !- Maximum Cooling Air Flow Rate {m3/s}
, !- Maximum Total Cooling Capacity {m3/s}
, !- Heating Availability Schedule Name
, !- Cooling Availability Schedule Name
None, !- Dehumidification Control Type
0.7, !- Cooling Sensible Heat Ratio
None, !- Humidification Control Type
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
ZONENAME Ideal Loads Outdoor Air Inlet, !- Outdoor Air Inlet Node Name
None, !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, !- Heat Recovery Type
0.7, !- Sensible Heat Recovery Effectiveness
0.65; !- Latent Heat Recovery Effectiveness
ZoneHVAC:EquipmentConnections,
ZONENAME, !- Zone Name
ZONENAME Equipment, !- Zone Conditioning Equipment List Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
ZONENAME Zone Air Node, !- Zone Air Node Name
ZONENAME Return Outlet; !- Zone Return Air Node Name
ZoneHVAC:EquipmentList,
ZONENAME Equipment, !- Name
ZoneHVAC:IdealLoadsAirSystem, !- Zone Equipment Object Type
ZONENAME Ideal Loads Air System, !- Zone Equipment Name
1, !- Zone Equipment Cooling Sequence
1; !- Zone Equipment Heating or No-Load Sequence
ThermostatSetpoint:DualSetpoint,
ZONENAME_HVAC Dual SP Control, !- Name
HeatStPoint_BP, !- Heating Setpoint Temperature Schedule Name
CoolingStPoint_BP; !- Cooling Setpoint Temperature Schedule Name
ScheduleTypeLimits,
HVACTemplate Any Number; !- Name
Schedule:Compact,
HVACTemplate-Always 4, !- Name
HVACTemplate Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
4; !- Field 4
ZoneControl:Thermostat,
ZONENAME Thermostat, !- Name
ZONENAME, !- Zone or ZoneList Name
HVACTemplate-Always 4, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control Object Type
ZONENAME_HVAC Dual SP Control; !- Control Name
Sizing:Zone,
ZONENAME, !- Zone or ZoneList Name
SupplyAirTemperature, !- Zone Cooling Design Supply Air Temperature Input Method
13, !- Zone Cooling Design Supply Air Temperature {C}
, !- Zone Cooling Design Supply Air Temperature Difference {delta C}
SupplyAirTemperature, !- Zone Heating Design Supply Air Temperature Input Method
40, !- Zone Heating Design Supply Air Temperature {C}
, !- Zone Heating Design Supply Air Temperature Difference {delta C}
0.0085, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H20/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
, !- Zone Heating Sizing Factor
, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction {}
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0, !- Heating Maximum Air Flow Fraction {}
; !- Design Specification Zone Air Distribution Object Name
Does anybody have an idea as to why ?
Zone Ideal Loads mismatch
Hi guys
I can't get the following equation (for both heating and cooling) to match in my simulations (example file idf):
Zone Ideal Loads Supply Air Total Cooling Energy + Zone Ideal Loads Heat Recovery Total Cooling Energy
= Zone Ideal Loads Zone Total Cooling Energy+ Zone Ideal Loads Outdoor Air Total Cooling Energy
<=>
2312.1212797468634 + 0 = 8598.715438236986 + 77.11803171210939 [kWh/year]
EnergyPlus version 8.5
----- Update ----
Have the same issue in version 8.9, also for both heating and cooling
+++++ Info +++++
HVAC objects from expanded idf:
ZoneHVAC:IdealLoadsAirSystem,
ZONENAME Ideal Loads Air System, !- Name
, !- Availability Schedule Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Supply Air Node Name
, !- Zone Exhaust Air Node Name
40, !- Maximum Heating Supply Air Temperature [C]
13, !- Minimum Cooling Supply Air Temperature [C]
0.008, !- Maximum Heating Supply Air Humidity Ratio [kg-H20/kg-air]
0.0085, !- Minimum Cooling Supply Air Humidity Ratio [kg-H20/kg-air]
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, !- Maximum Sensible Heating Capacity {m3/s}
LimitFlowRate, !- Cooling Limit
autosize, !- Maximum Cooling Air Flow Rate {m3/s}
, !- Maximum Total Cooling Capacity {m3/s}
, !- Heating Availability Schedule Name
, !- Cooling Availability Schedule Name
None, !- Dehumidification Control Type
0.7, !- Cooling Sensible Heat Ratio
None, !- Humidification Control Type
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
ZONENAME Ideal Loads Outdoor Air Inlet, !- Outdoor Air Inlet Node Name
None, !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, !- Heat Recovery Type
0.7, !- Sensible Heat Recovery Effectiveness
0.65; !- Latent Heat Recovery Effectiveness
ZoneHVAC:EquipmentConnections,
ZONENAME, !- Zone Name
ZONENAME Equipment, !- Zone Conditioning Equipment List Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
ZONENAME Zone Air Node, !- Zone Air Node Name
ZONENAME Return Outlet; !- Zone Return Air Node Name
ZoneHVAC:EquipmentList,
ZONENAME Equipment, !- Name
ZoneHVAC:IdealLoadsAirSystem, !- Zone Equipment Object Type
ZONENAME Ideal Loads Air System, !- Zone Equipment Name
1, !- Zone Equipment Cooling Sequence
1; !- Zone Equipment Heating or No-Load Sequence
ThermostatSetpoint:DualSetpoint,
ZONENAME_HVAC Dual SP Control, !- Name
HeatStPoint_BP, !- Heating Setpoint Temperature Schedule Name
CoolingStPoint_BP; !- Cooling Setpoint Temperature Schedule Name
ScheduleTypeLimits,
HVACTemplate Any Number; !- Name
Schedule:Compact,
HVACTemplate-Always 4, !- Name
HVACTemplate Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
4; !- Field 4
ZoneControl:Thermostat,
ZONENAME Thermostat, !- Name
ZONENAME, !- Zone or ZoneList Name
HVACTemplate-Always 4, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control Object Type
ZONENAME_HVAC Dual SP Control; !- Control Name
Sizing:Zone,
ZONENAME, !- Zone or ZoneList Name
SupplyAirTemperature, !- Zone Cooling Design Supply Air Temperature Input Method
13, !- Zone Cooling Design Supply Air Temperature {C}
, !- Zone Cooling Design Supply Air Temperature Difference {delta C}
SupplyAirTemperature, !- Zone Heating Design Supply Air Temperature Input Method
40, !- Zone Heating Design Supply Air Temperature {C}
, !- Zone Heating Design Supply Air Temperature Difference {delta C}
0.0085, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H20/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
, !- Zone Heating Sizing Factor
, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction {}
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0, !- Heating Maximum Air Flow Fraction {}
; !- Design Specification Zone Air Distribution Object Name
Does anybody have an idea as to why ?
Zone Ideal Loads mismatch
Hi guys
I can't get the following equation (for both heating and cooling) to match in my simulations (example file idf):
Zone Ideal Loads Supply Air Total Cooling Energy + Zone Ideal Loads Heat Recovery Total Cooling Energy
= Zone Ideal Loads Zone Total Cooling Energy+ Zone Ideal Loads Outdoor Air Total Cooling Energy
<=>
2312.1212797468634 + 0 = 8598.715438236986 + 77.11803171210939 [kWh/year]
EnergyPlus version 8.5
----- Update ----
Have the same issue in version 8.9, also for both heating and cooling
+++++ Info +++++
EnergyPlus version 8.5
HVAC objects from expanded idf:
ZoneHVAC:IdealLoadsAirSystem,
ZONENAME Ideal Loads Air System, !- Name
, !- Availability Schedule Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Supply Air Node Name
, !- Zone Exhaust Air Node Name
40, !- Maximum Heating Supply Air Temperature [C]
13, !- Minimum Cooling Supply Air Temperature [C]
0.008, !- Maximum Heating Supply Air Humidity Ratio [kg-H20/kg-air]
0.0085, !- Minimum Cooling Supply Air Humidity Ratio [kg-H20/kg-air]
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, !- Maximum Sensible Heating Capacity {m3/s}
LimitFlowRate, !- Cooling Limit
autosize, !- Maximum Cooling Air Flow Rate {m3/s}
, !- Maximum Total Cooling Capacity {m3/s}
, !- Heating Availability Schedule Name
, !- Cooling Availability Schedule Name
None, !- Dehumidification Control Type
0.7, !- Cooling Sensible Heat Ratio
None, !- Humidification Control Type
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
ZONENAME Ideal Loads Outdoor Air Inlet, !- Outdoor Air Inlet Node Name
None, !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, !- Heat Recovery Type
0.7, !- Sensible Heat Recovery Effectiveness
0.65; !- Latent Heat Recovery Effectiveness
ZoneHVAC:EquipmentConnections,
ZONENAME, !- Zone Name
ZONENAME Equipment, !- Zone Conditioning Equipment List Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
ZONENAME Zone Air Node, !- Zone Air Node Name
ZONENAME Return Outlet; !- Zone Return Air Node Name
ZoneHVAC:EquipmentList,
ZONENAME Equipment, !- Name
ZoneHVAC:IdealLoadsAirSystem, !- Zone Equipment Object Type
ZONENAME Ideal Loads Air System, !- Zone Equipment Name
1, !- Zone Equipment Cooling Sequence
1; !- Zone Equipment Heating or No-Load Sequence
ThermostatSetpoint:DualSetpoint,
ZONENAME_HVAC Dual SP Control, !- Name
HeatStPoint_BP, !- Heating Setpoint Temperature Schedule Name
CoolingStPoint_BP; !- Cooling Setpoint Temperature Schedule Name
ScheduleTypeLimits,
HVACTemplate Any Number; !- Name
Schedule:Compact,
HVACTemplate-Always 4, !- Name
HVACTemplate Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
4; !- Field 4
ZoneControl:Thermostat,
ZONENAME Thermostat, !- Name
ZONENAME, !- Zone or ZoneList Name
HVACTemplate-Always 4, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control Object Type
ZONENAME_HVAC Dual SP Control; !- Control Name
Sizing:Zone,
ZONENAME, !- Zone or ZoneList Name
SupplyAirTemperature, !- Zone Cooling Design Supply Air Temperature Input Method
13, !- Zone Cooling Design Supply Air Temperature {C}
, !- Zone Cooling Design Supply Air Temperature Difference {delta C}
SupplyAirTemperature, !- Zone Heating Design Supply Air Temperature Input Method
40, !- Zone Heating Design Supply Air Temperature {C}
, !- Zone Heating Design Supply Air Temperature Difference {delta C}
0.0085, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H20/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
, !- Zone Heating Sizing Factor
, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction {}
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0, !- Heating Maximum Air Flow Fraction {}
; !- Design Specification Zone Air Distribution Object Name
Does anybody have an idea as to why ?
Zone Ideal Loads mismatch
Hi guys
I can't get the following equation (for both heating and cooling) to match in my simulations (example file idf):
Zone Ideal Loads Supply Air Total Cooling Energy + Zone Ideal Loads Heat Recovery Total Cooling Energy
= Zone Ideal Loads Zone Total Cooling Energy+ Zone Ideal Loads Outdoor Air Total Cooling Energy
<=>
2312.1212797468634 + 0 = 8598.715438236986 + 77.11803171210939 [kWh/year]
+++++ Info +++++
EnergyPlus version 8.5
HVAC objects from expanded idf:
ZoneHVAC:IdealLoadsAirSystem,
ZONENAME Ideal Loads Air System, !- Name
, !- Availability Schedule Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Supply Air Node Name
, !- Zone Exhaust Air Node Name
40, !- Maximum Heating Supply Air Temperature [C]
13, !- Minimum Cooling Supply Air Temperature [C]
0.008, !- Maximum Heating Supply Air Humidity Ratio [kg-H20/kg-air]
0.0085, !- Minimum Cooling Supply Air Humidity Ratio [kg-H20/kg-air]
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, !- Maximum Sensible Heating Capacity {m3/s}
LimitFlowRate, !- Cooling Limit
autosize, !- Maximum Cooling Air Flow Rate {m3/s}
, !- Maximum Total Cooling Capacity {m3/s}
, !- Heating Availability Schedule Name
, !- Cooling Availability Schedule Name
None, !- Dehumidification Control Type
0.7, !- Cooling Sensible Heat Ratio
None, !- Humidification Control Type
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
ZONENAME Ideal Loads Outdoor Air Inlet, !- Outdoor Air Inlet Node Name
None, !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, !- Heat Recovery Type
0.7, !- Sensible Heat Recovery Effectiveness
0.65; !- Latent Heat Recovery Effectiveness
ZoneHVAC:EquipmentConnections,
ZONENAME, !- Zone Name
ZONENAME Equipment, !- Zone Conditioning Equipment List Name
ZONENAME Ideal Loads Supply Inlet, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
ZONENAME Zone Air Node, !- Zone Air Node Name
ZONENAME Return Outlet; !- Zone Return Air Node Name
ZoneHVAC:EquipmentList,
ZONENAME Equipment, !- Name
ZoneHVAC:IdealLoadsAirSystem, !- Zone Equipment Object Type
ZONENAME Ideal Loads Air System, !- Zone Equipment Name
1, !- Zone Equipment Cooling Sequence
1; !- Zone Equipment Heating or No-Load Sequence
ThermostatSetpoint:DualSetpoint,
ZONENAME_HVAC Dual SP Control, !- Name
HeatStPoint_BP, !- Heating Setpoint Temperature Schedule Name
CoolingStPoint_BP; !- Cooling Setpoint Temperature Schedule Name
ScheduleTypeLimits,
HVACTemplate Any Number; !- Name
Schedule:Compact,
HVACTemplate-Always 4, !- Name
HVACTemplate Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
4; !- Field 4
ZoneControl:Thermostat,
ZONENAME Thermostat, !- Name
ZONENAME, !- Zone or ZoneList Name
HVACTemplate-Always 4, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control Object Type
ZONENAME_HVAC Dual SP Control; !- Control Name
Sizing:Zone,
ZONENAME, !- Zone or ZoneList Name
SupplyAirTemperature, !- Zone Cooling Design Supply Air Temperature Input Method
13, !- Zone Cooling Design Supply Air Temperature {C}
, !- Zone Cooling Design Supply Air Temperature Difference {delta C}
SupplyAirTemperature, !- Zone Heating Design Supply Air Temperature Input Method
40, !- Zone Heating Design Supply Air Temperature {C}
, !- Zone Heating Design Supply Air Temperature Difference {delta C}
0.0085, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H20/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
, !- Zone Heating Sizing Factor
, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction {}
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0, !- Heating Maximum Air Flow Fraction {}
; !- Design Specification Zone Air Distribution Object Name
Does anybody have an idea as to why ?
Zone Ideal Loads mismatch
Hi guys
I can't get the following equation (for both heating and cooling) to match in my simulations (example file idf):
Zone Ideal Loads Supply Air Total Cooling Energy + Zone Ideal Loads Heat Recovery Total Cooling Energy
= Zone Ideal Loads Zone Total Cooling Energy+ Zone Ideal Loads Outdoor Air Total Cooling Energy
<=>
2312.1212797468634 + 0 = 8598.715438236986 + 77.11803171210939 [kWh/year]
+++++ Info +++++
EnergyPlus version 8.5
HVAC objects from expanded idf:objects:
ZoneHVAC:IdealLoadsAirSystem,
ZONENAME Ideal Loads Air System, !- Name
, HVACTemplate:Zone:IdealLoadsAirSystem,
ZONENAME, !- Zone Name
ZONENAME_HVAC, !- Template Thermostat Name
, !- Availability Schedule Name
ZONENAME Ideal Loads 40, !- Heating Supply Inlet, !- Zone Air Temp {C}
, !- Cooling Supply Air Node Name
, !- Zone Exhaust Air Node Name
40, Temp {C}
0.008, !- Max Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.0085, !- Min Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
, !- Heating Limit
, !- Maximum Heating Supply Air Temperature [C]
13, !- Minimum Cooling Supply Air Temperature [C]
0.008, !- Maximum Heating Supply Air Humidity Ratio [kg-H20/kg-air]
0.0085, !- Minimum Cooling Supply Air Humidity Ratio [kg-H20/kg-air]
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, , !- Maximum Sensible Heating Capacity Heat Capacity
LimitFlowRate, !- Cooling Limit
autosize, !- Maximum Cooling Air Flow Rate {m3/s}
LimitFlowRate, !- Cooling Limit
autosize, !- Maximum Cooling Air Flow Rate {m3/s}
, , !- Maximum Total Cooling Capacity {m3/s}
, Capacity
, !- Heating Availability Schedule Name
, Schedule
, !- Cooling Availability Schedule Name
Schedule
None, !- Dehumidification Control Type
0.7, , !- Cooling Sensible Heat Ratio
, !- Dehumidification Setpoint
None, !- Humidification Control Type
, !- Humidification Setpoint
DetailedSpecification, !- Outdoor Air Method
, !- Outdoor Air Flow Rate Per Person
, !- Outdoor Air Flow Rate Per Floor Zone Area
, !- Outdoor Air Flow Rate Per Zone
ZONENAMEOutdoorAirCntrl, !- Design Specification Outdoor Air Object Name
ZONENAME Ideal Loads Outdoor Air Inlet, !- Outdoor Air Inlet Node Name
None, , !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, , !- Heat Recovery Type
0.7, , !- Sensible Heat Recovery Effectiveness
0.65; ; !- Latent Heat Recovery Effectiveness
DesignSpecification:OutdoorAir,
ZONENAMEOutdoorAirCntrl, !- Name
Sum, !- Outdoor Air Method
0.0, !- Outdoor Air Flow per Person {m3/s-person}
0.0040000000000000001, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
0, !- Outdoor Air Flow per Zone {m3/s}
0, !- Outdoor Air Flow Air Changes per Hour {1/hr}
occ_BP; !- Outdoor Air Flow Rate Fraction Schedule Name
Does anybody have an idea as to why ??