Revision history [back]
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working on a research project (which is NOT focused on finding the most efficient HVAC system) I need to pick a HVAC system for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most energy-saving (and/or most common) for high-rise office buildings in tropical desert climate (Dubai), and why? Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
.-1. Thermostat Only
.0. Ideal Air Loads
.1. PTAC | Residential
.2. PTHP | Residential
.3. Packaged Single Zone - AC
.4. Packaged Single Zone - HP
.5. Packaged VAV w/ Reheat
.6. Packaged VAV w/ PFP Boxes
.7. VAV w/ Reheat
.8. VAV w/ PFP Boxes
.9. Warm Air Furnace - Gas Fired
.10.Warm Air Furnace - Electric
.11.Fan Coil Units + DOAS
.12.Active Chilled Beams + DOAS
.13.Radiant Floors + DOAS
.14.Custom Rad Surfaces + DOAS
.15.Heated Surfaces + VAV Cooling
.16.VRF + DOAS
.17.Ground Source WSHP + DOAS
.18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working on a research project (which is NOT focused on finding the most efficient HVAC system) I need to pick a HVAC system for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most energy-saving (and/or most common) for high-rise office buildings in tropical desert climate (Dubai), and why? Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
.-1. Thermostat Only
.0. Ideal Air Loads
.1. PTAC | Residential
.2. PTHP | Residential
.3. Packaged Single Zone - AC
.4. Packaged Single Zone - HP
.5. Packaged VAV w/ Reheat
.6. Packaged VAV w/ PFP Boxes
.7. VAV w/ Reheat
.8. VAV w/ PFP Boxes
.9. Warm Air Furnace - Gas Fired
.10.Warm Air Furnace - Electric
.11.Fan Coil Units + DOAS
.12.Active Chilled Beams + DOAS
.13.Radiant Floors + DOAS
.14.Custom Rad Surfaces + DOAS
.15.Heated Surfaces + VAV Cooling
.16.VRF + DOAS
.17.Ground Source WSHP + DOAS
.18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working on a research project (which is NOT focused on finding the most efficient HVAC system) I need to pick a HVAC system for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most energy-saving (and/or most common) for high-rise office buildings in tropical desert climate (Dubai), and why? Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
.-1. Thermostat Only
.0. Ideal Air Loads
.1. PTAC | Residential
.2. PTHP | Residential
.3. Packaged Single Zone - AC
.4. Packaged Single Zone - HP
.5. Packaged VAV w/ Reheat
.6. Packaged VAV w/ PFP Boxes
.7. VAV w/ Reheat
.8. VAV w/ PFP Boxes
.9. Warm Air Furnace - Gas Fired
.10.Warm Air Furnace - Electric
.11.Fan Coil Units + DOAS
.12.Active Chilled Beams + DOAS
.13.Radiant Floors + DOAS
.14.Custom Rad Surfaces + DOAS
.15.Heated Surfaces + VAV Cooling
.16.VRF + DOAS
.17.Ground Source WSHP + DOAS
.18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working on a research project (which is NOT focused on finding the most efficient HVAC system) I need to pick a HVAC system for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most energy-saving (and/or most common) for high-rise office buildings in tropical desert climate (Dubai), and why? Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
.-1. Thermostat Only
.0. Ideal Air Loads
.1. PTAC | Residential
.2. PTHP | Residential
.3. Packaged Single Zone - AC
.4. Packaged Single Zone - HP
.5. Packaged VAV w/ Reheat
.6. Packaged VAV w/ PFP Boxes
.7. VAV w/ Reheat
.8. VAV w/ PFP Boxes
.9. Warm Air Furnace - Gas Fired
.10.Warm Air Furnace - Electric
.11.Fan Coil Units + DOAS
.12.Active Chilled Beams + DOAS
.13.Radiant Floors + DOAS
.14.Custom Rad Surfaces + DOAS
.15.Heated Surfaces + VAV Cooling
.16.VRF + DOAS
.17.Ground Source WSHP + DOAS
.18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working on a research project (which is NOT focused on finding the most efficient HVAC system) I need to pick a HVAC system for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most energy-saving (and/or most common) for high-rise office buildings in tropical desert climate (Dubai), and why? Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
.-1. -1. Thermostat Only
.0.
0. Ideal Air Loads
.1.
1. PTAC | Residential
.2.
2. PTHP | Residential
.3.
3. Packaged Single Zone - AC
.4.
4. Packaged Single Zone - HP
.5.
5. Packaged VAV w/ Reheat
.6.
6. Packaged VAV w/ PFP Boxes
.7.
7. VAV w/ Reheat
.8.
8. VAV w/ PFP Boxes
.9.
9. Warm Air Furnace - Gas Fired
.10.Warm
10.Warm Air Furnace - Electric
.11.Fan
11.Fan Coil Units + DOAS
.12.Active
12.Active Chilled Beams + DOAS
.13.Radiant
13.Radiant Floors + DOAS
.14.Custom
14.Custom Rad Surfaces + DOAS
.15.Heated
15.Heated Surfaces + VAV Cooling
.16.VRF + DOAS
.17.Ground 16.VRF + DOAS
17.Ground Source WSHP + DOAS
.18.Ground
18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working on a research project (which is NOT focused on finding the most efficient HVAC system) I need to pick a HVAC system for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most energy-saving (and/or most common) for high-rise office buildings in tropical desert climate (Dubai), and why? Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
-1. Thermostat Only
0. Ideal Air Loads
1. PTAC | Residential
2. PTHP | Residential
3. Packaged Single Zone - AC
4. Packaged Single Zone - HP
5. Packaged VAV w/ Reheat
6. Packaged VAV w/ PFP Boxes
7. VAV w/ Reheat
8. VAV w/ PFP Boxes
9. Warm Air Furnace - Gas Fired
10.Warm Air Furnace - Electric
11.Fan Coil Units + DOAS
12.Active Chilled Beams + DOAS
13.Radiant Floors + DOAS
14.Custom Rad Surfaces + DOAS
15.Heated Surfaces + VAV Cooling
16.VRF + DOAS
17.Ground Source WSHP + DOAS
18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working on a research project (which is NOT focused on finding the most efficient HVAC system) I need to pick a HVAC system for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most energy-saving (and/or most common) for high-rise office buildings in tropical desert climate (Dubai), and why? Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
-1. Thermostat Only
0. Ideal Air Loads
1. PTAC | Residential
2. PTHP | Residential
3. Packaged Single Zone - AC
4. Packaged Single Zone - HP
5. Packaged VAV w/ Reheat
6. Packaged VAV w/ PFP Boxes
7. VAV w/ Reheat
8. VAV w/ PFP Boxes
9. Warm Air Furnace - Gas Fired
10.Warm Air Furnace - Electric
11.Fan Coil Units + DOAS
12.Active Chilled Beams + DOAS
13.Radiant Floors + DOAS
14.Custom Rad Surfaces + DOAS
15.Heated Surfaces + VAV Cooling
16.VRF + DOAS
17.Ground Source WSHP + DOAS
18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
Working I'm working on a research project (which which is NOT focused on finding most efficient HVAC system) system but anyway I need to pick a HVAC system one for energy simulation.
I would be grateful if you could let me know which HVAC systems are the most more energy-saving (and/or most more common) for high-rise office buildings building in tropical desert climate (Dubai), and why?
Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):
-1. Thermostat Only
0. Ideal Air Loads
1. PTAC | Residential
2. PTHP | Residential
3. Packaged Single Zone - AC
4. Packaged Single Zone - HP
5. Packaged VAV w/ Reheat
6. Packaged VAV w/ PFP Boxes
7. VAV w/ Reheat
8. VAV w/ PFP Boxes
9. Warm Air Furnace - Gas Fired
10.Warm Air Furnace - Electric
11.Fan Coil Units + DOAS
12.Active Chilled Beams + DOAS
13.Radiant Floors + DOAS
14.Custom Rad Surfaces + DOAS
15.Heated Surfaces + VAV Cooling
16.VRF + DOAS
17.Ground Source WSHP + DOAS
18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
I'm working on a research project which is NOT focused on finding most efficient HVAC system but anyway I need to pick one for energy simulation.
I would be grateful if you could let me know which HVAC systems are more energy-saving (and/or more common) for high-rise office building in tropical desert climate (Dubai), and why?
Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB):(LB/HB)
-1. Thermostat Only
0. Ideal Air Loads
1. PTAC | Residential
2. PTHP | Residential
3. Packaged Single Zone - AC
4. Packaged Single Zone - HP
5. Packaged VAV w/ Reheat
6. Packaged VAV w/ PFP Boxes
7. VAV w/ Reheat
8. VAV w/ PFP Boxes
9. Warm Air Furnace - Gas Fired
10.Warm Air Furnace - Electric
11.Fan Coil Units + DOAS
12.Active Chilled Beams + DOAS
13.Radiant Floors + DOAS
14.Custom Rad Surfaces + DOAS
15.Heated Surfaces + VAV Cooling
16.VRF + DOAS
17.Ground Source WSHP + DOAS
18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
I'm working on a research project which is NOT focused on finding most efficient HVAC system but anyway I need to pick one for energy simulation.
I would be grateful if you could let me know which HVAC systems are more energy-saving (and/or more common) for high-rise office building in tropical desert climate (Dubai), and why?
Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List of available HVAC systems in Honeybee (LB/HB)
(LB/HB)
-1. Thermostat Only
0. Ideal Air Loads
1. PTAC | Residential
2. PTHP | Residential
3. Packaged Single Zone - AC
4. Packaged Single Zone - HP
5. Packaged VAV w/ Reheat
6. Packaged VAV w/ PFP Boxes
7. VAV w/ Reheat
8. VAV w/ PFP Boxes
9. Warm Air Furnace - Gas Fired
10.Warm Air Furnace - Electric
11.Fan Coil Units + DOAS
12.Active Chilled Beams + DOAS
13.Radiant Floors + DOAS
14.Custom Rad Surfaces + DOAS
15.Heated Surfaces + VAV Cooling
16.VRF + DOAS
17.Ground Source WSHP + DOAS
18.Ground Source VRF + DOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
I'm working on a research project which is NOT focused on finding most efficient HVAC system but anyway I need to pick one for energy simulation.
I would be grateful if you could let me know which HVAC systems are more energy-saving (and/or more common) for high-rise office building in tropical desert climate (Dubai), and why?
Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (*please (please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
*List List of available HVAC systems in Honeybee (LB/HB)
-1. Thermostat Only
0.
Ideal Air Loads
1.PTAC | Residential
2.PTHP | Residential
3.Packaged Single Zone - AC
4.Packaged Single Zone - HP
5.Packaged VAV w/ Reheat
6.Packaged VAV w/ PFP Boxes
7.VAV w/ Reheat
8.VAV w/ PFP Boxes
9.Warm Air Furnace - Gas Fired
10.Warm Air Furnace - Electric
11.Fan Coil Units + DOAS
12.Active Chilled Beams + DOAS
13.Radiant Floors + DOAS
14.Custom Rad Surfaces + DOAS
15.Heated Surfaces + VAV Cooling
16.VRF + DOAS
17.Ground Source WSHP + DOAS
18.Ground Source VRF + DOASDOAS
What is the most efficient HVAC system for tall office building in tropical desert climate?
I'm working on a research project which is NOT focused on finding most efficient HVAC system but anyway I need to pick one for energy simulation.
I would be grateful if you could let me know which HVAC systems are more energy-saving (and/or more common) for high-rise office building in tropical desert climate (Dubai), and why?
Could you please also send links to available literature supporting your reply?
I have read about pros and cons of some HVAC systems in some papers including: this and this
I use Ladybug/Honeybee (LB/HB) for connecting Rhino models to Energyplus and OpenStudio. It has a list of different HVAC systems to pick from (please see the list below the text).
I guess one of these systems might be a good option: VAV w/ Reheat or VAV w/ PFP Boxes or VRF + DOAS. Please correct me if I'm wrong.
Any help would be appreciated.
List of available HVAC systems in Honeybee (LB/HB) -1. Thermostat Only
Ideal Air Loads
PTAC | Residential
PTHP | Residential
Packaged Single Zone - AC
Packaged Single Zone - HP
Packaged VAV w/ Reheat
Packaged VAV w/ PFP Boxes
VAV w/ Reheat
VAV w/ PFP Boxes
Warm Air Furnace - Gas Fired
10.Warm Air Furnace - Electric
11.Fan Coil Units + DOAS
12.Active Chilled Beams + DOAS
13.Radiant Floors + DOAS
14.Custom Rad Surfaces + DOAS
15.Heated Surfaces + VAV Cooling
16.VRF + DOAS
17.Ground Source WSHP + DOAS
18.Ground Source VRF + DOAS