Revision history [back]
Openstudio fatal errors natural ventilation
I can't seem to find where the error is. The error is fully displayed as shown below. Where do I have to look to address this error? The zone is called "Basement thermal zone" and the object is just called "duct". I'm also not sure what out of range and blank fields I have, since I didn't change that much to the HVAC system.
Thanks in advance.
**** Severe ** IP: IDF line~503 Error detected in Object=ZONEHVAC:EQUIPMENTLIST, name=BASEMENT THERMAL ZONE EQUIPMENT LIST
** ~~~ ** Field [Zone Equipment 1 Name] is required but was blank
** Severe ** IP: Blank "required" fields found in input
** Severe ** IP: Out of "range" values and/or blank required fields found in input
EDIT: I tried several other things but I just can't work it out. I have a simple building with just 1 room and a crawling space. Both spaces have natural ventilation and the room also has an electric heater and airconditioner (only cooling). I'm not familiair with the HVAC names, but I think I got the right heater and airconditioning. For the airconditioning I used a VRF and set the rated heat capacity to 0. Now here comes the part what seems to keep go wrong. Both the room and crawling space have natural ventilation, but they are both separate ventilation holes. The two spaces are also different thermal zones. How can I insert this? I use OpenStudio 2.3 for Windows.
I currently get this error as well:
** Severe ** IP: IDF line~2649 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~3665 Error detected in Object=ZONEINFILTRATION:EFFECTIVELEAKAGEAREA, name=SPACE INFILTRATION EFFECTIVE LEAKAGE AREA 1
** ~~~ ** Field [Zone Name] is required but was blank
** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
** Severe ** IP: Blank "required" fields found in input
** ~~~ ** Possible Invalid Numerics or other problems
** Fatal ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
Openstudio fatal errors natural ventilationerror zone equipment
I can't seem to find where the error is. The error is fully displayed as shown below. Where do I have to look to address this error? The zone is called "Basement thermal zone" and the object is just called "duct". I'm also not sure what out of range and blank fields I have, since I didn't change that much to the HVAC system.
Thanks in advance.
**** Severe ** ** Severe *
IP: IDF line~503 Error detected in Object=ZONEHVAC:EQUIPMENTLIST, name=BASEMENT THERMAL ZONE EQUIPMENT LISTEDIT: I tried several other things but I just can't work it out. I have a simple building with just 1 room and a crawling space. Both spaces have natural ventilation and the room also has an electric heater and airconditioner (only cooling). I'm not familiair with the HVAC names, but I think I got the right heater and airconditioning. For the airconditioning I used a VRF and set the rated heat capacity to 0. Now here comes the part what seems to keep go wrong. Both the room and crawling space have natural ventilation, but they are both separate ventilation holes. The two spaces are also different thermal zones. How can I insert this? I use OpenStudio 2.3 for Windows.
I currently get this error as well:
** Severe ** * Severe *
IP: IDF line~2649 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was ** Severe ** * Severe *
IP: IDF line~3665 Error detected in Object=ZONEINFILTRATION:EFFECTIVELEAKAGEAREA, name=SPACE INFILTRATION EFFECTIVE LEAKAGE AREA 1Openstudio fatal error zone equipment
I can't seem to find where the error is. The error is fully displayed as shown below. Where do I have to look to address this error? The zone is called "Basement thermal zone" and the object is just called "duct". I'm also not sure what out of range and blank fields I have, since I didn't change that much to the HVAC system.
Thanks in advance.
** Severe * IP: IDF line~503 Error detected in Object=ZONEHVAC:EQUIPMENTLIST, name=BASEMENT THERMAL ZONE EQUIPMENT LIST * ~~~ * Field [Zone Equipment 1 Name] is required but was blank * Severe * IP: Blank "required" fields found in input * Severe ** IP: Out of "range" values and/or blank required fields found in input
EDIT: I tried several other things but I just can't work it out. I have a simple building with just 1 room and a crawling space. Both spaces have natural ventilation and the room also has an electric heater and airconditioner (only cooling). I'm not familiair with the HVAC names, but I think I got the right heater and airconditioning. For the airconditioning I used a VRF and set the rated heat capacity to 0. Now here comes the part what seems to keep go wrong. Both the room and crawling space have natural ventilation, but they are both separate ventilation holes. The two spaces are also different thermal zones. How can I insert this? I use OpenStudio 2.3 for Windows.
I currently get this error as well:
* Severe * IP: IDF line~2649 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank.
* Severe * IP: IDF line~3665 Error detected in Object=ZONEINFILTRATION:EFFECTIVELEAKAGEAREA, name=SPACE INFILTRATION EFFECTIVE LEAKAGE AREA 1 * ~~~ * Field [Zone Name] is required but was blank * Warning * IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details. * Severe * IP: Blank "required" fields found in input * ~~~ * Possible Invalid Numerics or other problems * Fatal * IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
Openstudio fatal error zone equipment
I can't seem to find where the error is. The error is fully displayed as shown below. Where do I have to look to address this error? The zone is called "Basement thermal zone" and the object is just called "duct". I'm also not sure what out of range and blank fields I have, since I didn't change that much to the HVAC system.
Thanks in advance.
** Severe * IP: IDF line~503 Error detected in Object=ZONEHVAC:EQUIPMENTLIST, name=BASEMENT THERMAL ZONE EQUIPMENT LIST * ~~~ * Field [Zone Equipment 1 Name] is required but was blank * Severe * IP: Blank "required" fields found in input * Severe ** IP: Out of "range" values and/or blank required fields found in input
EDIT: I tried several other things but I just can't work it out. I have a simple building with just 1 room and a crawling space. Both spaces have natural ventilation and the room also has an electric heater and airconditioner (only cooling). I'm not familiair with the HVAC names, but I think I got the right heater and airconditioning. For the airconditioning I used a VRF and set the rated heat capacity to 0. Now here comes the part what seems to keep go wrong. Both the room and crawling space have natural ventilation, but they are both separate ventilation holes. The two spaces are also different thermal zones. How can I insert this? I use OpenStudio 2.3 for Windows.
I currently get this error as well:
* Severe * IP: IDF line~2649 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank.
* Severe * IP: IDF line~3665 Error detected in Object=ZONEINFILTRATION:EFFECTIVELEAKAGEAREA, name=SPACE INFILTRATION EFFECTIVE LEAKAGE AREA 1 * ~~~ * Field [Zone Name] is required but was blank * Warning * IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details. * Severe * IP: Blank "required" fields found in input * ~~~ * Possible Invalid Numerics or other problems * Fatal * IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
Openstudio fatal error zone equipment
I can't seem to find where the error is. The error is fully displayed as shown below. Where do I have to look to address this error? The zone is called "Basement thermal zone" and the object is just called "duct". I'm also not sure what out of range and blank fields I have, since I didn't change that much to the HVAC system.
Thanks in advance.
** Severe * IP: IDF line~503 Error detected in Object=ZONEHVAC:EQUIPMENTLIST, name=BASEMENT THERMAL ZONE EQUIPMENT LIST * ~~~ * Field [Zone Equipment 1 Name] is required but was blank * Severe * IP: Blank "required" fields found in input * Severe ** IP: Out of "range" values and/or blank required fields found in input
EDIT: I tried several other things but I just can't work it out. I have a simple building with just 1 room and a crawling space. Both spaces have natural ventilation and the room also has an electric heater and airconditioner (only cooling). I'm not familiair with the HVAC names, but I think I got the right heater and airconditioning. For the airconditioning I used a VRF and set the rated heat capacity to 0. Now here comes the part what seems to keep go wrong. Both the room and crawling space have natural ventilation, but they are both separate ventilation holes. The two spaces are also different thermal zones. How can I insert this? I use OpenStudio 2.3 for Windows.
I currently get this error as well:
* Severe * IP: IDF line~2649 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank.
* Severe * IP: IDF line~3665 Error detected in Object=ZONEINFILTRATION:EFFECTIVELEAKAGEAREA, name=SPACE INFILTRATION EFFECTIVE LEAKAGE AREA 1 * ~~~ * Field [Zone Name] is required but was blank * Warning * IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details. * Severe * IP: Blank "required" fields found in input * ~~~ * Possible Invalid Numerics or other problems * Fatal * IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
Openstudio fatal error zone equipment
I can't seem to find where the error is. The error is fully displayed as shown below. Where do I have to look to address this error? The zone is called "Basement thermal zone" and the object is just called "duct". I'm also not sure what out of range and blank fields I have, since I didn't change that much to the HVAC system.
Thanks in advance.
*Program Version,EnergyPlus, Version 8.8.0-7c3bbe4830, YMD=2018.01.11 11:54,IDD_Version 8.8.0
*** IDF Context for following error/warning message:
*** Note -- lines truncated at 300 characters, if necessary...
*** 500 ZoneHVAC:EquipmentList,
*** indicated Name=Basement thermal zone Equipment List
*** Only last 3 lines before error line shown.....
*** 501 Basement thermal zone Equipment List, !- Name
*** 502 Duct, !- Zone Equipment Object Type 1
*** 503 , !- Zone Equipment Name 1
* Severe * * IP: IDF line~503 Error detected in Object=ZONEHVAC:EQUIPMENTLIST, name=BASEMENT THERMAL ZONE EQUIPMENT LIST
* * ~~~ * * Field [Zone Equipment 1 Name] is required but was blank
* * Severe * * IP: Blank "required" fields found in input
* * Severe ** * IP: Out of "range" values and/or blank required fields found in inputinput
* Fatal * IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=3
..... Last severe error=IP: Out of "range" values and/or blank required fields found in input
*** Warning: Node connection errors not checked - most system input has not been read (see previous warning).
*** Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
*** EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
*** EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 3 Severe Errors; Elapsed Time=00hr 00min 0.99sec
EDIT: I tried several other things but I just can't work it out. I have a simple building with just 1 room and a crawling space. Both spaces have natural ventilation and the room also has an electric heater and airconditioner (only cooling). I'm not familiair with the HVAC names, but I think I got the right heater and airconditioning. For the airconditioning I used a VRF and set the rated heat capacity to 0. Now here comes the part what seems to keep go wrong. Both the room and crawling space have natural ventilation, but they are both separate ventilation holes. The two spaces are also different thermal zones. How can I insert this? I use OpenStudio 2.3 for Windows.