Sequential load distribution scheme seems not working

I am modelling with multiple water cooled chiller in energyplus.
In idf file, I specified SequentialLoad for Chilled Water Distribution Scheme. However, looking at the result, it seems that multiple chiller is operating before 1 chiller get to full load as shown below graph.(x:part load ratio/y:COP)
image description
Does anyone know why this happen?

Added
Timeseries stack plot and stack plot by ascending total cooling rate is added following @aparker instruction.
Looking at the 2nd graph, I can see the fluctuation when the consequent chiller start to be operated. Is this usual? or something is causing this fluctuation?

image description

image description

Sequential load distribution scheme seems not working

I am modelling with multiple water cooled chiller in energyplus.
In idf file, I specified SequentialLoad for Chilled Water Distribution Scheme. However, looking at the result, it seems that multiple chiller is operating before 1 chiller get to full load as shown below graph.(x:part load ratio/y:COP)
image description
Does anyone know why this happen?

Added
Timeseries stack plot and stack plot by ascending total cooling rate is added following @aparker instruction.
Looking at the 2nd graph, I can see the fluctuation when the consequent chiller start to be operated. Is this usual? or something is causing this fluctuation?

image description

image description

Sequential load distribution scheme seems not working

I am modelling with multiple water cooled chiller in energyplus.
In idf file, I specified SequentialLoad for Chilled Water Distribution Scheme. However, looking at the result, it seems that multiple chiller is operating before 1 chiller get to full load as shown below graph.(x:part load ratio/y:COP)
image description
Does anyone know why this happen?

Added
Timeseries stack plot and stack plot by ascending total cooling rate is added following @aparker instruction.
image description

image description

Sequential load distribution scheme seems not working

I am modelling with multiple water cooled chiller in energyplus.
In idf file, I specified SequentialLoad for Chilled Water Distribution Scheme. However, looking at the result, it seems that multiple chiller is operating before 1 chiller get to full load as shown below graph.(x:part load ratio/y:COP)
image description
Does anyone know why this happen?