Revision history [back]
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name
Demand Mixer Name
Demand Splitter A Name
Demand Splitter B Name
Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows differences:
|-----------------------------------------------|--------|--------|
| Value | 1.14.0 | 2.2.0 |
|-----------------------------------------------|--------|--------|
| EUI | 49.91 | 49.07 |
| time setpoint not met during occupied heating | 82.0 | 79.33 |
| time setpoint not met during occupied cooling | 130.5 | 915.17 |
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name
Demand Mixer Name
Demand Splitter A Name
Demand Splitter B Name
Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows differences:
|-----------------------------------------------|--------|--------|
|-----------------------------------------------|--------|-------|
| Value | 1.14.0 | 2.2.0 |
|-----------------------------------------------|--------|--------|
| EUI | 49.91 | 49.07 |
| time setpoint not met during occupied heating | 82.0 | 79.33 |
| time setpoint not met during occupied cooling | 130.5 | 915.17 |
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name
Demand Mixer Name
Demand Splitter A Name
Demand Splitter B Name
Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows differences:
|-----------------------------------------------|--------|-------|
|-----------------------------------------------|-----------------|
| Value | 1.14.0 | 2.2.0 |
|-----------------------------------------------|--------|--------|
| EUI | 49.91 | 49.07 |
| time setpoint not met during occupied heating | 82.0 | 79.33 |
| time setpoint not met during occupied cooling | 130.5 | 915.17 |
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name
Demand Mixer Name
Demand Splitter A Name
Demand Splitter B Name
Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows differences:
|-----------------------------------------------|-----------------|
| Value
|
| 1.14.0 | 2.2.0 | |-----------------------------------------------|--------|--------| | EUI | 49.91 | 49.07 | | time setpoint not met during occupied heating | 82.0 | 79.33 | | time setpoint not met during occupied cooling | 130.5 | 915.17openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name
Demand Mixer Name
Demand Splitter A Name
Demand Splitter B Name
Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows differences:
| | 1.14.0 | 2.2.0 |
|-----------------------------------------------|--------|--------|
| a site EUI | of 49.91 | 49.07 |
| and 82.0/130.5 time setpoint not met during occupied heating | 82.0 | 79.33 |
| time setpoint not met during occupied cooling | 130.5 | 915.17 |heating/cooling in 1.14.0, but 49.07 and 79.33/915.17 in 2.2.0?
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows a site EUI of 49.91 and 82.0/130.5 time setpoint not met during occupied heating/cooling in 1.14.0, but 49.07 and 79.33/915.17 in 2.2.0?
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name Demand Mixer Name Demand Splitter A Name Demand Splitter B Name Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows a site EUI of 49.91 and 82.0/130.5 time setpoint not met during occupied heating/cooling in 1.14.0, but 49.07 and 79.33/915.17 in 2.2.0?
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name Demand Mixer Name Demand Splitter A Name Demand Splitter B Name Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. I would not even know what that would be. That is to say, I can vaguely vague imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows a site EUI of 49.91 and 82.0/130.5 time setpoint not met during occupied heating/cooling in 1.14.0, but 49.07 and 79.33/915.17 in 2.2.0?
openstudio 2.2.0 vs. 1.14.0 airloop
I appears that OS:AirLoopHVAC has gained a few more entries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name Demand Mixer Name Demand Splitter A Name Demand Splitter B Name Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to them. hem. I would not even know what that would be. That is to say, I can vague imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows a site EUI of 49.91 and 82.0/130.5 time setpoint not met during occupied heating/cooling in 1.14.0, but 49.07 and 79.33/915.17 in 2.2.0?
openstudio 2.2.0 vs. 1.14.0 airloop1.14.0
I appears that OS:AirLoopHVAC has gained a few more entries ntries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name Demand Mixer Name Demand Splitter A Name Demand Splitter B Name Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to hem. I would not even know what that would be. That is to say, I can vague imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows a site EUI of 49.91 and 82.0/130.5 time setpoint not met during occupied heating/cooling in 1.14.0, but 49.07 and 79.33/915.17 in 2.2.0?
openstudio 2.2.0 vs. 1.14.0
I appears that OS:AirLoopHVAC has gained a few more ntries in OpenStudio 2.2.0 compared to 1.14.0. Notably, these appear to be:
Return Air Bypass Flow Temperature Setpoint Schedule Name Demand Mixer Name Demand Splitter A Name Demand Splitter B Name Supply Splitter Name
Is it crucial that these be assigned correctly, or can they remain at their default values. I created my original OSM file in 1.14.0, and after importing to 2.2.0, these extra fields show values which I am sure are wrong if it were critical that they be correct. Then again, if I had to assign something to hem. I would not even know what that would be. That is to say, I can vague imagine where the demand mixer is, namely the branch collecting the returns form all my zones (?). But what are the demand splitters A and B? And, there really seems to be no supply splitter, as all my return just goes right back to the AHU?
I am concerned because the very same file shows a site EUI of 49.91 and 82.0/130.5 time setpoint not met during occupied heating/cooling in 1.14.0, but 49.07 and 79.33/915.17 in 2.2.0?