Revision history [back]
Why is the result of plantloop operation incompatible with the strategy specified in EMS:Program?
I used an EMS:Program(see the following blockquote) to control the operation of PlantLoop. In short, the program will decide the number of chillers to stage on according the cooling demand. ( 1chiller if demand is between [0,Cap], and 2 chillers if demand is between [Cap, 2Cap]) Cap here means the rated capacity of the chiller and is 1481477 in this case.
EnergyManagementSystem:Program,
Cooling_dispatch_Values, !- Name
IF CoolSys1_LoopDmnd < -1481477, !- Program Line 1
SET Chil1_Disptch = CoolSys1_LoopDmnd/2, !- Program Line 2
SET Chil2_Disptch = CoolSys1_LoopDmnd/2, !- A4
ELSEIF CoolSys1_LoopDmnd < 0, !- A5
SET Chil1_Disptch = CoolSys1_LoopDmnd, !- A6
SET Chil2_Disptch = 0.0, !- A7
ELSE, !- A8
SET Chil1_Disptch = 0.0, !- A9
SET Chil2_Disptch = 0.0, !- A10
ENDIF; !- A11
However, the result is confusing in that even if the cooling demand is larger than 1481477(rated cap), there are still some moments when only one chiller is turned on. Parts of these inconsistencies are shown in the following table.
----------------Table1-----------------------------------------------------------
Date/Time coolingDmnd Ele-PowerOfchil1 Ele-PowerOfchil2
01/01 08:35:00 1484323.003 106556.5292 0
01/01 10:11:15 1493364.145 110266.0414 0
01/01 10:15:00 1488649.626 109615.4136 0
01/01 11:12:16 1499195.511 110652.2023 0
01/01 11:53:10 1502321.217 110640.5195 0
01/01 12:26:15 1514519.749 111723.4092 0
01/01 12:43:38 1502297.995 110866.6415 0
01/01 13:03:19 1506863.348 109632.451 0
01/01 15:17:08 1514534.598 110532.2262 0
01/01 16:12:30 1515863.384 112271.376 0
01/02 05:45:00 1490389.698 107734.7433 0
01/02 06:10:00 1508263.231 109458.4895 0
So why do these situations occur, and how can I avoid these situations?
Any help will be greatly appreciated.
Updated
I have uploaded the .idf file to Github(ASHRAE90.1_OfficeLarge_STD2013_Miami_V1.idf in this repository: https://github.com/faithefeng/EnergyPlus-Note.git) . This model is a prototypical building in Miami as indicated by file name, and I have modified the control scheme for Plant Loop using EMS.
Updated 2
I have used the EDD to trace the Erl Program. Here is one record of these inconsistencies.
COOLING_DISPATCH_VALUES,Line 1,SET AA = COOLSYS1_LOOPDMND,-1484323.002751, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 2,IF COOLSYS1_LOOPDMND < -1481477,1.000000, Occurrence info=Miami Intl
Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 3,SET CHIL1_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 4,SET CHIL2_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
As shown, both ChIL1_DISPTCH and ChIL2_DISPTCH are -742161.501375, which means at this moment(01/01 08:32 - 08:35), both these two chillers are turned on. But the confusing part is that in the output files only chiller1 is used( see table1). How could this be so?
Why is the result of plantloop operation incompatible with the strategy specified in EMS:Program?
I used an EMS:Program(see the following blockquote) to control the operation of PlantLoop. In short, the program will decide the number of chillers to stage on according the cooling demand. ( 1chiller if demand is between [0,Cap], and 2 chillers if demand is between [Cap, 2Cap]) Cap here means the rated capacity of the chiller and is 1481477 in this case.
EnergyManagementSystem:Program,
Cooling_dispatch_Values, !- Name
IF CoolSys1_LoopDmnd < -1481477, !- Program Line 1
SET Chil1_Disptch = CoolSys1_LoopDmnd/2, !- Program Line 2
SET Chil2_Disptch = CoolSys1_LoopDmnd/2, !- A4
ELSEIF CoolSys1_LoopDmnd < 0, !- A5
SET Chil1_Disptch = CoolSys1_LoopDmnd, !- A6
SET Chil2_Disptch = 0.0, !- A7
ELSE, !- A8
SET Chil1_Disptch = 0.0, !- A9
SET Chil2_Disptch = 0.0, !- A10
ENDIF; !- A11
However, the result is confusing in that even if the cooling demand is larger than 1481477(rated cap), there are still some moments when only one chiller is turned on. Parts of these inconsistencies are shown in the following table.
----------------Table1-----------------------------------------------------------
Date/Time coolingDmnd Ele-PowerOfchil1 Ele-PowerOfchil2
01/01 08:35:00 1484323.003 106556.5292 0
01/01 10:11:15 1493364.145 110266.0414 0
01/01 10:15:00 1488649.626 109615.4136 0
01/01 11:12:16 1499195.511 110652.2023 0
01/01 11:53:10 1502321.217 110640.5195 0
01/01 12:26:15 1514519.749 111723.4092 0
01/01 12:43:38 1502297.995 110866.6415 0
01/01 13:03:19 1506863.348 109632.451 0
01/01 15:17:08 1514534.598 110532.2262 0
01/01 16:12:30 1515863.384 112271.376 0
01/02 05:45:00 1490389.698 107734.7433 0
01/02 06:10:00 1508263.231 109458.4895 0
So why do these situations occur, and how can I avoid these situations?
Any help will be greatly appreciated.
Updated
I have uploaded the .idf file to Github(ASHRAE90.1_OfficeLarge_STD2013_Miami_V1.idf in this repository: https://github.com/faithefeng/EnergyPlus-Note.git) . This model is a prototypical building in Miami as indicated by file name, and I have modified the control scheme for Plant Loop using EMS.
Updated 2
I have used the EDD to trace the Erl Program. Here is one record of these inconsistencies.
COOLING_DISPATCH_VALUES,Line 1,SET AA = COOLSYS1_LOOPDMND,-1484323.002751, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 2,IF COOLSYS1_LOOPDMND < -1481477,1.000000, Occurrence info=Miami Intl
Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 3,SET CHIL1_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 4,SET CHIL2_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
As shown, both ChIL1_DISPTCH and ChIL2_DISPTCH are -742161.501375, which means at this moment(01/01 08:32 - 08:35), both these two chillers are turned on. But the confusing part is that in the output files only chiller1 is used( see table1). How could this be so?
Why is the result of plantloop operation incompatible with the strategy specified in EMS:Program?
I used an EMS:Program(see the following blockquote) to control the operation of PlantLoop. In short, the program will decide the number of chillers to stage on according the cooling demand. ( 1chiller if demand is between [0,Cap], and 2 chillers if demand is between [Cap, 2Cap]) Cap here means the rated capacity of the chiller and is 1481477 in this case.
EnergyManagementSystem:Program,
Cooling_dispatch_Values, !- Name
IF CoolSys1_LoopDmnd < -1481477, !- Program Line 1
SET Chil1_Disptch = CoolSys1_LoopDmnd/2, !- Program Line 2
SET Chil2_Disptch = CoolSys1_LoopDmnd/2, !- A4
ELSEIF CoolSys1_LoopDmnd < 0, !- A5
SET Chil1_Disptch = CoolSys1_LoopDmnd, !- A6
SET Chil2_Disptch = 0.0, !- A7
ELSE, !- A8
SET Chil1_Disptch = 0.0, !- A9
SET Chil2_Disptch = 0.0, !- A10
ENDIF; !- A11
However, the result is confusing in that even if the cooling demand is larger than 1481477(rated cap), there are still some moments when only one chiller is turned on. Parts of these inconsistencies are shown in the following table.
----------------Table1-----------------------------------------------------------
Date/Time coolingDmnd Ele-PowerOfchil1 Ele-PowerOfchil2
01/01 08:35:00 1484323.003 106556.5292 0
01/01 10:11:15 1493364.145 110266.0414 0
01/01 10:15:00 1488649.626 109615.4136 0
01/01 11:12:16 1499195.511 110652.2023 0
01/01 11:53:10 1502321.217 110640.5195 0
01/01 12:26:15 1514519.749 111723.4092 0
01/01 12:43:38 1502297.995 110866.6415 0
01/01 13:03:19 1506863.348 109632.451 0
01/01 15:17:08 1514534.598 110532.2262 0
01/01 16:12:30 1515863.384 112271.376 0
01/02 05:45:00 1490389.698 107734.7433 0
01/02 06:10:00 1508263.231 109458.4895 0
So why do these situations occur, and how can I avoid these situations?
Any help will be greatly appreciated.
Updated
I have uploaded the .idf file to Github(ASHRAE90.1_OfficeLarge_STD2013_Miami_V1.idf in this repository: https://github.com/faithefeng/EnergyPlus-Note.git) . This model is a prototypical building in Miami as indicated by file name, and I have modified the control scheme for Plant Loop using EMS.
Updated 2
I have used the EDD to trace the Erl Program. Here is one record of these inconsistencies.
COOLING_DISPATCH_VALUES,Line 1,SET AA = COOLSYS1_LOOPDMND,-1484323.002751, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 2,IF COOLSYS1_LOOPDMND < -1481477,1.000000, Occurrence info=Miami Intl
Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 3,SET CHIL1_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 4,SET CHIL2_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
As shown, both ChIL1_DISPTCH and ChIL2_DISPTCH are -742161.501375, which means at this moment(01/01 08:32 - 08:35), both these two chillers are turned on. But the confusing part is that in the output files only chiller1 is used( see table1). How could this be so?table1)
Why is the result of plantloop operation incompatible with the strategy specified in EMS:Program?
I used an EMS:Program(see the following blockquote) to control the operation of PlantLoop. In short, the program will decide the number of chillers to stage on according the cooling demand. ( 1chiller if demand is between [0,Cap], and 2 chillers if demand is between [Cap, 2Cap]) Cap here means the rated capacity of the chiller and is 1481477 in this case.
EnergyManagementSystem:Program,
Cooling_dispatch_Values, !- Name
IF CoolSys1_LoopDmnd < -1481477, !- Program Line 1
SET Chil1_Disptch = CoolSys1_LoopDmnd/2, !- Program Line 2
SET Chil2_Disptch = CoolSys1_LoopDmnd/2, !- A4
ELSEIF CoolSys1_LoopDmnd < 0, !- A5
SET Chil1_Disptch = CoolSys1_LoopDmnd, !- A6
SET Chil2_Disptch = 0.0, !- A7
ELSE, !- A8
SET Chil1_Disptch = 0.0, !- A9
SET Chil2_Disptch = 0.0, !- A10
ENDIF; !- A11
However, the result is confusing in that even if the cooling demand is larger than 1481477(rated cap), there are still some moments when only one chiller is turned on. Parts of these inconsistencies are shown in the following table.
----------------Table1-----------------------------------------------------------
-------------------------------------------------------------------------------
Date/Time coolingDmnd Ele-PowerOfchil1 Ele-PowerOfchil2
01/01 08:35:00 1484323.003 106556.5292 0
01/01 10:11:15 1493364.145 110266.0414 0
01/01 10:15:00 1488649.626 109615.4136 0
01/01 11:12:16 1499195.511 110652.2023 0
01/01 11:53:10 1502321.217 110640.5195 0
01/01 12:26:15 1514519.749 111723.4092 0
01/01 12:43:38 1502297.995 110866.6415 0
01/01 13:03:19 1506863.348 109632.451 0
01/01 15:17:08 1514534.598 110532.2262 0
01/01 16:12:30 1515863.384 112271.376 0
01/02 05:45:00 1490389.698 107734.7433 0
01/02 06:10:00 1508263.231 109458.4895 0
So why do these situations occur, and how can I avoid these situations?
Any help will be greatly appreciated.
Updated
I have uploaded the .idf file to Github(ASHRAE90.1_OfficeLarge_STD2013_Miami_V1.idf in this repository: https://github.com/faithefeng/EnergyPlus-Note.git) . This model is a prototypical building in Miami as indicated by file name, and I have modified the control scheme for Plant Loop using EMS.
Updated 2
I have used the EDD to trace the Erl Program. Here is one record of these inconsistencies.
COOLING_DISPATCH_VALUES,Line 1,SET AA = COOLSYS1_LOOPDMND,-1484323.002751, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 2,IF COOLSYS1_LOOPDMND < -1481477,1.000000, Occurrence info=Miami Intl
Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 3,SET CHIL1_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
COOLING_DISPATCH_VALUES,Line 4,SET CHIL2_DISPTCH = COOLSYS1_LOOPDMND/2,-742161.501375, Occurrence info=Miami Intl Ap FL USA TMY3 WMO#=722020, 01/01 08:32 - 08:35
As shown, both ChIL1_DISPTCH and ChIL2_DISPTCH are -742161.501375, which means at this moment(01/01 08:32 - 08:35), both these two chillers are turned on. But the confusing part is that in the output files only chiller1 is used( see table1)
Why is the result of plantloop operation incompatible with the strategy specified in EMS:Program?
I used an EMS:Program(see the following blockquote) to control the operation of PlantLoop. In short, the program will decide the number of chillers to stage on according the cooling demand. ( 1chiller if demand is between [0,Cap], and 2 chillers if demand is between [Cap, 2Cap]) Cap here means the rated capacity of the chiller and is 1481477 in this case.
EnergyManagementSystem:Program,
Cooling_dispatch_Values, !- Name
IF CoolSys1_LoopDmnd < -1481477, !- Program Line 1
SET Chil1_Disptch = CoolSys1_LoopDmnd/2, !- Program Line 2
SET Chil2_Disptch = CoolSys1_LoopDmnd/2, !- A4
ELSEIF CoolSys1_LoopDmnd < 0, !- A5
SET Chil1_Disptch = CoolSys1_LoopDmnd, !- A6
SET Chil2_Disptch = 0.0, !- A7
ELSE, !- A8
SET Chil1_Disptch = 0.0, !- A9
SET Chil2_Disptch = 0.0, !- A10
ENDIF; !- A11
However, the result is confusing in that even if the cooling demand is larger than 1481477(rated cap), there are still some moments when only one chiller is turned on. Parts of these inconsistencies are shown in the following table.
-------------------------------------------------------------------------------
Date/Time coolingDmnd Ele-PowerOfchil1 Ele-PowerOfchil2
01/01 08:35:00 1484323.003 106556.5292 0
01/01 10:11:15 1493364.145 110266.0414 0
01/01 10:15:00 1488649.626 109615.4136 0
01/01 11:12:16 1499195.511 110652.2023 0
01/01 11:53:10 1502321.217 110640.5195 0
01/01 12:26:15 1514519.749 111723.4092 0
01/01 12:43:38 1502297.995 110866.6415 0
01/01 13:03:19 1506863.348 109632.451 0
01/01 15:17:08 1514534.598 110532.2262 0
01/01 16:12:30 1515863.384 112271.376 0
01/02 05:45:00 1490389.698 107734.7433 0
01/02 06:10:00 1508263.231 109458.4895 0
So why do these situations occur, and how can I avoid these situations?
Any help will be greatly appreciated.
Updated
Updated I have uploaded the .idf file to Github(ASHRAE90.1_OfficeLarge_STD2013_Miami_V1.idf in this repository: https://github.com/faithefeng/EnergyPlus-Note.git) . This model is a prototypical building in Miami as indicated by file name, and I have modified the control scheme for Plant Loop using EMS.
Why is the result of plantloop operation incompatible with the strategy specified in EMS:Program?
I used an EMS:Program(see the following blockquote) to control the operation of PlantLoop. In short, the program will decide the number of chillers to stage on according the cooling demand. ( 1chiller if demand is between [0,Cap], and 2 chillers if demand is between [Cap, 2Cap]) Cap here means the rated capacity of the chiller and is 1481477 in this case.
EnergyManagementSystem:Program,
Cooling_dispatch_Values, !- Name
IF CoolSys1_LoopDmnd < -1481477, !- Program Line 1
SET Chil1_Disptch = CoolSys1_LoopDmnd/2, !- Program Line 2
SET Chil2_Disptch = CoolSys1_LoopDmnd/2, !- A4
ELSEIF CoolSys1_LoopDmnd < 0, !- A5
SET Chil1_Disptch = CoolSys1_LoopDmnd, !- A6
SET Chil2_Disptch = 0.0, !- A7
ELSE, !- A8
SET Chil1_Disptch = 0.0, !- A9
SET Chil2_Disptch = 0.0, !- A10
ENDIF; !- A11
However, the result is confusing in that even if the cooling demand is larger than 1481477(rated cap), there are still some moments when only one chiller is turned on. Parts of these inconsistencies are shown in the following table.
-------------------------------------------------------------------------------
Date/Time coolingDmnd Ele-PowerOfchil1 Ele-PowerOfchil2
01/01 08:35:00 1484323.003 106556.5292 0
01/01 10:11:15 1493364.145 110266.0414 0
01/01 10:15:00 1488649.626 109615.4136 0
01/01 11:12:16 1499195.511 110652.2023 0
01/01 11:53:10 1502321.217 110640.5195 0
01/01 12:26:15 1514519.749 111723.4092 0
01/01 12:43:38 1502297.995 110866.6415 0
01/01 13:03:19 1506863.348 109632.451 0
01/01 15:17:08 1514534.598 110532.2262 0
01/01 16:12:30 1515863.384 112271.376 0
01/02 05:45:00 1490389.698 107734.7433 0
01/02 06:10:00 1508263.231 109458.4895 0
So why do these situations occur, and how can I avoid these situations?
Any help will be greatly appreciated.
Updated I have uploaded the .idf file to Github(ASHRAE90.1_OfficeLarge_STD2013_Miami_V1.idf in this repository: https://github.com/faithefeng/EnergyPlus-Note.git) . This model is a prototypical building in Miami as indicated by file name, and I have modified the control scheme for Plant Loop using EMS.