Revision history [back]
EnergyPlus ignores the design values on my AirloopHVAC
I have an AirLoopHVAC
with a fan constant volume, a DX cooling coil and a gas heating coil. Multiple zones are connected with ATUs of type AirTerminal:SingleDuct:Uncontrolled
(autosized)
I want my loop to work at $X$ CFM of supply air constantly.
Here's what I've done:
- Specified $X$ for the
AirLoopHVAC
Design Supply Air Flow Rate - Specified $X$ for the
Fan:ConstantVolume
Maximum Flow Rate - Specified $X$ for the DX coil Rated Air Flow Rate
I was expecting the loop to run at this value, but it doesn't.
Even weirder, I had set the minimum and the maximum outdoor airflow rate of the Controller:OutdoorAir
attached to the AirLoopHVAC:OutdoorAirSystem
to a value $Y$, and the loop ends up running at a constant value that is even below this $Y$ value...
I've found that to have it run at $X$ CFM, I have to either:
- Modify the
Sizing:System
object attached to the AirLoopHVAC to have a Cooling/Heating Design Air Flow Method set toFlow/System
and to enter $X$ for theCooling/Heating Design Air Flow Method
- Hardsize the ATUs
- Set a different
DesignSpecification:OutdoorAir
(DSOA) for the zones
So it seems that E+ is just simple ignoring the Design Supply Air Flow Rate that I've entered for the AirLoopHVAC, and calculating another value that will meet the ATUs need (My Sizing:System is set to Type of Load to Size On at Sensible, though I've tried VentilationRequirement). Why is that? Is this the expected behavior?
For the record, I'm using OpenStudio 1.12.1, as I think this could be linked to the way OpenStudio uses and forward translates the Controller:MechanicalVentilation
set to ZoneSum
with all the DSOA for the zones served by the AirLoopHVAC