Revision history [back]
Error Opening OSM file
I have edidted an .osm with notepad, in order to quickly change the lines:
No, !- Account for Dedicated Outdoor Air System
NeutralSupplyAir, !- Dedicated Outdoor Air System Control Strategy
into
Yes, !- Account for Dedicated Outdoor Air System
ColdSupplyAir, !- Dedicated Outdoor Air System Control Strategy
for all the thermal zones. The problem is that, when I try to open the file with OS, it fails and prompt this error message:
**Model with Version 1.11.0 IDD is not valid to draft strictness level.
The collection is INVALID at strictness level 'Draft', because of the errors:
Object level data error of type NoIdd .
Error pertains to an object of type 'Catchall', named ''.
Additional information about the error type: input data definition is missing or empty.
Field level data error of type DataType .
Error is in an object of type 'OS:ConvergenceLimits', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:HeatBalanceAlgorithm', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:RunPeriod', named '{17c33f47-c9b9-463a-84bc-12596f349148}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ShadowCalculation', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:SimulationControl', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:SurfaceConvectionAlgorithm:Inside', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:SurfaceConvectionAlgorithm:Outside', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Timestep', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:YearDescription', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ZoneAirContaminantBalance', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ZoneAirHeatBalanceAlgorithm', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ZoneCapacitanceMultiplier:ResearchSpecial', named '', in field 1.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ClimateZones', named '', in field 5.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Site', named '{f38b0e3c-04e1-4822-940e-9b46c436222c}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:SizingPeriod:DesignDay', named '{c40cf383-953c-44d1-84ce-25c9d456b9c6}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:BuildingStory', named '{f39c9759-96f4-49e5-ac4e-6ba1630585ae}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Rendering:Color', named '{0539d7c9-b042-49d1-9f23-320ba3d68eb9}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Material', named '{757eaf6b-2061-4eb3-bf0d-44c2148624b9}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Material:AirGap', named '{80083eb9-afca-4c51-9fac-33efa295c2b9}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:WindowMaterial:Blind', named '{62a015ff-e368-43e2-a07f-45804723e48a}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:WindowMaterial:Glazing', named '{f33caf9c-f7e8-461b-b0ec-08d6310278da}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:WindowMaterial:SimpleGlazingSystem', named '{7c1858ff-7dad-49e6-af33-8eddba3421fd}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:StandardsInformation:Construction', named '', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:People:Definition', named '{def152c4-e2f3-489d-99d6-299545978bd8}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Lights:Definition', named '{31359b96-cb29-4fb0-9395-3eb200f157c0}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ElectricEquipment:Definition', named '{25394380-09b5-42e2-9d53-0b6e34153d23}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Schedule:Day', named '{804c12ea-a23c-4355-9f7e-c89012f7c3cd}', in field 3.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Schedule:Rule', named '{68218032-fb91-450b-9278-85ca77e0e8d1}', in field 3.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Schedule:Constant', named '{a20fb1f5-484d-4e5b-99c3-69298616587d}', in field 3.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ScheduleTypeLimits', named '{77d0546b-ed83-491c-a2fe-13df223048fc}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Building', named '{e0ce3521-4e53-4eca-8017-2f1c8dec2b50}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ShadingSurface', named '{dc5bb2c2-5430-43af-8cfd-c5ee10ea8961}', in field 23.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ShadingSurfaceGroup', named '{c2b4cf24-3829-4b25-a541-9a3438262d50}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Space', named '{6455d359-3a71-4da5-b793-f2a91c2ed94d}', in field 11.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Surface', named '{faf969fb-efbb-4158-a2b1-2b7d9b8a35df}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:SubSurface', named '{6438b781-3de5-41a8-9f8c-c659c2a6d472}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:SpaceInfiltration:DesignFlowRate', named '{1043fcb3-38da-49c1-896d-68c42177e5f1}', in field 5.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Connection', named '{2dd6aa5e-167d-4ecd-a06f-862050edb811}', in field 3.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Curve:Quadratic', named '{cc5b9152-153b-4342-8fcb-827d4773d357}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Curve:Biquadratic', named '{9b451480-1394-4b60-9c64-d2ba899b66cc}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:DesignSpecification:OutdoorAir', named '{7ecf29b5-5225-4791-84cc-e5c71fcc460c}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:Sizing:Zone', named '', in field 3.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:ThermalZone', named '{06544a7c-5bb7-44c1-8a11-ade18c77b97c}', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type DataType .
Error is in an object of type 'OS:LifeCycleCost:Parameters', named '', in field 2.
Additional information about the error type: field-level data is of an incorrect type.
Field level data error of type NumericBound .
Error is in an object of type 'OS:ShadowCalculation', named '', in field 2.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:SizingPeriod:DesignDay', named '{c40cf383-953c-44d1-84ce-25c9d456b9c6}', in field 5.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:WeatherFile', named '', in field 6.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:BuildingStory', named '{f39c9759-96f4-49e5-ac4e-6ba1630585ae}', in field 3.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:Material', named '{757eaf6b-2061-4eb3-bf0d-44c2148624b9}', in field 7.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:WindowMaterial:Glazing', named '{f33caf9c-f7e8-461b-b0ec-08d6310278da}', in field 12.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:WindowMaterial:SimpleGlazingSystem', named '{7c1858ff-7dad-49e6-af33-8eddba3421fd}', in field 3.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:Schedule:Day', named '{0523d01a-0466-45e8-9971-a9690b3e6a3f}', in field 7.
Additional information about the error type: numeric data violates a min or max bound.
Field level data error of type NumericBound .
Error is in an object of type 'OS:Schedule:Rule', named '{68218032-fb91-450b-9278-85ca77e0e8d1}', in field 18.
Additional information about the error type: numeric data violates a min or max bound.
OS:Connection object does not specify Inlet Port
...
...
...
...
OS:Connection object does not specify Outlet Port **
I have tried to fix this using the "OSM diagnostic script" in Sketch-up and it runs with no errors, but it does not save any diagnostic copy of the file (I assume because it does not find anything wrong in the original file).
As far as I know, when I previously found this error it was related to idf import into OS, and deleting the idf object reported into the error message usually fixed the issue. This time I dont really know what went wrong in the editing phase. Any hints?
Error Opening OSM file
I have edidted an .osm with notepad, in order to quickly change the lines:
into
for all the thermal zones. The problem is that, when I try to open the file with OS, it fails and prompt this error message:
I have tried to fix this using the "OSM diagnostic script" in Sketch-up and it runs with no errors, but it does not save any diagnostic copy of the file (I assume because it does not find anything wrong in the original file).
As far as I know, when I previously found this error it was related to idf import into OS, and deleting the idf object reported into the error message usually fixed the issue. This time I dont really know what went wrong in the editing phase. Any hints?
Error Opening OSM file
I have edidted an .osm with notepad, in order to quickly change the lines:
No, !- Account for Dedicated Outdoor Air System
NeutralSupplyAir, !- Dedicated Outdoor Air System Control Strategy
into
Yes, !- Account for Dedicated Outdoor Air System
ColdSupplyAir, !- Dedicated Outdoor Air System Control Strategy
for all the thermal zones. The problem is that, when I try to open the file with OS, it fails and prompt this error message:
**Model with Version 1.11.0 IDD is not valid to draft strictness level.
The collection is INVALID at strictness level 'Draft', because of the errors: Object level data error of type NoIdd . Error pertains to an object of type 'Catchall', named ''. Additional information about the error type: input data definition is missing or empty. Field level data error of type DataType . Error is in an object of type 'OS:ConvergenceLimits', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:HeatBalanceAlgorithm', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:RunPeriod', named '{17c33f47-c9b9-463a-84bc-12596f349148}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ShadowCalculation', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:SimulationControl', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:SurfaceConvectionAlgorithm:Inside', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:SurfaceConvectionAlgorithm:Outside', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Timestep', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:YearDescription', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ZoneAirContaminantBalance', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ZoneAirHeatBalanceAlgorithm', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ZoneCapacitanceMultiplier:ResearchSpecial', named '', in field 1. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ClimateZones', named '', in field 5. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Site', named '{f38b0e3c-04e1-4822-940e-9b46c436222c}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:SizingPeriod:DesignDay', named '{c40cf383-953c-44d1-84ce-25c9d456b9c6}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:BuildingStory', named '{f39c9759-96f4-49e5-ac4e-6ba1630585ae}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Rendering:Color', named '{0539d7c9-b042-49d1-9f23-320ba3d68eb9}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Material', named '{757eaf6b-2061-4eb3-bf0d-44c2148624b9}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Material:AirGap', named '{80083eb9-afca-4c51-9fac-33efa295c2b9}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:WindowMaterial:Blind', named '{62a015ff-e368-43e2-a07f-45804723e48a}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:WindowMaterial:Glazing', named '{f33caf9c-f7e8-461b-b0ec-08d6310278da}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:WindowMaterial:SimpleGlazingSystem', named '{7c1858ff-7dad-49e6-af33-8eddba3421fd}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:StandardsInformation:Construction', named '', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:People:Definition', named '{def152c4-e2f3-489d-99d6-299545978bd8}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Lights:Definition', named '{31359b96-cb29-4fb0-9395-3eb200f157c0}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ElectricEquipment:Definition', named '{25394380-09b5-42e2-9d53-0b6e34153d23}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Schedule:Day', named '{804c12ea-a23c-4355-9f7e-c89012f7c3cd}', in field 3. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Schedule:Rule', named '{68218032-fb91-450b-9278-85ca77e0e8d1}', in field 3. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Schedule:Constant', named '{a20fb1f5-484d-4e5b-99c3-69298616587d}', in field 3. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ScheduleTypeLimits', named '{77d0546b-ed83-491c-a2fe-13df223048fc}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Building', named '{e0ce3521-4e53-4eca-8017-2f1c8dec2b50}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ShadingSurface', named '{dc5bb2c2-5430-43af-8cfd-c5ee10ea8961}', in field 23. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ShadingSurfaceGroup', named '{c2b4cf24-3829-4b25-a541-9a3438262d50}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Space', named '{6455d359-3a71-4da5-b793-f2a91c2ed94d}', in field 11. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Surface', named '{faf969fb-efbb-4158-a2b1-2b7d9b8a35df}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:SubSurface', named '{6438b781-3de5-41a8-9f8c-c659c2a6d472}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:SpaceInfiltration:DesignFlowRate', named '{1043fcb3-38da-49c1-896d-68c42177e5f1}', in field 5. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Connection', named '{2dd6aa5e-167d-4ecd-a06f-862050edb811}', in field 3. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Curve:Quadratic', named '{cc5b9152-153b-4342-8fcb-827d4773d357}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Curve:Biquadratic', named '{9b451480-1394-4b60-9c64-d2ba899b66cc}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:DesignSpecification:OutdoorAir', named '{7ecf29b5-5225-4791-84cc-e5c71fcc460c}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:Sizing:Zone', named '', in field 3. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:ThermalZone', named '{06544a7c-5bb7-44c1-8a11-ade18c77b97c}', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type DataType . Error is in an object of type 'OS:LifeCycleCost:Parameters', named '', in field 2. Additional information about the error type: field-level data is of an incorrect type. Field level data error of type NumericBound . Error is in an object of type 'OS:ShadowCalculation', named '', in field 2. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:SizingPeriod:DesignDay', named '{c40cf383-953c-44d1-84ce-25c9d456b9c6}', in field 5. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:WeatherFile', named '', in field 6. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:BuildingStory', named '{f39c9759-96f4-49e5-ac4e-6ba1630585ae}', in field 3. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:Material', named '{757eaf6b-2061-4eb3-bf0d-44c2148624b9}', in field 7. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:WindowMaterial:Glazing', named '{f33caf9c-f7e8-461b-b0ec-08d6310278da}', in field 12. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:WindowMaterial:SimpleGlazingSystem', named '{7c1858ff-7dad-49e6-af33-8eddba3421fd}', in field 3. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:Schedule:Day', named '{0523d01a-0466-45e8-9971-a9690b3e6a3f}', in field 7. Additional information about the error type: numeric data violates a min or max bound. Field level data error of type NumericBound . Error is in an object of type 'OS:Schedule:Rule', named '{68218032-fb91-450b-9278-85ca77e0e8d1}', in field 18. Additional information about the error type: numeric data violates a min or max bound.
OS:Connection object does not specify Inlet Port ... ... ... ... OS:Connection object does not specify Outlet Port **
I have tried to fix this using the "OSM diagnostic script" in Sketch-up and it runs with no errors, but it does not save any diagnostic copy of the file (I assume because it does not find anything wrong in the original file).
As far as I know, when I previously found this error it was related to idf import into OS, and deleting the idf object reported into the error message usually fixed the issue. This time I dont really know what went wrong in the editing phase. Any hints?