Difference in defined and calculated air flow

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image description

image description

Difference in defined and calculated air flowZone Ventilation Design Flow Rate results

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image description

image description

Zone Ventilation Design Flow Rate resultsFlowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image description

image description

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image description

image description

Zone Ventilation Design Flowrate and Design Specification Outdoor AirFlow Rate results

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image description

image descriptionResults

Thermal zone tab

Zone Ventilation Design Flow Rate resultsFlowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: Results

image: Thermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor AirFlow Rate results

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: Results(/C:\Users\Johannes Mayer\Desktop\Picture/results.jpg "results")

image: Thermal zone tab

Zone Ventilation Design Flow Rate resultsFlowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: (/C:\Users\Johannes Mayer\Desktop\Picture/results.jpg "results")Results)

image: Thermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: Results)

image: Thermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: Results) ![Results] (/C:\Users\Johannes Mayer\Desktop\Picture/results.jpg "results"))

image: Thermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: ![Results] (/C:\Users\Johannes Mayer\Desktop\Picture/results.jpg "results")) Mayer\Desktop\Picture/results.jpg"results"))

image: Thermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: ![Results] (/C:\Users\Johannes Mayer\Desktop\Picture/results.jpg"results")) Results

image: Thermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: Results

image: Thermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: ResultsResults

image: Thermal zone tabThermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: ResultsResults

image: Thermal zone tabThermal zone tab

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image: Resultsimage:alt text

image: Thermal zone tabimage:alt text

Zone Ventilation Design Flowrate and Design Specification Outdoor Air

Hey, I have modeled my building with ZoneVenitlation:DesignFLowrate objects in each thermal zone since I have only exhaust fans. The supply air is directly provided by the outdoor air.

In the ZoneVenitlation:DesignFLowrate objects I have set the type of ventilation to 'Exhaust', defined the Design Flow Rate, the schedule, the efficiency, and the pressure rise. I kept the default values in the other fields (e.g. constant term coefficient, temperature term coefficient, etc.)

I did not define the 'Design Specification Outdoor Air' since this is only used to size the HVAC systems, but I do not have any air loops under the HVAC Systems tab. (Please correct me if I am wrong)

When I run the simulation now and look at the Results summary I can see in the e+ 'HVAC Sizing Summary' report the 'Calculated Design Air Flow' and the 'User Design Air Flow'. Both values show me the same value because I have set the sizing factor to 1 but these Air Flows are not the one I have specified in the ZoneVenitlation:DesignFLowRate object. The values for the flow rate in the results summary are approximately 3 times greater than defined and also vary with each zone even though I have defined the same airflow for each zone.

So my question is what the reason for this could be and how I can fix it?

Below you can see the values I have defined and and the values as shown in the results summary.

image:alt text

image:alt text