Revision history  [back]

Not heat from water to air loop in OpenStudio

Starting from the OS template 'Packaged Rooftop VAV with Reheat', I tried to change the terminal for VAV NoReheat. I have no errors, but there is no heating in my zone.

To illustrate:

  • This case works fine (some unmet hours but no problem with the simulation):

Reheat.PNG

  • But this case doesn't work:

NoReheat.PNG

I don't think there is any problem with the object AirTerminal:SingleDuct:VAV:NoReheat, as it works fine with other cases such as:

othercase.PNG

What I have tested: different setpoint manager, supply air temperature, variable or constant fan/terminal, hardsized some parameters... In all cases the result is the same: no heating !

For all my tests, the common point when the problem occurs is the presence of a 'Coil:Heating:Water' and a AirTerminal:SingleDuct:VAV:NoReheat. So I think the problem is between the water and air loop. The E+ Output:DebuggingData also shows some strange behavior. For example the node between the air terminal and the thermal zone in the air loop shows: 'Fluid Type: Water'. It seems it lacks a heat exchanger (water to air) but I can't simply add a Fluid-toFluid HX in my air loop...

Someone has an idea to fix it ?

Not heat from water to air loop in OpenStudio

Starting from the OS template 'Packaged Rooftop VAV with Reheat', I tried to change the terminal for VAV NoReheat. I have no errors, but there is no heating in my zone.

To illustrate:

  • This case works fine (some unmet hours but no problem with the simulation):simulation): Reheat.PNG

Reheat.PNG

  • But this case doesn't work:work: NoReheat.PNG

NoReheat.PNG

I don't think there is any problem with the object AirTerminal:SingleDuct:VAV:NoReheat, 'AirTerminal:SingleDuct:VAV:NoReheat', as it works fine with other cases such as:

as: othercase.PNG

What I have tested: different setpoint manager, supply air temperature, variable or constant fan/terminal, hardsized some parameters... In all cases the result is the same: same : no heating !

For all my tests, the common point when the problem occurs is the presence of a 'Coil:Heating:Water' and a AirTerminal:SingleDuct:VAV:NoReheat. 'AirTerminal:SingleDuct:VAV:NoReheat'. So I think the problem is between the water and air loop. The E+ Output:DebuggingData also shows some strange behavior. behaviour. For example the node between the air terminal and the thermal zone in the air loop shows: shows : 'Fluid Type: Water'. It seems it lacks a heat exchanger (water to air) but I can't simply add a Fluid-toFluid HX in my air loop...

Someone has an idea to fix it ?

Not heat from water to air loop in OpenStudio

Starting from the OS template 'Packaged Rooftop VAV with Reheat', I tried to change the terminal for VAV NoReheat. I have no errors, but there the is no heating in my zone.

To illustrate:

  • This case works fine (some unmet hours but no problem with the simulation): Reheat.PNG

  • But this case doesn't work: NoReheat.PNG

I don't think there is any problem with the object 'AirTerminal:SingleDuct:VAV:NoReheat', as it works fine with other cases such as: othercase.PNG

What I have tested: different setpoint manager, supply air temperature, variable or constant fan/terminal, hardsized some parameters... In all cases the result is the same : no heating !

For all my tests, the common point when the problem occurs is the presence of a 'Coil:Heating:Water' and a 'AirTerminal:SingleDuct:VAV:NoReheat'. So I think the problem is between the water and air loop. The E+ Output:DebuggingData also shows some strange behaviour. For example the node between the air terminal and the thermal zone in the air loop shows : 'Fluid Type: Water'. It seems it lacks heat exchanger (water to air) but I can't simply add a Fluid-toFluid HX in my air loop...

Someone has an idea to fix it ?

Not heat from water to air loop in OpenStudio

Starting from the OS template 'Packaged Rooftop VAV with Reheat', I tried to change the terminal for VAV NoReheat. I have no errors, but the is no heating in my zone.

To illustrate:

  • This case works fine (some unmet hours Unmethours but no problem with the simulation): Reheat.PNG

  • But this case doesn't work: NoReheat.PNG

I don't think there is any problem with the object 'AirTerminal:SingleDuct:VAV:NoReheat', as it works fine with other cases such as: othercase.PNG

What I have tested: different setpoint manager, supply air temperature, variable or constant fan/terminal, hardsized some parameters... In all cases the result is the same : no heating !

For all my tests, the common point when the problem occurs is the presence of a 'Coil:Heating:Water' and a 'AirTerminal:SingleDuct:VAV:NoReheat'. So I think the problem is between the water and air loop. The E+ Output:DebuggingData also shows some strange behaviour. For example the node between the air terminal and the thermal zone in the air loop shows : 'Fluid Type: Water'. It seems it lacks heat exchanger (water to air) but I can't simply add a Fluid-toFluid HX in my air loop...

Someone has an idea to fix it ?