Revision history [back]
Modeling a building with heavy electrical component gains
I need to model a building (31 x 18 x 4 m) with no windows. The building is made of polyurethanic panels that should assure the insulation during hot months. Inside the building I have a very high electric load (50MW) that can dissipate up to 5% of this power as thermal contribution. Obviously this electrical load is not working at full capacity all the time. How can I simulate this kind of load? I have tryed with both "electric equipment" and "other equipment" loads but the simulation stops with this error:
Temperature (high) out of bounds (209.38] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:30 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [4480.287] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
I assumed that the temeprature rises too much also because I have not well defined the materials, infact I have simulated a hot day (15 august) and the temperature inside the building with NO gains in it rises up to 34 °C. This should not happen since the panels are supposed to insulate the building.
I have tryed to turn on ideal loads to have an idea of the size of the HVAC system that have to be installed there.
For the polyurethane panels I have defined a new material with these specifics:

The load schedule is a fractional set to be 0 except for an hour a day, in which I have the maximum thermal dispersion from the electical load.
edit: I have set the radiant fraction to 0 and rerun the simulation that unfortunately stops with the following error:
* Severe * Temperature (high) out of bounds (212.96] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [448.029] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
* Severe * Temperature (high) out of bounds (221.06] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-127.12] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-126.17] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (221.80] for zone="THERMAL ZONE 1", for surface="SURFACE 2" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (228.70] for zone="THERMAL ZONE 1", for surface="SURFACE 3" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (226.33] for zone="THERMAL ZONE 1", for surface="SURFACE 4" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (222.05] for zone="THERMAL ZONE 1", for surface="SURFACE 6" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
edit: I followed MatthewSteen suggestions, but the simulation stops and the errors I get are the following:
* Severe * Temperature (high) out of bounds (601.03] for zone="THERMAL ZONE 1", for surface="SURFACE 2" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [89605.735] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
* Severe * Temperature (high) out of bounds (601.50] for zone="THERMAL ZONE 1", for surface="SURFACE 3" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (601.01] for zone="THERMAL ZONE 1", for surface="SURFACE 4" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (601.02] for zone="THERMAL ZONE 1", for surface="SURFACE 6" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (490.39] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (629.08] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
Modeling a building with heavy electrical component gains
I need to model a building (31 x 18 x 4 m) with no windows. The building is made of polyurethanic panels that should assure the insulation during hot months. Inside the building I have a very high electric load (50MW) that can dissipate up to 5% of this power as thermal contribution. Obviously this electrical load is not working at full capacity all the time. How can I simulate this kind of load? I have tryed with both "electric equipment" and "other equipment" loads but the simulation stops with this error:
Temperature (high) out of bounds (209.38] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:30 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [4480.287] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
I assumed that the temeprature rises too much also because I have not well defined the materials, infact I have simulated a hot day (15 august) and the temperature inside the building with NO gains in it rises up to 34 °C. This should not happen since the panels are supposed to insulate the building.
I have tryed to turn on ideal loads to have an idea of the size of the HVAC system that have to be installed there.
For the polyurethane panels I have defined a new material with these specifics:

The load schedule is a fractional set to be 0 except for an hour a day, in which I have the maximum thermal dispersion from the electical load.
edit: I have set the radiant fraction to 0 and rerun the simulation that unfortunately stops with the following error:
* Severe * Temperature (high) out of bounds (212.96] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [448.029] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
* Severe * Temperature (high) out of bounds (221.06] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-127.12] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-126.17] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (221.80] for zone="THERMAL ZONE 1", for surface="SURFACE 2" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (228.70] for zone="THERMAL ZONE 1", for surface="SURFACE 3" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (226.33] for zone="THERMAL ZONE 1", for surface="SURFACE 4" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (222.05] for zone="THERMAL ZONE 1", for surface="SURFACE 6" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
edit: I followed MatthewSteen suggestions, but the simulation stops and the errors I get are the following:
* Severe * Temperature (high) out of bounds (601.03] for zone="THERMAL ZONE 1", for surface="SURFACE 2" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [89605.735] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
* Severe * Temperature (high) out of bounds (601.50] for zone="THERMAL ZONE 1", for surface="SURFACE 3" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (601.01] for zone="THERMAL ZONE 1", for surface="SURFACE 4" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (601.02] for zone="THERMAL ZONE 1", for surface="SURFACE 6" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (490.39] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (629.08] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
Modeling a building with heavy electrical component gains
I need to model a building (31 x 18 x 4 m) with no windows. The building is made of polyurethanic panels that should assure the insulation during hot months. Inside the building I have a very high electric load (50MW) that can dissipate up to 5% of this power as thermal contribution. Obviously this electrical load is not working at full capacity all the time. How can I simulate this kind of load? I have tryed with both "electric equipment" and "other equipment" loads but the simulation stops with this error:
Temperature (high) out of bounds (209.38] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:30 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [4480.287] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
I assumed that the temeprature rises too much also because I have not well defined the materials, infact I have simulated a hot day (15 august) and the temperature inside the building with NO gains in it rises up to 34 °C. This should not happen since the panels are supposed to insulate the building.
I have tryed to turn on ideal loads to have an idea of the size of the HVAC system that have to be installed there.
For the polyurethane panels I have defined a new material with these specifics:

The load schedule is a fractional set to be 0 except for an hour a day, in which I have the maximum thermal dispersion from the electical load.
edit: I have set the radiant fraction to 0 and rerun the simulation that unfortunately stops with the following error:
* Severe * Temperature (high) out of bounds (212.96] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [448.029] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
* Severe * Temperature (high) out of bounds (221.06] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-127.12] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-126.17] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (221.80] for zone="THERMAL ZONE 1", for surface="SURFACE 2" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (228.70] for zone="THERMAL ZONE 1", for surface="SURFACE 3" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (226.33] for zone="THERMAL ZONE 1", for surface="SURFACE 4" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (222.05] for zone="THERMAL ZONE 1", for surface="SURFACE 6" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
edit: I followed MatthewSteen suggestions, but the simulation stops and the errors I get are the following:
* Severe * Temperature (high) out of bounds (601.03] for zone="THERMAL ZONE 1", for surface="SURFACE 2" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [89605.735] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
* Severe * Temperature (high) out of bounds (601.50] for zone="THERMAL ZONE 1", for surface="SURFACE 3" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (601.01] for zone="THERMAL ZONE 1", for surface="SURFACE 4" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (601.02] for zone="THERMAL ZONE 1", for surface="SURFACE 6" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (490.39] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
* Severe * Temperature (high) out of bounds (629.08] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:21
Modeling a building with heavy electrical component gains
I need to model a building (31 x 18 x 4 m) with no windows. The building is made of polyurethanic panels that should assure the insulation during hot months. Inside the building I have a very high electric load (50MW) that can dissipate up to 5% of this power as thermal contribution. Obviously this electrical load is not working at full capacity all the time. How can I simulate this kind of load? I have tryed with both "electric equipment" and "other equipment" loads but the simulation stops with this error:
Temperature (high) out of bounds (209.38] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:30 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [4480.287] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
I assumed that the temeprature rises too much also because I have not well defined the materials, infact I have simulated a hot day (15 august) and the temperature inside the building with NO gains in it rises up to 34 °C. This should not happen since the panels are supposed to insulate the building.
I have tryed to turn on ideal loads to have an idea of the size of the HVAC system that have to be installed there.
For the polyurethane panels I have defined a new material with these specifics:

The load schedule is a fractional set to be 0 except for an hour a day, in which I have the maximum thermal dispersion from the electical load.
edit: I have set the radiant fraction to 0 and rerun the simulation that unfortunately stops with the following error:
* Severe * Temperature (high) out of bounds (212.96] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [448.029] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.
* Severe * Temperature (high) out of bounds (221.06] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-127.12] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (low) out of bounds [-126.17] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (221.80] for zone="THERMAL ZONE 1", for surface="SURFACE 2" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (228.70] for zone="THERMAL ZONE 1", for surface="SURFACE 3" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (226.33] for zone="THERMAL ZONE 1", for surface="SURFACE 4" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41
* Severe * Temperature (high) out of bounds (222.05] for zone="THERMAL ZONE 1", for surface="SURFACE 6" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41