OpenStudio error FindRootSimpleController

Hi All, I have a project with several 90.1-2007 App G Baseline System 8 - VAV systems with CHW cooling and electric heating. The model is meeting loads and the simulation completes successfully, but I get a severe error for each CHW coil controller that looks like this:

** Severe  ** FindRootSimpleController: Controller error for controller = "CONTROLLER WATER COIL 2"
**   ~~~   **  Environment=DENVER INTL AP ANN CLG .4% CONDNS DP=>MDB, at Simulation time=07/21 20:00 - 20:15
**   ~~~   **   Controller function is inconsistent with user specified controller action = Reverse action
**   ~~~   **   Actuator will be set to maximum action
**   ~~~   ** Controller control type=Temperature
**   ~~~   ** Controller temperature setpoint = 11.39 [C]
**   ~~~   ** Controller sensed temperature = 12.16 [C]
**   ~~~   ** Controller actuator mass flow rate set to 0.60 [kg/s]
**   ~~~   ** Controller actuator temperature = 12.22 [C]
**   ~~~   **   Note: Chilled water coils should be reverse action and the entering chilled
**   ~~~   **         water temperature (controller actuator temperature) should be below the setpoint temperature
**   ~~~   **   Note: Hot water coils should be normal action and the entering hot
**   ~~~   **         water temperature (controller actuator temperature) should be above the setpoint temperature

I have triple checked the model and the coil controllers have the correct action. I have heard that this error may show up because of something else going on with airloops, but I can't find anything amiss. The model seems ok otherwise, though I suspect that heating use might be a bit low (multifamily building), which might be triggering this issue: https://github.com/NREL/EnergyPlus/issues/4187

Should I be concerned? Any resolution? I am using OpenStudio v1.8.0. Thanks in advance!

OpenStudio error FindRootSimpleController

Hi All, I have a project with several 90.1-2007 App G Baseline System 8 - VAV systems with CHW cooling and electric heating. The model is meeting loads and the simulation completes successfully, but I get a severe error for each CHW coil controller that looks like this:

** 

* Severe ** * FindRootSimpleController: Controller error for controller = "CONTROLLER WATER COIL 2" ** ~~~ ** 2"

* ~~~ * Environment=DENVER INTL AP ANN CLG .4% CONDNS DP=>MDB, at Simulation time=07/21 20:00 - 20:15 ** ~~~ ** 20:15

* ~~~ * Controller function is inconsistent with user specified controller action = Reverse action ** ~~~ ** action

* ~~~ * Actuator will be set to maximum action ** ~~~ ** action

* ~~~ * Controller control type=Temperature ** ~~~ ** type=Temperature

* ~~~ * Controller temperature setpoint = 11.39 [C] ** ~~~ ** [C]

* ~~~ * Controller sensed temperature = 12.16 [C] ** ~~~ ** [C]

* ~~~ * Controller actuator mass flow rate set to 0.60 [kg/s] ** ~~~ ** [kg/s]

* ~~~ * Controller actuator temperature = 12.22 [C] ** ~~~ ** [C]

* ~~~ * Note: Chilled water coils should be reverse action and the entering chilled ** ~~~ ** chilled

* ~~~ * water temperature (controller actuator temperature) should be below the setpoint temperature ** ~~~ ** temperature

* ~~~ * Note: Hot water coils should be normal action and the entering hot ** ~~~ ** hot

* ~~~ * water temperature (controller actuator temperature) should be above the setpoint temperature

temperature


I have triple checked the model and the coil controllers have the correct action. I have heard that this error may show up because of something else going on with airloops, but I can't find anything amiss. The model seems ok otherwise, though I suspect that heating use might be a bit low (multifamily building), which might be triggering this issue: https://github.com/NREL/EnergyPlus/issues/4187

Should I be concerned? Any resolution? I am using OpenStudio v1.8.0. Thanks in advance!

OpenStudio error FindRootSimpleController

Hi All, I have a project with several 90.1-2007 App G Baseline System 8 - VAV systems with CHW cooling and electric heating. The model is meeting loads and the simulation completes successfully, but I get a severe error for each CHW coil controller that looks like this:


* Severe * FindRootSimpleController: Controller error for controller = "CONTROLLER WATER COIL 2"

* ~~~ * Environment=DENVER INTL AP ANN CLG .4% CONDNS DP=>MDB, at Simulation time=07/21 20:00 - 20:15

* ~~~ * Controller function is inconsistent with user specified controller action = Reverse action

* ~~~ * Actuator will be set to maximum action

* ~~~ * Controller control type=Temperature

* ~~~ * Controller temperature setpoint = 11.39 [C]

* ~~~ * Controller sensed temperature = 12.16 [C]

* ~~~ * Controller actuator mass flow rate set to 0.60 [kg/s]

* ~~~ * Controller actuator temperature = 12.22 [C]

* ~~~ * Note: Chilled water coils should be reverse action and the entering chilled

* ~~~ * water temperature (controller actuator temperature) should be below the setpoint temperature

* ~~~ * Note: Hot water coils should be normal action and the entering hot

* ~~~ * water temperature (controller actuator temperature) should be above the setpoint temperature


I have triple checked the model and the coil controllers have the correct action. I have heard that this error may show up because of something else going on with airloops, but I can't find anything amiss. The model seems ok otherwise, though I suspect that heating use might be a bit low (multifamily building), which might be triggering this issue: https://github.com/NREL/EnergyPlus/issues/4187

Should I be concerned? Any resolution? I am using OpenStudio v1.8.0. Thanks in advance!