How can I simulate a CoolingCoilDX with a high air flow (rated air volume flow rate)?

I'm simulating a DataCenter equipped with CRACs. These devices have a very high rated air volume flow rate. For the equipment I'm using the ratio is 0.00006822 m³/s per W (0.2456 m³/h per W or 865 m³/h per TR).

The problem is that the equipment Coil:Cooling:DX:SingleSpeed accepts a maximum 0.00006041 m³/s per W and when I put a higher flow relation than this, EnergyPlus reports an error that the flow ratio by load is higher than the maximum acceptable.

** Severe  ** Sizing: Coil:Cooling:DX:SingleSpeed "CRAC - DATA CENTER": Rated air volume flow rate per watt of rated total cooling capacity is out of range.
   **   ~~~   ** Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[6.821E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input Output Reference Manual for valid range.

Is there any other component in EnergyPlus that properly represents a CRAC and supports a greater rated air volume flow rate ratio?

How can I simulate a CoolingCoilDX with a high air flow (rated air volume flow rate)?

I'm simulating a DataCenter equipped with CRACs. These devices have a very high rated air volume flow rate. For the equipment I'm using the ratio is 0.00006822 m³/s per W (0.2456 m³/h per W or 865 m³/h per TR).

The problem is that the equipment Coil:Cooling:DX:SingleSpeed accepts a maximum 0.00006041 m³/s per W and when I put a higher flow relation than this, EnergyPlus reports an error that the flow ratio by load is higher than the maximum acceptable.

** Severe  ** Sizing: Coil:Cooling:DX:SingleSpeed "CRAC - DATA CENTER": Rated air volume flow rate per watt of rated total cooling capacity is out of range.
   **   ~~~   ** Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[6.821E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input Output Reference Manual for valid range.

Is there any other component in EnergyPlus that properly represents a CRAC and supports a greater rated air volume flow rate ratio?

How can I simulate a CoolingCoilDX with a high air flow (rated air volume flow rate)?

I'm simulating a DataCenter equipped with CRACs. These devices have a very high rated air volume flow rate. For the equipment I'm using the ratio is 0.00006822 m³/s per W (0.2456 m³/h per W or 865 m³/h per TR).

The problem is that the equipment Coil:Cooling:DX:SingleSpeed accepts a maximum 0.00006041 m³/s per W and when I put a higher flow relation than this, EnergyPlus reports an error that the flow ratio by load is higher than the maximum acceptable.

** Severe  ** Sizing: Coil:Cooling:DX:SingleSpeed "CRAC - DATA CENTER": Rated air volume flow rate per watt of rated total cooling capacity is out of range.
   **   ~~~   ** Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[6.821E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input Output Reference Manual for valid range.

Is there any other component in EnergyPlus that properly represents a CRAC and supports a greater rated air volume flow rate ratio?

How can I simulate a CoolingCoilDX with a high air flow (rated air volume flow rate)?

I'm simulating a DataCenter equipped with CRACs. These devices have a very high rated air volume flow rate. For the equipment I'm using the ratio is 0.00006822 m³/s per W (0.2456 m³/h per W or 865 m³/h per TR).

The problem is that the equipment Coil:Cooling:DX:SingleSpeed Coil equipment: Cooling: DX: Single: Speed accepts a maximum 0.00006041 m³/s per W and when I put a higher flow relation than to this, the error of EnergyPlus reports an error reporting me that the flow ratio by load is higher than the maximum acceptable.

** 

* Severe ** * Sizing: Coil:Cooling:DX:SingleSpeed "CRAC - DATA CENTER": Rated air volume flow rate per watt of rated total cooling capacity is out of range. ** * ~~~ ** * Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[6.821E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input Output Reference Manual for valid range.

range.



Is there any other component in the EnergyPlus that properly represents a CRAC and supports a greater rated air volume flow rate ratio?ratio.